I would like to run regular Romex up the interior wall of our garage
and then switch to conduit running along the ceiling.

What do I need to do to transition at the point where the Romex exits
the wall and enters the conduit?

I assume I need some type of brushing to hold the wire in place and
prevent it from scraping. Beyond that is it sufficient just to push
the conduit entrance up tight to the exit hole from the wall?

What specifically do I need to use here?

Thanks

  #2   Report Post  
SQLit
 
Posts: n/a
Default Transitioning from in-wall wiring to EMT (conduit)...


"blueman" wrote in message
...
I would like to run regular Romex up the interior wall of our garage
and then switch to conduit running along the ceiling.

What do I need to do to transition at the point where the Romex exits
the wall and enters the conduit?

I assume I need some type of brushing to hold the wire in place and
prevent it from scraping. Beyond that is it sufficient just to push
the conduit entrance up tight to the exit hole from the wall?

What specifically do I need to use here?

Thanks


a box with a conduit connector on side side and a romex connector on the
other would work.


  #3   Report Post  
RBM
 
Posts: n/a
Default Transitioning from in-wall wiring to EMT (conduit)...

You can use an EMT to Romex connector


"blueman" wrote in message
...
I would like to run regular Romex up the interior wall of our garage
and then switch to conduit running along the ceiling.

What do I need to do to transition at the point where the Romex exits
the wall and enters the conduit?

I assume I need some type of brushing to hold the wire in place and
prevent it from scraping. Beyond that is it sufficient just to push
the conduit entrance up tight to the exit hole from the wall?

What specifically do I need to use here?

Thanks



  #4   Report Post  
 
Posts: n/a
Default Transitioning from in-wall wiring to EMT (conduit)...

What do I need to do to transition at the point where the Romex exits
the wall and enters the conduit?


I have the same situation with some #6 stranded wire I'm running for a
subpanel out to the garage. It's 50ft of three wire in a black jacket
and I wanted to run it in from the back through the joist cavity. But
the back of the subpanel I have does not have a rear knock-out, so I
have to run the feeder in through the top of the panel, which leaves
the cable exposed on the wall.

If anyone can advise, I don't want the cable exposed on the wall. I'm
thinking of having a metal conduit run from the panel up to a j-box in
the corner of the wall/ceiling. Run the cable into the j-box from the
ceiling with the jacket on. Out the other side of the j-box through
conduit, to the sub-panel. Does this make sense? I'd remove the outer
jacket from the cable run into the conduit.

Do they make j-boxes that big for #6 stranded (heat concern?) or is
there some kind of transition device used to go from sheathed cable to
conduit?

Thanks!

  #5   Report Post  
RBM
 
Posts: n/a
Default Transitioning from in-wall wiring to EMT (conduit)...

There is no need to have a junction box as you don't have a junction. You
can use whatever size conduit you need, and if you can't find an EMT to
romex connector in the size you need, you can get an EMT connector, a
threaded coupling, and a romex connector of whatever size you want and
thread them together



wrote in message
oups.com...
What do I need to do to transition at the point where the Romex exits
the wall and enters the conduit?


I have the same situation with some #6 stranded wire I'm running for a
subpanel out to the garage. It's 50ft of three wire in a black jacket
and I wanted to run it in from the back through the joist cavity. But
the back of the subpanel I have does not have a rear knock-out, so I
have to run the feeder in through the top of the panel, which leaves
the cable exposed on the wall.

If anyone can advise, I don't want the cable exposed on the wall. I'm
thinking of having a metal conduit run from the panel up to a j-box in
the corner of the wall/ceiling. Run the cable into the j-box from the
ceiling with the jacket on. Out the other side of the j-box through
conduit, to the sub-panel. Does this make sense? I'd remove the outer
jacket from the cable run into the conduit.

Do they make j-boxes that big for #6 stranded (heat concern?) or is
there some kind of transition device used to go from sheathed cable to
conduit?

Thanks!





  #6   Report Post  
blueman
 
Posts: n/a
Default Transitioning from in-wall wiring to EMT (conduit)...

"SQLit" writes:
"blueman" wrote in message
...
I would like to run regular Romex up the interior wall of our garage
and then switch to conduit running along the ceiling.

What do I need to do to transition at the point where the Romex exits
the wall and enters the conduit?

I assume I need some type of brushing to hold the wire in place and
prevent it from scraping. Beyond that is it sufficient just to push
the conduit entrance up tight to the exit hole from the wall?

What specifically do I need to use here?

Thanks


a box with a conduit connector on side side and a romex connector on the
other would work.


Is a box necessary? I would prefer something less intrusive since the
conduit itself looks "ugly" enough...
  #7   Report Post  
blueman
 
Posts: n/a
Default Transitioning from in-wall wiring to EMT (conduit)...

