I installed 4 recessed lights in an unfinished (now finished) room of my
house...the leg was installed to that room by the electricians during
original construction. I just replaced the single light with 4 new recessed
lights. Now when I turn on those 4 lights the other lights on the circuit
give a quick one-time flicker. This is a room off the master bedroom and is
on the master bedroom's arc-fault circuit breaker.

Best way to track this down? Loose wire in one of the new lights? Weak
breaker?

Thanks for the suggestions.


  #2   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 1,029
Default Electrical Question - Light Flicker


tsltrek wrote:
I installed 4 recessed lights in an unfinished (now finished) room of my
house...the leg was installed to that room by the electricians during
original construction. I just replaced the single light with 4 new recessed
lights. Now when I turn on those 4 lights the other lights on the circuit
give a quick one-time flicker. This is a room off the master bedroom and is
on the master bedroom's arc-fault circuit breaker.

Best way to track this down? Loose wire in one of the new lights? Weak
breaker?


Size of breaker/wiring on this circuit?

Sounds like probably was/is a 15A/14ga lighting circuit and you've now
added too much wattage w/ the new fixtures and are seeing the temporary
voltage drop when the added load comes on.

How much _total_ wattage is now on this circuit when you observe this?
And, how much did you add?

As a quick/easy test, take all the bulbs but one out of the new
fixtures and make it a small one -- say 60W. Now, does the flicker go
away? If so, put the original back in and do the same test
sequentially. I'll hazard a guess after one or two, you'll see the
symptoms reappear.

  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default Electrical Question - Light Flicker

possible, but I don't think so.
15amp/14g...had about 600w on then flipped on the new 260 w of
lights...hardly an overload.

i will do the removal of the new bulbs test though just to cover the bases.

"dpb" wrote in message
ps.com...

tsltrek wrote:
I installed 4 recessed lights in an unfinished (now finished) room of my
house...the leg was installed to that room by the electricians during
original construction. I just replaced the single light with 4 new
recessed
lights. Now when I turn on those 4 lights the other lights on the
circuit
give a quick one-time flicker. This is a room off the master bedroom and
is
on the master bedroom's arc-fault circuit breaker.

Best way to track this down? Loose wire in one of the new lights? Weak
breaker?


Size of breaker/wiring on this circuit?

Sounds like probably was/is a 15A/14ga lighting circuit and you've now
added too much wattage w/ the new fixtures and are seeing the temporary
voltage drop when the added load comes on.

How much _total_ wattage is now on this circuit when you observe this?
And, how much did you add?

As a quick/easy test, take all the bulbs but one out of the new
fixtures and make it a small one -- say 60W. Now, does the flicker go
away? If so, put the original back in and do the same test
sequentially. I'll hazard a guess after one or two, you'll see the
symptoms reappear.



  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 222
Default Electrical Question - Light Flicker


Switch for older set of lights.....contacts dirty possibly? Good luck.

  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 222
Default Electrical Question - Light Flicker


Switch for older set of lights.....contacts dirty possibly? Good luck.



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,196
Default Electrical Question - Light Flicker

tsltrek wrote:
I installed 4 recessed lights in an unfinished (now finished) room of my
house...the leg was installed to that room by the electricians during
original construction. I just replaced the single light with 4 new recessed
lights. Now when I turn on those 4 lights the other lights on the circuit
give a quick one-time flicker. This is a room off the master bedroom and is
on the master bedroom's arc-fault circuit breaker.

Best way to track this down? Loose wire in one of the new lights? Weak
breaker?

Thanks for the suggestions.

I'll add my guess. The new 4 lights are
probably 150 watt floods or something
like that. They have a very low startup
resistance, therefore a high inrush. Now,
if the circuit is fairly far from the
breaker box, you will get a momentary
voltage
drop until the filaments get fully hot.
The further you are from the breaker, the
higher the resistance, the bigger the
voltage drop. This is especially seen
on circuit
with aluminum wiring because of higher
per foot resistance. I see this all the
time in my 2nd floor bedroom/bath. The
4 halogen lamps in the bathroom, when
turned on, will cause a momentary
voltage dip for the other bathroom. BTW,
this circuit is aluminum and is about 50
- 70 cable feet from the breaker box.
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 590
Default Electrical Question - Light Flicker


"Art Todesco" wrote in message
. net...
tsltrek wrote:
I installed 4 recessed lights in an unfinished (now finished) room of my
house...the leg was installed to that room by the electricians during
original construction. I just replaced the single light with 4 new
recessed lights. Now when I turn on those 4 lights the other lights on
the circuit give a quick one-time flicker. This is a room off the master
bedroom and is on the master bedroom's arc-fault circuit breaker.

Best way to track this down? Loose wire in one of the new lights? Weak
breaker?

Thanks for the suggestions.

