Church solar heating improvements
When the Pottstown PA UU church was built, one part of the plan
was a sunspace on the south wall. That hasn't been built yet... The main room is about 44'x48'x16' tall. The 48' east and west walls slope in 4' as they rise to 8'. The ceiling has a 4'x48' north-south horizontal strip. The south wall includes 4 sliding glass doors D, each about 6'x8', with no eyebrows for summer shading. Here's a flattened view from above, in a fixed font like Courier: . ---------------------- . -- | \ | 430 ft^2 | / | 4' ..D..| \ |----------------------| / | -- D | |\ |d | /| | . | D | \ | 860 ft^2 | / | | D f | | \ |d | / | | . u | | \| |/ | | | D t | D | |----------------------| | | -- S . u | | |4' 192 ft^2 |160 |320 | 36' D r | D | |----------------------|ft^2|ft^2| . e | | /| |\ | | | D ? | | / |d 860 ft^2 | \ | | . | D | / | | \ | | D | |/ |d | \| | ..D..| / |----------------------| \ | -- | / | 430 ft^2 | \ | 4' . ---------------------- . -- | 8' | 8' | 8' | - 48' - | 8' | 8' | R20 walls and ceiling with 3540ft^2/R20 = 177 Btu/h-F plus R2 doors with 192ft^2/R2 = 96 would make G = 273 Btu/h-F of conductance, including 10 Btu/h-F for the ceiling strip. On an average January day, we might keep the room 50 F for 6 hours with sun shining through the doors and room air thermosyphoning through a new air heater on the upper part of the south wall. When the room is warm enough, we might push room air from the north part of the ceiling south through a horizontal plastic film duct under the ceiling into the lower part of the air heater and stop thermosyponing with one-way plastic film dampers in vents from the room to the air heater just above the doors, using Grainger's $62.90 4WT44 10" diameter 26 watt 665 cfm fan (which has a 176 F max temperature rating.) The existing slow ceiling fans and a thermostat could warm the room at night and on cloudy days. With 160 ft^2 of U0.58 Thermaglas twinwall polycarbonate glazing with 80% solar transmission over the upper south wall and 3520 pounds of water under the ceiling strip (eg 64 10'x4" thinwall PVC pipes or a 4'x48'x3.5" tray with water in a 4' layflat poly film duct), we could have 100% solar heat in December, according to a simple simulation with Phila TMY2 weather data: 20 DAYSTART=344'display start time (days) 30 DS=DAYSTART*24'display start time (hours) 40 RANGE=8760-DS'display range (hours) 50 TMIN=10:TMAX=160'temp display range (F) 60 LINE (0,0)-(639,349),,B:XDF=640/RANGE:YDF=349/(TMAX-TMIN) 70 FOR TR=TMIN TO TMAX STEP 10'temp ref lines 80 LINE (0,349-YDF*(TR-10))-(639,349-YDF*(TR-10)):NEXT 90 GL=263'lower church conductance (Btu/h-F) 100 GU=10'upper church conductance (Btu/h-F) 110 PL=640'length of 4" ceiling pipe (feet) 120 CHU=5.5*PL'upper church capacitance (Btu/F) 130 GP=2*PL'pipe conductance (Btu/h-F) 140 TH=50'constant church temp (F) 150 TU=155'initialize upper church temp (F) 160 TUMIN=200'initialize min upper church temp (F) 170 OPEN "ecayear" FOR INPUT AS #1:LINE INPUT#1,H$ 180 FOR H=1 TO 8760'hours of typical (TMY2) year 190 INPUT#1,MONTH,DAY,HOUR,TDB,WIND,TDP,IGLOH,SS,WS,NS ,ES 200 Q=-(TH-TDB)*GL'lower heat loss (Btu) 210 Q=Q+.6*192*SS'add solar gain from existing doors (Btu) 220 Q=Q-(TU-TDB)*GU'add upper heat loss (Btu) 230 QUW=.8*SS*160-(TU-TDB)*160*.58'solar gain from upper wall (Btu) 240 IF QUW0 THEN Q=Q+QUW'add solar gain from upper wall (Btu) 250 TU=TU+Q/CHU'new upper church temp (F) 260 IF TU180 THEN TU=180'limit upper church temp (F) 270 IF TUTUMIN THEN TUMIN=TU:HMIN=H:CLOSS=(TH-TDB)*GL 280 PSET(XDF*(H-DS),349-YDF*(TDB-10))'plot outdoor temp (F) 290 PSET(XDF*(H-DS),349-YDF*(TU-10))'plot upper church temp (F) 300 IF DAY=1 AND HOUR=.5 THEN LINE (XDF*(H-DS),349)-(XDF*(H-DS),345)'months 310 NEXT H 