GFCI outlet for radial arm saw
In my garage I have a 20 Amp circuit which has two 15 amp GFCI outlets.
On this same circuit these are also two GFCI's in the kitchen and another in a bathroom. My problem is that I have a radial arm saw which apparently draws too much current in starting up resulting a tripped GFCI and i can't run the saw. The book that came with the saw says that there should be "a time delay 15 amp circuit breaker installed." I'm not sure that GFCI outlets were installed when this saw was made. An inquiry at an electric supply store resulted in the information that there is no such thing as a time delay GFCI." My question is, since it is a 20 amp circuit can I replace the 15 amp GFCI with a 20 amp one, and will this solve the problem of starting the saw motor? |
#2
Posted to alt.home.repair
|
|||
|
|||
GFCI outlet for radial arm saw
wrote in message oups.com... In my garage I have a 20 Amp circuit which has two 15 amp GFCI outlets. On this same circuit these are also two GFCI's in the kitchen and another in a bathroom. My problem is that I have a radial arm saw which apparently draws too much current in starting up resulting a tripped GFCI and i can't run the saw. The book that came with the saw says that there should be "a time delay 15 amp circuit breaker installed." I'm not sure that GFCI outlets were installed when this saw was made. An inquiry at an electric supply store resulted in the information that there is no such thing as a time delay GFCI." My question is, since it is a 20 amp circuit can I replace the 15 amp GFCI with a 20 amp one, and will this solve the problem of starting the saw motor? I'm not an electrician but my table saw used to trip the breaker until I started using a 12ga extension cord on it. But even though it was on a GFCI circuit, it never tripped that but would trip the breaker in the main box. Sounds like you may have a slight ground problem with the saw. I'm not qualified to answer your question, however, just relating my experience. Tom G. |
#3
Posted to alt.home.repair
|
|||
|
|||
GFCI outlet for radial arm saw
|
#4
Posted to alt.home.repair
|
|||
|
|||
GFCI outlet for radial arm saw
Seems normal to me... I mean, don't most household circuits that are
20A with 12/2 wire have "several" 15A outlets on them? |
#5
Posted to alt.home.repair
|
|||
|
|||
GFCI outlet for radial arm saw
Yes, you can have a 15 amp GFCI outlet on a 20 AMP breaker, as long as
the wire is 12 gauge. But what does sound a little strange is that he appears to have 5 GFCI's on the same circuit. One GFCI can protect not only the outlet it is installed in, but also the downstream outlets. Or a single GFCI breaker could protect all of them. As to whether going to a 20 amp GFCI outlet would help, I think the answer is no. GFCI outlets are tripped by ground faults, not normal hot to neutral current that exceeds the outlet rating. In fact, as far as I know, none of the GFCI outlets check for excess current at all. Having a large inductive load on an GFCI is not recommended because in some cases they can cause the type of tripping problems the OP is having. |
#6
Posted to alt.home.repair
|
|||
|
|||
GFCI outlet for radial arm saw
Joseph Meehan wrote:
wrote: Why am I not comfortable with "20 Amp circuit which has two 15 amp" ??? That's allowed on household circuts. My house was built in 1972 and we have that setup in the kitchen and family room. Can't cite chapter and verse in the code, but generally it's allowed. -- Jim Nugent |
#7
Posted to alt.home.repair
|
|||
|
|||
GFCI outlet for radial arm saw
As Trader said, it's normal to have 15 amp GFCI's on a 20 amp circuit as the
"feed through of a 15 amp GFCI is rated for 20 amp and kitchen outlet circuits should not be on with any other circuits except dining room outlets. Ground fault outlets are not circuit breakers, so if the outlet is tripping, it would be caused by a "ground fault" not an overloaded circuit, which would cause the circuit breaker to trip wrote in message oups.com... In my garage I have a 20 Amp circuit which has two 15 amp GFCI outlets. On this same circuit these are also two GFCI's in the kitchen and another in a bathroom. My problem is that I have a radial arm saw which apparently draws too much current in starting up resulting a tripped GFCI and i can't run the saw. The book that came with the saw says that there should be "a time delay 15 amp circuit breaker installed." I'm not sure that GFCI outlets were installed when this saw was made. An inquiry at an electric supply store resulted in the information that there is no such thing as a time delay GFCI." My question is, since it is a 20 amp circuit can I replace the 15 amp GFCI with a 20 amp one, and will this solve the problem of starting the saw motor? |
#8
Posted to alt.home.repair
|
|||
|
|||
GFCI outlet for radial arm saw
