We are about to upgrade our panel from 100A to 200A.
The run from the electric company drop to the panel is about 15 ft
vertical drop followed by 30 feet horizontal run within the house.

- Other than the fact that copper costs much more than aluminum, what
are the pros/cons of copper vs. aluminum?

- Is copper worth the added cost?

- Also, the supply will run through the unfinished utility portion of
the basement at joist level. Is it worth it to encase the cable in
metal (or pvc) conduit?

  #2   Report Post  
w_tom
 
Posts: n/a
Default

Running a service wire that far inside the building means it
must be in conduit. You have no choice. More important
question is how big a conduit must be so that you can run
those cables. Other important factors - don't drive holes
through structural supporting members (ie joists) for a
conduit that large. Many utilities have specific requirements
on everything from size of conduit to what kind of cutoff box
is permitted. But then if you have first consulted the
electric company, then these facts, unique requirements
demanded by each utility, were already provided.

"Jeffrey J. Kosowsky" wrote:
We are about to upgrade our panel from 100A to 200A.
The run from the electric company drop to the panel is about 15 ft
vertical drop followed by 30 feet horizontal run within the house.

- Other than the fact that copper costs much more than aluminum, what
are the pros/cons of copper vs. aluminum?

- Is copper worth the added cost?

- Also, the supply will run through the unfinished utility portion of
the basement at joist level. Is it worth it to encase the cable in
metal (or pvc) conduit?

  #3   Report Post  
TURTLE
 
Posts: n/a
Default


"Jeffrey J. Kosowsky" wrote in message
...
We are about to upgrade our panel from 100A to 200A.
The run from the electric company drop to the panel is about 15 ft
vertical drop followed by 30 feet horizontal run within the house.

- Other than the fact that copper costs much more than aluminum, what
are the pros/cons of copper vs. aluminum?

- Is copper worth the added cost?

- Also, the supply will run through the unfinished utility portion of
the basement at joist level. Is it worth it to encase the cable in
metal (or pvc) conduit?


This is Turtle.

If you ask about the electric service being in conduit between the service
entrance and the main service box. I sure hope your going to get a Electrician
to do this job. Yes it must be encased.

Aluminum is ok but Copper is better in the long run for joints getting loose or
having connection burning off. Al. is called the poor man's wire.

TURTLE


  #4   Report Post  
Jeffrey J. Kosowsky
 
Posts: n/a
Default

"TURTLE" writes:
"Jeffrey J. Kosowsky" wrote in message
...
We are about to upgrade our panel from 100A to 200A.
The run from the electric company drop to the panel is about 15 ft
vertical drop followed by 30 feet horizontal run within the house.

- Other than the fact that copper costs much more than aluminum, what
are the pros/cons of copper vs. aluminum?

- Is copper worth the added cost?

- Also, the supply will run through the unfinished utility portion of
the basement at joist level. Is it worth it to encase the cable in
metal (or pvc) conduit?


This is Turtle.

If you ask about the electric service being in conduit between the service
entrance and the main service box. I sure hope your going to get a Electrician
to do this job. Yes it must be encased.


That's interesting.... because the current 100A service doesn't appear
to be conduit -- it appears to be just a fat (2x1 inch oval), gray
flexible wire.

Also, I asked our electrician who said you can always pay extra to put
in rigid conduit but it is not necessary. BTW both the electrician who
did the original job and the current electrician are licensed. Also,
the house passed inspection.

Maybe the wire is in some type of flexible plastic conduit that looks
just like wire


  #5   Report Post  
TURTLE
 
Posts: n/a
Default


"Jeffrey J. Kosowsky" wrote in message
...
"TURTLE" writes:
"Jeffrey J. Kosowsky" wrote in message
...
We are about to upgrade our panel from 100A to 200A.
The run from the electric company drop to the panel is about 15 ft
vertical drop followed by 30 feet horizontal run within the house.

