Need some electrical advice / suggestions on adding a circuit. Got a
shop close to the house with 100ft of 10-2 wgrnd going from fuse box to shop. How big a 220 breaker can I use in the main panel in the house? How big a 220 outlet in the shop? Guess I should put in a disconnect panel in the shop? and maybe some 120 outlets or should I forget the 120's. Already some 120's out there on a different 10-2 wgrnd. What about ground? |
#2
Posted to alt.home.repair
|
|||
|
|||
220 to shop
"Slim" wrote in message ... Need some electrical advice / suggestions on adding a circuit. Got a shop close to the house with 100ft of 10-2 wgrnd going from fuse box to shop. How big a 220 breaker can I use in the main panel in the house? How big a 220 outlet in the shop? Guess I should put in a disconnect panel in the shop? and maybe some 120 outlets or should I forget the 120's. Already some 120's out there on a different 10-2 wgrnd. What about ground? Easy part is that you can't put 120v on a 10/2 240v line; no neutral. Assuming it is copper, you can use a 50a breaker; but then you will need a subpanel to run 20a circuits for your tools. Unless you plan on running several large 240v tools at the same time, just put a 20a breaker in and run 20a outlets. |
#3
Posted to alt.home.repair
|
|||
|
|||
220 to shop
Slim wrote:
How big a 220 breaker can I use in the main panel in the house? 10ga copper is takes 30amp max. -- If I had something to say, this is where I'd say it. |
#4
Posted to alt.home.repair
|
|||
|
|||
220 to shop
Easy part is that you can't put 120v on a 10/2 240v line; no neutral.
Assuming it is copper, you can use a 50a breaker 30 amp breaker "Toller" wrote in message ... "Slim" wrote in message ... Need some electrical advice / suggestions on adding a circuit. Got a shop close to the house with 100ft of 10-2 wgrnd going from fuse box to shop. How big a 220 breaker can I use in the main panel in the house? How big a 220 outlet in the shop? Guess I should put in a disconnect panel in the shop? and maybe some 120 outlets or should I forget the 120's. Already some 120's out there on a different 10-2 wgrnd. What about ground? Easy part is that you can't put 120v on a 10/2 240v line; no neutral. Assuming it is copper, you can use a 50a breaker; but then you will need a subpanel to run 20a circuits for your tools. Unless you plan on running several large 240v tools at the same time, just put a 20a breaker in and run 20a outlets. |
#5
Posted to alt.home.repair
|
|||
|
|||
220 to shop
"RBM" rbm2(remove wrote in message ... Easy part is that you can't put 120v on a 10/2 240v line; no neutral. Assuming it is copper, you can use a 50a breaker 30 amp breaker I'm sorry, you are certainly correct! 100' of #10 does not exceed the voltage drop requirement for 50a, but #10 can't can't handle 50a! That brings up an interesting question... If there is little voltage drop, then there is little power being lost as heat. If there is little heat, why can't it handle greater current? Isn't the capacity of wire related to heat? |
#6
Posted to alt.home.repair
|
|||
|
|||
220 to shop
"Toller" wrote in message ... "RBM" rbm2(remove wrote in message ... Easy part is that you can't put 120v on a 10/2 240v line; no neutral. Assuming it is copper, you can use a 50a breaker 30 amp breaker I'm sorry, you are certainly correct! 100' of #10 does not exceed the voltage drop requirement for 50a, but #10 can't can't handle 50a! That brings up an interesting question... If there is little voltage drop, then there is little power being lost as heat. If there is little heat, why can't it handle greater current? Isn't the capacity of wire related to heat? The capacity is related to the heat of the wire and insulation heat rating. As # 10 copper wire has a resistance of about 1 ohms per 100 feet and there are several wires in the cable and not if free air where the heat buildup can be dissapated very well , it will not take too much power to build up a lot of heat. Do the calculations and see how much heat you get at the various currents. It is power is equal to the current squared times the resistance. Remenber this is for just one wire in a bundle and you have several wires. |
