  #1   Report Post  
Posted to alt.home.repair
Jim Redelfs
 
Posts: n/a
Default Downsize Furnace?

Imagine all the added elbow room if the adjoining water heater was GONE during
a furnace retrofit. Well, that's what I'm going to be doing (See Downsize
Water Heater ) in a
little less than two weeks.

My contractor wants to DOWNSIZE to 75k from the 100k size of my 14-year-old,
conventional (spec) gas furnace. Of course, this will be done with a "90" (or
better) model. He claims that the improved efficiency of the new furnace will
compensate for the difference. Do you agree?

He also mentioned, after taking measurements TWICE, that I need an
18-inch-frame unit and that a bigger unit would require a reducing "boot",
which he represents as a compromise. What's with that?

Then there's the PVC vent(s) outside. He claims that it is legit to use only
ONE - an exhaust line - that the furnace uses INTERIOR air for combustion. He
represents this as a DESIRABLE way to EXCHANGE interior air with fresh.

I am old enough that this furnace may well be part a big part of the resale
value of our home. He wants to install a "Weathermaker" furnace and a Rheem
ac condensing unit outside. He says that the Weathermaker FURNACE is
virtually the same unit as a Rheem so this would be an up-front cost-saving
issue ONLY, assuming he's right. What about resale then?

He further says that the condensing units are different and therefore,
recommends a Rheem unit outside.
--

JR
  #2   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default Downsize Furnace?

I would get at least 3 and preferably 5 estimates and quotes, then
compare.

did he measure you entire home and do a heat loss calculation??

since he advocated downsizing the hot water tank I would question his
other recomendations

you better off using outside air for combustion, old houses already
exchange air enough and besides certain home chemicals have caused
furnace heat exchanger failures in the past. everything I have seen
says outside cold air, is more dense and better.

how long has he been in business? buy a furnace ONLY with a lifetime
heat exchanger warranty and at least 10 year parts and labor for
everything else.

are you buying a 2 speed furnace? they run on low speed in moderate
temps, then step up for more demanding situations like zero days.
slightly more expensive, but selling point if your moving

  #3   Report Post  
Posted to alt.home.repair
Bob
 
Posts: n/a
Default Downsize Furnace?

Go with what your contractor says, it sounds like he knows what he's doing.
Rheem lets you use just an exhaust. They also let you downsize the last 18"
from 2" to 1-1/2" PVC in certain instances.
If you put in the bigger unit, the blower will produce more CFM, and
velocity of air out the ducts will most likely be offensive. Rheem Mfg.
bought out Weathermaker years ago. They might even be the same color now. No
buyer is going to notice that they both don't have the same name. I sell
Ruud because my wholesaler stocks that in my area. When they can't get a
matching unit, they go to other parts of the country for a Rheem.

"Jim Redelfs" wrote in message
...
Imagine all the added elbow room if the adjoining water heater was GONE

during
a furnace retrofit. Well, that's what I'm going to be doing (See Downsize
Water Heater ) in

a
little less than two weeks.

My contractor wants to DOWNSIZE to 75k from the 100k size of my

14-year-old,
conventional (spec) gas furnace. Of course, this will be done with a "90"

(or
better) model. He claims that the improved efficiency of the new furnace

will
compensate for the difference. Do you agree?

He also mentioned, after taking measurements TWICE, that I need an
18-inch-frame unit and that a bigger unit would require a reducing "boot",
which he represents as a compromise. What's with that?

Then there's the PVC vent(s) outside. He claims that it is legit to use

only
ONE - an exhaust line - that the furnace uses INTERIOR air for combustion.

He
represents this as a DESIRABLE way to EXCHANGE interior air with fresh.

I am old enough that this furnace may well be part a big part of the

resale
value of our home. He wants to install a "Weathermaker" furnace and a

Rheem
ac condensing unit outside. He says that the Weathermaker FURNACE is
virtually the same unit as a Rheem so this would be an up-front

cost-saving
issue ONLY, assuming he's right. What about resale then?

He further says that the condensing units are different and therefore,
recommends a Rheem unit outside.
--

JR



  #4   Report Post  
Posted to alt.home.repair
Bob
 
Posts: n/a
Default Downsize Furnace?