"RBM" rbm2(remove writes:

There is no need to have a junction box as you don't have a junction. You
can use whatever size conduit you need, and if you can't find an EMT to
romex connector in the size you need, you can get an EMT connector, a
threaded coupling, and a romex connector of whatever size you want and
thread them together


In my case where I am transitioning from Romex in a wall to a conduit
along the garage ceiling do I need anything to make sure that the
transition stays snug against the wall without any of the Romex
peaking through?
  #8   Report Post  
RBM
 
Posts: n/a
Default Transitioning from in-wall wiring to EMT (conduit)...

No, just keep it as close as you can. The object is to protect the cable
from damage



"blueman" wrote in message
...
"RBM" rbm2(remove writes:

There is no need to have a junction box as you don't have a junction. You
can use whatever size conduit you need, and if you can't find an EMT to
romex connector in the size you need, you can get an EMT connector, a
threaded coupling, and a romex connector of whatever size you want and
thread them together


In my case where I am transitioning from Romex in a wall to a conduit
along the garage ceiling do I need anything to make sure that the
transition stays snug against the wall without any of the Romex
peaking through?



  #9   Report Post  
James \Cubby\ Culbertson
 
Posts: n/a
Default Transitioning from in-wall wiring to EMT (conduit)...


"blueman" wrote in message
...
I would like to run regular Romex up the interior wall of our garage
and then switch to conduit running along the ceiling.

What do I need to do to transition at the point where the Romex exits
the wall and enters the conduit?

I assume I need some type of brushing to hold the wire in place and
prevent it from scraping. Beyond that is it sufficient just to push
the conduit entrance up tight to the exit hole from the wall?

What specifically do I need to use here?

Thanks


So you're planning to pull the romex through the EMT? I believe code allows
this but it seems to me a j-box to transition from the Romex to regular wire
might make more sense.
Cheers,
cc


  #10   Report Post  
_firstname_@lr_dot_los-gatos_dot_ca.us
 
Posts: n/a
Default Transitioning from in-wall wiring to EMT (conduit)...

In article .com,
wrote:
What do I need to do to transition at the point where the Romex exits
the wall and enters the conduit?


I have the same situation with some #6 stranded wire I'm running for a
subpanel out to the garage. It's 50ft of three wire in a black jacket
and I wanted to run it in from the back through the joist cavity. But
the back of the subpanel I have does not have a rear knock-out, so I
have to run the feeder in through the top of the panel, which leaves
the cable exposed on the wall.

If anyone can advise, I don't want the cable exposed on the wall. I'm
thinking of having a metal conduit run from the panel up to a j-box in
the corner of the wall/ceiling. Run the cable into the j-box from the
ceiling with the jacket on. Out the other side of the j-box through
conduit, to the sub-panel. Does this make sense? I'd remove the outer
jacket from the cable run into the conduit.

Do they make j-boxes that big for #6 stranded (heat concern?) or is
there some kind of transition device used to go from sheathed cable to
conduit?

Thanks!


They make direct EMT-to-Romex fittings. I have only ever seen them in
1/2", to small Romex; the Romex clamp (officially known as NM cable,
BTW) is 3/8", and suitable for 14-2, 12-2, and maybe even for 14-3 and
12-3. The next large solution has already been mentioned: Use an
EMT-to-threaded connector, followed by a threaded coupling, followed
by a clamp for the Romex.

To make sure you hide all the cable in the wall, drill a hole deep
enough that the first 1/2" or 1" of the EMT is hidden in the wall. By
the way, drywalling around the EMT will be no fun, hard to get it nice
and smooth.

There is one more annoying little issue: the EMT has to be grounded,
at the minimum by being connected to a grounded metal box on at least
one end. If you use an EMT-to-NM fitting, or the method with the
threaded coupling, there is no place to attach the ground, so you
better hope you can ground from the other end. Also, the NEC allows
small sections of unstripped Romex in conduit only. If you have a
long run in conduit, you shall strip the outer jacket off; the
conductors used inside the Romex are perfectly happy to continue on
inside the conduit.

For the rear exit from the subpanel: What I've seen done is simply to
drill or punch a hole in the back of the subpanel. Do the experts
think that this is legal? We did this to two of our panels, and
passed inspection, but that means nothing (could be that our inspector
was a fool or sloppy).

Getting a J-box for three strands of #6 cable is trivial. Just look
up the rules in the NEC for required cable volume per conductor. I
would use at the very minimum a 4" square box, because #6 cable is
stiff enough that working with it in anything smaller is an incredible
pain, and has the risk of chafing the insulation. In general, using
bigger boxes makes life much more pleasant.

