Default 3' X 5' X 8" thick slab. rebar required?

I'm going to be pouring a 3 x 5 slab 8" thick. 2" below ground and 6" above.
It will need to support about 500lbs.

I'll be using quikrete for this. Do you think I'll need rebar for this
small slab?







  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 161
Default 3' X 5' X 8" thick slab. rebar required?


I am curious why so thick? You are holding up a bit more than 30
pounds/SF. Hand batching that much sack goods will have you worn
out. 15-20 bags of 80 #. Normal sack goods makes about 2500 PSF
concrete if you don't add excess water (most people do).


______________________________
Keep the whole world singing . . . .
DanG (remove the sevens)




"mook Johnson" wrote in message
...
I'm going to be pouring a 3 x 5 slab 8" thick. 2" below ground
and 6" above. It will need to support about 500lbs.

I'll be using quikrete for this. Do you think I'll need rebar
for this small slab?









  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 66
Default 3' X 5' X 8" thick slab. rebar required?

I need to lift surface high enough so that it won't flood during heavy
rains. putting it 6" above ground level will insure that. The most I've
seen in that area is 2" of water during an extremely heavy downpour bfore
the water had a chance to drain off.

Just want to be safe.

I will rent a mixer for this job for sure!




"DanG" wrote in message
news:AKjKg.227026$k%3.144636@dukeread12...

I am curious why so thick? You are holding up a bit more than 30
pounds/SF. Hand batching that much sack goods will have you worn out.
15-20 bags of 80 #. Normal sack goods makes about 2500 PSF concrete if
you don't add excess water (most people do).


______________________________
Keep the whole world singing . . . .
DanG (remove the sevens)




"mook Johnson" wrote in message
...
I'm going to be pouring a 3 x 5 slab 8" thick. 2" below ground and 6"
above. It will need to support about 500lbs.

I'll be using quikrete for this. Do you think I'll need rebar for this
small slab?











  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,313
Default 3' X 5' X 8" thick slab. rebar required?

On Sat, 02 Sep 2006 17:59:20 GMT, "mook Johnson"
wrote:

I'm going to be pouring a 3 x 5 slab 8" thick. 2" below ground and 6" above.
It will need to support about 500lbs.

I'll be using quikrete for this. Do you think I'll need rebar for this
small slab?


I'd use welded wire grid, an inch and a half from the bottom and top.

Either that, or place about half the concrete, and then dump rocks
in to bulk it up, and then another layer of concrete.
(Always assuming I could resist the temptation to cast
a storage vault under the damn thing.)
  #5   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 1,029
Default 3' X 5' X 8" thick slab. rebar required?


mook Johnson wrote:
I'm going to be pouring a 3 x 5 slab 8" thick. 2" below ground and 6" above.
It will need to support about 500lbs.

I'll be using quikrete for this. Do you think I'll need rebar for this
small slab?


I'm w/ Dan--why in the world use an 8" pour for such a small load?
What is the footprint of the object(s) to be mounted on the slab? If
the purpose of the thickness is to get the height above surrounding
grade, I'd recommend strongly considering accomplishing that by grade
adjustment and a resulting thinner slab. A standard nominal 4" slab
would easily support the load unless it is a very small footprint (and
in that case it would make a lot more sense to make local mounting
piers thicker rather than the whole slab).

As for the bar, I wouldn't worry about bar, but I'd probably use 6"
square mesh just for doing it (and because I've got a roll remnant
around ).

HTH, and better or more specific answers would undoubtedly be
forthcoming w/ some more info on what the objective actually is...

BTW, iirc (and I think I do) the 80-lb Quikrete sack is 2/3 cu-ft so
your proposal would be a roughly 3x5x(2/3) cu-ft * (3/2) bags/cu-ft --
15 bags. That's a lot of hand mixing considering the time element
since you presumably want a continuous pour.



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 286
Default 3' X 5' X 8" thick slab. rebar required?

in my experience the next person to own your piece of property is going
to try to use your 3 x 5 slab of cement as the base of a full scale
replica of the brooklin bridge. If you are going to make it that thick
then someday someone will overkill it thinking it can handle it.

