Default why does a furnace need outside air?

I was doing some insulation in the basement, and I noticed that the
previous owner had disconnected some ductwork (4") which connected to
the cold air return of the furnace. This ductwork lead to an outside
vent, and was intended to bring in outside air to the furnace.

I assume that since the builder went through the trouble to put that
in, that it's necessary.. but why is it necessary? Isn't there enough
air in the house for the furnace to use? The furnace has been running
for at least 4 years without it. I'm willing to repair this, but I'd
like to know the reasoning behind it. I've found out that vent is a
pretty major source of cold air coming into the basement.

Another bit of information: The house is very drafty, so there's no
concern about it being so sealed up that all the oxygen is gone. LOL

  #2   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default why does a furnace need outside air?

outside COLD air is more dense so it burns better, more energy
efficent.

Indoor air sometimes has pollutants like bleach that can rot out high
effceny furnace heat exchangers, this is a verified issue

burning indoor air means your pulling a vacuumn losing heated air and
dragging even more outdoor cold air indoors making your gas bill go up.

put the original vent arrangement back if you want your gas bill to be
lower

  #3   Report Post  
Posted to alt.home.repair
Joseph Meehan
 
Posts: n/a
Default why does a furnace need outside air?

bf wrote:
I was doing some insulation in the basement, and I noticed that the
previous owner had disconnected some ductwork (4") which connected to
the cold air return of the furnace. This ductwork lead to an outside
vent, and was intended to bring in outside air to the furnace.

I assume that since the builder went through the trouble to put that
in, that it's necessary.. but why is it necessary? Isn't there enough
air in the house for the furnace to use? The furnace has been running
for at least 4 years without it. I'm willing to repair this, but I'd
like to know the reasoning behind it. I've found out that vent is a
pretty major source of cold air coming into the basement.

Another bit of information: The house is very drafty, so there's no
concern about it being so sealed up that all the oxygen is gone. LOL


Giving the furnace its own direct source of outside air will make you
home less drafty. Really.

All furnaces (non-electric that is) use air to burn their fuel. That air
needs to be replaced. It will come from those cracks and holes all around
your home bringing cold air in and moving it around your home. If it has
its own air source it will mean less drafts.

--
Joseph Meehan

Dia duit


  #4   Report Post  
Posted to alt.home.repair
RayV
 
Posts: n/a
Default why does a furnace need outside air?

I'm with you the OP said "...the previous owner had disconnected some
ductwork (4") which connected to the cold air return of the
furnace...". That doesn't sound to me like it is being used for
combustion.

  #5   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default why does a furnace need outside air?

wrote:

outside COLD air is more dense so it burns better, more energy efficent.


Air burns?

Nick



  #6   Report Post  
Posted to alt.home.repair
dnoyeB
 
Posts: n/a
Default why does a furnace need outside air?

RayV wrote:
I'm with you the OP said "...the previous owner had disconnected some
ductwork (4") which connected to the cold air return of the
furnace...". That doesn't sound to me like it is being used for
combustion.


Yes and no. I have such a connection in my home. There is a 4" or so
duct that is piped into the return duct. That 4" pipe comes from
outside. So anytime hot air leavs the house through the roof, or the
bathroom fan, or furnace/hot water heater exhause, the cold air sucked
in is through the furnace. (in theory)

Its not directly used for combustion, but its for pressure equalization.
The air used for combustion which is exhausted is replaced by air coming
in from this pipe and into the return.

--
Thank you,



"Then said I, Wisdom [is] better than strength: nevertheless the poor
man's wisdom [is] despised, and his words are not heard." Ecclesiastes 9:16
  #7   Report Post  
Posted to alt.home.repair
Tony Hwang
 
Posts: n/a
Default why does a furnace need outside air?

RayV wrote:
I'm with you the OP said "...the previous owner had disconnected some
ductwork (4") which connected to the cold air return of the
furnace...". That doesn't sound to me like it is being used for
combustion.

Hi,
They ducted fresh air like that in old days. Now thay don't do it any
more. Combustion air intake is separate from cold air return duct.
Just simply law of physics.
  #8   Report Post  
Posted to alt.home.repair
Don Phillipson
 
Posts: n/a
Default why does a furnace need outside air?

"bf" wrote in message
ups.com...

