I have a 10-7501 Emergen manual transfer switch for my generator. I
want to hook my hot water tank to this panel for use when the power is
out during our hurricane season. Here's what I have - the hot water
tank says 4500 watts on the upper and 4500 watts on the lower for a
total of 4500 watts. Wired at 240v - if I did my math right, that
should be about 18.75 amps. Currently it is on a 25 amp breaker on my
main panel. The Emergen switch has 20 amp breakers. So if I use the
switch bar to combine two 20 amp breakers to pick up both wires, one on
each breaker, on the Emergen panel, I should be ok, right? My generator
is rated at 5250w, so I know that all other breakers on my Emergen
switch need to be off while the hot water tank is on, but I only plan
on running the hot water tank maybe for an hour every other day. Thanks
much fo your responses.

  #2   Report Post  
m Ransley
 
Posts: n/a
Default Conneticut Electric Transfer Panel EmerGen Switch

On my Generac 6 circuit the 2 center breakers are prewired for locking
together for 220. Or separate 120. Yours might be this way also, my
panel was prewired so it was easy, I dont know if yours is

  #3   Report Post  
RBM
 
Posts: n/a
Default Conneticut Electric Transfer Panel EmerGen Switch

The switches in your transfer panel are to light for the water heater. you
need a double pole switch rated at 30 amps or you'll burn it out. Keep in
mind that the electricity from the utility company is going to run through
your transfer switch as well, so you will constantly be overloading the 20
amp switch, not just when the generator is in use




wrote in message
oups.com...
I have a 10-7501 Emergen manual transfer switch for my generator. I
want to hook my hot water tank to this panel for use when the power is
out during our hurricane season. Here's what I have - the hot water
tank says 4500 watts on the upper and 4500 watts on the lower for a
total of 4500 watts. Wired at 240v - if I did my math right, that
should be about 18.75 amps. Currently it is on a 25 amp breaker on my
main panel. The Emergen switch has 20 amp breakers. So if I use the
switch bar to combine two 20 amp breakers to pick up both wires, one on
each breaker, on the Emergen panel, I should be ok, right? My generator
is rated at 5250w, so I know that all other breakers on my Emergen
switch need to be off while the hot water tank is on, but I only plan
on running the hot water tank maybe for an hour every other day. Thanks
much fo your responses.



  #4   Report Post  
m Ransley
 
Posts: n/a
Default Conneticut Electric Transfer Panel EmerGen Switch

My transfer panel is prewired and designed for 220 heavy loads, yours
may be , call the manufacturer.

  #5   Report Post  
 
Posts: n/a
Default Conneticut Electric Transfer Panel EmerGen Switch

"Here's what I have - the hot water
tank says 4500 watts on the upper and 4500 watts on the lower for a
total of 4500 watts. Wired at 240v - if I did my math right, that
should be about 18.75 amps. Currently it is on a 25 amp breaker on my
main panel."

Thats 18.75 amps per heating element. Aren't these normally wired so
that both elements can be on at the same time? That would then be 37
amps on a 25 amp breaker?



  #6   Report Post  
John Grabowski
 
Posts: n/a
Default Conneticut Electric Transfer Panel EmerGen Switch

It is not likely that you have 240 volts coming into your house. The
voltage coming in is probably somewhere between 208 and 220. In that case
the calculated amperage draw will be higher than 18.75. I suggest that you
put an ammeter on the circuit to see what the actual load is. I'm guessing
that it may be lower than what you calculated.



wrote in message
oups.com...
I have a 10-7501 Emergen manual transfer switch for my generator. I
want to hook my hot water tank to this panel for use when the power is
out during our hurricane season. Here's what I have - the hot water
tank says 4500 watts on the upper and 4500 watts on the lower for a
total of 4500 watts. Wired at 240v - if I did my math right, that
should be about 18.75 amps. Currently it is on a 25 amp breaker on my
main panel. The Emergen switch has 20 amp breakers. So if I use the
switch bar to combine two 20 amp breakers to pick up both wires, one on
each breaker, on the Emergen panel, I should be ok, right? My generator
is rated at 5250w, so I know that all other breakers on my Emergen
switch need to be off while the hot water tank is on, but I only plan
on running the hot water tank maybe for an hour every other day. Thanks
much fo your responses.