- Other than the fact that copper costs much more than aluminum, what
are the pros/cons of copper vs. aluminum?

- Is copper worth the added cost?

- Also, the supply will run through the unfinished utility portion of
the basement at joist level. Is it worth it to encase the cable in
metal (or pvc) conduit?


This is Turtle.

If you ask about the electric service being in conduit between the service
entrance and the main service box. I sure hope your going to get a
Electrician
to do this job. Yes it must be encased.


That's interesting.... because the current 100A service doesn't appear
to be conduit -- it appears to be just a fat (2x1 inch oval), gray
flexible wire.

Also, I asked our electrician who said you can always pay extra to put
in rigid conduit but it is not necessary. BTW both the electrician who
did the original job and the current electrician are licensed. Also,
the house passed inspection.

Maybe the wire is in some type of flexible plastic conduit that looks
just like wire


This is Turtle.

It was done by a friend or a None Electician before the codes were inforced in
your area.

TURTLE




  #6   Report Post  
Jeffrey J. Kosowsky
 
Posts: n/a
Default

"TURTLE" writes:

"Jeffrey J. Kosowsky" wrote in message
...
"TURTLE" writes:
"Jeffrey J. Kosowsky" wrote in message
...
We are about to upgrade our panel from 100A to 200A.
The run from the electric company drop to the panel is about 15 ft
vertical drop followed by 30 feet horizontal run within the house.

- Other than the fact that copper costs much more than aluminum, what
are the pros/cons of copper vs. aluminum?

- Is copper worth the added cost?

- Also, the supply will run through the unfinished utility portion of
the basement at joist level. Is it worth it to encase the cable in
metal (or pvc) conduit?


This is Turtle.

If you ask about the electric service being in conduit between the service
entrance and the main service box. I sure hope your going to get a
Electrician
to do this job. Yes it must be encased.


That's interesting.... because the current 100A service doesn't appear
to be conduit -- it appears to be just a fat (2x1 inch oval), gray
flexible wire.

Also, I asked our electrician who said you can always pay extra to put
in rigid conduit but it is not necessary. BTW both the electrician who
did the original job and the current electrician are licensed. Also,
the house passed inspection.

Maybe the wire is in some type of flexible plastic conduit that looks
just like wire


This is Turtle.

It was done by a friend or a None Electician before the codes were inforced in
your area.


No, house was just inspected. Electrician is licensed and no
relationship. Again, I am just stating the facts, not arguing code or
not code. Also, maybe this stuff that looks like wire counts as conduit.
  #7   Report Post  
zxcvbob
 
Posts: n/a
Default

Jeffrey J. Kosowsky wrote:
"TURTLE" writes:


"Jeffrey J. Kosowsky" wrote in message
...

"TURTLE" writes:

"Jeffrey J. Kosowsky" wrote in message
...

We are about to upgrade our panel from 100A to 200A.
The run from the electric company drop to the panel is about 15 ft
vertical drop followed by 30 feet horizontal run within the house.

- Other than the fact that copper costs much more than aluminum, what
are the pros/cons of copper vs. aluminum?

- Is copper worth the added cost?

- Also, the supply will run through the unfinished utility portion of
the basement at joist level. Is it worth it to encase the cable in
metal (or pvc) conduit?


This is Turtle.

If you ask about the electric service being in conduit between the service
entrance and the main service box. I sure hope your going to get a
Electrician
to do this job. Yes it must be encased.

That's interesting.... because the current 100A service doesn't appear
to be conduit -- it appears to be just a fat (2x1 inch oval), gray
flexible wire.

Also, I asked our electrician who said you can always pay extra to put
in rigid conduit but it is not necessary. BTW both the electrician who
did the original job and the current electrician are licensed. Also,
the house passed inspection.

Maybe the wire is in some type of flexible plastic conduit that looks
just like wire


This is Turtle.

