  #1   Report Post  
Posted to alt.home.repair
JJ
 
Posts: n/a
Default Need Help Urgently! Surface mount electric panel

Hi,

I have installed a surface mount 125 A combination meter main. I have
brought all my home runs, 14 of them, all except 2 are 14-2 NM cables
through two 1 1/2" knock outs from the back into the panel with a chase
nipple. Before entering the chase nipple all cables are stapled to the
stud where the panel is mounted. NOW, here is my problem, the inspector
now all of the sudden doesn't accept that (used to be accepted by him
and others just weeks ago) tells me to run them through a gutter and no
more than 2 NMs in a single connector and refers to article 312.5 in
NEC.

I am hoping for help here, there are only few knock outs at the bottom
of the panel, this a Murray 125 A surface mount panel (JA2442B1125SEC)
and of course being a surface mount all are outside. My only other
option is to have min. 7 knock outs in the back of the panel, that is
to punch them, which might be another problem. The inspector could
claim that I am not allowed to punch holes there. Siemens/Murray are of
absolutly of NO help. I will think twice before using their stuff
again.

How are you guys installing these panels with home runs or having NMs
coming into them, they got place for 24 full size breakers. Somebody
must have thought about this, it can't be that every of these panels
needs a gutter. Again your help is very mich apprerciated. By the way
the NEC referrence is the one on 2004.

Thanks

JJ


PS: someone else had this question before but I couldn't find any
answer to it.

"While pawing through the 1999 NEC (the one the county inspects to) I
found
that 373-5(c) no longer allows the arrangement in the current box, all
of
the NM cables coming in through a single opening with a bushing in the
back
of the box.

So two questions, please.

First, what is the preferred method for bringing NM loads into a box
like
this? 20 or so individual cable clamps seems bad, and I don't get how
the
exception for one or more 18" conduits into the top of the panel is
supposed to work."

  #2   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default Need Help Urgently! Surface mount electric panel

dunno, but here's the old thread you cite:

http://groups.google.com/group/alt.h...8e817f0011abcc

  #3   Report Post  
Posted to alt.home.repair
Edwin Pawlowski
 
Posts: n/a
Default Need Help Urgently! Surface mount electric panel


"JJ" wrote in message

The inspector could
claim that I am not allowed to punch holes there. Siemens/Murray are of
absolutly of NO help. I will think twice before using their stuff
again.


Don't blame Siemens/Murray, blame either yourself or the inspector. Why not
ask him if he will accept the holes there? Sometimes you are 100% right,
but the inspector has some other idea. He wins.


  #4   Report Post  
Posted to alt.home.repair
JJ
 
Posts: n/a
Default Need Help Urgently! Surface mount electric panel


Edwin Pawlowski wrote:
"JJ" wrote in message

The inspector could
claim that I am not allowed to punch holes there. Siemens/Murray are of
absolutly of NO help. I will think twice before using their stuff
again.


Don't blame Siemens/Murray, blame either yourself or the inspector. Why not
ask him if he will accept the holes there? Sometimes you are 100% right,
but the inspector has some other idea. He wins.


I was hoping on a logical, meaningfull reasoning.

Thanks

  #5   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default Need Help Urgently! Surface mount electric panel

A 200 amp panel proobably has more slots...

may still be a viable answer



  #6   Report Post  
Posted to alt.home.repair
Edwin Pawlowski
 
Posts: n/a
Default Need Help Urgently! Surface mount electric panel


"JJ" wrote in message

I was hoping on a logical, meaningfull reasoning.

Thanks


Some inspectors will give you that. Others make Hannibal look like a
pussycat.


  #7   Report Post  
Posted to alt.home.repair
JJ
 
Posts: n/a
Default Need Help Urgently! Surface mount electric panel


Edwin Pawlowski wrote:
"JJ" wrote in message

I was hoping on a logical, meaningfull reasoning.

Thanks


Some inspectors will give you that. Others make Hannibal look like a
pussycat.


I know, I have run into one of those and am trying not let have him the
say. We suppose to go by the same code, NEC and I am not living in some
third world country.

I am not sure I got my point across. Simply put, how do you get 20+
cables into a surface mount panel no matter what amps from the back and
cofirm to NEC, that is article 312.5 ?

I am looking for answers from experienced electricians, not things like
"inspectors have the say and such"

  #8   Report Post  
Posted to alt.home.repair
Bud--
 
Posts: n/a
Default Need Help Urgently! Surface mount electric panel

JJ wrote:

Hi,

I have installed a surface mount 125 A combination meter main. I have
brought all my home runs, 14 of them, all except 2 are 14-2 NM cables
through two 1 1/2" knock outs from the back into the panel with a chase
nipple. Before entering the chase nipple all cables are stapled to the
stud where the panel is mounted. NOW, here is my problem, the inspector
now all of the sudden doesn't accept that (used to be accepted by him
and others just weeks ago) tells me to run them through a gutter and no
more than 2 NMs in a single connector and refers to article 312.5 in
NEC.

I am hoping for help here, there are only few knock outs at the bottom
of the panel, this a Murray 125 A surface mount panel (JA2442B1125SEC)
and of course being a surface mount all are outside. My only other
option is to have min. 7 knock outs in the back of the panel, that is
to punch them, which might be another problem. The inspector could
claim that I am not allowed to punch holes there. Siemens/Murray are of
absolutly of NO help. I will think twice before using their stuff
again.