wrote in message oups.com... In my garage I have a 20 Amp circuit which has two 15 amp GFCI outlets. On this same circuit these are also two GFCI's in the kitchen and another in a bathroom. My problem is that I have a radial arm saw which apparently draws too much current in starting up resulting a tripped GFCI and i can't run the saw. The book that came with the saw says that there should be "a time delay 15 amp circuit breaker installed." I'm not sure that GFCI outlets were installed when this saw was made. An inquiry at an electric supply store resulted in the information that there is no such thing as a time delay GFCI." My question is, since it is a 20 amp circuit can I replace the 15 amp GFCI with a 20 amp one, and will this solve the problem of starting the saw motor? I think you are a bit confused here about the function of a GFCI. A GFCI tripping has nothing to do with how many amps are being used on the circuit. That is what the breaker in your main panel is for. The GFCI will only detect a current imbalance between hot and neutral. If some current is going somewhere else like through you to ground then the GFCI trips. It is not uncommon for GFCI's to false trip with large motors or compressors in things like power tools, large appliances etc. This is why code allows you to put your refrigerator on a non GFCI outlet. Some GFCI's brands/models are worse than others at false trips. If your GFCI's are pretty old then try replacing the one you use for the power saw with a new one and see if that helps. It may be the power saw that has the problem The tool may be defective. But some older tools just won't work on a GFCI. Using a 20 amp GFCI will not make a difference. The 20 amp rating is only the configuration of the plug that the outlet will accept. If you don't have any 20 amp appliances with the one horizontal blade | -- then it does not matter. I think all GFCI's are made to feed thru 20 amps in the wires. The 15 amp version will not accept a 20 amp plug, which is pretty rare to have in the home. If the breaker in your panel is not tripping then I would just leave it alone. If you do replace it don't change the 20 to a 15 just because the power saw manual specified that. That is a min. spec. If you must replace it then get a 20 amp if that is what you have. You would be better off running a dedicated circuit to your garage. Newer construction would have 3 dedicated circuits min. where you have only one. (one to bath, one + to kitchen, one to garage). However a dedicated circuit may not help the GFCI tripping unless other items plugged into the same circuit are contributing to the problem. Kevin |
#9
Posted to alt.home.repair
|
|||
|
|||
GFCI outlet for radial arm saw
RBM wrote:
As Trader said, it's normal to have 15 amp GFCI's on a 20 amp circuit as the "feed through of a 15 amp GFCI is rated for 20 amp and kitchen outlet circuits should not be on with any other circuits except dining room outlets. Ground fault outlets are not circuit breakers, so if the outlet is tripping, it would be caused by a "ground fault" not an overloaded circuit, which would cause the circuit breaker to trip Thanks, that makes sense. Thanks to all the others who also replied. wrote in message oups.com... In my garage I have a 20 Amp circuit which has two 15 amp GFCI outlets. On this same circuit these are also two GFCI's in the kitchen and another in a bathroom. My problem is that I have a radial arm saw which apparently draws too much current in starting up resulting a tripped GFCI and i can't run the saw. The book that came with the saw says that there should be "a time delay 15 amp circuit breaker installed." I'm not sure that GFCI outlets were installed when this saw was made. An inquiry at an electric supply store resulted in the information that there is no such thing as a time delay GFCI." My question is, since it is a 20 amp circuit can I replace the 15 amp GFCI with a 20 amp one, and will this solve the problem of starting the saw motor? -- Joseph Meehan Dia duit |
#10
Posted to alt.home.repair
|
|||
|
|||
GFCI outlet for radial arm saw
I just realised we never came up with a solution for the OP. Assuming
the radial arm saw doesn't have a real ground fault, then I see a couple of possible solutions. He needs to get the saw off of a GFCI. Now I know code says outlets in a garage need to be on a GFCI, but what about if the saw could be wired in directly, instead of plugged into an outlet? Is that exempt from needing a GFCI? If so, he could wire the garage so the outlets are on GFCI, but the saw is not. Alternatively, he could make the one outlet the saw is plugged into non-GFCI, while leaving the rest of the garage outlets GFCI. That is a code violation, however if it were my garage, and the only reasonable way to do it, I would consider it. I'd also make sure the saw was properly grounded, plug up the other outlet on the receptacle, and put up a warning label. |
#11
Posted to alt.home.repair
|
|||
|
|||
GFCI outlet for radial arm saw
|
#12
Posted to alt.home.repair
|
|||
|
|||
GFCI outlet for radial arm saw
On Sat, 25 Feb 2006 13:15:59 GMT, "Kevin Ricks"
wrote: wrote in message roups.com... In my garage I have a 20 Amp circuit which has two 15 amp GFCI outlets. On this same circuit these are also two GFCI's in the kitchen and another in a bathroom. My problem is that I have a radial arm saw which apparently draws too much current in starting up resulting a tripped GFCI and i can't run the saw. The book that came with the saw says that there should be "a time delay 15 amp circuit breaker installed." I'm not sure that GFCI outlets were installed when this saw was made. An inquiry at an electric supply store resulted in the information that there is no such thing as a time delay GFCI." My question is, since it is a 20 amp circuit can I replace the 15 amp GFCI with a 20 amp one, and will this solve the problem of starting the saw motor? The NEC did allow a dedicated appliance outlet to exist without GFCI protection. A single-outlet (Hubbell twist-lock comes to mind) could serve the appliance (saw) as long as it did not serve plug-in hand tools/appliances. I have been retired for several years and NEC has probably changed some. Check with your Authority Having Jurisdiction or a knowledgeable electrician. -- Mr.E |