It was done by a friend or a None Electician before the codes were inforced in
your area.



No, house was just inspected. Electrician is licensed and no
relationship. Again, I am just stating the facts, not arguing code or
not code. Also, maybe this stuff that looks like wire counts as conduit.



That's service entrance cable (SE), and it does not need to be run in a
conduit -- in fact, I don't think you're allowed to run it in a conduit.

I don't know about the 30 feet run of it inside the house, unless you
have a disconnect at the meter (and even then I don't know if you can
use SE for that long of a run.)

Bob
  #8   Report Post  
John Grabowski
 
Posts: n/a
Default

Here in New Jersey on a single family residence the 30' of wire does not
have to be in conduit, but it must be protected by a circuit breaker or
fused switch located just below the meter. On larger services for
commercial or industrial buildings it would have to be in conduit encased by
2" of concrete all around.

If aluminum is installed correctly you shouldn't have any problems for a
long time, but copper is still a better choice.

There is no reason to use conduit unless you anticipate the cable becoming
subject to abuse.


John Grabowski
http://www.mrelectrician.tv



"Jeffrey J. Kosowsky" wrote in message
...
We are about to upgrade our panel from 100A to 200A.
The run from the electric company drop to the panel is about 15 ft
vertical drop followed by 30 feet horizontal run within the house.

- Other than the fact that copper costs much more than aluminum, what
are the pros/cons of copper vs. aluminum?

- Is copper worth the added cost?

- Also, the supply will run through the unfinished utility portion of
the basement at joist level. Is it worth it to encase the cable in
metal (or pvc) conduit?



  #9   Report Post  
TURTLE
 
Posts: n/a
Default


"zxcvbob" wrote in message
...
Jeffrey J. Kosowsky wrote:
"TURTLE" writes:


"Jeffrey J. Kosowsky" wrote in message
...

"TURTLE" writes:

"Jeffrey J. Kosowsky" wrote in message
...

We are about to upgrade our panel from 100A to 200A.
The run from the electric company drop to the panel is about 15 ft
vertical drop followed by 30 feet horizontal run within the house.

- Other than the fact that copper costs much more than aluminum, what
are the pros/cons of copper vs. aluminum?

- Is copper worth the added cost?

- Also, the supply will run through the unfinished utility portion of
the basement at joist level. Is it worth it to encase the cable in
metal (or pvc) conduit?


This is Turtle.

If you ask about the electric service being in conduit between the service
entrance and the main service box. I sure hope your going to get a
Electrician
to do this job. Yes it must be encased.

That's interesting.... because the current 100A service doesn't appear
to be conduit -- it appears to be just a fat (2x1 inch oval), gray
flexible wire.

Also, I asked our electrician who said you can always pay extra to put
in rigid conduit but it is not necessary. BTW both the electrician who
did the original job and the current electrician are licensed. Also,
the house passed inspection.

Maybe the wire is in some type of flexible plastic conduit that looks
just like wire


This is Turtle.

It was done by a friend or a None Electician before the codes were inforced
in your area.



No, house was just inspected. Electrician is licensed and no
relationship. Again, I am just stating the facts, not arguing code or
not code. Also, maybe this stuff that looks like wire counts as conduit.



That's service entrance cable (SE), and it does not need to be run in a
conduit -- in fact, I don't think you're allowed to run it in a conduit.

I don't know about the 30 feet run of it inside the house, unless you have a
disconnect at the meter (and even then I don't know if you can use SE for that
long of a run.)

Bob


This is Turtle.

This is new to me of using SE cable in a basement to connect the meter pan to
the switch box and also going one end of the basement to the other in open air.
If you would have a short in the SE cable before getting to the switch box the
only breaker you would have is the 1,000+ amp breaker for the transformer to
protect it. Like you said , The only way I could see this would be a 200 amp
breaker & disconnect at meter pan to protect it before it gets to the switch
box. I will have to pass this by my City inspector on SE cable run in open air
30 something feet in a basement and being before the switch box main and after
the Meter pan. I would not want this in my house but NEC and city codes do let
some funny things go by that I would not want , like Al. Wire for lighting
circuits.