Does outside mean it is raintight made for exposed outside installation?
Are you mounting it weather exposed? If yes the KOs generally have to
be below the interior guts.

How are you guys installing these panels with home runs or having NMs
coming into them, they got place for 24 full size breakers. Somebody
must have thought about this, it can't be that every of these panels
needs a gutter. Again your help is very mich apprerciated. By the way
the NEC referrence is the one on 2004.

Thanks

JJ


PS: someone else had this question before but I couldn't find any
answer to it.

"While pawing through the 1999 NEC (the one the county inspects to) I
found
that 373-5(c) no longer allows the arrangement in the current box, all
of
the NM cables coming in through a single opening with a bushing in the
back
of the box.

So two questions, please.

First, what is the preferred method for bringing NM loads into a box
like
this? 20 or so individual cable clamps seems bad, and I don't get how
the
exception for one or more 18" conduits into the top of the panel is
supposed to work."


I agree with the inspector that using a chase nipple is a code
violation. There are NM connectors that can connect 2 2-wire NMs through
a 1/2" KO and that would require 7 KOs as you said. If you need to add
any KOs, ask the inspector if that is acceptable. I would think it would
be if they are at the bottom away from the interior guts. Can you use
side/bottom KOs?

The point of conduit entry 18" into the top of a surface mount box is
to protect NM as it runs down a wall. For example for a surface mount
receptacle on a concrete wall you can run 1/2" EMT from the box up into
the protected ceiling area and run the NM through the EMT into the box.
The EMT protects the NM and gives a clean look. There are some other
installation requirements - I'm assuming you have a copy of the code. I
don't know as how I'd bet that many NMs in a single EMT would be acceptable.

bud--
  #9   Report Post  
Posted to alt.home.repair
John Grabowski
 
Posts: n/a
Default Need Help Urgently! Surface mount electric panel


"JJ" wrote in message
oups.com...
Hi,

I have installed a surface mount 125 A combination meter main. I have
brought all my home runs, 14 of them, all except 2 are 14-2 NM cables
through two 1 1/2" knock outs from the back into the panel with a chase
nipple. Before entering the chase nipple all cables are stapled to the
stud where the panel is mounted. NOW, here is my problem, the inspector
now all of the sudden doesn't accept that (used to be accepted by him
and others just weeks ago) tells me to run them through a gutter and no
more than 2 NMs in a single connector and refers to article 312.5 in
NEC.

I am hoping for help here, there are only few knock outs at the bottom
of the panel, this a Murray 125 A surface mount panel (JA2442B1125SEC)
and of course being a surface mount all are outside. My only other
option is to have min. 7 knock outs in the back of the panel, that is
to punch them, which might be another problem. The inspector could
claim that I am not allowed to punch holes there. Siemens/Murray are of
absolutly of NO help. I will think twice before using their stuff
again.

How are you guys installing these panels with home runs or having NMs
coming into them, they got place for 24 full size breakers. Somebody
must have thought about this, it can't be that every of these panels
needs a gutter. Again your help is very mich apprerciated. By the way
the NEC referrence is the one on 2004.

Thanks

JJ


PS: someone else had this question before but I couldn't find any
answer to it.

"While pawing through the 1999 NEC (the one the county inspects to) I
found
that 373-5(c) no longer allows the arrangement in the current box, all
of
the NM cables coming in through a single opening with a bushing in the
back
of the box.

So two questions, please.

First, what is the preferred method for bringing NM loads into a box
like
this? 20 or so individual cable clamps seems bad, and I don't get how
the
exception for one or more 18" conduits into the top of the panel is
supposed to work."


I usually don't bring any cables in through the rear of the panel except the
service entrance cable. There are plenty of knockouts on the top and bottom
for cables. Using the chase nipples provides no strain relief and can also
be considered bundling. I suggest that you pull the cables out and put
knockout seals in the rear openings. Reroute your cables to enter the top
and/or the bottom. A two screw romex squeeze connector is approved for two
cables. That should give you plenty of space. You can buy reducing washers
at an electrical supply house for larger knockouts. If there is room you
can use a 7/8" unibit or holesaw to make additional openings. If your
cables are too short to reroute than your other option is the trough. If
you wanted to hide the wires you should have installed a flush mount panel.

I have found that the GE panels have loads of knockouts on the top and
bottom.

Please don't blame inspectors or manufacturers for your lack of experience.


John Grabowski
http://www.mrelectrician.tv

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
identify surface mount capacitor? [email protected] Electronics Repair 1 January 30th 06 08:33 PM
Wanted: GPIB panel mount socket David C. Partridge Electronics Repair 0 January 20th 06 03:09 PM
Removing surface mount diode Hamad bin Turki Salami Electronics Repair 9 January 13th 06 12:20 PM
OT - Global Warming (Was "Lying Liberals.") wmbjk Metalworking 6 June 17th 05 08:11 AM
Electric Panel Rating Bruce Home Repair 2 July 12th 03 08:23 AM


All times are GMT +1. The time now is 12:45 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"