  #1   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2
Default Rheem Classic 90 Plus furnace

I have a Rheem Classic 90 Plus furnace. Lately it has been shutting
down, normally at night and sometimes just switching the power off
then back on is enough to get it going. At other times turning the
power off and on will do nothing and then the furnace will start
working again on its own several hours later. We had a technician in
and he checked the furnace over and said because it was intermittent
he couldn't do much, cost $60.00 When the problem next appeared it was
a little different in that the burners would fire up for a couple of
seconds then shut down, then fire up and shut down, then the flame
light would flash on the control board. I cleaned the Remote Sensor
and the spark ignition and sensor and it seemed to work for about 4
days before it shut down again. Now it just tries to cycle on (no
Burn) and then shuts down, keeps trying to cycle on and at some point
is successful as the furnace eventually starts and runs. The other
evening it shut down and it was about 40 degrees when I got up, trying
to recycle the power did nothing. We called a technician right away,
but he showed up 5 hours later and by then the furnace had restarted.
He checked the inlet and outlet pressures which were OK and he said
the air inlet pipe was slanted downward going outside. He corrected
this so now it is slanted up going outside. That cost me $110.00 and
the following morning the furnace had once again shut down. Recycling
the power switch got it going again. The inlet pipe is 4" PVC which
has one 90 degree elbow and then reduces to 2 1/2" PVC going outside,
total length is about 6 feet. The outside inlet pipe is horizontal
with no 45 or 90 degree elbow. There is a moisture hose on the 4" PVC
inlet and there is water in the trap. Could wind or snow blowing into
this pipe cause the above problems? Any other suggestions, it is cold
up here and local technical help is limited where we live?

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,586
Default Rheem Classic 90 Plus furnace

wrote:
I have a Rheem Classic 90 Plus furnace. Lately it has been shutting
down, normally at night and sometimes just switching the power off
then back on is enough to get it going. At other times turning the
power off and on will do nothing and then the furnace will start
working again on its own several hours later. We had a technician in
and he checked the furnace over and said because it was intermittent
he couldn't do much, cost $60.00 When the problem next appeared it was
a little different in that the burners would fire up for a couple of
seconds then shut down, then fire up and shut down, then the flame
light would flash on the control board. I cleaned the Remote Sensor
and the spark ignition and sensor and it seemed to work for about 4
days before it shut down again. Now it just tries to cycle on (no
Burn) and then shuts down, keeps trying to cycle on and at some point
is successful as the furnace eventually starts and runs. The other
evening it shut down and it was about 40 degrees when I got up, trying
to recycle the power did nothing. We called a technician right away,
but he showed up 5 hours later and by then the furnace had restarted.
He checked the inlet and outlet pressures which were OK and he said
the air inlet pipe was slanted downward going outside. He corrected
this so now it is slanted up going outside. That cost me $110.00 and
the following morning the furnace had once again shut down. Recycling
the power switch got it going again. The inlet pipe is 4" PVC which
has one 90 degree elbow and then reduces to 2 1/2" PVC going outside,
total length is about 6 feet. The outside inlet pipe is horizontal
with no 45 or 90 degree elbow. There is a moisture hose on the 4" PVC
inlet and there is water in the trap. Could wind or snow blowing into
this pipe cause the above problems? Any other suggestions, it is cold
up here and local technical help is limited where we live?

Hi,
Most furnace retries 3 times before it goes into lock up mode. You can
initialize logic board by powering on/off or it will reset itself to
normal mode after 3 hours or so and try again. With my little bit of
experience, it is usually inducer pressure switch or flame sensor
causing that kind of symptom. Does your logic board give out trouble
code by way of blinking LED? Once I had a problem on logic board. High
Wattage resistor caused a cracked solder joint making the furnace
intermittent. It is a simple sequential logic, to trouble-shoot logical
sequence you need logical mind, LOL! If it reaches a ignition
stage(flame on), next sequence is sensing the flame by sensor and then
after some delay fan comes on. Trying new flame sensor may not be a bad
idea. Also check loose wires/connectors I always keep spare ignitor and
flame sensor.
Good luck,


  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2
Default Rheem Classic 90 Plus furnace


Tony Hwang wrote:
wrote:
I have a Rheem Classic 90 Plus furnace. Lately it has been shutting
down, normally at night and sometimes just switching the power off
then back on is enough to get it going. At other times turning the
power off and on will do nothing and then the furnace will start
working again on its own several hours later. We had a technician in
and he checked the furnace over and said because it was intermittent
he couldn't do much, cost $60.00 When the problem next appeared it was
a little different in that the burners would fire up for a couple of
seconds then shut down, then fire up and shut down, then the flame
light would flash on the control board. I cleaned the Remote Sensor
and the spark ignition and sensor and it seemed to work for about 4
days before it shut down again. Now it just tries to cycle on (no
Burn) and then shuts down, keeps trying to cycle on and at some point
is successful as the furnace eventually starts and runs. The other
evening it shut down and it was about 40 degrees when I got up, trying
to recycle the power did nothing. We called a technician right away,
but he showed up 5 hours later and by then the furnace had restarted.
He checked the inlet and outlet pressures which were OK and he said
the air inlet pipe was slanted downward going outside. He corrected
this so now it is slanted up going outside. That cost me $110.00 and
the following morning the furnace had once again shut down. Recycling
the power switch got it going again. The inlet pipe is 4" PVC which
has one 90 degree elbow and then reduces to 2 1/2" PVC going outside,
total length is about 6 feet. The outside inlet pipe is horizontal
with no 45 or 90 degree elbow. There is a moisture hose on the 4" PVC
inlet and there is water in the trap. Could wind or snow blowing into
this pipe cause the above problems? Any other suggestions, it is cold
up here and local technical help is limited where we live?

