Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
 
Posts: n/a
Default Checking on electric contractor; adjacent sub-panel question

A contractor had to put in a sub-panel in my home because the main box
was full. I have a few questions on what he did that I hope some
experienced electricians can answer.

The new sub-panel is located immediately (about 4") below the main
panel and connected to it with metal conduit. To feed the sub-panel,
two existing circuits were removed (and replaced by a dual-pole
breaker) and those existing circuits were extended to breakers in the
sub-panel.

My questions:

1 - Do the neutral and ground need to be separated in this sub-panel?
He bonded them. Most info in the NEC talks about sub-panels in
separate buildings or at remote locations. I don't know if the
situation changes if the sub-panel is located so closely to the main
panel.

2 - The hot wires for the moved circuits were extended into the
sub-panel. Do the neutral and ground wires need to be extended also?
He left them in the main panel and only extended the hot wire.

3 - Given that 2 20A furnace branch circuits (A/C operation and
_electric_ heat) were what was moved, and two additional 20A (patio and
landscape lighting & power) branch circuits added, what is a suitable
breaker to feed the sub-panel? He put in a 25A and wired the sub-panel
with #10 wire, which seems a bit light considering the 2 furnace
(heater) circuits.

Thank you for any clarification on these issues.

-W

  #2   Report Post  
SQLit
 
Posts: n/a
Default


wrote in message
oups.com...
A contractor had to put in a sub-panel in my home because the main box
was full. I have a few questions on what he did that I hope some
experienced electricians can answer.

The new sub-panel is located immediately (about 4") below the main
panel and connected to it with metal conduit. To feed the sub-panel,
two existing circuits were removed (and replaced by a dual-pole
breaker) and those existing circuits were extended to breakers in the
sub-panel.

My questions:

1 - Do the neutral and ground need to be separated in this sub-panel?
He bonded them. Most info in the NEC talks about sub-panels in
separate buildings or at remote locations. I don't know if the
situation changes if the sub-panel is located so closely to the main
panel.


Absolutely not bonded together in a sub panel. This guy is an electrician,
NOT

Neutral should be isolated from ground, fix this as soon as possible. Not
that your house will burn down it is just not the right way to do it.



2 - The hot wires for the moved circuits were extended into the
sub-panel. Do the neutral and ground wires need to be extended also?
He left them in the main panel and only extended the hot wire.


It is a good idea. A craftsman would do it.

3 - Given that 2 20A furnace branch circuits (A/C operation and
_electric_ heat) were what was moved, and two additional 20A (patio and
landscape lighting & power) branch circuits added, what is a suitable
breaker to feed the sub-panel? He put in a 25A and wired the sub-panel
with #10 wire, which seems a bit light considering the 2 furnace
(heater) circuits.


Need to do a load calcualation on the service then on the additional loads.
Not what size the breaker is what the acutal load is. 25 amp breaker not
what I would have used (30).
Figuring the heaters are on each phase (balanced loading) and the patio
circuits are the same then it will work just fine. Odds are when the patio
is under a load the heaters will not be used.
What did you pay for?


Thank you for any clarification on these issues.

-W



  #3   Report Post  
 
Posts: n/a
Default

1 - Do the neutral and ground need to be separated in this sub-panel?
He bonded them. Most info in the NEC talks about sub-panels in
separate buildings or at remote locations. I don't know if the
situation changes if the sub-panel is located so closely to the main
panel.


Yes they should be separate with a 4 wire feeder.



Thank you; I suspected as much. I questioned him directly about this
and he said it was not necessary. I've installed a separate ground bus
in the sub-panel and separated them.


2 - The hot wires for the moved circuits were extended into the
sub-panel. Do the neutral and ground wires need to be extended also?
He left them in the main panel and only extended the hot wire.


Yes to extending the neutral, all circuit conductors in a given
circuit should go through the raceway. The ground can stay.



OK, I will make this change. It just seems more correct to me.


3 - Given that 2 20A furnace branch circuits (A/C operation and
_electric_ heat) were what was moved, and two additional 20A (patio and
landscape lighting & power) branch circuits added, what is a suitable
breaker to feed the sub-panel? He put in a 25A and wired the sub-panel
with #10 wire, which seems a bit light considering the 2 furnace
(heater) circuits.


40a and 8ga would have been a better choice. That is not a code issue,
it is a design issue. You can swap it out for a 30a without changing
the wire.



Thank you again; I upgraded the wire to #6 stranded and replaced the
sub-panel feed breaker with a 40A. I was afraid the first time we used
both heater this winter, that it would trip the breaker.

-W

  #4   Report Post  
Tim Fischer
 
Posts: n/a
Default

Wow, you re-did most of the work. Why did you hire the guy again? ;-)

-Tim


  #5   Report Post  
zxcvbob
 
Posts: n/a
Default

wrote:
A contractor had to put in a sub-panel in my home because the main box
was full. I have a few questions on what he did that I hope some
experienced electricians can answer.