320 TUL=TU'end of year upper church temp (F) 330 CLOSE #1 340 PRINT CHU;HMIN;TUMIN,TH+CLOSS/GP,TUL 350 LINE (XDF*(HMIN-DS),100)-(XDF*(HMIN-DS),0)'mark Hmin Chu min min water min water end of year (Btu/F) hour temp temp need water temp 3520 8674 52.96889 F 53.92035 F 152.5393 F The ceiling pipe water temp drops to about 53 F at 10 AM on 12/27... The mass of the room itself (about 2K Btu/F, with 1/2" drywall) isn't important in the simulation, since the room temp is constant. We can't store useful heat in a thermal mass that doesn't change temperature. Fin-tube vs PVC pipe would weigh less and might double the system cost, counting 2 pumps and a stratified tank on the ground and controls, but we could heat more of the church, and warm it up on Sunday mornings. We could collect more heat with a new 36'x8'x8'-tall sunroom on the south wall with 8 American Craftsman 6068-2 6'x80" U0.48 sliding glass doors ($269 each at Home Depot) with 63% transmission and a $300 layer of corrugated Dynaglas R1 polycarbonate greenhouse roofing with 90% transmission, with 80% black horizontal shadecloth under 50% of the roof to shade the existing doors in summertime. (The fin tubes could also naturally cool the church.) In wintertime, we could pump cool water up from the stratified tank in the crawlspace through the fin tubes to store solar heat and pump or thermosyphon hot water up to warm the room, with a thermostat on the cold end of the fin tube to run the hot pump when the cold end is less than 80 F and a differential thermostat on the hot end to run the cold pump when the hot end is warmer than the higher tank temp. The stratified tank might be a 2'-tall plywood box lined with a single folded piece of EPDM rubber, with a 2'-tall vertical wall to separate warm and cool sections and a pipe in the upper part of the warm section that goes to a lower pipe in the cool section. If the room needs (70-30)273 = 11K Btu/h at 70 F (50 people make about 15K Btu/h) and 100 F ceiling mass with a low-e surface (e = 0.3) below the ceiling strip radiates 192ft^2se((100+460)^4-(460+70)^4) = 1.9K Btu/h, where s = 0.1714x10^-8, the ceiling fans with a room temp thermostat and an occupancy sensor could supply the rest with about (11K-1.9K)/(100-70) = 300 cfm of airflow. Nick |
#2
Posted to alt.solar.thermal,misc.consumers.frugal-living,alt.home.repair,alt.energy.renewable,alt.energy.homepower
|
|||
|
|||
Church solar heating improvements
|
#3
Posted to alt.solar.thermal,misc.consumers.frugal-living,alt.home.repair,alt.energy.renewable,alt.energy.homepower
|
|||
|
|||
Church solar heating improvements
|
#4
Posted to alt.solar.thermal,misc.consumers.frugal-living,alt.home.repair,alt.energy.renewable,alt.energy.homepower
|
|||
|
|||
Church solar heating improvements
SJC wrote:
"Lawrence" wrote in message ups.com... wrote: You post is rather long and contains a lot of detail. I don't see a single question mark though. What exactly is your question(s)? I am not an expert in such matters but there are others who are. If you can boil your post down to one or two questions it would be quite helpful. Being a news group, this is Nick's news about a new application I would guess. Nick is FULL of ideas Nick has ENORMOUS confidence that everything he thinks up will work, and cost almost nothing to build, install, and operate. My view of what Nick has done is that he floated a proposal, inviting us to show him where any flaws exist with his proposal. Traditionally, Nick's view is that his proposal is PERFECT, no changes are needed. Attempts to convince him of an error, or a flaw have been rebuffed STRONGLY. |
#5
Posted to alt.home.repair
|
|||
|
|||
Church solar heating improvements
Nick how is your Easy Bake lightbulb sauna going.