I was doing some insulation in the basement, and I noticed that the
previous owner had disconnected some ductwork (4") which connected to
the cold air return of the furnace. This ductwork lead to an outside
vent, and was intended to bring in outside air to the furnace.

I assume that since the builder went through the trouble to put that
in, that it's necessary.. but why is it necessary? Isn't there enough
air in the house for the furnace to use? The furnace has been running


Consult your local building permits office. Many
jurisdictions nowadays require an outside air duct
to supply air to non-electric furnaces. The building
code in Ontario, Canada, added this requiremennt
about 20 years ago (and made iit retroactive.)

If your house is appropriately insulated against
draughts, the outside air duct will be more efficient
and cheaper rather than less.

--
Don Phillipson
Carlsbad Springs
(Ottawa, Canada)


  #9   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default why does a furnace need outside air?


dnoyeB wrote:
RayV wrote:
I'm with you the OP said "...the previous owner had disconnected some
ductwork (4") which connected to the cold air return of the
furnace...". That doesn't sound to me like it is being used for
combustion.


Yes and no. I have such a connection in my home. There is a 4" or so
duct that is piped into the return duct. That 4" pipe comes from
outside. So anytime hot air leavs the house through the roof, or the
bathroom fan, or furnace/hot water heater exhause, the cold air sucked
in is through the furnace. (in theory)

Its not directly used for combustion, but its for pressure equalization.
The air used for combustion which is exhausted is replaced by air coming
in from this pipe and into the return.

--


Boy, I'd disconnect that crap real fast. This is an energy disaster.
What makes you think outside air is only coming in to equalize pressure
when air is leaving via say a bathroom fan? In reality, the powrful
furnace blower is gonna draw outside air in all the time. And the
inside air will make it's way out, via things like the bathroom fan,
whether it's turned on or not, or any other ways to exit the house.

A normal house shouldn't need any air specifically brought in from the
outside when the furnace is heating/cooling. Housed get enough from
existing air leaks around doors, windows, opening/closing doors, etc.
If you have a high energy efficiency house that is sealed very tight
and you need more outside air, then an arrangement with a heat
exchanger is used. Anything else is just wasting a lot of energy.
IMO, the arrangement you have is similar to leaving a window partially
open.





Thank you,



"Then said I, Wisdom [is] better than strength: nevertheless the poor
man's wisdom [is] despised, and his words are not heard." Ecclesiastes 9:16


  #10   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default why does a furnace need outside air?


Don Phillipson wrote:
"bf" wrote in message
ups.com...

I was doing some insulation in the basement, and I noticed that the
previous owner had disconnected some ductwork (4") which connected to
the cold air return of the furnace. This ductwork lead to an outside
vent, and was intended to bring in outside air to the furnace.

I assume that since the builder went through the trouble to put that
in, that it's necessary.. but why is it necessary? Isn't there enough
air in the house for the furnace to use? The furnace has been running


Consult your local building permits office. Many
jurisdictions nowadays require an outside air duct
to supply air to non-electric furnaces. The building
code in Ontario, Canada, added this requiremennt
about 20 years ago (and made iit retroactive.)

If your house is appropriately insulated against
draughts, the outside air duct will be more efficient
and cheaper rather than less.


From his description, what he has is not for combustion air, which

would make sense. He says the outside air connection is to the return
duct.




--
Don Phillipson
Carlsbad Springs
(Ottawa, Canada)




  #11   Report Post  
Posted to alt.home.repair
Pop
 
Posts: n/a
Default why does a furnace need outside air?


wrote in message
...
wrote:

outside COLD air is more dense so it burns better, more energy
efficent.


Air burns?

Nick

Go back to sleep.


  #12   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default why does a furnace need outside air?


Bud-- wrote:
bf wrote:

I was doing some insulation in the basement, and I noticed that the
previous owner had disconnected some ductwork (4") which connected to
the cold air return of the furnace. This ductwork lead to an outside
vent, and was intended to bring in outside air to the furnace.

I assume that since the builder went through the trouble to put that
in, that it's necessary.. but why is it necessary? Isn't there enough
air in the house for the furnace to use? The furnace has been running
for at least 4 years without it. I'm willing to repair this, but I'd
like to know the reasoning behind it. I've found out that vent is a
pretty major source of cold air coming into the basement.

Another bit of information: The house is very drafty, so there's no
concern about it being so sealed up that all the oxygen is gone. LOL


And yet another opinion-
The outside intake to the air return runs the house at a slightly
elevated pressure which makes it less "drafty" (all the drafts are going
out).