The new sub-panel is located immediately (about 4") below the main
panel and connected to it with metal conduit. To feed the sub-panel,
two existing circuits were removed (and replaced by a dual-pole
breaker) and those existing circuits were extended to breakers in the
sub-panel.

My questions:

1 - Do the neutral and ground need to be separated in this sub-panel?
He bonded them. Most info in the NEC talks about sub-panels in
separate buildings or at remote locations. I don't know if the
situation changes if the sub-panel is located so closely to the main
panel.

2 - The hot wires for the moved circuits were extended into the
sub-panel. Do the neutral and ground wires need to be extended also?
He left them in the main panel and only extended the hot wire.


#1 and #2 are both wrong, but they are also perfectly safe in my opinion
(assuming that conduit connecting the 2 boxes is a rigid or IMC conduit
and has threaded locknuts.) The new box is supposed be wired as a
subpanel. I'm not sure that I would change it though. What did the
electrical inspector say?

3 - Given that 2 20A furnace branch circuits (A/C operation and
_electric_ heat) were what was moved, and two additional 20A (patio and
landscape lighting & power) branch circuits added, what is a suitable
breaker to feed the sub-panel? He put in a 25A and wired the sub-panel
with #10 wire, which seems a bit light considering the 2 furnace
(heater) circuits.


I would have used #6 copper wire and a 50A or 60A breaker. I wonder
where he found a 25A breaker instead of a 30.

-Bob


  #6   Report Post  
 
Posts: n/a
Default

3 - Given that 2 20A furnace branch circuits (A/C operation and
_electric_ heat) were what was moved, and two additional 20A (patio and
landscape lighting & power) branch circuits added, what is a suitable
breaker to feed the sub-panel? He put in a 25A and wired the sub-panel
with #10 wire, which seems a bit light considering the 2 furnace
(heater) circuits.


Need to do a load calcualation on the service then on the additional loads.
Not what size the breaker is what the acutal load is. 25 amp breaker not
what I would have used (30).
Figuring the heaters are on each phase (balanced loading) and the patio
circuits are the same then it will work just fine.



Yes, that is the case; I specifically made sure of it when I went into
the box.


Odds are when the patio
is under a load the heaters will not be used.



Not really true -- we're in Texas, so we may be running the heaters in
the house and still be using the patio, fan, landscape lighting, and
fountain outside.


What did you pay for?


A learning experience it seems. Originally I did not want to mess
around with the main panel so I hired this guy who was recommended by
the contractor doing the rest of the landscaping work, but I was so
bothered by the final electrical work that I redid almost all of it.

I've not mentioned how he used white wires for hot leads (without
marking them in any way), how he installed the fan in the arbor without
a GFCI and without the wet location kit supplied in the box (both which
I've since added, and which it clearly calls for), how he fed the wire
to the fan through a whole drilled straight up through the mounting
board on the arbor (allowing rain to run right down the wire into the
fan), how he ran the hot from one circuit but the neutrals from two
different circuits through the load side of the one GFCI he did
install, how he ran exposed standard household cable across the arbor
for the fan rather than wet and sun rated cable, nor how he used a
mixture of 4 hole metal and 2 hole plastic weatherproof boxes which
looked horrible and which I've all replaced with the same plastic
weatherproof boxes. I've since fixed all of this.

In the end, I was not explicit enough with what I needed installed,
trusting him to know what he was doing and to care enough to do the
best job, neither of which it seems were really the case,
unfortunately.

Thanks for answering my questions and verifying my concerns.

-W

  #7   Report Post  
 
Posts: n/a
Default

1 - Do the neutral and ground need to be separated in this sub-panel?
...


2 - The hot wires for the moved circuits were extended into the
sub-panel. Do the neutral and ground wires need to be extended also? ...


#1 and #2 are both wrong, but they are also perfectly safe in my opinion
(assuming that conduit connecting the 2 boxes is a rigid or IMC conduit
and has threaded locknuts.)



Rigid metal conduit with threaded locknuts.


The new box is supposed be wired as a
subpanel. I'm not sure that I would change it though. What did the
electrical inspector say?


I was told by the general contractor as well as this electrical
contractor that no electrical inspection was necessary because the
electrician is a state-licensed journeyman.

  #8   Report Post  
Jeff Wisnia
 
Posts: n/a
Default

wrote:
1 - Do the neutral and ground need to be separated in this sub-panel?
He bonded them. Most info in the NEC talks about sub-panels in
separate buildings or at remote locations. I don't know if the
situation changes if the sub-panel is located so closely to the main
panel.


Yes they should be separate with a 4 wire feeder.