|
#6
Posted to alt.solar.thermal,misc.consumers.frugal-living,alt.home.repair,alt.energy.renewable,alt.energy.homepower
|
|||
|
|||
Church solar heating improvements
On Sun, 24 Sep "SJC" wrote:
"Lawrence" wrote in message oups.com... wrote: You post is rather long and contains a lot of detail. I don't see a single question mark though. What exactly is your question(s)? I am not an expert in such matters but there are others who are. If you can boil your post down to one or two questions it would be quite helpful. Being a news group, this is Nick's news about a new application I would guess. SJC, when you cut and paste prior text, please add quote marks, as I did here for correct attribution. Until you suggested it might be news, I was kind of waiting to find out what the question was. :-) Joe Fischer |
#7
Posted to alt.solar.thermal,misc.consumers.frugal-living,alt.home.repair,alt.energy.renewable,alt.energy.homepower
|
|||
|
|||
Church solar heating improvements
"Joe Fischer" wrote in message ... On Sun, 24 Sep "SJC" wrote: "Lawrence" wrote in message roups.com... wrote: You post is rather long and contains a lot of detail. I don't see a single question mark though. What exactly is your question(s)? I am not an expert in such matters but there are others who are. If you can boil your post down to one or two questions it would be quite helpful. Being a news group, this is Nick's news about a new application I would guess. SJC, when you cut and paste prior text, please add quote marks, as I did here for correct attribution. Until you suggested it might be news, I was kind of waiting to find out what the question was. :-) Joe Fischer I did not cut and paste, just replied. I turned on the indent and mark feature. |
#8
Posted to alt.solar.thermal,misc.consumers.frugal-living,alt.home.repair,alt.energy.renewable,alt.energy.homepower
|
|||
|
|||
Church solar heating improvements
wrote in message ... When the Pottstown PA UU church was built, one part of the plan was a sunspace on the south wall. That hasn't been built yet... snip On an average January day, we might keep the room 50 F for 6 hours with sun shining through the doors and room air thermosyphoning through a new air heater on the upper part of the south wall. When the room is warm enough, we might push room air from the north part of the ceiling south through a horizontal plastic film duct under the ceiling into the lower part of the air heater and stop thermosyponing with one-way plastic film dampers in vents from the room to the air heater just above the doors, using Grainger's $62.90 4WT44 10" diameter 26 watt 665 cfm fan (which has a 176 F max temperature rating.) The existing slow ceiling fans and a thermostat could warm the room at night and on cloudy days. Nick, At the end of the day, what all church attendees/members want is to be as comfortable as the next church. Nothing hurts worse than 50° pews on very old tithe paying bones. They want energy savings, they just don't want energy savings when they're in/around the building. "Hear me now and believe me later." ...It just is. And yes they all will litigate after the fact, no matter what they "told you" they wanted. So, the most acceptable solution is.... highest R-value insulation all around (set a new worlds R-value record!) with multiple high efficiency heat/cool units, zoned to accommodate scheduled events and activities. A single central multiple zone controller for all the HVAC systems, WITH, a very simple looking large momentary push button that says "occupied" in every room/zone as needed so unexpected meetings, youth gatherings or services can easily bypass the standby settings for a one-shot timed event. A minimal learning curve for all involved. With all that being said... once again, as many things in life, the best answer (maximum energy savings) is not necessarily the correct answer. -zero snip |
#9
Posted to alt.home.repair
|
|||
|
|||
Church solar heating improvements
m Ransley wrote:
Nick how is your Easy Bake lightbulb sauna going. and how is the PE tubing replacement for a GFX waste heat recovery system working??? |
#10
Posted to alt.solar.thermal,misc.consumers.frugal-living,alt.home.repair,alt.energy.renewable,alt.energy.homepower
|
|||
|
|||
Church solar heating improvements
-zero wrote:
wrote in message ... When the Pottstown PA UU church was built, one part of the plan was a sunspace on the south wall. That hasn't been built yet... snip On an average January day, we might keep the room 50 F for 6 hours with sun shining through the doors and room air thermosyphoning through a new air heater on the upper part of the south wall. When the room is warm enough, we might push room air from the north part of the ceiling south through a horizontal plastic film duct under the ceiling into the lower part of the air heater and stop thermosyponing with one-way plastic film dampers in vents from the room to the air heater just above the doors, using Grainger's $62.90 4WT44 10" diameter 26 watt 665 cfm fan (which has a 176 F max temperature rating.) The existing slow ceiling fans and a thermostat could warm the room at night and on cloudy days. Nick, At the end of the day, what all church attendees/members want is to be as comfortable as the next church. Nothing hurts worse than 50° pews on very old tithe paying bones. They want energy savings, they just don't want energy savings when they're in/around the building. "Hear me now and believe me later." ...It just is. And yes they all will litigate after the fact, no matter what they "told you" they wanted. So, the most acceptable solution is.... highest R-value insulation all around (set a new worlds R-value record!) with multiple high