  #7   Report Post  
Toller
 
Posts: n/a
Default Conneticut Electric Transfer Panel EmerGen Switch


wrote in message
oups.com...
I have a 10-7501 Emergen manual transfer switch for my generator. I
want to hook my hot water tank to this panel for use when the power is
out during our hurricane season. Here's what I have - the hot water
tank says 4500 watts on the upper and 4500 watts on the lower for a
total of 4500 watts. Wired at 240v - if I did my math right, that
should be about 18.75 amps. Currently it is on a 25 amp breaker on my
main panel. The Emergen switch has 20 amp breakers. So if I use the
switch bar to combine two 20 amp breakers to pick up both wires, one on
each breaker, on the Emergen panel, I should be ok, right? My generator
is rated at 5250w, so I know that all other breakers on my Emergen
switch need to be off while the hot water tank is on, but I only plan
on running the hot water tank maybe for an hour every other day. Thanks
much fo your responses.

How is 4500w on the top and 4500w on the bottom a total of 4500w? I get
9000w.

My water heater is small and draws 23a, so I expect yours is probably 37a.

Just in general, resistance heating is not a good use for a generator.


  #8   Report Post  
 
Posts: n/a
Default Conneticut Electric Transfer Panel EmerGen Switch

Elements are powered either/or, not both. Thus 4500w & 4500w elements
draw 4500 between them.

IMHO resistive heating is lousy, inefficient use of energy input. Max
overall efficiency about 30%. One reason gas costs so much less.

Too bad you can't use generator's waste heat (exhaust) to heat the
water! About the same actual power (energy rate) available there as at
alternator output.

J

  #9   Report Post  
Toller
 
Posts: n/a
Default Conneticut Electric Transfer Panel EmerGen Switch



Elements are powered either/or, not both. Thus 4500w & 4500w elements
draw 4500 between them.

I learn something new everyday, mine had just one element.
What is the point of two elements then?


  #10   Report Post  
SQLit
 
Posts: n/a
Default Conneticut Electric Transfer Panel EmerGen Switch


wrote in message
oups.com...
"Here's what I have - the hot water
tank says 4500 watts on the upper and 4500 watts on the lower for a
total of 4500 watts. Wired at 240v - if I did my math right, that
should be about 18.75 amps. Currently it is on a 25 amp breaker on my
main panel."

Thats 18.75 amps per heating element. Aren't these normally wired so
that both elements can be on at the same time? That would then be 37
amps on a 25 amp breaker?


Not usually in my experience. The upper stat should be set higher and only
works when there is a large demand. Most of the time the lower stat (set ~5
F less than the upper) is the one that runs.
At least on the ones I have seen.




  #11   Report Post  
 
Posts: n/a
Default Conneticut Electric Transfer Panel EmerGen Switch

"Not usually in my experience. The upper stat should be set higher and
only
works when there is a large demand. Most of the time the lower stat
(set ~5
F less than the upper) is the one that runs.
At least on the ones I have seen. "

The issue isn't what happens MOST of the time. The issue is whether
water heaters are usually wired so that both elements CAN be on at the
same time. If they are, then the circuit and breaker need to be able
to support both elements at a time, not one.

  #12   Report Post  
RBM
 
Posts: n/a
Default Conneticut Electric Transfer Panel EmerGen Switch

I suppose because the hot water rises, the upper thermostat powers the upper
element, then when its temp is satisfied it disconnects power and sends it
to the lower thermostat which powers the lower element. They never work at
the same time.



"Toller" wrote in message
...


Elements are powered either/or, not both. Thus 4500w & 4500w elements
draw 4500 between them.

I learn something new everyday, mine had just one element.
What is the point of two elements then?



  #13   Report Post  
Chris Lewis
 
Posts: n/a
Default Conneticut Electric Transfer Panel EmerGen Switch

According to :
"Not usually in my experience. The upper stat should be set higher and
only
works when there is a large demand. Most of the time the lower stat
(set ~5
F less than the upper) is the one that runs.
At least on the ones I have seen. "


The issue isn't what happens MOST of the time. The issue is whether
water heaters are usually wired so that both elements CAN be on at the
same time. If they are, then the circuit and breaker need to be able
to support both elements at a time, not one.


The thermostats are interlocked so that only one element can be on at
a time.

Otherwise, not even a 30A circuit would be big enough for a 4500W HWT.

Note that it said: "4500 lower, 4500 upper, 4500 total". Meaning, it can't
be more than 4500W.
--
Chris Lewis, Una confibula non set est
It's not just anyone who gets a Starship Cruiser class named after them.
  #14   Report Post  
Chris Lewis
 
Posts: n/a
Default Conneticut Electric Transfer Panel EmerGen Switch

According to RBM rbm2(remove :
I suppose because the hot water rises, the upper thermostat powers the upper
element, then when its temp is satisfied it disconnects power and sends it
to the lower thermostat which powers the lower element. They never work at
the same time.