Thank you; I suspected as much. I questioned him directly about this
and he said it was not necessary. I've installed a separate ground bus
in the sub-panel and separated them.



2 - The hot wires for the moved circuits were extended into the
sub-panel. Do the neutral and ground wires need to be extended also?
He left them in the main panel and only extended the hot wire.


Yes to extending the neutral, all circuit conductors in a given
circuit should go through the raceway. The ground can stay.




OK, I will make this change. It just seems more correct to me.



3 - Given that 2 20A furnace branch circuits (A/C operation and
_electric_ heat) were what was moved, and two additional 20A (patio and
landscape lighting & power) branch circuits added, what is a suitable
breaker to feed the sub-panel? He put in a 25A and wired the sub-panel
with #10 wire, which seems a bit light considering the 2 furnace
(heater) circuits.


40a and 8ga would have been a better choice. That is not a code issue,
it is a design issue. You can swap it out for a 30a without changing
the wire.




Thank you again; I upgraded the wire to #6 stranded and replaced the
sub-panel feed breaker with a 40A. I was afraid the first time we used
both heater this winter, that it would trip the breaker.

-W


Was your "contractor" a licensed electrician?

If he made that many errors I think that before correcting things you
should have weighed whether your need to stay on speaking terms with him
was worth more than the risk that his slipshod ways might create a real
life threatening situation on the next job he did.

I would have asked him to correct things pronto, and if he gave me any
BS about it being ok as is, I'd have asked the local electrical
inspector to drop over and look at the job. There are times you just
have to stand up and be counted, even if it makes some other people
think you're a creep.

********

I may have already bloviated on this group about last spring's adventure
with an HVAC tech who, while replacing a couple of Heat Pump compressor
units at our home, used one of the outdoor fused disconnect switch
housing as a "splice box" for the low voltage control wiring to the
compressor unit.

http://home.comcast.net/~jwisnia18/temp/box.html

I e-mailed that photo of what he'd done to his boss, and the next day
the job was made right by a different tech who installed a separate
weatherproof splice box for the control wiring.

Now, what the first tech had done would probably have worked fine
forever if nothing fell apart inside that switch box, but it wasn't to
code. And, if I ever get a chance to retire and sell the place before I
die it would be my bad luck to have the buyer's home inspector decide to
eyeball that disconnect switch and then force me to have to hire and pay
a licensed electrician to make it right.

Just my .02,

Jeff

--
Jeffry Wisnia

(W1BSV + Brass Rat '57 EE)

"Truth exists; only falsehood has to be invented."
  #10   Report Post  
Tim Fischer
 
Posts: n/a
Default

Jeff, good post, but my need to nitpick kicked in ;-)

If he made that many errors I think that before correcting things you
should have weighed whether your need to stay on speaking terms with him
was worth more than the risk that his slipshod ways might create a real
life threatening situation on the next job he did.


To be fair, nothing he did was particularly dangerous. With the panel so
close to the main panel, it's really splitting hairs as to why the grounds
need to be separated. If it's in another room/building/whatever certainly.
Not defending the guy's work, since it wasn't to code, but it isn't really a
safety problem that I can see...

I would have asked him to correct things pronto, and if he gave me any BS
about it being ok as is, I'd have asked the local electrical inspector to
drop over and look at the job.


Contractors are not immune from electrical inspections -- the inspector
SHOULD have dropped by. This was yet another violation.

it would be my bad luck to have the buyer's home inspector decide to
eyeball that disconnect switch and then force me to have to hire and pay a
licensed electrician to make it right.


They can't FORCE you to do anything. At worse, they could back out of the
sale. If this situation had come up in a sale and they wanted it fixed, you
can be darned sure I'd be fixing it myself, unless of course they want to
pay to have an electrician do it. I think just about every house has some
sort of 'violation' like this, so I think if a buyer were that picky, they
wouldn't be finding any home. But I can't blame you for making sure it was
done right.

As an aside (and I have no idea if this meets code or not), the low-voltage
wire from our HVAC unit to the outside unit is standard romex! I was poking
around in the ceiling of the utility room one time and was shocked (not
literally, thankfully) to find a wirenutted connection from the romex to a
standard T-stat type wire!

-Tim




  #11   Report Post  
Jeff Wisnia
 
Posts: n/a
Default

Tim Fischer wrote:
Jeff, good post, but my need to nitpick kicked in ;-)


If he made that many errors I think that before correcting things you
should have weighed whether your need to stay on speaking terms with him
was worth more than the risk that his slipshod ways might create a real
life threatening situation on the next job he did.



To be fair, nothing he did was particularly dangerous. With the panel so
close to the main panel, it's really splitting hairs as to why the grounds
need to be separated. If it's in another room/building/whatever certainly.
Not defending the guy's work, since it wasn't to code, but it isn't really a
safety problem that I can see...