Empress2454 #124457

The best Games

a href=http://www.gamestotal.com/Multiplayer Online Games/a a
href=http://www.gamestotal.com/Strategy Games/abra
href=http://uc.gamestotal.com/Unification Wars/a - a
href=http://uc.gamestotal.com/Massive Multiplayer Online
Games/abra href=http://gc.gamestotal.com/Galactic Conquest/a -
a href=http://gc.gamestotal.com/Strategy Games/abra
href=http://www.stephenyong.com/runescape.htmRunescape/abra
href=http://www.stephenyong.com/kingsofchaos.htmKings of chaos/abr





mook Johnson wrote:
I'm going to be pouring a 3 x 5 slab 8" thick. 2" below ground and 6" above.
It will need to support about 500lbs.

I'll be using quikrete for this. Do you think I'll need rebar for this
small slab?


  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,823
Default 3' X 5' X 8" thick slab. rebar required?


"mook Johnson" wrote in message
...
I need to lift surface high enough so that it won't flood during heavy
rains. putting it 6" above ground level will insure that. The most I've
seen in that area is 2" of water during an extremely heavy downpour bfore
the water had a chance to drain off.

Just want to be safe.

I will rent a mixer for this job for sure!


Before you mix all that concrete, look at some alternatives.

Can there be a platform on blocks? 500 pounds is not much so building a
wood platform with a 2 x 4 frame and decking boards on top it will be
sufficient. I'd use four concrete blocks to support it all. Once the
concrete is in place, you have a very permanent slab. With wood and block,
you can move, modify, eliminate, add height, as needed.

The concrete slab will weigh about 1600 pounds. Do you really want to
handle that when something a couple hundred will do the job just as good?
--
Ed
http://pages.cthome.net/edhome/


  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,079
Default 3' X 5' X 8" thick slab. rebar required?


"mook Johnson" wrote in message
...
I'm going to be pouring a 3 x 5 slab 8" thick. 2" below ground and 6"
above. It will need to support about 500lbs.

I'll be using quikrete for this. Do you think I'll need rebar for this
small slab?


No, you shouldn't need rebar, but as someone else suggested wire mesh
instead. The rebar is there for bending stress, it won't stop it from
cracking though.

Besides you didn't specify which gauge rebar you wanted to use, there's only
about 50 different types (well actually that's an exaggeration). Anyway if
it were me, I'd go with the other suggestions of pillar and post.



  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 66
Default 3' X 5' X 8" thick slab. rebar required?

OK teach me something about slab building as I am a rookie.

The object is a 500bs box that is 2' x 4'. It is fairly evenly distributed
over the box so load is not a problem.

Like I said in a previous post I'd like the surface of the slab to be 5" -
6" above the current ground level. This is in south texas so frost line is
not a major problem.

how would you recommend constructing this slab?


"dpb" wrote in message
oups.com...

mook Johnson wrote:
I'm going to be pouring a 3 x 5 slab 8" thick. 2" below ground and 6"
above.
It will need to support about 500lbs.

I'll be using quikrete for this. Do you think I'll need rebar for this
small slab?


I'm w/ Dan--why in the world use an 8" pour for such a small load?
What is the footprint of the object(s) to be mounted on the slab? If
the purpose of the thickness is to get the height above surrounding
grade, I'd recommend strongly considering accomplishing that by grade
adjustment and a resulting thinner slab. A standard nominal 4" slab
would easily support the load unless it is a very small footprint (and
in that case it would make a lot more sense to make local mounting
piers thicker rather than the whole slab).

As for the bar, I wouldn't worry about bar, but I'd probably use 6"
square mesh just for doing it (and because I've got a roll remnant
around ).

HTH, and better or more specific answers would undoubtedly be
forthcoming w/ some more info on what the objective actually is...

BTW, iirc (and I think I do) the 80-lb Quikrete sack is 2/3 cu-ft so
your proposal would be a roughly 3x5x(2/3) cu-ft * (3/2) bags/cu-ft --
15 bags. That's a lot of hand mixing considering the time element
since you presumably want a continuous pour.



  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 161
Default 3' X 5' X 8" thick slab. rebar required?

