Help...

I have a double breaker labelled as 50 amps that runs from my house to
my garage by two 6 gauge stranded wires. It goes to a box in the garage
that has 4 15 amp breakers in it, 2 on each leg. Each of the 6 gauge
wires connect to each leg in the box. I have a grounding rod 6 feet in
the ground as that is a far as it will go, must be rock below it, and
the rod is connected to the neutral / common strip in the box.

Is this setup correct? I can measure 125V on each leg to ground, but
once I put a load on one of the legs, the voltage drops to 70V and the
other leg reads 180V, what is going on here?

Thanks much,

Sean

  #2   Report Post  
Posted to alt.home.repair
Speedy Jim
 
Posts: n/a
Default Garage electrical issue

Sean wrote:

Help...

I have a double breaker labelled as 50 amps that runs from my house to
my garage by two 6 gauge stranded wires. It goes to a box in the garage
that has 4 15 amp breakers in it, 2 on each leg. Each of the 6 gauge
wires connect to each leg in the box. I have a grounding rod 6 feet in
the ground as that is a far as it will go, must be rock below it, and
the rod is connected to the neutral / common strip in the box.

Is this setup correct? I can measure 125V on each leg to ground, but
once I put a load on one of the legs, the voltage drops to 70V and the
other leg reads 180V, what is going on here?

Thanks much,

Sean


Not correct. They left a wire out when they ran the cable to the
garage.
The "ground" rod is not sufficient to act as a Neutral
conductor.

Jim
  #3   Report Post  
Posted to alt.home.repair
Tony Hwang
 
Posts: n/a
Default Garage electrical issue

Sean wrote:

Help...

I have a double breaker labelled as 50 amps that runs from my house to
my garage by two 6 gauge stranded wires. It goes to a box in the garage
that has 4 15 amp breakers in it, 2 on each leg. Each of the 6 gauge
wires connect to each leg in the box. I have a grounding rod 6 feet in
the ground as that is a far as it will go, must be rock below it, and
the rod is connected to the neutral / common strip in the box.

Is this setup correct? I can measure 125V on each leg to ground, but
once I put a load on one of the legs, the voltage drops to 70V and the
other leg reads 180V, what is going on here?

Thanks much,

Sean

Hi,
Ground or neutral? How many wired do you see coming into garage?
Tony
  #4   Report Post  
Posted to alt.home.repair
Sean
 
Posts: n/a
Default Garage electrical issue

There are two 6 guage to the garage. They come directly from the dual
breaker in the house. Nothing else, so I assume I will need to run
another 6 gauge for neutral?

  #5   Report Post  
Posted to alt.home.repair
Tony Hwang
 
Posts: n/a
Default Garage electrical issue

Sean wrote:

There are two 6 guage to the garage. They come directly from the dual
breaker in the house. Nothing else, so I assume I will need to run
another 6 gauge for neutral?

Hi,
And ground.
Looks like some one half finished the wiring job. Went to lunch break
and forgot to come back and finish?
Tony


  #6   Report Post  
Posted to alt.home.repair
Toller
 
Posts: n/a
Default Garage electrical issue


"Sean" wrote in message
ups.com...
There are two 6 guage to the garage. They come directly from the dual
breaker in the house. Nothing else, so I assume I will need to run
another 6 gauge for neutral?

You need to add two wires; a ground and a neutral. And they all have to run
through the same holes in metal.
Good example of a floating neutral.


  #7   Report Post  
Posted to alt.home.repair
ameijers
 
Posts: n/a
Default Garage electrical issue


"Sean" wrote in message
oups.com...
Help...

I have a double breaker labelled as 50 amps that runs from my house to
my garage by two 6 gauge stranded wires. It goes to a box in the garage
that has 4 15 amp breakers in it, 2 on each leg. Each of the 6 gauge
wires connect to each leg in the box. I have a grounding rod 6 feet in
the ground as that is a far as it will go, must be rock below it, and
the rod is connected to the neutral / common strip in the box.

Is this setup correct? I can measure 125V on each leg to ground, but
once I put a load on one of the legs, the voltage drops to 70V and the
other leg reads 180V, what is going on here?