#7
Posted to alt.home.repair
|
|||
|
|||
220 to shop
Also, the NEC recognizes the ampacity of AWG 14,12, 10 gauge to be higher,
but still limits those conductors to 15,20, and 30 amps regardless of insulation type "Ralph Mowery" wrote in message link.net... "Toller" wrote in message ... "RBM" rbm2(remove wrote in message ... Easy part is that you can't put 120v on a 10/2 240v line; no neutral. Assuming it is copper, you can use a 50a breaker 30 amp breaker I'm sorry, you are certainly correct! 100' of #10 does not exceed the voltage drop requirement for 50a, but #10 can't can't handle 50a! That brings up an interesting question... If there is little voltage drop, then there is little power being lost as heat. If there is little heat, why can't it handle greater current? Isn't the capacity of wire related to heat? The capacity is related to the heat of the wire and insulation heat rating. As # 10 copper wire has a resistance of about 1 ohms per 100 feet and there are several wires in the cable and not if free air where the heat buildup can be dissapated very well , it will not take too much power to build up a lot of heat. Do the calculations and see how much heat you get at the various currents. It is power is equal to the current squared times the resistance. Remenber this is for just one wire in a bundle and you have several wires. |
#8
Posted to alt.home.repair
|
|||
|
|||
220 to shop
"Toller" wrote in message ... "Slim" wrote in message ... Need some electrical advice / suggestions on adding a circuit. Got a shop close to the house with 100ft of 10-2 wgrnd going from fuse box to shop. How big a 220 breaker can I use in the main panel in the house? How big a 220 outlet in the shop? Guess I should put in a disconnect panel in the shop? and maybe some 120 outlets or should I forget the 120's. Already some 120's out there on a different 10-2 wgrnd. What about ground? Easy part is that you can't put 120v on a 10/2 240v line; no neutral. Assuming it is copper, you can use a 50a breaker; but then you will need a subpanel to run 20a circuits for your tools. Unless you plan on running several large 240v tools at the same time, just put a 20a breaker in and run 20a outlets. you use the bare wire as the neutral..but you must have another panel in the shop with an earth ground. |
#9
Posted to alt.home.repair
|
|||
|
|||
220 to shop
On Sun, 23 Apr 2006 03:54:22 GMT, "Toller" wrote:
"RBM" rbm2(remove wrote in message ... Easy part is that you can't put 120v on a 10/2 240v line; no neutral. Assuming it is copper, you can use a 50a breaker 30 amp breaker I'm sorry, you are certainly correct! 100' of #10 does not exceed the voltage drop requirement for 50a, but #10 can't can't handle 50a! That brings up an interesting question... If there is little voltage drop, then there is little power being lost as heat. If there is little heat, why can't it handle greater current? Isn't the capacity of wire related to heat? The size of the breaker (Ampacity) is matched to the size of the wire to protect it from melting the insulation and catching fire. Voltage drop is also an important consideration, but that doesn't change the first statement. A 50A circuit might have a 1A load connected to it. Great. There will be very little voltage drop because the current is so low. Now if the circuit is fully loaded (unusually) to the full 50 Amps, the voltage drop becomes a big deal and the wire may get warm to hot, yet still be within its rated value. The power lost in voltage drop is I^2 x R (I=current R=Resistance of the wire) The squaring factor is the main consideration. Even with an arbitrary low value for R, say 0.25 ohms, this yields P = 50 x 50 x 0.25 = 625 watts distributed evenly through the wire! That is a lot of lost power! If the wires are confined to cable or conduit, they are going to get hotter. If they are outside in free air, they can handle more current for a given size wire (the code allows for derating). To get a perspective of scale on this, some overloaded or fully loaded transmission circuits may have 1000 Amps or more running through individual conductors. If the line is at max. capacity, the conductors may operate in the temperature range of 100 C (212 F), the boiling point of water. Thus they are "hot" in more than just the sense of being "energized" with high voltage. Beachcomber |