TURTLE


  #10   Report Post  
Chris Lewis
 
Posts: n/a
Default

According to John Grabowski :
Here in New Jersey on a single family residence the 30' of wire does not
have to be in conduit, but it must be protected by a circuit breaker or
fused switch located just below the meter. On larger services for
commercial or industrial buildings it would have to be in conduit encased by
2" of concrete all around.


Here in Canada, ordinary NMD is perfectly code-acceptable for this, but, yup,
you MUST have a breaker/fuse box within 5' of the cable entering the
house.

[There are _occasionally_ variations allowed, but you have to get prior
permission from the inspector.]

If aluminum is installed correctly you shouldn't have any problems for a
long time, but copper is still a better choice.


Given costs that I last saw for wire this size, 30' would be about the most
I'd go with copper before I'd consider using Al.

There is no reason to use conduit unless you anticipate the cable becoming
subject to abuse.


Same here.
--
Chris Lewis, Una confibula non set est
It's not just anyone who gets a Starship Cruiser class named after them.


  #11   Report Post  
zxcvbob
 
Posts: n/a
Default

TURTLE wrote:
"zxcvbob" wrote in message
...

Jeffrey J. Kosowsky wrote:

"TURTLE" writes:



"Jeffrey J. Kosowsky" wrote in message
...


"TURTLE" writes:


"Jeffrey J. Kosowsky" wrote in message
...


We are about to upgrade our panel from 100A to 200A.
The run from the electric company drop to the panel is about 15 ft
vertical drop followed by 30 feet horizontal run within the house.

- Other than the fact that copper costs much more than aluminum, what
are the pros/cons of copper vs. aluminum?

- Is copper worth the added cost?

- Also, the supply will run through the unfinished utility portion of
the basement at joist level. Is it worth it to encase the cable in
metal (or pvc) conduit?


This is Turtle.

If you ask about the electric service being in conduit between the service
entrance and the main service box. I sure hope your going to get a
Electrician
to do this job. Yes it must be encased.

That's interesting.... because the current 100A service doesn't appear
to be conduit -- it appears to be just a fat (2x1 inch oval), gray
flexible wire.

Also, I asked our electrician who said you can always pay extra to put
in rigid conduit but it is not necessary. BTW both the electrician who
did the original job and the current electrician are licensed. Also,
the house passed inspection.

Maybe the wire is in some type of flexible plastic conduit that looks
just like wire


This is Turtle.

It was done by a friend or a None Electician before the codes were inforced
in your area.


No, house was just inspected. Electrician is licensed and no
relationship. Again, I am just stating the facts, not arguing code or
not code. Also, maybe this stuff that looks like wire counts as conduit.



That's service entrance cable (SE), and it does not need to be run in a
conduit -- in fact, I don't think you're allowed to run it in a conduit.

I don't know about the 30 feet run of it inside the house, unless you have a
disconnect at the meter (and even then I don't know if you can use SE for that
long of a run.)

Bob



This is Turtle.

This is new to me of using SE cable in a basement to connect the meter pan to
the switch box and also going one end of the basement to the other in open air.
If you would have a short in the SE cable before getting to the switch box the
only breaker you would have is the 1,000+ amp breaker for the transformer to
protect it. Like you said , The only way I could see this would be a 200 amp
breaker & disconnect at meter pan to protect it before it gets to the switch
box. I will have to pass this by my City inspector on SE cable run in open air
30 something feet in a basement and being before the switch box main and after
the Meter pan. I would not want this in my house but NEC and city codes do let
some funny things go by that I would not want , like Al. Wire for lighting
circuits.

TURTLE



I woudn't want it in my house either.

