Default Need help on how to wire 240 volt machines

Hello

I need some on understanding some basics on how to wire a 240 volt 40
amp Hypertherm Powermax 600 plasma cutter and a 240 volt 20 amp air
compressor to be exact.

First, let me describe my power supply situation.

I had an electrician recently upgrade my main panel and service from
100 amp fuse to 200 amp breakers.

My intention is to get a 100 amp sub panel in the attached garage on
the opposite side of the house.

From the main panel I ran 2-2-2-4 AL wire out the basement level, up

the out side of the house, back inside through the attic and across
the length of the house where it drops down into the attached garage
to feed a 100 amp sub panel. Total length of the wire is 80 feet.

The 2224 wire meets a 125 amp main lug sub panel in my garage. As i
was told, my ground and neutral are isolated. I installed the
supplied Ground bar, as the instruction book said if i was using it as
a main lug. Everything in the sub panel is how it should be.

My question comes in here... My plasma cutter has a NEMA 6-50 plug pre-
installed. It looks like a standard 120 plug, only bigger. Thats 3
prongs.

So i went to Home Depot and purchased a NEMA 6-50 outlet. What
confuses me, is that its only 3 prongs. I assume its supposed to be
the two hots are the narrow prongs, and the round one is supposed to
be the neutral? So how is it grounded?

I realize way back at the main panel the ground and neutrals are
connected.

So why did i bother to run 4 wires of 8 gauge (black, red, white,
bare) if i'm only using 3 of them. What do i do with the bare wire?
Will my machine be grounded?

I realize this will appear trivial to most electric guys on here, but
i just don't get it. I've looked quite a bit on the internet and
havn't found a clear answer. I paid too much money for the plasma
machine, and i don't really want to die, so i figured i would ask.

Thanks folks,
Tim

  #2   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Need help on how to wire 240 volt machines


wrote in message
oups.com...
Hello

I need some on understanding some basics on how to wire a 240 volt 40
amp Hypertherm Powermax 600 plasma cutter and a 240 volt 20 amp air
compressor to be exact.

First, let me describe my power supply situation.

I had an electrician recently upgrade my main panel and service from
100 amp fuse to 200 amp breakers.

My intention is to get a 100 amp sub panel in the attached garage on
the opposite side of the house.

From the main panel I ran 2-2-2-4 AL wire out the basement level, up

the out side of the house, back inside through the attic and across
the length of the house where it drops down into the attached garage
to feed a 100 amp sub panel. Total length of the wire is 80 feet.

The 2224 wire meets a 125 amp main lug sub panel in my garage. As i
was told, my ground and neutral are isolated. I installed the
supplied Ground bar, as the instruction book said if i was using it as
a main lug. Everything in the sub panel is how it should be.

My question comes in here... My plasma cutter has a NEMA 6-50 plug pre-
installed. It looks like a standard 120 plug, only bigger. Thats 3
prongs.

So i went to Home Depot and purchased a NEMA 6-50 outlet. What
confuses me, is that its only 3 prongs. I assume its supposed to be
the two hots are the narrow prongs, and the round one is supposed to
be the neutral? So how is it grounded?


Some equipment doesn't require a neutral, like this, it only requires a
ground




I realize way back at the main panel the ground and neutrals are
connected.

So why did i bother to run 4 wires of 8 gauge (black, red, white,
bare) if i'm only using 3 of them. What do i do with the bare wire?
Will my machine be grounded?


You only needed to run three wires to this particular machine


I realize this will appear trivial to most electric guys on here, but
i just don't get it. I've looked quite a bit on the internet and
havn't found a clear answer. I paid too much money for the plasma
machine, and i don't really want to die, so i figured i would ask.

Thanks folks,
Tim



  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default Need help on how to wire 240 volt machines

In article .com, wrote:

I need some on understanding some basics on how to wire a 240 volt 40
amp Hypertherm Powermax 600 plasma cutter and a 240 volt 20 amp air
compressor to be exact.


The first thing you need to understand is that a pure 240V circuit, in the
United States and Canada, _does_not_have_a_neutral_ .
[snip]

My question comes in here... My plasma cutter has a NEMA 6-50 plug pre-
installed. It looks like a standard 120 plug, only bigger. Thats 3
prongs.

So i went to Home Depot and purchased a NEMA 6-50 outlet. What
confuses me, is that its only 3 prongs. I assume its supposed to be
the two hots are the narrow prongs, and the round one is supposed to
be the neutral? So how is it grounded?


