Default New Hot Tub -- Electrical Supply Dilemma

I just purchased a new 5-person, 22 jet, 5 HP (no blower) hot tub that
recommends 200 Amp service. I only have 100 Amp service to my house.
Does anyone have any recommendations? The place that sold me the tub
said to get a spa box, but if my household electrical supply can't
handle the load, will a spa box really help?

  #2   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default New Hot Tub -- Electrical Supply Dilemma

My best guess is that they recommend a 200 Amp service so that when the
50 amp spa is running, there is some power left for the rest of the
house. With 100amps, it will work, but you you're taking close to half
of the capacity for one appliance. And I agree, 5hp sounds mighty high
for a spa pump.

If you can't live with 50 amps for the rest of the house, or need to
expand the panel for breaker space, etc, then it's time to upgrade the
service.

  #3   Report Post  
Posted to alt.home.repair
Toller
 
Posts: n/a
Default New Hot Tub -- Electrical Supply Dilemma


wrote in message
ups.com...
I just purchased a new 5-person, 22 jet, 5 HP (no blower) hot tub that
recommends 200 Amp service. I only have 100 Amp service to my house.
Does anyone have any recommendations? The place that sold me the tub
said to get a spa box, but if my household electrical supply can't
handle the load, will a spa box really help?

I am guessing a spa box is a subpanel? Won't make any difference one way or
another.
Possibly the hot tub used enough electricity that the manufacturer makes the
assumption that you will not have enough extra unless you have a 200a
service.

That is a little silly; only by checking out your service can you determine
if you have enough.
Odds are if you have your oven and airconditioner on at the same time it
will trip the main breaker; and if you have it on with nothing else big
going you will be okay.

100a is rather small; if you have a house full of electrical devices you
should be looking to upgrade.


  #4   Report Post  
Posted to alt.home.repair
PipeDown
 
Posts: n/a
Default New Hot Tub -- Electrical Supply Dilemma


wrote in message
ups.com...
My best guess is that they recommend a 200 Amp service so that when the
50 amp spa is running, there is some power left for the rest of the
house. With 100amps, it will work, but you you're taking close to half
of the capacity for one appliance. And I agree, 5hp sounds mighty high
for a spa pump.

If you can't live with 50 amps for the rest of the house, or need to
expand the panel for breaker space, etc, then it's time to upgrade the
service.


I agree, run the hottub and turn on the oven and you might trip the main
(even though neither branch exceeds its load). Add in the dryer or A/C and
you will for sure.

Its a shame they don't make conversion kits to run off a 5HP lawn mower
engine. 5 persons and 22 jets sounds like a real wet party, with all that
water in the pipes, starting torque would be quite high.


  #5   Report Post  
Posted to alt.home.repair
bluelagoon
 
Posts: n/a
Default New Hot Tub -- Electrical Supply Dilemma

Check inside your hot tub near the computer controller/ eletric pump
area, there should be a small metal plate stamped with the
manufacturers minimum amp breaker requirement...likely 50 amps in your
case. If your 100 Amp breaker box has the room for a 220 volt GCFI
breaker then you should be OK. Most homes under 2.000 square feet have
a 100 amp service panel.

Most important of all you must use a GCFI breaker!!! (Ground Circuit
Fault Interrupt)

GCFI breakers are quite expensive (usually $150 or more) , however,
it's mandatory, as this is required by law to prevent electrocution due
to a possible ground fault event. It will trip the breaker at even a
hint of ground fault/leakage.

Also, there should be a separate power/switch box (Spa Box) within 10
feet of the Hot tub so as to be able shut the power-off in an
emergency.

Check you local city building code for requirements in your area.



  #6   Report Post  
Posted to alt.home.repair
tom
 
Posts: n/a
Default New Hot Tub -- Electrical Supply Dilemma

Bluelaggon wrote: Also, there should be a separate power/switch box
(Spa Box) within 10
feet of the Hot tub so as to be able shut the power-off in an
emergency.


But no closer than 5 feet, per NEC. Tom

  #7   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default New Hot Tub -- Electrical Supply Dilemma


Bud-- wrote:
tom wrote:

Bluelaggon wrote: Also, there should be a separate power/switch box
(Spa Box) within 10
feet of the Hot tub so as to be able shut the power-off in an
emergency.


But no closer than 5 feet, per NEC. Tom


NEC is 5 ft min. (as per Tom - point is far enough to avoid contact with
water and electrical). That is generally true for all electrical.

Also readily accessible and in sight of, not necessarily 10 ft.

Appears to not be required for single family dwelling but may? be
required for outside.

There are quite a few requirements for a hot tub which may affect nearby
unrelated wiring or metal that may become energized.

bud--



I think the requirement for a nearby disconnect was added after a local
fatality here in NJ. A fat bottom girl drowned during a high school
party at a local health club. The large spa had only one suction
intake on the bottom. She got stuck on it and despite lots of people
trying to pull her loose, they couldn't. The only disconnect was back
at the electrical panel and no one knew how to shut the thing off.
This thing had two flaws, no obvious shut off and having only one main
intake.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
OT Electrical John Emmons Woodworking 13 September 6th 05 04:47 PM
A very long electrical supply to garden shed Cordless Crazy UK diy 8 August 26th 05 09:54 AM
Copper vs. aluminum electrical supply Jeffrey J. Kosowsky Home Repair 21 November 5th 04 01:45 AM
Outdoor Electrical Supply mike. buckley UK diy 14 May 26th 04 02:40 PM
LV Lighting supply dilemma andrewpreece UK diy 7 January 6th 04 05:29 PM


All times are GMT +1. The time now is 07:29 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"