Matching the CFM capacity of the ducts to the new furnace is more important
than a heat loss calculation. In some cases, drawing combustion air from
inside is preferable. Large amounts of some chemicals can ruin a heat
exchanger, but most people don't have that situation.

wrote in message
oups.com...
I would get at least 3 and preferably 5 estimates and quotes, then
compare.

did he measure you entire home and do a heat loss calculation??

since he advocated downsizing the hot water tank I would question his
other recomendations

you better off using outside air for combustion, old houses already
exchange air enough and besides certain home chemicals have caused
furnace heat exchanger failures in the past. everything I have seen
says outside cold air, is more dense and better.

how long has he been in business? buy a furnace ONLY with a lifetime
heat exchanger warranty and at least 10 year parts and labor for
everything else.

are you buying a 2 speed furnace? they run on low speed in moderate
temps, then step up for more demanding situations like zero days.
slightly more expensive, but selling point if your moving



  #5   Report Post  
Posted to alt.home.repair
Joseph Meehan
 
Posts: n/a
Default Downsize Furnace?

Jim Redelfs wrote:
Imagine all the added elbow room if the adjoining water heater was
GONE during a furnace retrofit. Well, that's what I'm going to be
doing (See Downsize Water Heater
) in a little
less than two weeks.

My contractor wants to DOWNSIZE to 75k from the 100k size of my
14-year-old, conventional (spec) gas furnace. Of course, this will
be done with a "90" (or better) model. He claims that the improved
efficiency of the new furnace will compensate for the difference. Do
you agree?


No one here can agree or disagree without doing measurements and
calculations for heat loss. You did not say how your contractor determined
you should downsize.

My guess is he is right, and did the calculations but I don't know.



He also mentioned, after taking measurements TWICE, that I need an
18-inch-frame unit and that a bigger unit would require a reducing
"boot", which he represents as a compromise. What's with that?

Then there's the PVC vent(s) outside. He claims that it is legit to
use only ONE - an exhaust line - that the furnace uses INTERIOR air
for combustion. He represents this as a DESIRABLE way to EXCHANGE
interior air with fresh.


While I would tend to put in a intake for outside air, with a higher
efficiency unit, your home is old enough (at least 14 years) to be loose
enough not to "need" it's own inlet.


I am old enough that this furnace may well be part a big part of the
resale value of our home. He wants to install a "Weathermaker"
furnace and a Rheem ac condensing unit outside. He says that the
Weathermaker FURNACE is virtually the same unit as a Rheem so this
would be an up-front cost-saving issue ONLY, assuming he's right.
What about resale then?

He further says that the condensing units are different and therefore,
recommends a Rheem unit outside.


--
Joseph Meehan

Dia duit




  #6   Report Post  
Posted to alt.home.repair
HeatMan
 
Posts: n/a
Default Downsize Furnace?


"Jim Redelfs" wrote in message
...
Imagine all the added elbow room if the adjoining water heater was GONE

during
a furnace retrofit. Well, that's what I'm going to be doing (See Downsize
Water Heater ) in

a
little less than two weeks.

I didn't comment on the WH thread, but again, look at resale. If you go
back with a tank type unit and you'll be selling soon, will the smaller one
fill the whirlpool tub for the new owner? For the 20-25 dollars difference
between the 40 and the 50, I'd go with the fifty. I have seen home
inspection reports that comment on the size of the WH not being enough to
fill the tub.

My contractor wants to DOWNSIZE to 75k from the 100k size of my

14-year-old,
conventional (spec) gas furnace. Of course, this will be done with a "90"

(or
better) model. He claims that the improved efficiency of the new furnace

will
compensate for the difference. Do you agree?

Yes and no.

He also mentioned, after taking measurements TWICE, that I need an
18-inch-frame unit and that a bigger unit would require a reducing "boot",
which he represents as a compromise. What's with that?

Simply called a transition. Furnaces come in 3 basic widths, 21", 17" and
14".

Then there's the PVC vent(s) outside. He claims that it is legit to use

only
ONE - an exhaust line - that the furnace uses INTERIOR air for combustion.