#10
Posted to alt.home.repair
|
|||
|
|||
220 to shop
In article , "Toller" wrote:
"Slim" wrote in message .. . Need some electrical advice / suggestions on adding a circuit. Got a shop close to the house with 100ft of 10-2 wgrnd going from fuse box to shop. How big a 220 breaker can I use in the main panel in the house? How big a 220 outlet in the shop? Guess I should put in a disconnect panel in the shop? and maybe some 120 outlets or should I forget the 120's. Already some 120's out there on a different 10-2 wgrnd. What about ground? Easy part is that you can't put 120v on a 10/2 240v line; no neutral. Assuming it is copper, you can use a 50a breaker; Excuse me? A 50A breaker on 10ga wire? NOT. 30A is the max. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#11
Posted to alt.home.repair
|
|||
|
|||
220 to shop
In article , "digitalmaster" wrote:
you use the bare wire as the neutral WRONG. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#12
Posted to alt.home.repair
|
|||
|
|||
220 to shop
Doug Miller wrote:
In article , "Toller" wrote: "Slim" wrote in message .. . Need some electrical advice / suggestions on adding a circuit. Got a shop close to the house with 100ft of 10-2 wgrnd going from fuse box to shop. How big a 220 breaker can I use in the main panel in the house? How big a 220 outlet in the shop? Guess I should put in a disconnect panel in the shop? and maybe some 120 outlets or should I forget the 120's. Already some 120's out there on a different 10-2 wgrnd. What about ground? Easy part is that you can't put 120v on a 10/2 240v line; no neutral. Assuming it is copper, you can use a 50a breaker; Excuse me? A 50A breaker on 10ga wire? NOT. 30A is the max. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. Incorrect, a 10ga wire can indeed be protected by a 50A circuit breaker under limited circumstances. Under typical residential conditions 30A is the max though. See NEC 240.4(D-G) and referenced articles. The bigger issue is the fact that the 10-2 w/grd does not provide the required separate neutral and ground conductors to feed a sub panel. Without the separate neutral and ground conductors you are limited to using this as a single branch circuit, either a 30A 120V circuit (hot, neutral and ground), or a 30A 240V circuit (hot, hot and ground). You can not feed a subpoena or use it as a 120/240V circuit. Pete C. |
#13
Posted to alt.home.repair
|
|||
|
|||
220 to shop
"Doug Miller" wrote in message m... In article , "Toller" wrote: "Slim" wrote in message . .. Need some electrical advice / suggestions on adding a circuit. Got a shop close to the house with 100ft of 10-2 wgrnd going from fuse box to shop. How big a 220 breaker can I use in the main panel in the house? How big a 220 outlet in the shop? Guess I should put in a disconnect panel in the shop? and maybe some 120 outlets or should I forget the 120's. Already some 120's out there on a different 10-2 wgrnd. What about ground? Easy part is that you can't put 120v on a 10/2 240v line; no neutral. Assuming it is copper, you can use a 50a breaker; Excuse me? A 50A breaker on 10ga wire? NOT. 30A is the max. Yup, you caught me in an error; 11 hours after I acknowledged it was an error. Good job. |
#14
Posted to alt.home.repair
|
|||
|
|||
220 to shop
On Sun, 23 Apr 2006 07:19:46 -0400, "RBM" rbm2(remove
wrote: Also, the NEC recognizes the ampacity of AWG 14,12, 10 gauge to be higher, but still limits those conductors to 15,20, and 30 amps regardless of insulation type Just to follow your lead... but some people might think of just table 310.16: For those disputing this, read 2005 NEC 240.4(d) tom "Ralph Mowery" wrote in message hlink.net... "Toller" wrote in message ... "RBM" rbm2(remove wrote in message ... Easy part is that you can't put 120v on a 10/2 240v line; no neutral. Assuming it is copper, you can use a 50a breaker 30 amp breaker I'm sorry, you are certainly correct! 