Think of it this way: when you need hot water fast, the upper unit is on.

When you want a lot of water maintained, the lower unit is on.

The amount of heat stratification in a HWT can be pretty amazing. Only
when you heat from the bottom do you get uniform heat. The top element
acts somewhat like an "on demand" when you pull a lot of water.
--
Chris Lewis, Una confibula non set est
It's not just anyone who gets a Starship Cruiser class named after them.
  #15   Report Post  
Chris Lewis
 
Posts: n/a
Default Conneticut Electric Transfer Panel EmerGen Switch

According to John Grabowski :
It is not likely that you have 240 volts coming into your house. The
voltage coming in is probably somewhere between 208 and 220. In that case
the calculated amperage draw will be higher than 18.75. I suggest that you
put an ammeter on the circuit to see what the actual load is. I'm guessing
that it may be lower than what you calculated.


Uh, no. The voltage will be somewhere between 230v and 250V approximately.
The utilities are required to provide 240V +/- 5% or so at the panel.

208V is an entirely different type of electrical service (part of
a three phase circuit), most often seen in industrial/commercial situations,
and is fairly rare in residential situations. Extremely rare in detached homes.
--
Chris Lewis, Una confibula non set est
It's not just anyone who gets a Starship Cruiser class named after them.


  #16   Report Post  
DW
 
Posts: n/a
Default Conneticut Electric Transfer Panel EmerGen Switch

Both elements are never on at the same time. And with utility power
running through it, it has never thrown the breakers. Hope this helps

  #17   Report Post  
Stretch
 
Posts: n/a
Default Conneticut Electric Transfer Panel EmerGen Switch

The elements and thermostats are wired so only ONE element can be on at
any one time. When first turned on, the top thermostat powers the top
element and disconnects the bottom element. This heats the only top
few gallons, so for that few gallons recovery is fast. Then when the
top part gets hot, the upper thermostat switches power to the botom
thermostat. The bottom thermostat powers the bottom element till the
entire tank has hot water. Then the bottom thermostat opens and the
power is off to both elements. When you start to use hot water, the
cold water comes into the bottom of the tank through the dip tube and
the bottom thermostat closes first. Since the top is still hot, the
bottom element comes on and you heat the water in the bottom, which
will convect up and therefore heat the entire tank. The hottest water
stays at the top and the coldest water stays at the bottom. If you use
all the hot water in the tank, the top thermostat switches power on to
the top element for quick recovery in the top of the tank, then
switches power back to the bottom again.

NOTE: Because there is no flue or flue losses, the efficiency is 100%,
not 30%. Electricity usually costs more than gas, so a gas water
heater that is 75% efficiency is usually cheaper to operate and
recovers faster because the burner usually provides more BTUs than an
electric element.

Your breaker should be sized at 125% of the continuous load.

That means that you need at least 25 amps. If your voltage is a little
high, you may need a 30 amp breaker, because with high voltage, the
amps will be higher as well.

Hope this helps.

Stretch

  #18   Report Post  
Stretch
 
Posts: n/a
Default Conneticut Electric Transfer Panel EmerGen Switch

Our voltage at my house is 248 volts. When I lived up north, it was
commonly about 220 volts due to older transformers and power
distribution systems (power company) It all depends on where you are.
Around here many condos are fed with 3 phase. Each unit gets single
phase 208 volts.

Stretch

  #19   Report Post  
MC
 
Posts: n/a
Default Conneticut Electric Transfer Panel EmerGen Switch

DW wrote:
Both elements are never on at the same time. And with utility power
running through it, it has never thrown the breakers. Hope this helps

Depends on how it may be wired. Many water heaters have the option of
having both to come on independently which means that can be on at the
same time. Most come factory wired in cascading operation where one is
off when the other is on.

That can mean the difference of 4500 watts or 9000 watts. Of course if
not wired can be for the latter operation so that only 4500 watts would
be needed at any time.




Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Home Generator / Automatic Transfer Switch Way Back Jack Home Repair 19 March 17th 05 05:35 AM
What size cable with my transfer switch? Toller Home Repair 12 June 11th 04 06:57 PM
Generator FAQ Gunner Metalworking 0 January 23rd 04 05:24 PM
Earthing Sparks UK diy 10 October 29th 03 01:27 AM
Electric Panel Rating Bruce Home Repair 2 July 12th 03 08:23 AM


All times are GMT +1. The time now is 03:47 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"