He
represents this as a DESIRABLE way to EXCHANGE interior air with fresh.

That depends. I use OA for any 90% furnace that is in living space
(basement or closet installation). Some attics get it, but very few
crawlspaces.

I am old enough that this furnace may well be part a big part of the

resale
value of our home. He wants to install a "Weathermaker" furnace and a

Rheem
ac condensing unit outside. He says that the Weathermaker FURNACE is
virtually the same unit as a Rheem so this would be an up-front

cost-saving
issue ONLY, assuming he's right. What about resale then?

Most people out there look at the age of the furnace, not the brand. The
one concern would be a matched system to get the proper efficiency for the
AC.

He further says that the condensing units are different and therefore,
recommends a Rheem unit outside.

As long as it's a ARI match, that's fine. Rheem has scroll compressors and
WK still uses recips. Scrolls will last longer.




  #7   Report Post  
Posted to alt.home.repair
HeatMan
 
Posts: n/a
Default Downsize Furnace?


wrote in message
oups.com...
I would get at least 3 and preferably 5 estimates and quotes, then
compare.

did he measure you entire home and do a heat loss calculation??

since he advocated downsizing the hot water tank I would question his
other recomendations

you better off using outside air for combustion, old houses already
exchange air enough and besides certain home chemicals have caused
furnace heat exchanger failures in the past. everything I have seen
says outside cold air, is more dense and better.

how long has he been in business? buy a furnace ONLY with a lifetime
heat exchanger warranty and at least 10 year parts and labor for
everything else.

Something along this line was pointed out to me recently. You have a
limited lifetime warranty on the HX in your furnace. After some time, the
manufacturer is going to stop making replacement parts for that furnace.

Besides, look at the Lennox Pulse furnace. They started going bad and
Lennox would give you a pittance towards a new Lennox furnace. No other
brand, just Lennox.

are you buying a 2 speed furnace? they run on low speed in moderate
temps, then step up for more demanding situations like zero days.
slightly more expensive, but selling point if your moving

Yep.


  #8   Report Post  
Posted to alt.home.repair
Bob
 
Posts: n/a
Default Downsize Furnace?

After reading my post, I realized that it was actually WeatherKing, and NOT
Weathermaker that Rheem bought out.

"Bob" wrote in message
. ..
Go with what your contractor says, it sounds like he knows what he's

doing.
Rheem lets you use just an exhaust. They also let you downsize the last

18"
from 2" to 1-1/2" PVC in certain instances.
If you put in the bigger unit, the blower will produce more CFM, and
velocity of air out the ducts will most likely be offensive. Rheem Mfg.
bought out Weathermaker years ago. They might even be the same color now.

No
buyer is going to notice that they both don't have the same name. I sell
Ruud because my wholesaler stocks that in my area. When they can't get a
matching unit, they go to other parts of the country for a Rheem.

"Jim Redelfs" wrote in message
...
Imagine all the added elbow room if the adjoining water heater was GONE

during
a furnace retrofit. Well, that's what I'm going to be doing (See

Downsize
Water Heater )

in
a
little less than two weeks.

My contractor wants to DOWNSIZE to 75k from the 100k size of my

14-year-old,
conventional (spec) gas furnace. Of course, this will be done with a

"90"
(or
better) model. He claims that the improved efficiency of the new

furnace
will
compensate for the difference. Do you agree?

He also mentioned, after taking measurements TWICE, that I need an
18-inch-frame unit and that a bigger unit would require a reducing

"boot",
which he represents as a compromise. What's with that?

Then there's the PVC vent(s) outside. He claims that it is legit to use

only
ONE - an exhaust line - that the furnace uses INTERIOR air for

combustion.
He
represents this as a DESIRABLE way to EXCHANGE interior air with fresh.

I am old enough that this furnace may well be part a big part of the

resale
value of our home. He wants to install a "Weathermaker" furnace and a

Rheem
ac condensing unit outside. He says that the Weathermaker FURNACE is
virtually the same unit as a Rheem so this would be an up-front

cost-saving
issue ONLY, assuming he's right. What about resale then?

