I need to upgrade my home electricity - I have a home built in 1946. I
don't have any grounded outlets, and most all are only 2 prong.

What are my options? Do I have to put a ground rod in (sounds hard)?

I'd like to have all 3 prong grounded outlets.

-c

  #2   Report Post  
toller
 
Posts: n/a
Default

Your electrical system has to be grounded already. If it isn't, you have
worse problems than not having grounded outlets.

Why do you want a ground?
Have you checked to see if a ground is available at the outlet, perhaps via
grounded conduit?


  #3   Report Post  
w_tom
 
Posts: n/a
Default

First decide what your objective is. For example, wall
receptacles are grounded firstmost for human safety. That
safety grounding also accomplishes other lesser functions.
But other, less expensive methods can provide same human
safety. Earthing the electric panel is both for human safety
AND for transistor safety. This being different from
grounding of wall receptacles. And there is no alternative to
earthing.

Converting all wall receptacles to 3 wire is a massive
undertaking - typically rewiring the house. Earthing the
breaker box is a minor job that should be installed
everywhere. Those are two different types of grounding. Both
are part of a human safety system. And both also have
different functions. First define your strategic objectives.
Then your question can be better answered. Why are you
grounding? What problems, current and future, do you want to
solve?

It is probably a good idea to consider three wire outlets in
the kitchen since 1946 kitchen wire is, by today's standards,
undersized. But again, first you must define the problem to
be solved.

nobertos wrote:
I need to upgrade my home electricity - I have a home built in 1946. I
don't have any grounded outlets, and most all are only 2 prong.

What are my options? Do I have to put a ground rod in (sounds hard)?

I'd like to have all 3 prong grounded outlets.

-c

  #4   Report Post  
Matt
 
Posts: n/a
Default

Get some quotes, get the money, and let an electrician do the work.

  #5   Report Post  
Bob Vaughan
 
Posts: n/a
Default

In article , toller wrote:
Your electrical system has to be grounded already. If it isn't, you have
worse problems than not having grounded outlets.

Why do you want a ground?
Have you checked to see if a ground is available at the outlet, perhaps via
grounded conduit?



If the house was built in 1946, there is a possibility that the service
was not grounded..

The house that I am renting was built during that time, and did not have
a grounded service until the service entrance was replaced last year when
rain gutters were added following a roof replacement.



--
-- Welcome My Son, Welcome To The Machine --
Bob Vaughan | techie @ tantivy.net |
| P.O. Box 19792, Stanford, Ca 94309 |
-- I am Me, I am only Me, And no one else is Me, What could be simpler? --


  #6   Report Post  
 
Posts: n/a
Default

On 24 May 2005 14:35:16 -0700, "nobertos" wrote:

I need to upgrade my home electricity - I have a home built in 1946. I
don't have any grounded outlets, and most all are only 2 prong.

What are my options? Do I have to put a ground rod in (sounds hard)?

I'd like to have all 3 prong grounded outlets.

-c


How many 3 prong appliances do you have ?

Seriously !

You may not need 3-prong outlets
except in the kitchen ( fridge )
and the laundry room ( washer/dryer )

Get 2-prong polarized outlets for the other room,
and be sure they're wired with "wide blade" = neutral



rj
  #7   Report Post  
Jeff Wisnia
 
Posts: n/a
Default

w_tom wrote:
First decide what your objective is. For example, wall
receptacles are grounded firstmost for human safety. That
safety grounding also accomplishes other lesser functions.
But other, less expensive methods can provide same human
safety. Earthing the electric panel is both for human safety
AND for transistor safety. This being different from
grounding of wall receptacles. And there is no alternative to
earthing.

Converting all wall receptacles to 3 wire is a massive
undertaking - typically rewiring the house. Earthing the
breaker box is a minor job that should be installed
everywhere. Those are two different types of grounding. Both
are part of a human safety system. And both also have
different functions. First define your strategic objectives.
Then your question can be better answered. Why are you
grounding? What problems, current and future, do you want to
solve?

It is probably a good idea to consider three wire outlets in
the kitchen since 1946 kitchen wire is, by today's standards,
undersized. But again, first you must define the problem to
be solved.


And for "person safety", as a minimum you should replace the kitchen
outlets with GFCI ones asap, labeled as "Unconnected Ground" if as you
say you have no grounds available in their boxes. That'll prevent
someone from getting electrocuted by an appliance with an insulation
fault if they touch it and a water faucet at the same time. (DON'T use a
GFCI on the refrigerator outlet.)



nobertos wrote:

I need to upgrade my home electricity - I have a home built in 1946. I
don't have any grounded outlets, and most all are only 2 prong.


You mean you already have *some* 3 prong outlets with no ground
connected to them? If you do, you really should label them as
"Unconnected Ground".

What are my options? Do I have to put a ground rod in (sounds hard)?


As someone else mentioned, "BX" armored cable was being used in homes
back then, and if your home is wired with it, you *may* be able to
distribute grounds to all your outlets through the steel armor of that
cable, but a check with your local electrical inspector would be in
order before doing that.