Of course that is only true for the short periods when the furnace
blower is running. What about the rest of the time? And if the
house is so drafty that it's noticeable, the drafts should be fixed.


Disconnected, your house would probably be draftier but cheaper to
heat since you are not forcing air out through cracks.


Yeah, that's for sure. Plus, by drawing air into the house purposely
to force air out cracks, you are doing exactly that. On a calm day
with no breeze when there would not be much air flow through these
cracks, and hence little energy loss, now you've got a blower creating
air flow.

Having a raw outside air intake into the return plenum is simply one of
the dumbest things imaginable



A new well sealed
house might use an air-to-air heat exchanger but with your leaky house
that wouldn't be effective. Having a source for combustion air that
leaves up the flue is also an issue but not so much, as you said, in
your drafty house. My house, drafty type, has a flexible insulated duct
for combustion make-up air with the end bent in a U shape at the end - a
block from cold air just flowing in.

bud--


  #13   Report Post  
Posted to alt.home.repair
Doug Kanter
 
Posts: n/a
Default why does a furnace need outside air?


"Pop" wrote in message
news:Xe0Qf.5567$eJ1.2166@trndny05...

wrote in message
...
wrote:

outside COLD air is more dense so it burns better, more energy
efficent.


Air burns?

Nick

Go back to sleep.


:-)


  #14   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default why does a furnace need outside air?

air intake should go to furnace burner area not plenum.

4 inch sounds right for air for combustion

  #15   Report Post  
Posted to alt.home.repair
George E. Cawthon
 
Posts: n/a
Default why does a furnace need outside air?

dnoyeB wrote:
RayV wrote:

I'm with you the OP said "...the previous owner had disconnected some
ductwork (4") which connected to the cold air return of the
furnace...". That doesn't sound to me like it is being used for
combustion.


Yes and no. I have such a connection in my home. There is a 4" or so
duct that is piped into the return duct. That 4" pipe comes from
outside. So anytime hot air leavs the house through the roof, or the
bathroom fan, or furnace/hot water heater exhause, the cold air sucked
in is through the furnace. (in theory)

Its not directly used for combustion, but its for pressure equalization.
The air used for combustion which is exhausted is replaced by air coming
in from this pipe and into the return.


Pressure equalization? Don't think so. That cold
air pipe is meant for a certain percentage of make
up air from the outside. Required in many
communities with newer homes that are built air
tight and is likely to be 10 to 15 percent of the
air. Seems like a bit much if in a cold place.
But the purpose is to supply fresh air because
much of the inside air is highly contaminated by
the materials used in building, furniture,
carpets, etc.


  #16   Report Post  
Posted to alt.home.repair
Mike Dobony
 
Posts: n/a
Default why does a furnace need outside air?

On 9 Mar 2006 07:05:01 -0800, wrote:

dnoyeB wrote:
RayV wrote:
I'm with you the OP said "...the previous owner had disconnected some
ductwork (4") which connected to the cold air return of the
furnace...". That doesn't sound to me like it is being used for
combustion.


Yes and no. I have such a connection in my home. There is a 4" or so
duct that is piped into the return duct. That 4" pipe comes from
outside. So anytime hot air leavs the house through the roof, or the
bathroom fan, or furnace/hot water heater exhause, the cold air sucked
in is through the furnace. (in theory)

Its not directly used for combustion, but its for pressure equalization.
The air used for combustion which is exhausted is replaced by air coming
in from this pipe and into the return.

--


Boy, I'd disconnect that crap real fast. This is an energy disaster.
What makes you think outside air is only coming in to equalize pressure
when air is leaving via say a bathroom fan? In reality, the powrful
furnace blower is gonna draw outside air in all the time. And the
inside air will make it's way out, via things like the bathroom fan,
whether it's turned on or not, or any other ways to exit the house.

A normal house shouldn't need any air specifically brought in from the
outside when the furnace is heating/cooling. Housed get enough from
existing air leaks around doors, windows, opening/closing doors, etc.
If you have a high energy efficiency house that is sealed very tight
and you need more outside air, then an arrangement with a heat
exchanger is used. Anything else is just wasting a lot of energy.
IMO, the arrangement you have is similar to leaving a window partially
open.