100' of #10 does not exceed the voltage drop requirement for 50a, but #10 can't can't handle 50a! That brings up an interesting question... If there is little voltage drop, then there is little power being lost as heat. If there is little heat, why can't it handle greater current? Isn't the capacity of wire related to heat? The capacity is related to the heat of the wire and insulation heat rating. As # 10 copper wire has a resistance of about 1 ohms per 100 feet and there are several wires in the cable and not if free air where the heat buildup can be dissapated very well , it will not take too much power to build up a lot of heat. Do the calculations and see how much heat you get at the various currents. It is power is equal to the current squared times the resistance. Remenber this is for just one wire in a bundle and you have several wires. |
#15
Posted to alt.home.repair
|
|||
|
|||
220 to shop
John Hines wrote:
Slim wrote: How big a 220 breaker can I use in the main panel in the house? 10ga copper is takes 30amp max. -- If I had something to say, this is where I'd say it. Thanks fro the advice, guys. Looks like I'll put a 20 or 30 amp breaker in the house and 20 or 30 amp outlet in the shop. Do I have to pound a ground rod in at garage to ground this puppy? |
#16
Posted to alt.home.repair
|
|||
|
|||
220 to shop
30 amp on what you gat.if you could run 8 wire with 50 amp you could do
alot more.. http://www.minibite.com/america/malone.htm |
#17
Posted to alt.home.repair
|
|||
|
|||
220 to shop
In article , "Pete C." wrote:
Doug Miller wrote: In article , "Toller" wrote: "Slim" wrote in message .. . Need some electrical advice / suggestions on adding a circuit. Got a shop close to the house with 100ft of 10-2 wgrnd going from fuse box to shop. How big a 220 breaker can I use in the main panel in the house? How big a 220 outlet in the shop? Guess I should put in a disconnect panel in the shop? and maybe some 120 outlets or should I forget the 120's. Already some 120's out there on a different 10-2 wgrnd. What about ground? Easy part is that you can't put 120v on a 10/2 240v line; no neutral. Assuming it is copper, you can use a 50a breaker; Excuse me? A 50A breaker on 10ga wire? NOT. 30A is the max. Incorrect, a 10ga wire can indeed be protected by a 50A circuit breaker under limited circumstances. Under typical residential conditions 30A is the max though. See NEC 240.4(D-G) and referenced articles. And which of those apply to this situation? None. The bigger issue is the fact that the 10-2 w/grd does not provide the required separate neutral and ground conductors to feed a sub panel. Without the separate neutral and ground conductors you are limited to using this as a single branch circuit, either a 30A 120V circuit (hot, neutral and ground), or a 30A 240V circuit (hot, hot and ground). You can not feed a subpoena or use it as a 120/240V circuit. Of course he can use it to feed a subpanel. What he *can't* do is use it to feed a subpanel that supplies both 120V and 240V loads. Consider: if the subpanel supplies only 240V loads, there's no need for a neutral, and 10/2 WG is fine. Also, if the subpanel supplies only 120V loads, there's no need for two hots, but of course only every other breaker stab in the panel will have power. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#18
Posted to alt.home.repair
|
|||
|
|||
220 to shop
Slim wrote:
John Hines wrote: Slim wrote: How big a 220 breaker can I use in the main panel in the house? 10ga copper is takes 30amp max. -- If I had something to say, this is where I'd say it. Thanks fro the advice, guys. Looks like I'll put a 20 or 30 amp breaker in the house and 20 or 30 amp outlet in the shop. Do I have to pound a ground rod in at garage to ground this puppy? Put a 6-space 100A main-lug panel in the garage and ground it with two ground rods. I don't remember the minimum spacing. The panel has to be rated for "Service Equipment", but most of them this size are. The grounded wire will serve as your neutral and ground (actually, you will make a new ground at the garage and tie it to the neutral.) Use a 30A 220 breaker in the house. This has to be the only circuit to the garage, so if there's another 110V circuit for the lights and one convenience outlet, you have to abandon that circuit. You don't need a main breaker in the garage panel. (You could use an 8-space panel but you can only use 6 circuits -- but a 240V circuit takes 2 spaces and only counts as one of your 6 maximum disconnect switches. Probably a moot point since you're only using a 30A feeder) You can't have any metal gas pipes or telephone or CATV wires connecting the house to the garage. Use GFCI outlets in the garage, or one GFCI outlet for each 110V circuit and connect the other outlets to its LOAD terminals. Best regards, Bob |