I was just tryin' to help identify what the OP has. If the service
conductors run more than 10' inside the house before they get to the
panel, there's gotta be an OPD (breaker or fuses) outside the house. I
don't think there's a limit to how far you can run the service
conductors outside the house without an OPD, but I've never needed to
look it up yet.

Bob
  #12   Report Post  
Greg
 
Posts: n/a
Default

From the 2002 NEC handbook
No maximum distance is specified from the point of entrance of service
conductors to a readily accessible location for the installation of a service
disconnecting means. The authority enforcing this Code has the responsibility
for, and is charged with, making the decision as to how far inside the building
the service-entrance conductors are allowed to travel to the main disconnecting
means. The length of service-entrance conductors should be kept to a minimum
inside buildings, because power utilities provide limited overcurrent
protection and, in the event of a fault, the service conductors could ignite
nearby combustible materials.
Some local jurisdictions have ordinances that allow service-entrance conductors
to run within the building up to a specified length to terminate at the
disconnecting means. The authority having jurisdiction may permit service
conductors to bypass fuel storage tanks or gas meters and the like, permitting
the service disconnecting means to be located in a readily accessible location.
However, if the authority judges the distance as being excessive, the
disconnecting means may be required to be located on the outside of the
building or near the building at a readily accessible location that is not
necessarily nearest the point of entrance of the conductors. See also 230.6 and
Exhibit 230.15 for conductors considered to be outside a building.
  #13   Report Post  
bill a
 
Posts: n/a
Default

i'm curious why you are running the 200a SE cable so far inside the house.
my guess is that you are doing the new entrance in a different location than
where the old service was, and you will be putting the new panel where the
old one was, in order to reconnect branch circuits.
if so, you might consider putting the new panel just inside the building
(like normal), and then make a feeder run of #2 or 0, whatever, over to the
old panel. You don't necessarily need 100a ampacity on this run, as long as
the breaker size protects the feeder wire. Depending on what's in use on
the old branch circuits, you may be able to feed with quite a bit less than
100a.
Then feed new branch circuits out of the new panel.
Just a thought.
Bill

"Jeffrey J. Kosowsky" wrote in message
...
We are about to upgrade our panel from 100A to 200A.
The run from the electric company drop to the panel is about 15 ft
vertical drop followed by 30 feet horizontal run within the house.

- Other than the fact that copper costs much more than aluminum, what
are the pros/cons of copper vs. aluminum?

- Is copper worth the added cost?

- Also, the supply will run through the unfinished utility portion of
the basement at joist level. Is it worth it to encase the cable in
metal (or pvc) conduit?


  #14   Report Post  
Jeffrey J. Kosowsky
 
Posts: n/a
Default

"bill a" writes:

i'm curious why you are running the 200a SE cable so far inside the
house. my guess is that you are doing the new entrance in a different
location than where the old service was, and you will be putting the
new panel where the old one was, in order to reconnect branch circuits.
if so, you might consider putting the new panel just inside the
building (like normal), and then make a feeder run of #2 or 0,
whatever, over to the old panel. You don't necessarily need 100a
ampacity on this run, as long as the breaker size protects the feeder
wire. Depending on what's in use on the old branch circuits, you may
be able to feed with quite a bit less than 100a.
Then feed new branch circuits out of the new panel.
Just a thought.
Bill


Well, this is the way the old feed went. It enters the house at one
end, goes through a 100A main breaker and then goes about 30 feet to
the other end of the house where the main 100A panel is.

We thought of various alternatives for the upgrade including:
1. Placing panel at entrance and moving all circuits to this new panel
-- however, then we would need to rewire all the branch circuits or
have some type of nasty junction box replacing the old panel

2. Placing a new 200A panel at the entrance and converting the old
panel into a 100A subpanel
-- however, we thought this might confusing and a PITA having the
two panels separated by the length of the house. Especially,
since given the mix of old and new wiring two circuits feeding
the same room could end up in different panels 30 ft away from
each other.