#13
Posted to alt.home.repair
|
|||
|
|||
GFCI outlet for radial arm saw
|
#14
Posted to alt.home.repair
|
|||
|
|||
GFCI outlet for radial arm saw
Thanks to all who replied to my saw problem. No one mentioned the
"time delay 15 amp circuit breaker" which is recommended in the saw manual. Does anyone know if such a thing exists? Dave |
#16
Posted to alt.home.repair
|
|||
|
|||
GFCI outlet for radial arm saw
wrote in message oups.com... Thanks to all who replied to my saw problem. No one mentioned the "time delay 15 amp circuit breaker" which is recommended in the saw manual. Does anyone know if such a thing exists? Dave Are you sure the manual was not referring to fuses? Fuses come in quick blow or time delay types. Sometimes the manuals will try to cover all possible cases the user might find. ie breakers and/or fuses. If your home had fuses then you may need to get the time delay type for the saw anyway. Even then I would not get the time delay fuses unless it actually blew out often. I think you can get time delay breakers but HD and such may have to special order. As I said in my reply if your breaker is not blowing with the saw then don't bother to replace it. If you do replace it, (with a time delay type), then you would need the 20Amp breaker. I think that is what your said you had.. If you put a 15 then you might find that other stuff in the house will overload and blow it. I am assuming that all your wiring is 12ga. Kevin |
#17
Posted to alt.home.repair
|
|||
|
|||
GFCI outlet for radial arm saw
Kevin Ricks wrote: wrote in message oups.com... Thanks to all who replied to my saw problem. No one mentioned the "time delay 15 amp circuit breaker" which is recommended in the saw manual. Does anyone know if such a thing exists? Dave Are you sure the manual was not referring to fuses? Fuses come in quick blow or time delay types. Sometimes the manuals will try to cover all possible cases the user might find. ie breakers and/or fuses. If your home had fuses then you may need to get the time delay type for the saw anyway. Even then I would not get the time delay fuses unless it actually blew out often. I think you can get time delay breakers but HD and such may have to special order. As I said in my reply if your breaker is not blowing with the saw then don't bother to replace it. If you do replace it, (with a time delay type), then you would need the 20Amp breaker. I think that is what your said you had.. If you put a 15 then you might find that other stuff in the house will overload and blow it. I am assuming that all your wiring is 12ga. Kevin The reason no one commented on the time delay breaker is that it won't solve your problem. You have a GFCI tripping do to either a real ground fault or do to the high inductance load of the saw. If it were the breaker tripping do to high start up current, that would be a different story. |
#19
Posted to alt.home.repair
|
|||
|
|||
GFCI outlet for radial arm saw
|
#20
Posted to alt.home.repair
|
|||
|
|||
GFCI outlet for radial arm saw
According to Kevin Ricks :
wrote in message oups.com... In my garage I have a 20 Amp circuit which has two 15 amp GFCI outlets. On this same circuit these are also two GFCI's in the kitchen and another in a bathroom. My problem is that I have a radial arm saw which apparently draws too much current in starting up resulting a tripped GFCI and i can't run the saw. The book that came with the saw says that there should be "a time delay 15 amp circuit breaker installed." I'm not sure that GFCI outlets were installed when this saw was made. An inquiry at an electric supply store resulted in the information that there is no such thing as a time delay GFCI." My question is, since it is a 20 amp circuit can I replace the 15 amp GFCI with a 20 amp one, and will this solve the problem of starting the saw motor? No. Are you sure it didn't say "time delay _fuse_ OR circuit breaker"? When using fuses, a time delay fuse is needed for large motors. Circuit breakers are inherently time delay. If the GFCI is tripping all the time, you have some sort of electrical leak in the saw. It is not uncommon for GFCI's to false trip with large motors or compressors in things like power tools, large appliances etc. It's sufficiently _uncommon_ that you will definately not see a GFCI trip every time you try to turn on a motor. The saw has a leak. Needs to be checked. I bought a RAS at an auction some years back. It would have tripped a GFCI if I had one in the garage. The ground wire in the electrical plug had come adrift from the screw and was contacting the hot wire. The whole frame went live. Used it several times until I noticed a slight tingle when touching it. H'm, then touched another grounded tool at the same time. OUCH! I'm smarter now ;-) -- Chris Lewis, Una confibula non set est It's not just anyone who gets a Starship Cruiser class named after them. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Trying to install a GFCI outlet where I have 4 wires total | Home Repair | |||
GFCI Outlet Wiring Question | Home Repair | |||
GFCI outlet / automated sprinkler system that plugs in it | Home Ownership | |||
Repeated noise coming from a GFCI outlet | Home Repair | |||
GFCI Outlet Question | Electronics Repair |