How can I find out if my Generator (factory original) has neutral
ground bonding. I am using it with a transfer switch that only switches
the hot and not the neutral. It need therefore to be unbonded. The unit
does have a gren wire that has a secrew connecting the generator and
the fram where it says grouns. Is this a means to change the bonding?
Any input is apprechiated

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 74
Default bonding on Genreac 5500EXL portable generator

Glia wrote:
How can I find out if my Generator (factory original) has neutral
ground bonding. I am using it with a transfer switch that only switches
the hot and not the neutral. It need therefore to be unbonded. The unit
does have a gren wire that has a secrew connecting the generator and
the fram where it says grouns. Is this a means to change the bonding?
Any input is apprechiated


You check between the housing of the generator's winding and the neutral
terminal of the receptacles with any type of resistance measurement
device or a continuity checker. If you get continuity or any resistance
other than infinity it is bonded. If not then your good to go.

It isn't as big a deal as some people make out as long as your talking
about a portable generator that is disconnected when not in use. The
biggest possible danger arises from the presence of a connection between
the neutral and the Equipment Grounding Conductor on the load side of
the service disconnecting means. If your transfer switch carries the
whole houses load then that is a non issue because both connections are
on the load side of the service disconnecting means.
--
Tom Horne

Well we aren't no thin blue heroes and yet we aren't no blackguards to.
We're just working men and woman most remarkable like you.
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 7
Default bonding on Genreac 5500EXL portable generator

I finally got an answer from Generac in case someone else has the same
problem.
The generators do have ground neutral bond that must be removed when
connected to a transfer panel.
This bond can be removed by removing a jumper wire between neutral and
ground found on the two outlet receptacle. Panel is easy to remove, as
is this wire.


Thomas D. Horne, FF EMT wrote:
Glia wrote:
How can I find out if my Generator (factory original) has neutral
ground bonding. I am using it with a transfer switch that only switches
the hot and not the neutral. It need therefore to be unbonded. The unit
does have a gren wire that has a secrew connecting the generator and
the fram where it says grouns. Is this a means to change the bonding?
Any input is apprechiated


You check between the housing of the generator's winding and the neutral
terminal of the receptacles with any type of resistance measurement
device or a continuity checker. If you get continuity or any resistance
other than infinity it is bonded. If not then your good to go.

It isn't as big a deal as some people make out as long as your talking
about a portable generator that is disconnected when not in use. The
biggest possible danger arises from the presence of a connection between
the neutral and the Equipment Grounding Conductor on the load side of
the service disconnecting means. If your transfer switch carries the
whole houses load then that is a non issue because both connections are
on the load side of the service disconnecting means.
--
Tom Horne

Well we aren't no thin blue heroes and yet we aren't no blackguards to.
We're just working men and woman most remarkable like you.


  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 818
Default bonding on Genreac 5500EXL portable generator

Thanks! So kind of you to share this information.

--

Christopher A. Young
You can't shout down a troll.
You have to starve them.
..

"Glia" wrote in message
ups.com...
I finally got an answer from Generac in case someone else has

the same
problem.
The generators do have ground neutral bond that must be removed

when
connected to a transfer panel.
This bond can be removed by removing a jumper wire between

neutral and
ground found on the two outlet receptacle. Panel is easy to

remove, as
is this wire.


Thomas D. Horne, FF EMT wrote:
Glia wrote:
How can I find out if my Generator (factory original) has

neutral
ground bonding. I am using it with a transfer switch that

only switches
the hot and not the neutral. It need therefore to be

unbonded. The unit
does have a gren wire that has a secrew connecting the

generator and
the fram where it says grouns. Is this a means to change

the bonding?
Any input is apprechiated


You check between the housing of the generator's winding and

the neutral
terminal of the receptacles with any type of resistance

measurement
device or a continuity checker. If you get continuity or any

resistance
other than infinity it is bonded. If not then your good to

go.

It isn't as big a deal as some people make out as long as

your talking
about a portable generator that is disconnected when not in

use. The
biggest possible danger arises from the presence of a

connection between
the neutral and the Equipment Grounding Conductor on the load

side of
the service disconnecting means. If your transfer switch

carries the
whole houses load then that is a non issue because both

connections are
on the load side of the service disconnecting means.
--
Tom Horne

Well we aren't no thin blue heroes and yet we aren't no

blackguards to.
We're just working men and woman most remarkable like you.




  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 118
Default bonding on Genreac 5500EXL portable generator

Glia wrote:
How can I find out if my Generator (factory original) has neutral
ground bonding. I am using it with a transfer switch that only switches
the hot and not the neutral. It need therefore to be unbonded. The unit
does have a gren wire that has a secrew connecting the generator and
the fram where it says grouns. Is this a means to change the bonding?
Any input is apprechiated

Thomas D. Horne, FF EMT wrote:
You check between the housing of the generator's winding and the neutral
terminal of the receptacles with any type of resistance measurement
device or a continuity checker. If you get continuity or any resistance
other than infinity it is bonded. If not then your good to go.

It isn't as big a deal as some people make out as long as your talking
about a portable generator that is disconnected when not in use. The
biggest possible danger arises from the presence of a connection between
the neutral and the Equipment Grounding Conductor on the load side of
the service disconnecting means. If your transfer switch carries the
whole houses load then that is a non issue because both connections are
on the load side of the service disconnecting means.
--
Tom Horne

Well we aren't no thin blue heroes and yet we aren't no blackguards to.
We're just working men and woman most remarkable like you.


Glia wrote:
I finally got an answer from Generac in case someone else has the same
problem.
The generators do have ground neutral bond that must be removed when
connected to a transfer panel.
This bond can be removed by removing a jumper wire between neutral and
ground found on the two outlet receptacle. Panel is easy to remove, as
is this wire.



Glia
If you use that generator set as a portable unit away from the house
that bond must be intact for the safety of people using the things that
generator will be powering. If the generator will not be connected to
the transfer switch when your using utility power then you don't have to
worry about the bonding.
--
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous
for general use." Thomas Alva Edison


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default bonding on Genreac 5500EXL portable generator


Here is a web page that covers this subject and Generac well.
You may want to have a look here; has some good info and pics on
Generac.

http://members.rennlist.org/warren/gt5000c.html

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Question on portable generator usage David Billington Metalworking 9 March 27th 06 04:50 PM
portable generator question Paul Oman Home Repair 8 September 22nd 05 04:05 AM
Running AC On Portable Generator IC_Clearly Home Repair 25 September 13th 05 12:29 AM
Portable Generator once more.. Chuck Home Repair 48 July 4th 05 04:52 PM
FA: Generac 5500EXL Generator with wheel kit - Pelham NH Spencer Metalworking 2 April 25th 05 04:24 AM


All times are GMT +1. The time now is 07:15 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"