efficiency heat/cool units, zoned to accommodate scheduled events and activities. A single central multiple zone controller for all the HVAC systems, WITH, a very simple looking large momentary push button that says "occupied" in every room/zone as needed so unexpected meetings, youth gatherings or services can easily bypass the standby settings for a one-shot timed event. A minimal learning curve for all involved. With all that being said... once again, as many things in life, the best answer (maximum energy savings) is not necessarily the correct answer. -zero snip Here Here, THIS IS THE ANSWER. Such a structure has MINIMAL use. Space conditioning is WASTED most of the time. HIGH INSULATION, efficient heat/cool equipment, zoning for weekly activity schedule, and a panic button for unscheduled events. Now if this was an office building or a school,we could go down Nick's path. |
#11
Posted to alt.solar.thermal,misc.consumers.frugal-living,alt.home.repair,alt.energy.renewable,alt.energy.homepower
|
|||
|
|||
Church solar heating improvements
In reality, no one gives a ****! It's a church, God is good business, just pass the god damn plate around a few more times for the heating oil fund.They screw them now, just screw them a little tighter in the winter. |
#12
Posted to alt.solar.thermal,misc.consumers.frugal-living,alt.home.repair,alt.energy.renewable,alt.energy.homepower
|
|||
|
|||
Church solar heating improvements
"Porgy Tirebiter" wrote in message m... In reality, no one gives a ****! It's a church, God is good business, just pass the god damn plate around a few more times for the heating oil fund.They screw them now, just screw them a little tighter in the winter. Well.... all I can say after that is; ** "Oh, your gonna HATE Friday's!" ;-) -zero ** http://www.bestoday.com.au/sick/arch...ys_in_hell.php |
#13
Posted to alt.solar.thermal,misc.consumers.frugal-living,alt.home.repair,alt.energy.renewable,alt.energy.homepower
|
|||
|
|||
Church solar heating improvements
On Sun, 24 Sep 2006 16:51:40 GMT, "Porgy Tirebiter"
wrote: In reality, no one gives a ****! It's a church, God is good business, just pass the god damn plate around a few more times for the heating oil fund.They screw them now, just screw them a little tighter in the winter. You might do some reading here http://www.uunashua.org/100q/c1.shtml. Some very good stuff, although not all their beliefs are credible. Such as "everyone is capable of reasoning." Obviously whoever thought that one up hasn't visited Usenet or the DMV. Still, think of UU as probably the least retarded religious organization. They're doomed to low membership though since they didn't think to include the four main tenets of more successful operations - god, heaven, hell, and sin-now-repent-later. Otherwise known as skydaddy, carrot, stick, and do-over. :-) Wayne |
#14
Posted to alt.solar.thermal,misc.consumers.frugal-living,alt.home.repair,alt.energy.renewable,alt.energy.homepower
|
|||
|
|||
Church solar heating improvements
wmbjk wrote:
On Sun, 24 Sep 2006 16:51:40 GMT, "Porgy Tirebiter" wrote: In reality, no one gives a ****! It's a church, God is good business, just pass the god damn plate around a few more times for the heating oil fund.They screw them now, just screw them a little tighter in the winter. You might do some reading here http://www.uunashua.org/100q/c1.shtml. Some very good stuff, although not all their beliefs are credible. Such as "everyone is capable of reasoning." Obviously whoever thought that one up hasn't visited Usenet or the DMV. Still, think of UU as probably the least retarded religious organization. They're doomed to low membership though since they didn't think to include the four main tenets of more successful operations - god, heaven, hell, and sin-now-repent-later. Otherwise known as skydaddy, carrot, stick, and do-over. :-) Wayne And are I say it, there are several notes on that page that Nick appears to be in CLEAR violation of. Everyone is capable of reasoning. (as you said above) Truth is not absolute; it changes over time Ideas should be open to criticism |
#15
Posted to alt.solar.thermal,misc.consumers.frugal-living,alt.home.repair,alt.energy.renewable,alt.energy.homepower
|
|||
|
|||
Church solar heating improvements
On Sun, 24 Sep 2006 21:18:11 GMT, Robert Gammon
wrote: wmbjk wrote: On Sun, 24 Sep 2006 16:51:40 GMT, "Porgy Tirebiter" wrote: In reality, no one gives a ****! It's a church, God is good business, just pass the god damn plate around a few more times for the heating oil fund.They screw them now, just screw them a little tighter in the winter. You might do some reading here http://www.uunashua.org/100q/c1.shtml. Some very good stuff, although not all their beliefs are credible. Such as "everyone is capable of reasoning." Obviously whoever thought that one up hasn't visited Usenet or the DMV. Still, think of UU as probably the least retarded religious organization. They're doomed to low membership though since they didn't think to include the four main tenets of more successful operations - god, heaven, hell, and sin-now-repent-later. Otherwise known as skydaddy, carrot, stick, and do-over. :-) Wayne And are I say it, there are several notes on that page that Nick appears to be in CLEAR violation of. Everyone is capable of reasoning. (as you said above) I find Nick quite reasonable. He's an innovator though, and many people resist innovation with a passion. Truth is not absolute; it changes over time I'm not sure what that's supposed to mean. Ideas should be open to criticism It's because Nick is open that posters get the opportunity to criticize him, and he takes it well IMO. He's a lot more polite to nitwits than I am. Wayne |