I'd like to have all 3 prong grounded outlets.

-c


Jeff

--
Jeffry Wisnia

(W1BSV + Brass Rat '57 EE)

"Truth exists; only falsehood has to be invented."
  #8   Report Post  
John Hines
 
Posts: n/a
Default

"nobertos" wrote:

What are my options? Do I have to put a ground rod in (sounds hard)?


It will run about $2-3K to get your panel upgraded to 100amp service,
which will include a new ground rod (if needed), as well as a ground
connection where the water service comes in (req by code).

That is best done by a pro, as permits and such may be required, not to
mention just being a good idea.

Then you can run as needed new circuits. For example, you probably
don't need grounded outlets in the living room for lamps, since they
have 2 prong plugs. You should run nice new 3 prong grounded circuits
where you want to plug in a/v equipment and computers.

Get an electrician in for a quote on the service panel upgrade, and ask
a lot of questions.
  #9   Report Post  
nobertos
 
Posts: n/a
Default

I believe my panel has already been upgraded to 100amps. I was under
the impression that i need to 'ground' *every* outlet in my house.
Probably by installing a ground rod that attaches to the panel, and
then a ground wire from the panel out to an outlet.

Am i high?

  #10   Report Post  
Doug Miller
 
Posts: n/a
Default

In article . com, "nobertos" wrote:
I believe my panel has already been upgraded to 100amps. I was under
the impression that i need to 'ground' *every* outlet in my house.


That is not necessary. Look at the appliances you're plugging into those
outlets: the vast majority of them have two-prong plugs and thus do not need a
grounded outlet.

Probably by installing a ground rod that attaches to the panel, and
then a ground wire from the panel out to an outlet.

Am i high?


For the areas where you need grounded outlets, you can install ground fault
circuit interrupters. Google-search this newsgroup; it's been discussed
repeatedly here.

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?


  #11   Report Post  
John Hines
 
Posts: n/a
Default

"nobertos" wrote:

I believe my panel has already been upgraded to 100amps. I was under
the impression that i need to 'ground' *every* outlet in my house.
Probably by installing a ground rod that attaches to the panel, and
then a ground wire from the panel out to an outlet.


If your panel is properly installed, it will already have a connection
to ground, usually where the water supply (metal pipe) comes into the
house. Look for a thin piece of BX that has only one wire in it, it
will run over to the piping, where it is clamped on. This is the code's
requirement for grounding.

The ground on the outlets needs to be connected to the panel metal box,
this has been done in the past by the metal covering of the wire (BX) or
the metal pipe (conduit) the wires are run in, and the metal outlet box.

Unless you are plugging in appliances with 3 conductor cords, you don't
"need" a 3 prong outlet.

You only need to drive a ground rod if the wires in you house come in
more than like 10 ft away from where the panel is. And all of these need
to be bonded (connected) together with any other ground connection like
at the water service.
  #12   Report Post  
w_tom
 
Posts: n/a
Default

As noted previously, earth ground and safety ground are two
different grounds required by the National Electrical Code
(NEC). A connection to water pipe is no longer sufficient to
earth an AC electric system. That connection to water pipe
remains to remove elecricity from water pipes. Never make a
connection to water pipes to dump electricity into those
pipes. This being so important for human safety especially in
bath, shower, and sinks.

Current code calls for a dedicated earthing connection. To
exceed code requirements, that earthing connection must be as
short as possible, no sharp bends, no splices, not bundled
with other non-earthing wires, and the ground must be shared
by all incoming utilities. That means each the CATV wire must
drop down to connect to that single point ground before rising
back up to enter the building. This paragraph only discussing
earth ground.

Volts500 has provided a good summary of household grounding
for human safety, in the newsgroup alt.home.repair entitled
"Grounding Rod Info" on 12 July 2003 at
http://tinyurl.com/hkjq

A recent discussion in the newsgroup alt.home.repair was
"Easiest way to ground a computer" from 5 May thru 10 May
2005.

The only place I would most want three wire outlets is in
the kitchen. Especially a dedicated outlet to the
refrigerator that cannot be on a GFCI, must be on its own
circuit, and that must have a three prong outlet. Kitchen
counter tops and things like the garbage disposal, electric
stove and oven, etc all do need that third wire safety
ground. Elsewhere in kitchens, bathrooms, outside outlets etc
can be GFCIed. Also required now is that all bedroom outlets
be AFGIed. Same should be installed on any interior
receptacle that lights a 'live' Christmas tree. These provide
safety not made available with three prong outlets. This
paragraph about making power wall receptacles for human
safety.

If running interconnected electronic appliances, then either
all should run on safety grounded three prong outlets OR all
must connect to a power strip so that equipment grounds share
a single point connection. For example, computer, its
external modem, and its printer should somehow share a common
equipment ground. This paragraph more about equipment
grounding for transistor safety.

nobertos wrote:
I believe my panel has already been upgraded to 100amps. I was under
the impression that i need to 'ground' *every* outlet in my house.
Probably by installing a ground rod that attaches to the panel, and
then a ground wire from the panel out to an outlet.