#19
Posted to alt.home.repair
|
|||
|
|||
220 to shop
zxcvbob wrote:
Put a 6-space 100A main-lug panel in the garage and ground it with two ground rods. I don't remember the minimum spacing. The panel has to be rated for "Service Equipment", but most of them this size are. The grounded wire will serve as your neutral and ground (actually, you will make a new ground at the garage and tie it to the neutral.) Use a 30A 220 breaker in the house. This has to be the only circuit to the garage, so if there's another 110V circuit for the lights and one convenience outlet, you have to abandon that circuit. You don't need a main breaker in the garage panel. (You could use an 8-space panel but you can only use 6 circuits -- but a 240V circuit takes 2 spaces and only counts as one of your 6 maximum disconnect switches. Probably a moot point since you're only using a 30A feeder) You can't have any metal gas pipes or telephone or CATV wires connecting the house to the garage. got coax and phone and network and alarm, am I screwed? What if I put just 1 30amp 220v outlet in the shop? Use GFCI outlets in the garage, or one GFCI outlet for each 110V circuit and connect the other outlets to its LOAD terminals. Best regards, Bob |
#20
Posted to alt.home.repair
|
|||
|
|||
220 to shop
Slim wrote:
zxcvbob wrote: [snip] You can't have any metal gas pipes or telephone or CATV wires connecting the house to the garage. got coax and phone and network and alarm, am I screwed? Yes. In that case, you'd have to have a proper subpanel with ground and neutral separated. How far is this? How much trouble would it be to run an 8-3 cable (or 6-3 aluminum) and have a nice 40A feeder with a separate ground and neutral conductors? What if I put just 1 30amp 220v outlet in the shop? As long as it's just a grounded 220v with no neutral wire. You could also put in a tiny subpanel (70A ?) so you could split that into two 15A or 20A circuits with proper overcurrent protection. And by doing that, if you trip a breaker it'll probably be one of 'em in the garage instead of the 30A in the house. Best regards, Bob |
#21
Posted to alt.home.repair
|
|||
|
|||
220 to shop
zxcvbob wrote:
Slim wrote: zxcvbob wrote: [snip] You can't have any metal gas pipes or telephone or CATV wires connecting the house to the garage. got coax and phone and network and alarm, am I screwed? Yes. In that case, you'd have to have a proper subpanel with ground and neutral separated. How far is this? about 50 ft How much trouble would it be to run an 8-3 cable (or 6-3 aluminum) and have a nice 40A feeder with a separate ground and neutral conductors? too much What if I put just 1 30amp 220v outlet in the shop? As long as it's just a grounded 220v with no neutral wire. that's the ticket You could also put in a tiny subpanel (70A ?) so you could split that into two 15A or 20A circuits with proper overcurrent protection. And by doing that, if you trip a breaker it'll probably be one of 'em in the garage instead of the 30A in the house. Best regards, Bob |
#22
Posted to alt.home.repair
|
|||
|
|||
220 to shop
zxcvbob wrote:
Slim wrote: John Hines wrote: Slim wrote: How big a 220 breaker can I use in the main panel in the house? 10ga copper is takes 30amp max. -- If I had something to say, this is where I'd say it. Thanks fro the advice, guys. Looks like I'll put a 20 or 30 amp breaker in the house and 20 or 30 amp outlet in the shop. Do I have to pound a ground rod in at garage to ground this puppy? Put a 6-space 100A main-lug panel in the garage and ground it with two ground rods. I don't remember the minimum spacing. The panel has to be rated for "Service Equipment", but most of them this size are. The grounded wire will serve as your neutral and ground (actually, you will make a new ground at the garage and tie it to the neutral.) Use a 30A 220 breaker in the house. This has to be the only circuit to the garage, so if there's another 110V circuit for the lights and one convenience outlet, you have to abandon that circuit. You don't need a main breaker in the garage panel. (You could use an 8-space panel but you can only use 6 circuits -- but a 240V circuit takes 2 spaces and only counts as one of your 6 maximum disconnect switches. Probably a moot point since you're only using a 30A feeder) You can't have any metal gas pipes or telephone or CATV wires connecting the house to the garage. Use GFCI outlets in the garage, or one GFCI outlet for each 110V circuit and connect the other outlets to its LOAD terminals. Best regards, Bob You can't use the bare ground wire as a neutral. If you have a garage subpanel, the supply ground wire goes to the ground bar. A grounding electrode is connected to the ground bar (usually 1 ground rod if measured under 25 ohms or 2 ground rods with no measurement). There is no neutral and only 220V loads can be connected. Use GFCI breakers. There can be other house-garage matalic paths - cable, .... bud-- |
#23
Posted to alt.home.repair
|
|||
|
|||
220 to shop
Bud-- wrote:
zxcvbob wrote: Slim wrote: John Hines wrote: Slim wrote: How big a 220 breaker can I use in the main panel in the house? 10ga copper is takes 30amp max. -- If I had something to say, this is where I'd say it. Thanks fro the advice, guys. Looks like I'll put a 20 or 30 amp breaker in the house and 20 or 30 amp outlet in the shop. Do I have to pound a ground rod in at garage to ground this puppy? Put a 6-space 100A main-lug panel in the garage and ground it with two ground rods. I don't remember the minimum spacing. The panel has to be rated for "Service Equipment", but most of them this size are. The grounded wire will serve as your neutral and ground (actually, you will make a new ground at the garage and tie it to the neutral.) Use a 30A 220 breaker in the house. This has to be the only circuit to the garage, so if there's another 110V circuit for the lights and one convenience outlet, you have to abandon that circuit. You don't need a main breaker in the garage panel. (You could use an 8-space panel but you can only use 6 circuits -- but a 240V circuit takes 2 spaces and only counts as one of your 6 maximum disconnect switches. Probably a moot point since you're only using a 30A feeder) You can't have any metal gas pipes or telephone or CATV wires connecting the house to the garage. Use GFCI outlets in the garage, or one GFCI outlet for each 110V circuit and connect the other outlets to its LOAD terminals. Best regards, Bob You can't use the bare ground wire as a neutral. If you have a garage subpanel, the supply ground wire goes to the ground bar. A grounding electrode is connected to the ground bar (usually 1 ground rod if measured under 25 ohms or 2 ground rods with no measurement). There is no neutral and only 220V loads can be connected. Use GFCI breakers. There can be other house-garage matalic paths - cable, .... bud-- I was telling him how to connect the existing cable as a service entrance, since the garage is detached. (not a great solution because the grounded wire in the feeder is bare) In a follow-up message OP said he does have other house-to-garage metal paths, so this doesn't work. Bob |
#24
Posted to alt.home.repair
|
|||
|
|||
220 to shop
Well he could run the 240 and use a transformer for 120
|
#25
Posted to alt.home.repair
|
|||
|
|||
220 to shop
"Doug Miller" wrote in message m... In article , "digitalmaster" wrote: you use the bare wire as the neutral WRONG. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. try again...shop has been running 220 volt on 3 wire for over 15 years now. |
#26
Posted to alt.home.repair
|
|||
|
|||
220 to shop
wrote in message ... On Tue, 25 Apr 2006 22:09:06 -0400, "digitalmaster" wrote: try again...shop has been running 220 volt on 3 wire for over 15 years now. Lots of things that "work" are not legal. Don't understand why 3 wire to a detached structure is not legal in your area. Mine was inspected and approved. The detached structure must have its own ground rod. |