Therefore, we are planning instead to consolidate all the circuits at
the location of the old panel. In doing this we considered two
options:

A. Place new large 200A panel next to the old panel and convert the
old 100A panel into a subpanel of the new panel. This would mean
leaving the bulk of the circuits in the old panel and keeping the
new main panel mostly unpopulated (but likely to fill in over
time).
-- we chose not to do this since this seems a little kludgey with
the subpanel having more circuits than our new main panel

B. Instead, we are planning to replace the old 30 circuit 100A panel
with a new 42 circuit 200A panel in place which requires a bit more
effort to move over the breakers and reattach neutrals and
grounds. Then, we will move the old 100A panel to a location next
to the new 200A panel to hold any circuits after we run out of
space in the new panel.

Finally, rather than having a meter outside, then a main breaker just
inside, and then a 30 ft run over to the panels, we are thinking about
placing a combo meter/breaker unit outside replacing our old meter and
then entering the house and running 30 feet directly over to the new
panel. This has the benefit:
- Reducing costs (since no need for separate main breaker just
inside the house)
- Eliminating "extra" box inside the house
- Allowing fire dept easy access to electrical shutoff in case
of emergency

Does this thinking make sense??

Jeff
  #15   Report Post  
Wayne Whitney
 
Posts: n/a
Default

On 2004-11-03, Jeffrey J. Kosowsky wrote:

Finally, rather than having a meter outside, then a main breaker
just inside, and then a 30 ft run over to the panels, we are
thinking about placing a combo meter/breaker unit outside replacing
our old meter and then entering the house and running 30 feet
directly over to the new panel.


My understanding is that by having an exterior main breaker (shutoff),
the interior panel is considered a subpanel, and so the conductors
leading to it are feeders, not service conductors. I have a similar
situated, I elected to use 1/0 Al SER cable as my feeder cable; it is
stapled to the underside of the joists in my crawl space.

Cheers, Wayne



  #16   Report Post  
Jeffrey J. Kosowsky
 
Posts: n/a
Default

Wayne Whitney writes:
On 2004-11-03, Jeffrey J. Kosowsky wrote:

Finally, rather than having a meter outside, then a main breaker
just inside, and then a 30 ft run over to the panels, we are
thinking about placing a combo meter/breaker unit outside replacing
our old meter and then entering the house and running 30 feet
directly over to the new panel.


My understanding is that by having an exterior main breaker (shutoff),
the interior panel is considered a subpanel, and so the conductors
leading to it are feeders, not service conductors. I have a similar
situated, I elected to use 1/0 Al SER cable as my feeder cable; it is
stapled to the underside of the joists in my crawl space.

Cheers, Wayne


I believe you are correct technically -- sorry for my misleading "lay"
use of the word "supply" when feeder (and subpanel) were more
technically correct.
  #17   Report Post  
Joe Fabeitz
 
Posts: n/a
Default

You don't know what area he's in so how do you know what the codes are
there?
"TURTLE" wrote in message
...

"Jeffrey J. Kosowsky" wrote in message
...
"TURTLE" writes:
"Jeffrey J. Kosowsky" wrote in message
...
We are about to upgrade our panel from 100A to 200A.
The run from the electric company drop to the panel is about 15 ft
vertical drop followed by 30 feet horizontal run within the house.

- Other than the fact that copper costs much more than aluminum, what
are the pros/cons of copper vs. aluminum?

- Is copper worth the added cost?

- Also, the supply will run through the unfinished utility portion of
the basement at joist level. Is it worth it to encase the cable in
metal (or pvc) conduit?


This is Turtle.

If you ask about the electric service being in conduit between the

service
entrance and the main service box. I sure hope your going to get a
Electrician
to do this job. Yes it must be encased.


That's interesting.... because the current 100A service doesn't appear
to be conduit -- it appears to be just a fat (2x1 inch oval), gray
flexible wire.

