Default Can blown bulb trip GFI?

I have an underwater pool light. Whenever I try to turn it on, the GFI
in the circuit trips. I replaced the GFI - same problem. Could a blown
bulb be tripping the GFI?

I ask because it's a pain to change the bulb - the screw head on the
face plate is damaged, and I would need to drain the pool to be able to
use a "screw-out" head to back-out the screw and change the bulb.

Ideas?

  #2   Report Post  
PipeDown
 
Posts: n/a
Default

A simply blown (open) bulb will not trip the GFCI. It is more likely that
you have a short between one of the lamp terminals and the faceplate or
housing (and thus the grounded pool water). It may be as simple as a
damaged rubber gasket or plastic spacer. Is there any water inside the
housing?

If the Breaker is GFCI it can be impossible to know if the trip is a ground
fault or a real short. If you have a breaker and a seperate GFCI outlet,
you can tell the difference.

Simplest short term solution is to cut and tape the wire to that bulb until
it is more convenient to fix the lamp housing. To troubleshoot, you need an
Ohmmeter and with it you can measure the resistance between each of the
wires to the bulb and a grounded point on the pool (like the ladder). The
resistance should be open, any resistance at all indicates a ground fault
and the breaker is doing its job saving your life.

Furthermore, with the bulb removed or dead, the resistance between the wires
should also be infinate (open) but if the bulb is not dead, there will be a
somewhat low resistance almost a short between the wires.

Hopefully you can gain access to the wires to the pool light somewhere
outside the pool of course, there may be an access cover on the deck or a
panel on a wall.

If your lamps are low voltage and powered by a transformer then the answer
would be a bit different as the ground fault would be near the transformer.




wrote in message
ups.com...
I have an underwater pool light. Whenever I try to turn it on, the GFI
in the circuit trips. I replaced the GFI - same problem. Could a blown
bulb be tripping the GFI?

I ask because it's a pain to change the bulb - the screw head on the
face plate is damaged, and I would need to drain the pool to be able to
use a "screw-out" head to back-out the screw and change the bulb.

Ideas?



  #3   Report Post  
RBM
 
Posts: n/a
Default

Most likely water has entered the sealed housing. There is a pipe which goes
from a metal niche that that light is installed in, to an above ground
splice box called a deck box. It's probably not far from the fixture and
possibly concealed under a diving board or in a bush. It has a plastic cover
held on by four screws. Open it up and disconnect the wires going to the
fixture and cap the feed wires. Then you should be able to reset the gfci
wrote in message
ups.com...
I have an underwater pool light. Whenever I try to turn it on, the GFI
in the circuit trips. I replaced the GFI - same problem. Could a blown
bulb be tripping the GFI?

I ask because it's a pain to change the bulb - the screw head on the
face plate is damaged, and I would need to drain the pool to be able to
use a "screw-out" head to back-out the screw and change the bulb.

Ideas?



  #4   Report Post  
Jeff Wisnia
 
Posts: n/a
Default

RBM wrote:

Most likely water has entered the sealed housing. There is a pipe which goes
from a metal niche that that light is installed in, to an above ground
splice box called a deck box. It's probably not far from the fixture and
possibly concealed under a diving board or in a bush. It has a plastic cover
held on by four screws. Open it up and disconnect the wires going to the
fixture and cap the feed wires. Then you should be able to reset the gfci
wrote in message
ups.com...

I have an underwater pool light. Whenever I try to turn it on, the GFI
in the circuit trips. I replaced the GFI - same problem. Could a blown
bulb be tripping the GFI?

I ask because it's a pain to change the bulb - the screw head on the
face plate is damaged, and I would need to drain the pool to be able to
use a "screw-out" head to back-out the screw and change the bulb.

Ideas?



You already have received the correct answer to your question.

Now, displaying my near total ignorance of swimming pool technology I
have to ask, can you properly change the bulb *without* lowering the
water level even if the screw head isn't damaged?

Jeff

--
Jeffry Wisnia

(W1BSV + Brass Rat '57 EE)

"Truth exists; only falsehood has to be invented."
  #5   Report Post  
SQLit
 
Posts: n/a
Default


"Jeff Wisnia" wrote in message
...
RBM wrote:

Most likely water has entered the sealed housing. There is a pipe which

goes
from a metal niche that that light is installed in, to an above ground
splice box called a deck box. It's probably not far from the fixture and
possibly concealed under a diving board or in a bush. It has a plastic

cover
held on by four screws. Open it up and disconnect the wires going to the
fixture and cap the feed wires. Then you should be able to reset the

gfci
wrote in message
ups.com...

I have an underwater pool light. Whenever I try to turn it on, the GFI
in the circuit trips. I replaced the GFI - same problem. Could a blown
bulb be tripping the GFI?

I ask because it's a pain to change the bulb - the screw head on the
face plate is damaged, and I would need to drain the pool to be able to
use a "screw-out" head to back-out the screw and change the bulb.

Ideas?



You already have received the correct answer to your question.

Now, displaying my near total ignorance of swimming pool technology I
have to ask, can you properly change the bulb *without* lowering the
water level even if the screw head isn't damaged?

Jeff


If you have a wet niche fixture,,,,,,,,,,,,,,,,,,,Yes. Dry niche fixture
,,,,,,,no. Most pool fixtures are wet niche.

Changing the bulb will not fix the GFCI issue. If the fixture seal is intact
which I will bet it is. Your looking at an new cord for the fixture. If it
is old they can be a bear to get out and replace. At least the last one I
tried was a real pain.