Mook,
Would it be fine if the grass formed a little hill with this slab
on top? Never pour concrete on grass. Remove sod as required.
Use gravel, fill sand, broken cement blocks, old bricks, rocks, or
select fill (compactable sand/gravel). Set a 2x4 edge form at the
height and slope that you want to end up with. Pack the bottom
edge with dirt or whatever so the concrete can't run out. Pour
and finish. Strip forms and add back top soil and sod.

If you want it high above the grass with nicely finished 6-8"
face. Set an edge form (2x8?) around the intended slab. You
still need to have removed the sod. Raise as much of the center
with rubble or select fill as possible, leaving the top and sides
at least 2" thick. Think about the finished concrete looking a
bit like an upside down cake pan.

______________________________
Keep the whole world singing . . . .
DanG (remove the sevens)




"mook Johnson" wrote in message
...
OK teach me something about slab building as I am a rookie.

The object is a 500bs box that is 2' x 4'. It is fairly evenly
distributed over the box so load is not a problem.

Like I said in a previous post I'd like the surface of the slab
to be 5" - 6" above the current ground level. This is in south
texas so frost line is not a major problem.

how would you recommend constructing this slab?


"dpb" wrote in message
oups.com...

mook Johnson wrote:
I'm going to be pouring a 3 x 5 slab 8" thick. 2" below ground
and 6" above.
It will need to support about 500lbs.

I'll be using quikrete for this. Do you think I'll need rebar
for this
small slab?


I'm w/ Dan--why in the world use an 8" pour for such a small
load?
What is the footprint of the object(s) to be mounted on the
slab? If
the purpose of the thickness is to get the height above
surrounding
grade, I'd recommend strongly considering accomplishing that by
grade
adjustment and a resulting thinner slab. A standard nominal 4"
slab
would easily support the load unless it is a very small
footprint (and
in that case it would make a lot more sense to make local
mounting
piers thicker rather than the whole slab).

As for the bar, I wouldn't worry about bar, but I'd probably
use 6"
square mesh just for doing it (and because I've got a roll
remnant
around ).

HTH, and better or more specific answers would undoubtedly be
forthcoming w/ some more info on what the objective actually
is...

BTW, iirc (and I think I do) the 80-lb Quikrete sack is 2/3
cu-ft so
your proposal would be a roughly 3x5x(2/3) cu-ft * (3/2)
bags/cu-ft --
15 bags. That's a lot of hand mixing considering the time
element
since you presumably want a continuous pour.







  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default 3' X 5' X 8" thick slab. rebar required?

whats it going to be used for? a generator?

I would bui;ld a block foundation and rise it to a foot so flooding
will never matter..

if its for emergenmcy equiptement like a generator

  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,743
Default 3' X 5' X 8" thick slab. rebar required?

mook Johnson wrote:
I'm going to be pouring a 3 x 5 slab 8" thick. 2" below ground and 6"
above. It will need to support about 500lbs.

I'll be using quikrete for this. Do you think I'll need rebar for
this small slab?


Eek!

Consider a few 4x4s, a decking of 2x6s, four (maybe six) concrete blocks for
support. You'll need a saw, a tape measure, and some nails. Total time of
construction for one person: 2 hours.

It'll take two hours just to MIX twenty 80-pound bags of concrete.

Also, consider what you'll have to do when the wife says: "It would look
better over there."


  #13   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 1,029
Default 3' X 5' X 8" thick slab. rebar required?


mook Johnson wrote:
OK teach me something about slab building as I am a rookie.

The object is a 500bs box that is 2' x 4'. It is fairly evenly distributed
over the box so load is not a problem.

Like I said in a previous post I'd like the surface of the slab to be 5" -
6" above the current ground level. This is in south texas so frost line is
not a major problem.

how would you recommend constructing this slab?

....

I'd do one of several things, assuming you don't want a wooden deck
type solution (which, in So TX I can certainly see) which as someone
else mentioned would certainly not be difficult to make to support the
load easily.

I'll outline basic choices/alternatives to consider--what, specifically
works for you depends on factors I don't have any way of knowing--where
you are, what sort of tools you have or have access to, etc., etc., ...