#27
Posted to alt.home.repair
|
|||
|
|||
220 to shop
In article , "digitalmaster" wrote:
"Doug Miller" wrote in message om... In article , "digitalmaster" wrote: you use the bare wire as the neutral WRONG. try again...shop has been running 220 volt on 3 wire for over 15 years now. Doesn't matter whether it works or not, it's still a Code violation. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#28
Posted to alt.home.repair
|
|||
|
|||
220 to shop
In article , "calhoun" wrote:
wrote in message .. . On Tue, 25 Apr 2006 22:09:06 -0400, "digitalmaster" wrote: try again...shop has been running 220 volt on 3 wire for over 15 years now. Lots of things that "work" are not legal. Don't understand why 3 wire to a detached structure is not legal in your area. Mine was inspected and approved. The detached structure must have its own ground rod. In service-entrance cable, or overhead triplex, it's ok. In NM cable, it's absolutely not ok. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#29
Posted to alt.home.repair
|
|||
|
|||
220 to shop
"Doug Miller" wrote in message et... In article , "calhoun" wrote: wrote in message . .. On Tue, 25 Apr 2006 22:09:06 -0400, "digitalmaster" wrote: try again...shop has been running 220 volt on 3 wire for over 15 years now. Lots of things that "work" are not legal. Don't understand why 3 wire to a detached structure is not legal in your area. Mine was inspected and approved. The detached structure must have its own ground rod. In service-entrance cable, or overhead triplex, it's ok. In NM cable, it's absolutely not ok. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. inspector in monroe county georgia says it is fine as long as sub panel is grounded. |
#30
Posted to alt.home.repair
|
|||
|
|||
220 to shop
Piggy back question on this shop thing...........I have a 220 line on 10ga
3wire plus ground on a 30 amp breaker coming from the main panel to the detached garage; there is no in ground rod. It is split down to 3/ 110 outlets to run the door opener and 2 15 amp receptacles. I assume that this is not up to any code. I happen to have a 20 slot panel with 100 A main breaker and numerous 15-20 A breakers that remain from a recent upgrade to 200 Amp service. What do I need to do to get this set up properly and can I use the panel I have? Thanks. "zxcvbob" wrote in message ... Slim wrote: John Hines wrote: Slim we rote: How big a 220 breaker can I use in the main panel in the house? 10ga copper is takes 30amp max. -- If I had something to say, this is where I'd say it. Thanks fro the advice, guys. Looks like I'll put a 20 or 30 amp breaker in the house and 20 or 30 amp outlet in the shop. Do I have to pound a ground rod in at garage to ground this puppy? Put a 6-space 100A main-lug panel in the garage and ground it with two ground rods. I don't remember the minimum spacing. The panel has to be rated for "Service Equipment", but most of them this size are. The grounded wire will serve as your neutral and ground (actually, you will make a new ground at the garage and tie it to the neutral.) Use a 30A 220 breaker in the house. This has to be the only circuit to the garage, so if there's another 110V circuit for the lights and one convenience outlet, you have to abandon that circuit. You don't need a main breaker in the garage panel. (You could use an 8-space panel but you can only use 6 circuits -- but a 240V circuit takes 2 spaces and only counts as one of your 6 maximum disconnect switches. Probably a moot point since you're only using a 30A feeder) You can't have any metal gas pipes or telephone or CATV wires connecting the house to the garage. Use GFCI outlets in the garage, or one GFCI outlet for each 110V circuit and connect the other outlets to its LOAD terminals. Best regards, Bob |
#31
Posted to alt.home.repair
|
|||
|
|||
220 to shop
On Wed, 26 Apr 2006 07:53:06 -0400, "digitalmaster"
