#1
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
I have a Lutron Skylark model 600-P dimmer that smokes and causes a
burning smell when it is turned on. I took the switch out and found that the smoke is coming from inside the switch itself; the external wiring connections are solid. I did not take apart the switch itself to inspect the connections inside, figuring that those connections are pre-configured. Am I simply looking at a switch that has gone bad, or is there something else that could be wrong? |
#2
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
"DaveR" wrote in message ... I have a Lutron Skylark model 600-P dimmer that smokes and causes a burning smell when it is turned on. I took the switch out and found that the smoke is coming from inside the switch itself; the external wiring connections are solid. I did not take apart the switch itself to inspect the connections inside, figuring that those connections are pre-configured. Am I simply looking at a switch that has gone bad, or is there something else that could be wrong? Your lucky your house didn't go bad with it |
#3
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
According to DaveR :
Am I simply looking at a switch that has gone bad, or is there something else that could be wrong? If it's been fine until the smoke, it's probably going bad. If there's a wiring fault (ie: a short), dimmers usually fry instantaneously[+]. It would be highly unusual for a wiring fault to only draw enough current to make the dimmer overheat without going kaboom. You should also check the wattage of what the thing is driving. Most dimmers are limited to 500-600W, and some to 300W. If this is a new installation, or you recently relamped the circuit with higher wattage bulbs, I'd strongly suspect a simple overload, which you can resolve by choosing a higher capacity dimmer, or reducing the quantity/wattage of the lamps. Check the wattage regardless of whether it's a new circuit or new bulbs. In any case, once a dimmer starts to smoke, I'd replace it. [+] dead shorts thru on-state Triacs tend to be a bit on the fast and spectacular (or at least noisy - "gunshot" type noises aren't uncommon) side. They usually fry faster than the fuses or breakers do. -- Chris Lewis, Una confibula non set est It's not just anyone who gets a Starship Cruiser class named after them. |
#4
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
DaveR wrote:
I have a Lutron Skylark model 600-P dimmer that smokes and causes a burning smell when it is turned on. I took the switch out and found that the smoke is coming from inside the switch itself; the external wiring connections are solid. I did not take apart the switch itself to inspect the connections inside, figuring that those connections are pre-configured. Am I simply looking at a switch that has gone bad, or is there something else that could be wrong? Just replace the switch, first make sure that the total load is less than the rated capacity of the switch. Don't try to fix the switch or continue to use it. If you like, I suspect that Lutron may replace it free if you send the damaged one back to them. Again only if it was controlling a circuit within it's rated value. -- Joseph Meehan Dia duit |
#6
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
According to DaveR :
Thanks for the advice. This dimmer was newly installed (professionally) 3 years ago and it has been working fine until recently. I did see the occasional spark when turning on the switch but I was told this is common in the Skylarks and not necessarily dangerous. None of the bulbs have been changed. It is a 600W dimmer driving exactly 6 100W bulbs. I guess I will just replace the switch. Uprate the dimmer to something beefier - say, 1KW, or, lower the wattage of the bulbs. Ie: switch to 75W quartz halogen - more light, less power. I don't like devices run at their extreme limit. It'll probably run warm all the time, and the lifetime will be shortened (as it was). -- Chris Lewis, Una confibula non set est It's not just anyone who gets a Starship Cruiser class named after them. |
#7
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
Chris Lewis wrote:
According to DaveR : Am I simply looking at a switch that has gone bad, or is there something else that could be wrong? If it's been fine until the smoke, it's probably going bad. Probably...? R |
#8
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
"RicodJour" wrote in message ups.com... Chris Lewis wrote: According to DaveR : Am I simply looking at a switch that has gone bad, or is there something else that could be wrong? If it's been fine until the smoke, it's probably going bad. Probably...? R Well, I think he meant "maybe". :-) |
#9
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
Doug Kanter wrote:
"RicodJour" wrote in message ups.com... Chris Lewis wrote: According to DaveR : Am I simply looking at a switch that has gone bad, or is there something else that could be wrong? If it's been fine until the smoke, it's probably going bad. Probably...? R Well, I think he meant "maybe". :-) I thought he meant "almost certainly." :-) -- The e-mail address in our reply-to line is reversed in an attempt to minimize spam. Our true address is of the form . |
#10
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
On Fri, 02 Dec 2005 10:24:18 -0500, DaveR
wrote: I have a Lutron Skylark model 600-P dimmer that smokes and causes a Smoking is bad for dimmer switches. Get the Patch or some nictoine gum, and try to get it to use that. If it won't, get rid of it and get a new switch. Why should you be responsible for its eventual medical bills. burning smell when it is turned on. I took the switch out and found that the smoke is coming from inside the switch itself; the external wiring connections are solid. I did not take apart the switch itself to inspect the connections inside, figuring that those connections are pre-configured. Am I simply looking at a switch that has gone bad, or is there something else that could be wrong? Remove NOPSAM to email me. Please let me know if you have posted also. |
#11
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
"RicodJour" wrote in message ups.com... Chris Lewis wrote: According to DaveR : Am I simply looking at a switch that has gone bad, or is there something else that could be wrong? If it's been fine until the smoke, it's probably going bad. It's common knowledge that dimmers run on smoke. When the smoke leaks out, they stop running. |
#12
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
Lutron has agreed to send a new switch and pay for shipping the old
one back, even though it is out of warranty. Great customer service! |
#13
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
smoke....fire.......bad...........
