I just installed a temp power pole with a temp power box (combination
box with meter, circuit breakers, and 120/240 V receptacles for
providing temporary power to construction site) . I noticed as I was
connecting it, that there was one "bus" bar for the ground wire from
the power company and that there was a separate ground bus bar for the
"true" ground from the ground rod (and the green ground wires from the
receptacles). I also noticed that these two bus bars were not
electrically connected. The ground line (or return line) from the
power company was never really grounded to the box. Is this normal?
I'm tempted to run a bare copper wire between the two "ground" bus
bars, but would like some comments from you electricians out there.
Thanks

  #5   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default Temp Power Electrical Question

Thanks for the responses. Found the "bonding bar" that is supposed to
be installed to ground the neutral from the power company to the box
case. The case is already grounded by the copper wire going to the
ground stake. Thanks again



  #6   Report Post  
Posted to alt.home.repair
dnoyeB
 
Posts: n/a
Default Temp Power Electrical Question

wrote:
On 14 Feb 2006 05:48:46 -0800,
wrote:


Thanks for the responses. Found the "bonding bar" that is supposed to
be installed to ground the neutral from the power company to the box
case. The case is already grounded by the copper wire going to the
ground stake. Thanks again



One thing you need to understand. The "ground" has nothing to do with
clearing a fault (tripping the breaker on a short). All of that
current must go through the bonding jumper and back to the X0
centertap of the transformer. The ground rod is only there to
establish a local reference for the supply, so your tools and the dirt
are at the same potential. Without the bonding jumper your ground rod
is nothing but a worm chaser in a fault.



The "Ground" that comes in from the service and that is also tied to the
water pipes and gas pipes, and the pole in the dirt is a safety
precaution and has to do with lightning protection. It is not normally
part of the circuit as no current flows into the earth, basically unless
its from the sky.

The "ground" you see inside the house which is the 3rd prong is
different. Its actually just a "better" return which is used under
failure conditions. It is also not normally part of the circuit and it
too eventually ties into the earth ground. But its purpose is not
lightning protection.

--
Thank you,



"Then said I, Wisdom [is] better than strength: nevertheless the poor
man's wisdom [is] despised, and his words are not heard." Ecclesiastes 9:16
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
PowerMac G4 (Quicksilver) Power Supply Chris Electronics Repair 7 January 31st 06 03:19 AM
Brown's gas?? T.Alan Kraus Metalworking 16 December 9th 05 07:36 AM
1 to 3 phase converter power factor question [email protected] Metalworking 12 September 7th 05 10:36 PM
Home circuit breaker box question Darmok Electronics Repair 11 July 22nd 05 04:53 AM
New Electrical Regs PoP UK diy 22 September 1st 03 08:41 PM


All times are GMT +1. The time now is 09:51 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"