Incorrect assumption. The two flat prongs are indeed the two hots. The round
one is GROUND. There is no neutral, and you do not need one.

I realize way back at the main panel the ground and neutrals are
connected.

So why did i bother to run 4 wires of 8 gauge (black, red, white,
bare) if i'm only using 3 of them.


Because you misunderstand how 240V circuits work. Three conductors --
black, red, and *bare* (or green) -- would have been enough.

What do i do with the bare wire?


Connect it to the grounding terminal on the receptacle, of course, and to the
grounding busbar in the subpanel.

You're asking the wrong question, though. The right question is, what do I do
with the *white* wire? The answer is: Put a wire nut over each end of it. You
don't need it. Or, if this is run through conduit, pull the white wire out.
You don't need it.

Will my machine be grounded?


It will be, if you wire the receptacle correctly.

I realize this will appear trivial to most electric guys on here, but
i just don't get it. I've looked quite a bit on the internet and
havn't found a clear answer. I paid too much money for the plasma
machine, and i don't really want to die, so i figured i would ask.


Good for you! Far better to ask, than to assume and do it wrong. The bottom
line is, neither your plasma cutter nor your compressor requires a *neutral*.
They both require a *ground*. So in the receptacles for both of them, you
connect the ground. There is no place to connect the neutral, so you don't
need to run four wires to the receps -- three will do.

At this point, you're probably wondering why you bothered running four wires
to the subpanel, if all you're going to need is three. The answer is, so that
you can run 120V circuits off that subpanel, too -- they need the neutral,
even though the 240V circuits don't. Maybe you don't ever plan on putting any
120V circuits in that panel... but the next guy to own your home might.


--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default Need help on how to wire 240 volt machines


Good for you! Far better to ask, than to assume and do it wrong. The bottom
line is, neither your plasma cutter nor your compressor requires a *neutral*.
They both require a *ground*. So in the receptacles for both of them, you
connect the ground. There is no place to connect the neutral, so you don't
need to run four wires to the receps -- three will do.

At this point, you're probably wondering why you bothered running four wires
to the subpanel, if all you're going to need is three. The answer is, so that
you can run 120V circuits off that subpanel, too -- they need the neutral,
even though the 240V circuits don't. Maybe you don't ever plan on putting any
120V circuits in that panel... but the next guy to own your home might.


Excellent. Thanks very much for your response. You really made it
clear for me.

And i do plan to run several 120 circuits of the panel too.

Again, thanks a lot.
Tim


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default Need help on how to wire 240 volt machines


At this point, you're probably wondering why you bothered running four wires
to the subpanel, if all you're going to need is three. The answer is, so that
you can run 120V circuits off that subpanel, too -- they need the neutral,
even though the 240V circuits don't. Maybe you don't ever plan on putting any
120V circuits in that panel... but the next guy to own your home might.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.


Yeah, i am. I understand the 120 volt thing. I think. So why does
240 volt not require a neutral? I thought everything
electric was based on supply (hot) and return (neutral). Ground was
only for when the **** hit the fan, and the power had to decide
between your body or the easier path to earth which was the green
wire.

Why is 240 different than 120 in that sense?

And why is it said that one should run 4 wire if its a 240 appliance?



  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default Need help on how to wire 240 volt machines


You're correct that everything needs a complete path. With 240V in
North America, you can think of it as one hot being at 120V and the
other at -120V. The difference between them is 240V.

If you only need pure 240V, then you don't really need the neutral--you
just use the two hots and ground. Current flows in one hot and out the
other, and the ground is for when things go wrong.

And why is it said that one should run 4 wire if its a 240 appliance?


Many 240V appliances in North America use 120V control circuits. This
requires a neutral conductor. The main load of the appliance uses the
two hots, and the ground is still for when things go wrong.



I had no idea. Honestly, what i've learned in this post gave some
bills to my electrician. Don't want to touch it.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
LED's on 240 volt ac Trevor Smith UK diy 23 November 15th 06 10:49 PM
Moving a 240 volt line [email protected] Home Repair 13 June 28th 06 06:36 PM
240 volt service James P. Javery Home Repair 6 November 24th 04 01:17 AM
240 volt wiring Charles Home Repair 11 December 30th 03 11:13 PM
Can you derive a 110 volt outlet from a 4 wire 220 volt in the US? Steven Kingsley Home Repair 30 August 1st 03 06:34 AM


All times are GMT +1. The time now is 12:44 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"