First choice would be to simply make a small "hill" to place the slab
on top of...will need some fill material from somewhere which can be a
pain if you're in a large metro area and don't have any hauling
capabilities. If you're lucky you've got enough of a lot you can
scrounge enough soil from one place to make the area you need large
enough high enough above the surrounding area. Assuming it's a yard,
ideally you would want it graded enough to plant back to grass and mow
along w/ the rest of the yard.

Next would be variations of the "wall and slab" method...rather than a
slab this thick all the way through, go ahead and form the full height
around the outer edge but fill in the center portion except for an area
around 4-6" wide (say) w/ fill material so that the bulk of the pour is
only 3-4" thick. Again, need something for some fill--can be old
brick, rock, clean dirt (not mixed w/ sod, sticks, etc.) or whatever
else you can find. Need it to be good enough that it can be packed
solidly, so settling isn't an issue later.

More sophisticated versions of the above include laying an outer wall
of block or brick, etc., and essentially proceeding as above from
there. Really all the point is is that there should be far less
labor-intensive and expensive ways to get the end result w/o pouring
such a huge block of solid concrete.

Second alternative would be to

  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 66
Default 3' X 5' X 8" thick slab. rebar required?

You guessed it. Its a Generac 15kW unit and it will be a perminant addition
to the house and won't move.

I thought about a wood solution but I don't like the idea of hot generator
on wood. Wood rot and termites are also issues to deal with.

Tell me about building a block foundation?


wrote in message
oups.com...
whats it going to be used for? a generator?

I would bui;ld a block foundation and rise it to a foot so flooding
will never matter..

if its for emergenmcy equiptement like a generator



  #15   Report Post  
Posted to alt.home.repair
EXT EXT is offline
external usenet poster
 
Posts: 1,661
Default 3' X 5' X 8" thick slab. rebar required?

Pour a standard 4" slab. Get 4 precast concrete deck anchor blocks. Drill 4
holes in alignment with the anchor holes in your genny's bottom/frame. Use
threaded anchors to mount about 1 foot lengths of 1/2" or 5/8" threaded rod.
Fit the four blocks over the threaded rods and mortar the blocks to the slab
and fill the center hole in the blocks around the threaded rods with morter.
Set your genny on top of the blocks with the threaded rods through the
mounting holes in the bottom of the genny and tighten into place with some
washers and nuts. This will provide an air space under the genny to keep it
dry reducing corrosion, help it cool with in operation and high enough to
prevent minor flooding from touching it. I did a similar installation in my
garage for a diesel generator.


"Mook Johnson" wrote in message
...
You guessed it. Its a Generac 15kW unit and it will be a perminant
addition to the house and won't move.

I thought about a wood solution but I don't like the idea of hot generator
on wood. Wood rot and termites are also issues to deal with.

Tell me about building a block foundation?


wrote in message
oups.com...
whats it going to be used for? a generator?

I would bui;ld a block foundation and rise it to a foot so flooding
will never matter..

if its for emergenmcy equiptement like a generator







  #16   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,079
Default 3' X 5' X 8" thick slab. rebar required?


"Mook Johnson" wrote in message
...
You guessed it. Its a Generac 15kW unit and it will be a perminant
addition to the house and won't move.

I thought about a wood solution but I don't like the idea of hot generator
on wood. Wood rot and termites are also issues to deal with.


What about motor mounts or similar things? I'm thinking rubber mounts or
polyurethane mounts - last for decades even under harsh conditions - like
the kind in your engine compartment.

Say split the difference, 4" concrete slab with diesel engine mounts -
should put it well over 10" total height.

Tell me about building a block foundation?



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Slab extension settled/settling, looking at options, risk in refinishing wood floors. JDS Home Repair 3 April 7th 05 05:22 PM
breaking up concrete pad 6 inches thick -concete breaker required?. tom patton UK diy 8 March 22nd 05 02:45 PM
Evaporative cooler question SteveB Home Repair 105 February 1st 05 01:06 PM
Radiant Heat in Slab -- HELP! Tom Newton Home Repair 25 March 19th 04 02:37 AM
Radiant Heat in Slab - HELP! Tom Newton Home Ownership 9 February 6th 04 01:53 PM


All times are GMT +1. The time now is 07:23 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"