He further says that the condensing units are different and therefore,
recommends a Rheem unit outside.
--

JR





  #9   Report Post  
Posted to alt.home.repair
Edwin Pawlowski
 
Posts: n/a
Default Downsize Furnace?


"Jim Redelfs" wrote in message
...
Imagine all the added elbow room if the adjoining water heater was GONE
during
a furnace retrofit. Well, that's what I'm going to be doing (See Downsize
Water Heater ) in
a
little less than two weeks.

My contractor wants to DOWNSIZE to 75k from the 100k size of my
14-year-old,
conventional (spec) gas furnace. Of course, this will be done with a "90"
(or
better) model. He claims that the improved efficiency of the new furnace
will
compensate for the difference. Do you agree?


Ratings are based on input. Assuming a 100,000 Btu unit of 80% efficiency,
20,000 is going up the flue, not into your house. With a 100,000 Btu unit
of 90%, only 10,000 is going away, so you have an extra 10,000 going to heat
your house. Thus, a reduction in capacity will give the same amount of
heat.

Other factors can come into play, this is meant as an example, not exact
calculations or your system.


  #10   Report Post  
Posted to alt.home.repair
m Ransley
 
Posts: n/a
Default Downsize Furnace?

Unless you get a written load calculation you will never know the truth.
Oversizing was and is common. I had 110000 btu, now I have 47000, on low
fire and on the coldest days I only run 12-14 hours. So I am still
oversized. If your unit is 80% efficient and you up efficiency to a 94%,
you can downsize 18% and get the same heat output. But nobody here kmows
how he is comming to that conclusion. Get several estimates, there is
alot to choose from.



  #11   Report Post  
Posted to alt.home.repair
SQLit
 
Posts: n/a
Default Downsize Furnace?


"Jim Redelfs" wrote in message
...
Imagine all the added elbow room if the adjoining water heater was GONE

during
a furnace retrofit. Well, that's what I'm going to be doing (See Downsize
Water Heater ) in

a
little less than two weeks.

My contractor wants to DOWNSIZE to 75k from the 100k size of my

14-year-old,
conventional (spec) gas furnace. Of course, this will be done with a "90"

(or
better) model. He claims that the improved efficiency of the new furnace

will
compensate for the difference. Do you agree?


Unless the contractor provided the manual calculations or you have added a
bunch of insulation improvements since the orginal install, I would be
concerned.
Do you heat more than cool?
Efficiency is not BTU's, efficiency might help the consumption but not the
heating load back to BTU's again.



He also mentioned, after taking measurements TWICE, that I need an
18-inch-frame unit and that a bigger unit would require a reducing "boot",
which he represents as a compromise. What's with that?


The boot may be changing the duct from one size to another. I call it a
transition. Very common and I can not see the installation. A good
sheetmetal man can make a round funnel with a square hole.

Then there's the PVC vent(s) outside. He claims that it is legit to use

only
ONE - an exhaust line - that the furnace uses INTERIOR air for combustion.

He
represents this as a DESIRABLE way to EXCHANGE interior air with fresh.


The UPC, or uniform plumbing code in my area does reconize using inside air
for combustion. But since your heating why would you do that. All of the
combustion air is heated and must be replaced by,,,,,,,,,,,, cold air.
Most new gas appliances have charts for the combustion air sizes.
Sounds lazy to me.,,,,,,, again I can not see the installation.



I am old enough that this furnace may well be part a big part of the

resale
value of our home. He wants to install a "Weathermaker" furnace and a

Rheem
ac condensing unit outside. He says that the Weathermaker FURNACE is
virtually the same unit as a Rheem so this would be an up-front

cost-saving
issue ONLY, assuming he's right. What about resale then?


Resale is what the buyer will pay. Sheetmetal and a pretty sticker are just
that. Most buyers are just begining to think about operting costs. Higher
effency, and higher SEER may help the resale, New installs after 1 Jan 2006
are to be SEER 13 min. SEER is a cooling rating and has not a damn thing to
do with heating. Heating is a COP number.


He further says that the condensing units are different and therefore,
recommends a Rheem unit outside.


I have not a clue what you or he means by this.

Like the others have said, more contractors, more quotes before you decide.


