pulling wire thru steel conduit
Is it possible/code to pull three #10 and three #8 wires thru a 3/4"
steel conduit? Thanks, Matt |
#2
Posted to alt.home.repair
|
|||
|
|||
pulling wire thru steel conduit
It's probably not physically possible and definitely a code violation. You
also have to consider that when you pull multiple conductors through a conduit, you must derate the capacity of the conductors as well wrote in message oups.com... Is it possible/code to pull three #10 and three #8 wires thru a 3/4" steel conduit? Thanks, Matt |
#3
Posted to alt.home.repair
|
|||
|
|||
pulling wire thru steel conduit
|
#4
Posted to alt.home.repair
|
|||
|
|||
pulling wire thru steel conduit
|
#5
Posted to alt.home.repair
|
|||
|
|||
pulling wire thru steel conduit
Speedy Jim wrote: #10 THHN 40 Amp X 80% = 32 Amps, so 30 Amp protection is suitable. #8 THHN 55 Amp X 80% = 44 Amps, so 40 Amp protection is suitable. Electrically looks OK, but how's he going to get all that around the bends? |
#6
Posted to alt.home.repair
|
|||
|
|||
pulling wire thru steel conduit
He can use a wire pulling lubricant like Ideal Yellow77.
http://www.idealindustries.com/IDEAL...s?OpenDocument "Nexus7" wrote in message ups.com... Speedy Jim wrote: #10 THHN 40 Amp X 80% = 32 Amps, so 30 Amp protection is suitable. #8 THHN 55 Amp X 80% = 44 Amps, so 40 Amp protection is suitable. Electrically looks OK, but how's he going to get all that around the bends? |
#7
Posted to alt.home.repair
|
|||
|
|||
pulling wire thru steel conduit
) said...
Is it possible/code to pull three #10 and three #8 wires thru a 3/4" steel conduit? It depends on what the insulation is! It is the cross sectional area that matters, as you are not supposed to exceed 40% of the conduit's area. If all these wires have T90 Nylon insulation, then their cross section area is only 31.8% of the conduit's. If they are TW75, then they are 39.6%, so they would also fit. If they are RWU75 EP, then they are 63.8% of the conduit's fill. I have a "conduit calculator" available for free at http://daxack.ca that comes with cross-section data for a number of different types of wire. -- Calvin Henry-Cotnam "Never ascribe to malice what can equally be explained by incompetence." - Napoleon ------------------------------------------------------------------------- NOTE: if replying by email, remove "remove." and ".invalid" |
#8
Posted to alt.home.repair
|
|||
|
|||
pulling wire thru steel conduit
Calvin Henry-Cotnam wrote:
) said... Is it possible/code to pull three #10 and three #8 wires thru a 3/4" steel conduit? It depends on what the insulation is! It is the cross sectional area that matters, as you are not supposed to exceed 40% of the conduit's area. If all these wires have T90 Nylon insulation, then their cross section area is only 31.8% of the conduit's. If they are TW75, then they are 39.6%, so they would also fit. If they are RWU75 EP, then they are 63.8% of the conduit's fill. I have a "conduit calculator" available for free at http://daxack.ca that comes with cross-section data for a number of different types of wire. Good link. Thanks! R |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Pulling large wire in conduit | Electronics Repair | |||
Pulling large wire in conduit | Electronics Repair | |||
Wire and conduit size | Home Repair | |||
My Air Conditioner -- I don't think I goofed up.... | Home Repair | |||
Is it possible to find wire insulation faults without a visual exam? | Home Ownership |