"DaveR" wrote in message ... I have a Lutron Skylark model 600-P dimmer that smokes and causes a burning smell when it is turned on. I took the switch out and found that the smoke is coming from inside the switch itself; the external wiring connections are solid. I did not take apart the switch itself to inspect the connections inside, figuring that those connections are pre-configured. Am I simply looking at a switch that has gone bad, or is there something else that could be wrong? |
#14
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
DaveR wrote:
Lutron has agreed to send a new switch and pay for shipping the old one back, even though it is out of warranty. Great customer service! Yea. I once wrote them about the possibility of getting a small plastic part that have broken off, also out of warranty. They called me as soon as they got the letter and wanted to know what color the switch was. I tried to explain that it was an internal part and the color was not important. They explained they did not have the part, but wanted to send me a new switch. They cost a little more and I would not normally worry about a broken switch, but I still appreciate their effort to provide a level of customer service not normally seen. -- Joseph Meehan Dia duit |
#15
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
Chris Lewis wrote:
According to DaveR : Thanks for the advice. This dimmer was newly installed (professionally) 3 years ago and it has been working fine until recently. I did see the occasional spark when turning on the switch but I was told this is common in the Skylarks and not necessarily dangerous. None of the bulbs have been changed. It is a 600W dimmer driving exactly 6 100W bulbs. I guess I will just replace the switch. Uprate the dimmer to something beefier - say, 1KW, or, lower the wattage of the bulbs. Ie: switch to 75W quartz halogen - more light, less power. I don't like devices run at their extreme limit. It'll probably run warm all the time, and the lifetime will be shortened (as it was). Even running well within limits a solid state controller can be damaged by an incandescent lamp burning out with a "tungsten arc". That happens occasionally when the filament opens and an arc starts through the vaporized tungsten between the broken ends. That arc burns back along the two filament pieces until it's consumed them, with the current increasing while that happens. It all takes place faster than Jill Robinson, and sometimes it's enough to blow a conventional 15 or 20 amp glass fuse, but they seldom last long enough to trip a breaker. If you've ever flipped on a light switch and had the bulb blow out with a bright flash, you've seen one. Better brands of incandescent bulbs used to have a fuse built into one of the internal bulb leads which was intended to blow when a tungsten arc occured, but a lot of the cheapies don't bother with them. I used to have trouble with several table lamps in out home which I'd fitted with solid state "touch switch" dimmers. Every once in a while a bulb blew with a tungsten arc and took the dimmer with it. I solved the problem by fitting fuseholders with 2 amp quick blow 3AG fuses in each lamp. I've had a few bulbs fail and blow the fuses, but the dimmers were saved. Jeff -- Jeffry Wisnia (W1BSV + Brass Rat '57 EE) "Truth exists; only falsehood has to be invented." |
#16
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
On Fri, 02 Dec 2005 10:24:18 -0500, DaveR
wrote: I have a Lutron Skylark model 600-P dimmer that smokes and causes a burning smell when it is turned on. I took the switch out and found that the smoke is coming from inside the switch itself; the external wiring connections are solid. I did not take apart the switch itself to inspect the connections inside, figuring that those connections are pre-configured. Am I simply looking at a switch that has gone bad, or is there something else that could be wrong? Replace it Be sure your load is not too high If the load is not too high, contact the manufacturer. They should know about the danger and will likely send you a free dimmer too. DO NOT reinstall that thing !!!! |
#18
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
In article , Chris Lewis wrote:
According to DaveR : Thanks for the advice. This dimmer was newly installed (professionally) 3 years ago and it has been working fine until recently. I did see the occasional spark when turning on the switch but I was told this is common in the Skylarks and not necessarily dangerous. None of the bulbs have been changed. It is a 600W dimmer driving exactly 6 100W bulbs. I guess I will just replace the switch. Uprate the dimmer to something beefier - say, 1KW, or, lower the wattage of the bulbs. Ie: switch to 75W quartz halogen - more light, less power. 75 watt halogen normally produces less light than 100 watt decent non-halogen incandescent. A 120V halogen needs 90 watts to produce the 1670-1750 lumens of a "standard" 100 watt 120V 750 hour incandescent. If you are using longlife or vibration-resistant or 130V 100 watt incandescent, or ones other than "Big 3" (GE/Sylvania/Philips and their store brand ones with same/similar lumen and hour ratings), then you could be able to downsize to 75 watts - and they may not have to be halogen. I don't like devices run at their extreme limit. It'll probably run warm all the time, and the lifetime will be shortened (as it was). I agree on that one! - Don Klipstein ) |
#19
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
I talked to Lutron about a client's Skylark and they seemed very
nervious that it was run at 600W. They asked if the heat sink tabs had been removed on the front. Definately replace the unit up to 1000W or bulb at 75W max as above. Richard |
#21
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
DaveR wrote:
On 4 Dec 2005 23:35:17 -0800, wrote: I talked to Lutron about a client's Skylark and they seemed very nervious that it was run at 600W. They asked if the heat sink tabs had been removed on the front. Definately replace the unit up to 1000W or bulb at 75W max as above. Seems strange to me that a device should be rated at 600W and yet be "pushing its limits" at that load. I would think the rating should be somewhat conservative. Nevertheless I don't doubt that my 600W load probably had something to do with the problem. I will pull out one of the 100W bulbs which I really don't need, and then eventually replace the rest with 75W which should be sufficient for this room. I have a bunch of other 600W Skylarks in my home but thankfully they are all pushing 300W or less. Switch over to compact fluorescents. They use about 25% of the energy, give excellent light and last far longer. R |
#22
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
Seems strange to me that a device should be rated at 600W and yet be "pushing its limits" at that load. I would think the rating should be somewhat conservative. Yah this lady had a problem with hers that was pushing 600W when her husband was home. He liked these lights up all the way and the lights would periodically go out. She liked the lights around 50% and never had a problem. I agree Lutron should rerate this model at around 500W! And that stuff about removing the heatsink tabs lowering the rating (although they never actually admitted to that it was implied) seemed totally out of line. Richard |
#23
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
In article .com,
RicodJour wrote: Switch over to compact fluorescents. They use about 25% of the energy, give excellent light and last far longer. Except that most CF bulbs can't be dimmed. -- Rich Greenberg Marietta, GA, USA richgr atsign panix.com + 1 770 321 6507 Eastern time. N6LRT I speak for myself & my dogs only. VM'er since CP-67 Canines:Val, Red & Shasta (RIP),Red, husky Owner:Chinook-L Atlanta Siberian Husky Rescue. www.panix.com/~richgr/ Asst Owner:Sibernet-L |
#24
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
On Fri, 02 Dec 2005 10:24:18 -0500, DaveR
wrote: I have a Lutron Skylark model 600-P dimmer that smokes and causes a burning smell when it is turned on. Let me guess. You forgot to put a "No Smoking" sign in that room !!!!! |
#25
Posted to alt.home.repair
|
|||
|
|||
Dimmer Switch Smoking
"RicodJour" wrote in message ups.com... Chris Lewis wrote: According to DaveR : Am I simply looking at a switch that has gone bad, or is there something else that could be wrong? If it's been fine until the smoke, it's probably going bad. Probably...? Ah, yes, the Magic Electric Smoke, that makes all electronic and electrical itens work. Once you let too much of the smoke escape, they don't work anymore. BTDT, too many times to count. (This house I bought had a similarly flaky dimmer. I looked at the 1 hall light it controlled, decided I would never need to run that at reduced power, and replaced it with a 3-buck single pole toggle.) aem sends... |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Re-Post for Wall Switch | Home Repair | |||
Is this the way a 3-way dimmer switch works? | Home Repair | |||
kitchen lights nightmare | Home Repair | |||
VS Dimmer Switch Use | Woodworking | |||
Dimmer switch on a ceilling fan controlled at one wall switch | Metalworking |