--
The address in the header is invalid for obvious reasons. Please
reconstruct the address from the information below (look for _).
Ralph Becker-Szendy


  #11   Report Post  
Chris Lewis
 
Posts: n/a
Default Transitioning from in-wall wiring to EMT (conduit)...

According to blueman :
"RBM" rbm2(remove writes:


There is no need to have a junction box as you don't have a junction. You
can use whatever size conduit you need, and if you can't find an EMT to
romex connector in the size you need, you can get an EMT connector, a
threaded coupling, and a romex connector of whatever size you want and
thread them together


In my case where I am transitioning from Romex in a wall to a conduit
along the garage ceiling do I need anything to make sure that the
transition stays snug against the wall without any of the Romex
peaking through?



I had the reverse situation: romex on the ceiling, wanting to run the
cables surface-mounted down the wall. (garage workshop, walls already
finished - these were drops to bench height outlets).

I chose grey PVC electrical conduit. Surface mounted a PVC outlet box,
ran the conduit up to the ceiling. There is 1x3 lathe (for mounting
drywall) on the ceiling, immediately adjacent to the wall. Bored
a hole in the lathe so that the conduit would emerge just flush with
the top of the lathe. Ran the romex down the conduit with a small
bit of slack at the top. No boots or anything. The inspector was
quite happy with it.

But with EMT you'll need fittings to prevent cutting the insulation.
See the other postings.


--
Chris Lewis, Una confibula non set est
It's not just anyone who gets a Starship Cruiser class named after them.
  #12   Report Post  
Chris Lewis
 
Posts: n/a
Default Transitioning from in-wall wiring to EMT (conduit)...

According to :
For the rear exit from the subpanel: What I've seen done is simply to
drill or punch a hole in the back of the subpanel. Do the experts
think that this is legal? We did this to two of our panels, and
passed inspection, but that means nothing (could be that our inspector
was a fool or sloppy).


This is almost always perfectly legal[1], as long as you use the
appropriate strain relief. Ie: knock-out sized hole, cable box clamp.

[1] Ie: if you don't exceed box fill and it's legal to have that cable
in the box. [Canadian codes, for example, wouldn't permit you doing
this for an ordinary circuit conductor in the main breaker compartment.]
--
Chris Lewis, Una confibula non set est
It's not just anyone who gets a Starship Cruiser class named after them.
  #13   Report Post  
Bob
 
Posts: n/a
Default Transitioning from in-wall wiring to EMT (conduit)...

blueman wrote:
I would like to run regular Romex up the interior wall of our garage
and then switch to conduit running along the ceiling.


Standard practice (possibly code) prohibits exposed Romex less than 7
feet above the floor, so you may want to just use conduit all around.
  #14   Report Post  
blueman
 
Posts: n/a
Default Transitioning from in-wall wiring to EMT (conduit)...

Bob writes:
blueman wrote:
I would like to run regular Romex up the interior wall of our garage
and then switch to conduit running along the ceiling.


Standard practice (possibly code) prohibits exposed Romex less than 7
feet above the floor, so you may want to just use conduit all
around.


The Romex runs up the *interior* of the wall so is not exposed
  #15   Report Post  
blueman
 
Posts: n/a
Default Transitioning from in-wall wiring to EMT (conduit)...

writes:
They make direct EMT-to-Romex fittings. I have only ever seen them in
1/2", to small Romex; the Romex clamp (officially known as NM cable,
BTW) is 3/8", and suitable for 14-2, 12-2, and maybe even for 14-3 and
12-3. The next large solution has already been mentioned: Use an
EMT-to-threaded connector, followed by a threaded coupling, followed
by a clamp for the Romex.


According to NEC, what is the smallest size EMT that you can run 14-2
Romex through?

To make sure you hide all the cable in the wall, drill a hole deep
enough that the first 1/2" or 1" of the EMT is hidden in the wall. By
the way, drywalling around the EMT will be no fun, hard to get it nice
and smooth.

There is one more annoying little issue: the EMT has to be grounded,
at the minimum by being connected to a grounded metal box on at least
one end. If you use an EMT-to-NM fitting, or the method with the
threaded coupling, there is no place to attach the ground, so you
better hope you can ground from the other end. Also, the NEC allows
small sections of unstripped Romex in conduit only. If you have a
long run in conduit, you shall strip the outer jacket off; the
conductors used inside the Romex are perfectly happy to continue on
inside the conduit.


Are you saying that NEC does not allow Romex to run up through EMT but
needs to be stripped first?

I am pretty sure our electrician wired the basement with exposed Romex running
along the ceiling and then dropping down through EMT to get to the
wall outlets.

Can you clarify please?


  #17   Report Post  
RBM
 
Posts: n/a
Default Transitioning from in-wall wiring to EMT (conduit)...