wrote: "Doug Miller" wrote in message . net... In article , "calhoun" wrote: wrote in message ... try again...shop has been running 220 volt on 3 wire for over 15 years now. inspector in monroe county georgia says it is fine as long as sub panel is grounded. The source of the confusion is that you started out by claiming you were using the bare ground as nuetral, (which is illegal and dangerous) and now suddenly you have an independant ground at the service entrance to the detached structure, and NO nuetral between the two buildings. |
#32
Posted to alt.home.repair
|
|||
|
|||
220 to shop
Piggy back question on this shop thing...........I have a 220 line on 10ga 3wire plus ground on a 30 amp breaker coming from the main panel to the detached garage; there is no in ground rod. It is split down to 3/ 110 outlets to run the door opener and 2 15 amp receptacles. I assume that this is not up to any code. I happen to have a 20 slot panel with 100 A main breaker and numerous 15-20 A breakers that remain from a recent upgrade to 200 Amp service. What do I need to do to get this set up properly and can I use the panel I have? Thanks. The only actual problem is that you have the shop-wiring and outlets "protected" by a 30A breaker. The EASIEST fix would be to replace the 30A 2-pole breaker with a 20A or 15A 2-pole breaker, depending on the guage of the garage wiring. But you probably want all 660 volt-amps, which means feeding a sub-panel in the garage, so you can stick smaller breakers on the individual circuts there. (Actually, my house has a ceramic thingamajig with two 15-A fuses in it, which does pretty much the same thing, but since it's not in a box, I assume it no longer meets code.) You should be able to use the panel you have, but you'll probably have to buy another buss-bar for the nuetrals. The two hots go to the main breaker in the sub-panel, The ground goes to a bround-bar in the panel, and the nuetral goes to a separate nuetral bar in the panel. The two bars should NOT be connected, and the nuetral-bar should be isolated from the box. Then you just put in normal breakers for each local circut. |
#33
Posted to alt.home.repair
|
|||
|
|||
220 to shop
|
#34
Posted to alt.home.repair
|
|||
|
|||
220 to shop
|
#35
Posted to alt.home.repair
|
|||
|
|||
220 to shop
In article , Tom The Great wrote:
On Wed, 26 Apr 2006 11:43:07 GMT, (Doug Miller) wrote: In article , "digitalmaster" wrote: "Doug Miller" wrote in message .com... In article , "digitalmaster" wrote: you use the bare wire as the neutral WRONG. try again...shop has been running 220 volt on 3 wire for over 15 years now. Doesn't matter whether it works or not, it's still a Code violation. Worse, could kill someone. Which is why it's a Code violation. :-) -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#36
Posted to alt.home.repair
|
|||
|
|||
220 to shop
|
#38
Posted to alt.home.repair
|
|||
|
|||
220 to shop
"Goedjn" wrote in message ... On Wed, 26 Apr 2006 07:53:06 -0400, "digitalmaster" wrote: "Doug Miller" wrote in message .net... In article , "calhoun" wrote: wrote in message m... try again...shop has been running 220 volt on 3 wire for over 15 years now. inspector in monroe county georgia says it is fine as long as sub panel is grounded. The source of the confusion is that you started out by claiming you were using the bare ground as nuetral, (which is illegal and dangerous) and now suddenly you have an independant ground at the service entrance to the detached structure, and NO nuetral between the two buildings. i clearly stated in my first post about the ground at the shop panel.Soryy i used the word nuetral..but that is how it is connected...the nuetral and ground are bonded at the panel. |
#39
Posted to alt.home.repair
|
|||
|
|||
220 to shop
digitalmaster posted for all of us...
I don't top post - see either inline or at bottom. you use the bare wire as the neutral..but you must have another panel in the shop with an earth ground. BZZZT you lose; next contestant please. -- My boss said I was dumb and apathetic. I said I don't know and I don't care... Tekkie |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Was Shop heat---update | Metalworking | |||
Radiant Heat, Shop related | Metalworking | |||
What projects did you make in HS woodshop class? | Woodworking | |||
Machine and Fab Shop Space Leased! | Metalworking | |||
OT (kinda) High School Wood Shop | Woodworking |