I would have asked him to correct things pronto, and if he gave me any BS
about it being ok as is, I'd have asked the local electrical inspector to
drop over and look at the job.



Contractors are not immune from electrical inspections -- the inspector
SHOULD have dropped by. This was yet another violation.


it would be my bad luck to have the buyer's home inspector decide to
eyeball that disconnect switch and then force me to have to hire and pay a
licensed electrician to make it right.



They can't FORCE you to do anything. At worse, they could back out of the
sale. If this situation had come up in a sale and they wanted it fixed, you
can be darned sure I'd be fixing it myself, unless of course they want to
pay to have an electrician do it. I think just about every house has some
sort of 'violation' like this, so I think if a buyer were that picky, they
wouldn't be finding any home. But I can't blame you for making sure it was
done right.


I agree that FORCE was too strong a word. But if the situation occurred
while we were in the "short strokes" of closing on the house, then I'm
pretty sure I'd do whatever necessary even if it cost a few hundred
bucks for Alec (Alec Trician) to keep us from having to start over again
attracting a buyer for a (not bragging) million buck home.

And while I damn sure could do it myself, and probably neater and more
workmanlike than that second HVAC tech did last spring, I believe the
buyer's lawyer would be within his rights to require that the work be
done by a licensed electrician, which I'm not; An MSEE from '58 don't
count for that. :-)


As an aside (and I have no idea if this meets code or not), the low-voltage
wire from our HVAC unit to the outside unit is standard romex! I was poking
around in the ceiling of the utility room one time and was shocked (not
literally, thankfully) to find a wirenutted connection from the romex to a
standard T-stat type wire!



I'm guessing that your compressor unit requires just a simple relay
pull-in needing only two conductors, or did they use multiple pieces of
Romex?

I'm not a licensed expert, but I can't think of any technical reason why
Romex wouldn't be fine.

You just reminded me that about ten years ago when I had to find out
what was wrong with one of our heat pumps I discovered after many
mutterings of "WTF" that when we built the house the sods who'd run the
five conductor control line to the compressor unit I was fixing had to
have made a hidden splice in the control cable between the air handler
and the compressor.

The insulation colors on two of the five leads "changed" from one end of
the run to the other. After about an hour ringing them out (I was
working alone at the time) I found and replaced the relay with an open
coil, which was the real problem, and all was well.

I put a note about those chameleon wire colors in my household "HVAC" file.

Jeff

--
Jeffry Wisnia

(W1BSV + Brass Rat '57 EE)

"Truth exists; only falsehood has to be invented."
  #12   Report Post  
Bud
 
Posts: n/a
Default

wrote:
1 - Do the neutral and ground need to be separated in this sub-panel?
He bonded them.


Yes they should be separate with a 4 wire feeder.


Thank you; I suspected as much. I questioned him directly about this
and he said it was not necessary. I've installed a separate ground bus
in the sub-panel and separated them.

I think bonding the neutral and ground is subpanels is a relatively
common code violation, but an electrician should know better. If you
havn't already, check for a "main bonding jumper" from the neutral bar
to ground - usually a screw. The subpanel can be grounded by the rigid
pipe and doesn't need a separate wire.

2 - The hot wires for the moved circuits were extended into the
sub-panel. Do the neutral and ground wires need to be extended also?
He left them in the main panel and only extended the hot wire.


Yes to extending the neutral, all circuit conductors in a given
circuit should go through the raceway. The ground can stay.


This is NOT necessary. Neutrals have to be run with hots so the total
current (with current going in one direction cancelling current going
the other direcction) is zero in a pipe or knockout. The current in the
hot load wires returning from the panel will cancel an equal current in
the supply wires so the total current is zero.

40a and 8ga would have been a better choice. That is not a code issue,
it is a design issue. You can swap it out for a 30a without changing
the wire.




Thank you again; I upgraded the wire to #6 stranded and replaced the
sub-panel feed breaker with a 40A. I was afraid the first time we used
both heater this winter, that it would trip the breaker.

Make sure the subpanel is rated for 40A (most likely is). Given the low
cost of a higher amp feed and the original panel being maxed out, it is
kind of dumb to only run the subpanel at 25A.

Bud--
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
240V vs. 120V electric baseboard heat? GFCI? hydronic? Paul Home Repair 21 April 16th 16 12:53 PM
Give Your Feet a Treat - electric radiant system Ablang Home Ownership 0 April 14th 05 06:12 AM
Pressure Washers, Electric, Karcher Bob Gir. Home Repair 8 July 7th 04 03:04 PM
Cutting floor tiles: Electric or Hand Operated cutter? Serial Bodger UK diy 12 August 17th 03 02:36 PM
o t ish changing gas and electric Jackie UK diy 4 August 10th 03 06:53 PM


All times are GMT +1. The time now is 08:48 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us