He's saying that romex does not have to be stripped inside of any conduit,,
"it's an urban myth"

"blueman" wrote in message
...
writes:
They make direct EMT-to-Romex fittings. I have only ever seen them in
1/2", to small Romex; the Romex clamp (officially known as NM cable,
BTW) is 3/8", and suitable for 14-2, 12-2, and maybe even for 14-3 and
12-3. The next large solution has already been mentioned: Use an
EMT-to-threaded connector, followed by a threaded coupling, followed
by a clamp for the Romex.


According to NEC, what is the smallest size EMT that you can run 14-2
Romex through?

To make sure you hide all the cable in the wall, drill a hole deep
enough that the first 1/2" or 1" of the EMT is hidden in the wall. By
the way, drywalling around the EMT will be no fun, hard to get it nice
and smooth.

There is one more annoying little issue: the EMT has to be grounded,
at the minimum by being connected to a grounded metal box on at least
one end. If you use an EMT-to-NM fitting, or the method with the
threaded coupling, there is no place to attach the ground, so you
better hope you can ground from the other end. Also, the NEC allows
small sections of unstripped Romex in conduit only. If you have a
long run in conduit, you shall strip the outer jacket off; the
conductors used inside the Romex are perfectly happy to continue on
inside the conduit.


Are you saying that NEC does not allow Romex to run up through EMT but
needs to be stripped first?

I am pretty sure our electrician wired the basement with exposed Romex
running
along the ceiling and then dropping down through EMT to get to the
wall outlets.

Can you clarify please?



  #18   Report Post  
Wayne Whitney
 
Posts: n/a
Default Transitioning from in-wall wiring to EMT (conduit)...

On 2005-10-21, blueman wrote:

Are you saying that NEC does not allow Romex to run up through EMT
but needs to be stripped first?


As others have said, the exact opposite is true. It's fine to run
Romex through EMT (but perhaps inefficient, design wise, as Romex is
much bigger than individual conductors, so you need bigger EMT).
Stripping Romex of the outer jacket and running the individual
conductors in EMT creates a situation where the conductors aren't
labeled for their use, so it is not strictly NEC-compliant.

According to NEC, what is the smallest size EMT that you can run
14-2 Romex through?


Well, Table 1 of Chapter 9 Tables (2002 NEC) gives percent usable
cross section of conduit and tubing for conductors: 1 conductor, 53%;
2 conductors, 31%; 3 or more conductors, 40%. However, Note 2 to
Table 1 says "Table 1 applies only to complete conduit or tubing
systems and is not intended to apply to sections of conduit or tubing
used to protect exposed wiring from physical damage."

So I think that means that for short runs used just to protect Romex
from physical damage (e.g. a riser in a basement to go from a surface
mounted outlet to an exposed overhead run), you can use whatever size
it will fit in and is convenient.

As to "complete conduit systems", I know 12-2 romex has a diameter of
0.39 in, so it has an equivalent circular cross-section of 0.119 in^2.
1/2" EMT is sufficient, as it has an interior diameter of 0.622 in,
for an area of 0.304 in^2, 53% of which is 0.161 in^2. If 1/2" EMT
can handle a single 12-2 cable, it can handle a single 14-2 cable.

Cheers, Wayne


  #19   Report Post  
Chris Lewis
 
Posts: n/a
Default Transitioning from in-wall wiring to EMT (conduit)...

According to Wayne Whitney :

As to "complete conduit systems", I know 12-2 romex has a diameter of
0.39 in, so it has an equivalent circular cross-section of 0.119 in^2.
1/2" EMT is sufficient, as it has an interior diameter of 0.622 in,
for an area of 0.304 in^2, 53% of which is 0.161 in^2. If 1/2" EMT
can handle a single 12-2 cable, it can handle a single 14-2 cable.


As a FYI, I've installed (and had approved) single runs of 14/2, 14/3,
12/3 and even 10/2 in half inch electrical PVC conduit. Most were NMD,
but the 12/3 was NMW (equivalent to your UF - direct burial rated).

[Surface mount, used as a cable protection, max length 7'].
--
Chris Lewis, Una confibula non set est
It's not just anyone who gets a Starship Cruiser class named after them.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wall Register Extension Matthew Simmons Home Ownership 0 July 27th 05 03:44 PM
telephone wiring question barry martin Home Repair 0 August 11th 04 02:43 AM
Building a retaining wall next to house wall. Adam UK diy 3 May 24th 04 04:19 PM
HELP: vertical foundation crack in new construction Zhixin Tang Home Ownership 25 October 26th 03 01:53 PM
Dry Rock Retaining Wall RedHeadAllDay Home Repair 4 August 18th 03 02:12 PM


All times are GMT +1. The time now is 06:20 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"