I'm no electrician, and even I can tell this setup ain't kosher. Sounds like
somone had a stone-age 2-wire setup for a 240v circuit (2 hots, one from
each side of the house panel, using each other as the 'neutral'), to run a
welder or something. They then tried to use it for 2 different branch
circuits, which as you found, doesn't really work, especially with
unbalanced loads.

My advice, and your insurance agent would agree- turned the 50-amp ganged
breaker off, and don't use that circuit, until you rewire it all properly.
If previous owner would do hillbilly crap like that, who knows what they did
where you haven't looked yet? I'd have a pro go over all the house wiring.

aem sends...

  #8   Report Post  
Posted to alt.home.repair
Beachcomber
 
Posts: n/a
Default Garage electrical issue


My advice, and your insurance agent would agree- turned the 50-amp ganged
breaker off, and don't use that circuit, until you rewire it all properly.
If previous owner would do hillbilly crap like that, who knows what they did
where you haven't looked yet? I'd have a pro go over all the house wiring.


Agreed.... You have a dangerous situation there. The only
applications where a neutral would not be present is in situations
where only 240 volt appliances were used. But you would still need a
hard-wire ground back to your main panel.

Beachcomber

  #9   Report Post  
Posted to alt.home.repair
PrecisionMachinisT
 
Posts: n/a
Default Garage electrical issue


"Tony Hwang" wrote in message
news:78Qff.538906$1i.393306@pd7tw2no...
Sean wrote:

There are two 6 guage to the garage. They come directly from the dual
breaker in the house. Nothing else, so I assume I will need to run
another 6 gauge for neutral?

Hi,
And ground.
Looks like some one half finished the wiring job. Went to lunch break
and forgot to come back and finish?


He forgot to install a transformer.

--

SVL


  #10   Report Post  
Posted to alt.home.repair
Bud--
 
Posts: n/a
Default Garage electrical issue

Tony Hwang wrote:
Sean wrote:

There are two 6 guage to the garage. They come directly from the dual
breaker in the house. Nothing else, so I assume I will need to run
another 6 gauge for neutral?

Hi,
And ground.
Looks like some one half finished the wiring job. Went to lunch break
and forgot to come back and finish?
Tony


2 options:
Add neutral. Neutral bar at garage connects to ground rod and
panel/ground bar (usually a screw in the ground bar). There can be no
continuous metal connections from the house to garage.

Add neutral and ground. Neutral bar at garage does not connect to
panel/ground bar. Ground wire from house connects to panel/ground bar
and ground rod.

bud--


  #11   Report Post  
Posted to alt.home.repair
glenn P
 
Posts: n/a
Default Garage electrical issue

Wow, to be completely honest with you - if you don't understand this
situation straight away, you should hire an electrician.

Your situation requires a relatively simple fix, but asking a NG, when
getting it wrong could mean your house may burn down isn't my idea of very
smart.


"Sean" wrote in message
oups.com...
Help...

I have a double breaker labelled as 50 amps that runs from my house to
my garage by two 6 gauge stranded wires. It goes to a box in the garage
that has 4 15 amp breakers in it, 2 on each leg. Each of the 6 gauge
wires connect to each leg in the box. I have a grounding rod 6 feet in
the ground as that is a far as it will go, must be rock below it, and
the rod is connected to the neutral / common strip in the box.

Is this setup correct? I can measure 125V on each leg to ground, but
once I put a load on one of the legs, the voltage drops to 70V and the
other leg reads 180V, what is going on here?

Thanks much,

Sean



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Kinda off topic...House electrical issue? hk538 Electronics Repair 3 November 22nd 05 10:15 AM
Kinda off topic...House electrical issue? hk538 Electronics Repair 6 November 21st 05 02:32 AM
Sears (Chamberlain) Garage Door Opener Randomly Opening Jeff Gaiche Home Ownership 1 February 12th 04 02:48 AM
OT Environmentalists may be in deep Kimchee Gunner Metalworking 562 January 6th 04 07:04 AM
Building a garage above public sewer (UK) Capitol UK diy 3 July 15th 03 11:43 PM


All times are GMT +1. The time now is 05:44 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"