  #6   Report Post  
RBM
 
Posts: n/a
Default

Jeff, on standard wet niche fixtures there is one screw in the face plate
which when you remove, you have a hermetically sealed unit that pulls out
and if properly installed has enough rubber cord attached to lift the whole
thing onto the pool deck where you can attempt to make repairs Roy
"Jeff Wisnia" wrote in message
...
RBM wrote:

Most likely water has entered the sealed housing. There is a pipe which
goes from a metal niche that that light is installed in, to an above
ground splice box called a deck box. It's probably not far from the
fixture and possibly concealed under a diving board or in a bush. It has
a plastic cover held on by four screws. Open it up and disconnect the
wires going to the fixture and cap the feed wires. Then you should be
able to reset the gfci
wrote in message
ups.com...

I have an underwater pool light. Whenever I try to turn it on, the GFI
in the circuit trips. I replaced the GFI - same problem. Could a blown
bulb be tripping the GFI?

I ask because it's a pain to change the bulb - the screw head on the
face plate is damaged, and I would need to drain the pool to be able to
use a "screw-out" head to back-out the screw and change the bulb.

Ideas?



You already have received the correct answer to your question.

Now, displaying my near total ignorance of swimming pool technology I have
to ask, can you properly change the bulb *without* lowering the water
level even if the screw head isn't damaged?

Jeff

--
Jeffry Wisnia

(W1BSV + Brass Rat '57 EE)

"Truth exists; only falsehood has to be invented."



  #7   Report Post  
Jeff Wisnia
 
Posts: n/a
Default

RBM wrote:
Jeff, on standard wet niche fixtures there is one screw in the face plate
which when you remove, you have a hermetically sealed unit that pulls out
and if properly installed has enough rubber cord attached to lift the whole
thing onto the pool deck where you can attempt to make repairs Roy
"Jeff Wisnia" wrote in message
...



snipped


Now, displaying my near total ignorance of swimming pool technology I have
to ask, can you properly change the bulb *without* lowering the water
level even if the screw head isn't damaged?

Jeff



Thanks, I'm glad I asked. Now I understand why he feels he needs a dry
access to get that mangled screw out.

Jeff

--
Jeffry Wisnia

(W1BSV + Brass Rat '57 EE)

"Truth exists; only falsehood has to be invented."
  #8   Report Post  
 
Posts: n/a
Default

Thanks for the info - Pipedown, you said:

"If the Breaker is GFCI it can be impossible to know if the trip is a
ground
fault or a real short. If you have a breaker and a seperate GFCI
outlet,
you can tell the difference."

I have a non-GFI-breaker that feeds three boxes in a row: a light
switch in a box, a GFI outlet plug and the third is a plain duplex
convenience receptacle. I replaced the light switch and GFI and used a
GFI tester to verify that it was correctly wired (it's got three leds
that show correct wiring and a "tripper" that works as it should).

The easiest place to gain access to the light wires seem like it would
be at the light switch - there are two blue wires there, but at least
one of them goes to the GFI, so if I remove the switch and test
continuity on the wires, won't I be testing *through* the GFI? Will
that be accurate? Do you think those two blue wires go directly to the
bulb?

No, not a low-volt system.

RBM: I see a black plastic square box right next to the electrical
boxes. Maybe that's where the light wires come up from the metal niche.
I'll check it out tomorrow AM! (Too hot in Phoenix to check anything at
4PM - it's 109 right now!

I see no water in the light fixture itself - and just FYI, the bulbs
are supposed to have a life of 1000 hrs or so....this puppy was still
pretty new when it stopped working!

  #9   Report Post  
 
Posts: n/a
Default

RBM & Jeff: You raise an interesting physics problem - and that is how
to be in the pool and exert a force against a screw that is underwater.
The more you *push* against the screw with a screwdriver, the more you
force your body away from the screw --- so it's almost impossible to
get much torque on the screw head (at least as far as I can figure).
I've ruled out taking my new battery drill under water. Draining is the
only solution I can think of unless you guys have a good trick!

Chuck
KG7JD - and lots of pals from tech in Beantown!

  #10   Report Post  
 
Posts: n/a
Default

The entire socket assembly is on a long cord that allows you to life it
above the water surface, open it, and replace the bulb. I just can't
figure out how to remove the fixture without draining the water because
of the bad screw head.



  #12   Report Post  
PipeDown
 
Posts: n/a
Default

If you have an air compressor, you can use an air grinder to grind the head
off the screw. Once the bezel is removed, you can grab onto the remaining
shaft with vice grips to remove it the rest of the way. Visibility may be
poor using an air tool underwater but there should be no safety issue as
with electric power tools.



wrote in message
ups.com...
The entire socket assembly is on a long cord that allows you to life it
above the water surface, open it, and replace the bulb. I just can't
figure out how to remove the fixture without draining the water because
of the bad screw head.



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
RCD or not to RCD ... Rick Hughes UK diy 53 August 13th 04 05:04 PM
Change a light bulb Usenet Style Stormin Mormon Home Repair 1 July 18th 04 11:03 AM
Changing a light bulb on R.C.M Tom Gardner Metalworking 24 June 6th 04 12:58 AM
Light bulb malfunction Oldylocks Home Repair 12 February 5th 04 01:51 PM
O-T light bulb Fuddzy Woodworking 2 January 15th 04 04:43 PM


All times are GMT +1. The time now is 09:53 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"