Hi,
Most furnace retries 3 times before it goes into lock up mode. You can
initialize logic board by powering on/off or it will reset itself to
normal mode after 3 hours or so and try again. With my little bit of
experience, it is usually inducer pressure switch or flame sensor
causing that kind of symptom. Does your logic board give out trouble
code by way of blinking LED? Once I had a problem on logic board. High
Wattage resistor caused a cracked solder joint making the furnace
intermittent. It is a simple sequential logic, to trouble-shoot logical
sequence you need logical mind, LOL! If it reaches a ignition
stage(flame on), next sequence is sensing the flame by sensor and then
after some delay fan comes on. Trying new flame sensor may not be a bad
idea. Also check loose wires/connectors I always keep spare ignitor and
flame sensor.
Good luck,

If it was a consistent problem it would be easier to fix. The first
time it went off for a long time, well over 3 hours and would not come
back on by recycling the power. The next time it would reach ignition
stage for a few seconds and then shut off then reach ignition again,
then shut off and show a blinking Flame LED. This was when I cleaned
the Flame sensor and the Ignitor and Sensor combination. This worked
for a few days. Now, at least this morning, it would not get to the
ignition phase until I reset the power. The furnace has worked well
since this morning, but I am worried about tomorow morning. I
understand the logical sequence, but this is not logical, it is random
and that much harder to diagnose. This furnace is about 6 years old
and all the wires/connectors seem fine and there is no noticeable
cracking anywhere on the logic board. The technican supposedly checked
the pressure switch and said it was working to specs. Any other
suggestions?

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,586
Default Rheem Classic 90 Plus furnace

wrote:

Tony Hwang wrote:

wrote:

I have a Rheem Classic 90 Plus furnace. Lately it has been shutting
down, normally at night and sometimes just switching the power off
then back on is enough to get it going. At other times turning the
power off and on will do nothing and then the furnace will start
working again on its own several hours later. We had a technician in
and he checked the furnace over and said because it was intermittent
he couldn't do much, cost $60.00 When the problem next appeared it was
a little different in that the burners would fire up for a couple of
seconds then shut down, then fire up and shut down, then the flame
light would flash on the control board. I cleaned the Remote Sensor
and the spark ignition and sensor and it seemed to work for about 4
days before it shut down again. Now it just tries to cycle on (no
Burn) and then shuts down, keeps trying to cycle on and at some point
is successful as the furnace eventually starts and runs. The other
evening it shut down and it was about 40 degrees when I got up, trying
to recycle the power did nothing. We called a technician right away,
but he showed up 5 hours later and by then the furnace had restarted.
He checked the inlet and outlet pressures which were OK and he said
the air inlet pipe was slanted downward going outside. He corrected
this so now it is slanted up going outside. That cost me $110.00 and
the following morning the furnace had once again shut down. Recycling
the power switch got it going again. The inlet pipe is 4" PVC which
has one 90 degree elbow and then reduces to 2 1/2" PVC going outside,
total length is about 6 feet. The outside inlet pipe is horizontal
with no 45 or 90 degree elbow. There is a moisture hose on the 4" PVC
inlet and there is water in the trap. Could wind or snow blowing into
this pipe cause the above problems? Any other suggestions, it is cold
up here and local technical help is limited where we live?


Hi,
Most furnace retries 3 times before it goes into lock up mode. You can
initialize logic board by powering on/off or it will reset itself to
normal mode after 3 hours or so and try again. With my little bit of
experience, it is usually inducer pressure switch or flame sensor
causing that kind of symptom. Does your logic board give out trouble
code by way of blinking LED? Once I had a problem on logic board. High
Wattage resistor caused a cracked solder joint making the furnace
intermittent. It is a simple sequential logic, to trouble-shoot logical
sequence you need logical mind, LOL! If it reaches a ignition
stage(flame on), next sequence is sensing the flame by sensor and then
after some delay fan comes on. Trying new flame sensor may not be a bad
idea. Also check loose wires/connectors I always keep spare ignitor and
flame sensor.
Good luck,


If it was a consistent problem it would be easier to fix. The first
time it went off for a long time, well over 3 hours and would not come
back on by recycling the power. The next time it would reach ignition
stage for a few seconds and then shut off then reach ignition again,
then shut off and show a blinking Flame LED. This was when I cleaned
the Flame sensor and the Ignitor and Sensor combination. This worked
for a few days. Now, at least this morning, it would not get to the
ignition phase until I reset the power. The furnace has worked well
since this morning, but I am worried about tomorow morning. I
understand the logical sequence, but this is not logical, it is random
and that much harder to diagnose. This furnace is about 6 years old
and all the wires/connectors seem fine and there is no noticeable
cracking anywhere on the logic board. The technican supposedly checked
the pressure switch and said it was working to specs. Any other
suggestions?

Hi,
If logic board has cracked or cold soder joints by vibration of heat
from big resistor, it's underside of the board.(opposite of component
side)
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Rheem Furnace stuck in on off cycle [email protected] Home Repair 5 November 29th 05 12:02 AM
Goodman or Rheem gas furnace? Vintage Pinballs & Jukeboxes Home Repair 3 October 8th 05 01:40 AM
blower motor on rheem rged furnace patliz1 Home Repair 7 January 13th 05 07:53 PM
blower motor on rheem rged furnace [email protected] Home Ownership 0 January 11th 05 11:50 PM
Rheem 80 plus furnace blowing cold air Kam Home Repair 2 April 23rd 04 05:20 AM


All times are GMT +1. The time now is 03:26 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"