I'll add my guess. The new 4 lights are probably 150 watt floods or
something
like that. They have a very low startup resistance, therefore a high
inrush. Now,
if the circuit is fairly far from the breaker box, you will get a
momentary voltage
drop until the filaments get fully hot. The further you are from the
breaker, the
higher the resistance, the bigger the voltage drop. This is especially
seen on circuit
with aluminum wiring because of higher per foot resistance. I see this
all the
time in my 2nd floor bedroom/bath. The 4 halogen lamps in the bathroom,
when
turned on, will cause a momentary voltage dip for the other bathroom.
BTW,
this circuit is aluminum and is about 50 - 70 cable feet from the breaker
box.


Good post Art ... I'd guess you are correct (even with copper).


  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 557
Default Electrical Question - Light Flicker

On Thu, 4 Jan 2007 10:12:15 -0500, "tsltrek"
wrote:

I installed 4 recessed lights in an unfinished (now finished) room of my
house...the leg was installed to that room by the electricians during
original construction. I just replaced the single light with 4 new recessed
lights. Now when I turn on those 4 lights the other lights on the circuit
give a quick one-time flicker. This is a room off the master bedroom and is
on the master bedroom's arc-fault circuit breaker.

Best way to track this down? Loose wire in one of the new lights? Weak
breaker?

Thanks for the suggestions.



Are these regular lights or fluorescent lights?

tom @ www.Consolidated-Loans.info

  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,431
Default Electrical Question - Light Flicker

In article om,
avid_hiker wrote:

Switch for older set of lights.....contacts dirty possibly? Good luck.


I don't see how dirty switch contacts would make the other lights do
that bit of flicker.

It sounds to me like voltage drop in the wiring from the surge of
current drawn by the freshly-turned-on lights while their filaments are
warming up.

Meanwhile, I would suggest to the OP to check total wattage of lights on
that circuit and the wire size and breaker size. If the wire is AWG 14,
maximum allowed breaker size is 15 amps which means 1800 watts.
The code only allows "continuous loads" up to 80% of the breaker rating,
and it appears to me that lighting qualifies as a "continuous load".

I also somewhat remember that wire size is supposed to be adequate to
have voltage drop less than 5% at full current. For 14 AWG at 15 amps,
that is roughly 75 feet from breaker to load. For 12 AWG at 20 amps, that
is about 90 feet. 12 AWG with a 15 amp breaker is good for about 120
feet, and I would mark the breaker box so that nobody in the future
replaces the 15 amp breaker with a 20 amp one on the basis of wire size.

Another note - I remember reading somewhere recently that a branch
circuit must have all permanently installed wiring identical in maximum
allowable overcurrent protection. I do not know for sure this is NEC;
it might be a local building code for all I know. I guess the reasoning
is to prevent someone from putting in a breaker that is too big for all of
the wiring on the basis of seeing only some of it.

Meanwhile, since incandescents briefly draw up to 10-15 times their
normal current during a cold start, some significant voltage drops in
wiring resulting from this can be perfectly normal. Keep in mind that
light output of an incandescent is roughly proportional to the cube of
applied voltage (normally varies a little more drastically than that
even)! A 5% voltage drop causes incandescents to dim by 15-17%.

If 300 watts of incandescents have simultaneous cold starts, that can
mean a brief load of 4000 watts or 33 amps, possibly a little more. This
is allowed. If this surge flows through just 35 feet (breaker to load) of
14 AWG wire, that can cause a brief voltage drop to already-on lights
downstream of this hypothetical 35 foot wire run of 5% and briefly dim
them possibly by 15-17%.
A fix is not required if a voltage drop of more than 5% occurs only
while filaments are warming up. Brief overcurrents are allowable - there
are even fuses and breakers specifically designed to not blow/trip from
more serious allowable brief overcurrents - moderate and moderately severe
overcurrent will not overheat wiring in a split second.

One more solution, should you determine that a fix is needed - put a
junction box only a few feet from the breaker box and split the new
lighting wire run from the existing one at that point. Keep in mind to
have all wiring on that circuit identical in maximum allowable overcurrent
protection and to have all lights not exceed 80% of the allowable
overcurrent protection - otherwise upgrade all wiring in the circuit or
add another circuit.

More questions or if you have doubts that you can competently do any
such needed work yourself - that's what professional licensed electricians
are for.

- Don Klipstein )
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical question about splicing into one hot wire for a light from a set of hots for 220 circuit Home Repair 0 July 19th 06 02:35 AM
Darky Sky lighting question (output, buzz, flicker) Chuck Home Repair 3 July 18th 06 11:21 PM
Electrical question about splicing into one hot wire for a light from a set of hots for 220 circuit Home Repair 10 July 16th 06 03:03 AM
An electrical grease for a light bulb? Teh Suck Home Repair 28 February 26th 06 02:35 AM
Light not working -Electrical Higglity Home Ownership 4 June 9th 05 08:26 PM


All times are GMT +1. The time now is 09:04 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"