JR



  #12   Report Post  
Posted to alt.home.repair
Mark
 
Posts: n/a
Default Downsize Furnace?


?

Ratings are based on input. Assuming a 100,000 Btu unit of 80% efficiency,
20,000 is going up the flue, not into your house. With a 100,000 Btu unit
of 90%, only 10,000 is going away, so you have an extra 10,000 going to heat
your house. Thus, a reduction in capacity will give the same amount of
heat.



Is that true?????

I thought furnace ratings were based on OUTPUT...i.e

a 100,000 BTU/Hr 90% furnace DELIVERS 100,000 BTU per hour.

and a 100,000 BTU/Hr 70% furncae also delivers 100,000 BTU/Hr but takes
more fuel to do it.

Correct?

My York (warm air oil fired) furnace nameplate says Bonnet BTU =
100,000 which I thought refers to the output not the input.

Correct?


Mark

  #13   Report Post  
Posted to alt.home.repair
Speedy Jim
 
Posts: n/a
Default Downsize Furnace?

Mark wrote:

?

Ratings are based on input. Assuming a 100,000 Btu unit of 80% efficiency,
20,000 is going up the flue, not into your house. With a 100,000 Btu unit
of 90%, only 10,000 is going away, so you have an extra 10,000 going to heat
your house. Thus, a reduction in capacity will give the same amount of
heat.




Is that true?????

I thought furnace ratings were based on OUTPUT...i.e

a 100,000 BTU/Hr 90% furnace DELIVERS 100,000 BTU per hour.

and a 100,000 BTU/Hr 70% furncae also delivers 100,000 BTU/Hr but takes
more fuel to do it.

Correct?

My York (warm air oil fired) furnace nameplate says Bonnet BTU =
100,000 which I thought refers to the output not the input.

Correct?


Mark



Oil furnaces are rated differently than gas.

Gas-fired ratings are input BTU, although output may also be listed.
  #14   Report Post  
Posted to alt.home.repair
Eugene Nine
 
Posts: n/a
Default Downsize Furnace?

Jim Redelfs wrote:

Imagine all the added elbow room if the adjoining water heater was GONE
during
a furnace retrofit. Well, that's what I'm going to be doing (See Downsize
Water Heater ) in
a little less than two weeks.

My contractor wants to DOWNSIZE to 75k from the 100k size of my
14-year-old,
conventional (spec) gas furnace. Of course, this will be done with a "90"
(or
better) model. He claims that the improved efficiency of the new furnace
will
compensate for the difference. Do you agree?

He also mentioned, after taking measurements TWICE, that I need an
18-inch-frame unit and that a bigger unit would require a reducing "boot",
which he represents as a compromise. What's with that?

Then there's the PVC vent(s) outside. He claims that it is legit to use
only
ONE - an exhaust line - that the furnace uses INTERIOR air for combustion.
He represents this as a DESIRABLE way to EXCHANGE interior air with
fresh.

I am old enough that this furnace may well be part a big part of the
resale
value of our home. He wants to install a "Weathermaker" furnace and a
Rheem
ac condensing unit outside. He says that the Weathermaker FURNACE is
virtually the same unit as a Rheem so this would be an up-front
cost-saving
issue ONLY, assuming he's right. What about resale then?

He further says that the condensing units are different and therefore,
recommends a Rheem unit outside.

He could be correct. I'm looking at replacing the 1979 furnace in my house
which is a 125000 BTU and current size estimates say I should have a 75,000
BTU so it appears mine was was oversized. How often does yours run now and
for how long, too large will short cycle.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Purchasing Furnace - 2-Stage Variable vs. Standard pipco Home Repair 21 January 27th 06 01:48 PM
Help. Furnace improperly installed? Chuck Home Repair 11 November 2nd 04 02:26 AM
Clueless Inspector Faults Furnace Install Hell Toupee Home Repair 3 October 8th 04 06:47 PM
Furnace problems - repair, replace or ???? Paul Home Repair 11 March 24th 04 12:59 AM
Furnace Problem...HELP! torque Home Repair 5 January 6th 04 01:24 AM


All times are GMT +1. The time now is 09:12 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"