Also, I asked our electrician who said you can always pay extra to put
in rigid conduit but it is not necessary. BTW both the electrician who
did the original job and the current electrician are licensed. Also,
the house passed inspection.

Maybe the wire is in some type of flexible plastic conduit that looks
just like wire


This is Turtle.

It was done by a friend or a None Electician before the codes were

inforced in
your area.

TURTLE




  #18   Report Post  
TURTLE
 
Posts: n/a
Default


"Joe Fabeitz" wrote in message
. ..
You don't know what area he's in so how do you know what the codes are
there?


This is Turtle.

I know it is a problem for NEC and the International Mechnical Code would not
allow this without a breaker before the switch box. All 50 use these codes and
stick by them. Now he could be in Mexico or Canada and i could be wrong.

TURTLE


  #19   Report Post  
HA HA Budys Here
 
Posts: n/a
Default

(Jeffrey J. Kosowsky)


"bill a" writes:

i'm curious why you are running the 200a SE cable so far inside the
house. my guess is that you are doing the new entrance in a different
location than where the old service was, and you will be putting the
new panel where the old one was, in order to reconnect branch circuits.
if so, you might consider putting the new panel just inside the
building (like normal), and then make a feeder run of #2 or 0,
whatever, over to the old panel. You don't necessarily need 100a
ampacity on this run, as long as the breaker size protects the feeder
wire. Depending on what's in use on the old branch circuits, you may
be able to feed with quite a bit less than 100a.
Then feed new branch circuits out of the new panel.
Just a thought.
Bill


Well, this is the way the old feed went. It enters the house at one
end, goes through a 100A main breaker and then goes about 30 feet to
the other end of the house where the main 100A panel is.

We thought of various alternatives for the upgrade including:
1. Placing panel at entrance and moving all circuits to this new panel
-- however, then we would need to rewire all the branch circuits or
have some type of nasty junction box replacing the old panel

2. Placing a new 200A panel at the entrance and converting the old
panel into a 100A subpanel
-- however, we thought this might confusing and a PITA having the
two panels separated by the length of the house. Especially,
since given the mix of old and new wiring two circuits feeding
the same room could end up in different panels 30 ft away from
each other.

Therefore, we are planning instead to consolidate all the circuits at
the location of the old panel. In doing this we considered two
options:

A. Place new large 200A panel next to the old panel and convert the
old 100A panel into a subpanel of the new panel. This would mean
leaving the bulk of the circuits in the old panel and keeping the
new main panel mostly unpopulated (but likely to fill in over
time).
-- we chose not to do this since this seems a little kludgey with
the subpanel having more circuits than our new main panel

B. Instead, we are planning to replace the old 30 circuit 100A panel
with a new 42 circuit 200A panel in place which requires a bit more
effort to move over the breakers and reattach neutrals and
grounds.



Then, we will move the old 100A panel to a location next

to the new 200A panel to hold any circuits after we run out of
space in the new panel.


This might not fly with the inspector. If the old 100a panel is being gutted of
all circuits and simply being re-installed as a secondary subpanel, which would
likely have no circuits until the space is needed, it becomes "used equipment."

Better to just go with another new main-lug 100a panel next to the new 200a
panel for 35.00 - 40.00 extra and be done with it.


Finally, rather than having a meter outside, then a main breaker just
inside, and then a 30 ft run over to the panels, we are thinking about
placing a combo meter/breaker unit outside replacing our old meter and
then entering the house and running 30 feet directly over to the new
panel. This has the benefit:
- Reducing costs (since no need for separate main breaker just
inside the house)
- Eliminating "extra" box inside the house
- Allowing fire dept easy access to electrical shutoff in case
of emergency

Does this thinking make sense??

Jeff


Makes sense. Or you could get a w/p outdoor main disconnect which holds not
only a 200a main but also at least one additional 2-pole breaker for an outdoor
hottub or pool panel.