You obviously never heard of Sick Building Syndrome! Indoor air is highly
polluted and needs a replenishment of fresh air. In the winter time the
house is usually shut up more than in the summer and contaminants just
build up. This is especially bad if someone has allergies to indoor
contaminants, a growing cause of asthma! Also the air exchanged with
opening a door is contributing unheated air to the house. The outdoor air
supply is being heated before entering the house.

http://www.epa.gov/iaq/pubs/sbs.html
  #17   Report Post  
Posted to alt.home.repair
PaPaPeng
 
Posts: n/a
Default why does a furnace need outside air?

On Thu, 9 Mar 2006 19:01:04 -0600, Mike Dobony
wrote:

You obviously never heard of Sick Building Syndrome! Indoor air is highly
polluted and needs a replenishment of fresh air. In the winter time the
house is usually shut up more than in the summer and contaminants just
build up. This is especially bad if someone has allergies to indoor
contaminants, a growing cause of asthma! Also the air exchanged with
opening a door is contributing unheated air to the house. The outdoor air
supply is being heated before entering the house.



I went through a building design construction course. Community
college level, once a week for 12 weeks if I remember.

On the furnace heating system picture it this way. Your house is an
insulated box with insulation for the outside walls only and on the
ceiling. The furnace fires up and the heated is recirculated
within this tightly insulated box to bring the air up to your set
(comfort) temperature.

Heated air will cool on its own mainly conduction loss with some loss
through leakage. The (heated) leakage air loss has to be replaced by
outside air. The best route for this outside air to enter the house
is to duct outside air into the return air duct so that it is heated
first before it joins the circulation.

It is very dangerous to over seal the house, ie make it too airtight,
and not have this outside fresh air intake. The reason is that heated
air normally rises up the chimney. But when the room air cools air
contracts and it will suck air (in the reverse direction) down the
chimney. This suction includes toxic burnt gases present in the
chimney and can be blown back into the house. You breath this stuff.
This is slow poisoning.

Another reason for the fresh air intake is that in the absence of one
the heated air inside the house will be drawn up the chimney together
with the furnace gasses. You lose expensive heated air up the chimney
every time the furnace fires up. The best solution is to have a
separate fresh air supply to the furnace burners. This way outside
air goes direct to the burners and goes up the chimney immediately
after combustion. The burners do not use up warmed room air.

Often all the contractors do is to have an open duct from the outside
to an opening near the burner assembly. Of course in winter this lets
in freezing cold air. Many homeowners plug this duct up with
fiberglass or remove the duct altogether. It will work but you will
be sending warmed room air up the chimney. I fabricated an enclosed
duct to trunk the duct air into the furnace. Cold air is drawn in
only when the furnace fires up, a per normal convection, and the cold
air never gets into the basement. I understand newer furnaces already
have this feature.

To recap there should be a fresh air duct from the outside and
connected to the furnace return air trunk. There should be a separate
fresh air duct to supply fresh air to the furnace burners.
  #18   Report Post  
Posted to alt.home.repair
bf
 
Posts: n/a
Default why does a furnace need outside air?


mm wrote:
On 9 Mar 2006 04:40:22 -0800, "bf" wrote:

I was doing some insulation in the basement, and I noticed that the
previous owner had disconnected some ductwork (4") which connected to
the cold air return of the furnace.

--------------------
Are you talking about the cold air *return* via which the air heated
by the furnace returns to the furnace to be heated again.

Or are you talking about a duct to supply combustion air to the fire,
which then goes up the smoke stack or out the combustion air
discharge?

This ductwork lead to an outside
vent, and was intended to bring in outside air to the furnace.


I'm curious how big this duct is.


I'm sorry it took me so long to respond (Thanks for all the replies
from everyone)
It is a 4" circular ductwork that leads from the outside into the
regular "cold air return" (inside air source) from the furnace.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Purchasing Furnace - 2-Stage Variable vs. Standard pipco Home Repair 21 January 27th 06 01:48 PM
Help. Furnace improperly installed? Chuck Home Repair 11 November 2nd 04 02:26 AM
Clueless Inspector Faults Furnace Install Hell Toupee Home Repair 3 October 8th 04 06:47 PM
Furnace problems - repair, replace or ???? Paul Home Repair 11 March 24th 04 12:59 AM
Furnace Problem...HELP! torque Home Repair 5 January 6th 04 01:24 AM


All times are GMT +1. The time now is 10:31 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"