In my jurisdiction, outdoor tubs and pools can not be fed from subpanels due to
proper grounding and bonding issues.
  #20   Report Post  
Tekkie
 
Posts: n/a
Default

Jeffrey J. Kosowsky posted for all of us....

We are about to upgrade our panel from 100A to 200A.
The run from the electric company drop to the panel is about 15 ft
vertical drop followed by 30 feet horizontal run within the house.

- Other than the fact that copper costs much more than aluminum, what
are the pros/cons of copper vs. aluminum?

- Is copper worth the added cost?

- Also, the supply will run through the unfinished utility portion of
the basement at joist level. Is it worth it to encase the cable in
metal (or pvc) conduit?


Hey Jeffy, going to the warehouse to get some cable and connectors cheap?
Say volts, amps, shorts and you will impress them with your knowledge and
they will drop their drawers, er prices to suit you.
--
Tekkie


  #21   Report Post  
Jeffrey J. Kosowsky
 
Posts: n/a
Default

Tekkie writes:
Jeffrey J. Kosowsky posted for all of us....

We are about to upgrade our panel from 100A to 200A.
The run from the electric company drop to the panel is about 15 ft
vertical drop followed by 30 feet horizontal run within the house.

- Other than the fact that copper costs much more than aluminum, what
are the pros/cons of copper vs. aluminum?

- Is copper worth the added cost?

- Also, the supply will run through the unfinished utility portion of
the basement at joist level. Is it worth it to encase the cable in
metal (or pvc) conduit?


Hey Jeffy, going to the warehouse to get some cable and connectors cheap?
Say volts, amps, shorts and you will impress them with your knowledge and
they will drop their drawers, er prices to suit you.
--
Tekkie


What is your problem? Didn't your mommy ever teach you that if you
have nothing relevant or nice to say, then keep your mouth shut?

Sounds like you must be one of those incompetent, shady contractors
who can only get by through cheating naive customers -- if you were
any good and if you were an honest worker, I can guarantee you that
you wouldn't feel so threatened...
  #22   Report Post  
Tekkie
 
Posts: n/a
Default

Jeffrey J. Kosowsky posted for all of us....

Tekkie writes:
Jeffrey J. Kosowsky posted for all of us....

We are about to upgrade our panel from 100A to 200A.
The run from the electric company drop to the panel is about 15 ft
vertical drop followed by 30 feet horizontal run within the house.

- Other than the fact that copper costs much more than aluminum, what
are the pros/cons of copper vs. aluminum?

- Is copper worth the added cost?

- Also, the supply will run through the unfinished utility portion of
the basement at joist level. Is it worth it to encase the cable in
metal (or pvc) conduit?


Hey Jeffy, going to the warehouse to get some cable and connectors cheap?
Say volts, amps, shorts and you will impress them with your knowledge and
they will drop their drawers, er prices to suit you.
--
Tekkie


What is your problem? Didn't your mommy ever teach you that if you
have nothing relevant or nice to say, then keep your mouth shut?

Sounds like you must be one of those incompetent, shady contractors
who can only get by through cheating naive customers -- if you were
any good and if you were an honest worker, I can guarantee you that
you wouldn't feel so threatened...

Hey Jeffy this isn't like the nasty emails you sent me.

You have bi-polar or penis envy? Probaby both.
--
Tekkie
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Copper Casting In America (Trevelyan) Yuri Kuchinsky Metalworking 330 July 21st 04 11:59 PM
Mix copper and pvc/cpvc supply lines? Mike Dapkus Home Repair 4 March 11th 04 09:53 PM
Copper pipe sizing. Is bigger better? Paul J Home Repair 19 February 29th 04 07:52 PM
New Electrical Regs PoP UK diy 22 September 1st 03 08:41 PM


All times are GMT +1. The time now is 12:46 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"