Am i high?

  #13   Report Post  
Vic Dura
 
Posts: n/a
Default

On Wed, 25 May 2005 17:49:55 -0400, in alt.home.repair
Grounding w_tom wrote:

As noted previously, earth ground and safety ground are two
different grounds required by the National Electrical Code
(NEC). A connection to water pipe is no longer sufficient to
earth an AC electric system.


Just curious.

It was sufficient for many years. Now it's not sufficient. What
changed? Is the electricity we use different?

--
To reply to me directly, remove the CLUTTER from my email address.
  #14   Report Post  
Charles Spitzer
 
Posts: n/a
Default


"Vic Dura" wrote in message
...
On Wed, 25 May 2005 17:49:55 -0400, in alt.home.repair
Grounding w_tom wrote:

As noted previously, earth ground and safety ground are two
different grounds required by the National Electrical Code
(NEC). A connection to water pipe is no longer sufficient to
earth an AC electric system.


Just curious.

It was sufficient for many years. Now it's not sufficient. What
changed? Is the electricity we use different?

--
To reply to me directly, remove the CLUTTER from my email address.


for one thing, plastic pipes are now used a lot more than in the past.


  #15   Report Post  
Mike O'Donnell
 
Posts: n/a
Default

The electricity isn't different, but the water pipe may be..

I did a panel replacment/upgrade in my house a couple of years ago and asked
the inspector. He said a lot of water systems aren't using copper pipe as
much. The piece of copper coming into your house may be only be a few feet
long before it's connected to plastic.

Mike O.

"Vic Dura" wrote in message
...
On Wed, 25 May 2005 17:49:55 -0400, in alt.home.repair
Grounding w_tom wrote:

As noted previously, earth ground and safety ground are two
different grounds required by the National Electrical Code
(NEC). A connection to water pipe is no longer sufficient to
earth an AC electric system.


Just curious.

It was sufficient for many years. Now it's not sufficient. What
changed? Is the electricity we use different?

--
To reply to me directly, remove the CLUTTER from my email address.





  #16   Report Post  
Vic Dura
 
Posts: n/a
Default

On Wed, 25 May 2005 16:38:32 -0700, in alt.home.repair
Grounding "Charles Spitzer"
wrote:


"Vic Dura" wrote in message
.. .
On Wed, 25 May 2005 17:49:55 -0400, in alt.home.repair
Grounding w_tom wrote:

As noted previously, earth ground and safety ground are two
different grounds required by the National Electrical Code
(NEC). A connection to water pipe is no longer sufficient to
earth an AC electric system.


Just curious.

It was sufficient for many years. Now it's not sufficient. What
changed? Is the electricity we use different?

--
To reply to me directly, remove the CLUTTER from my email address.


for one thing, plastic pipes are now used a lot more than in the past.


Ok, that make good sense to me. Thanks for the explanation.

--
To reply to me directly, remove the CLUTTER from my email address.
  #17   Report Post  
Jeff Wisnia
 
Posts: n/a
Default

Mike O'Donnell wrote:

The electricity isn't different, but the water pipe may be..

I did a panel replacment/upgrade in my house a couple of years ago and asked
the inspector. He said a lot of water systems aren't using copper pipe as
much. The piece of copper coming into your house may be only be a few feet
long before it's connected to plastic.

Mike O.

"Vic Dura" wrote in message
...

On Wed, 25 May 2005 17:49:55 -0400, in alt.home.repair
Grounding w_tom wrote:


As noted previously, earth ground and safety ground are two
different grounds required by the National Electrical Code
(NEC). A connection to water pipe is no longer sufficient to
earth an AC electric system.


Just curious.

It was sufficient for many years. Now it's not sufficient. What
changed? Is the electricity we use different?

--
To reply to me directly, remove the CLUTTER from my email address.





And, if the city pipes are still metal, they may be using an "impressed
current" cathodic protection system on them and installed an
electrically insulating pipe coupling where their pipe ends and yours
begins, to avoid "shorting out" the impressed voltage on their pipes to
your electrical system's ground. That was a pretty common technique with
gas pipes in some areas too.

Some info on impressed current protection is found in:

http://www.usace.army.mil/inet/usace...hap31VOL-2.pdf

Jeff

--
Jeffry Wisnia

(W1BSV + Brass Rat '57 EE)

"Truth exists; only falsehood has to be invented."
  #18   Report Post  
w_tom
 
Posts: n/a
Default

First thing that changed is plastic pipe. A plumber need
not worry about electricity nor risk electrocution when
working on pipes while standing in water. Second, other
functions of the earthing system (beyond the NEC's primary
purpose) demand an earthing ground connection be short.
Connections to water pipes often are well beyond 10 feet. If
the code ever fully addresses transistor safety, then earthing
requirements would be further enhanced - significantly.
Easily accomplished if installed when a house is first
constructed. We still don't ground as if the transistor
exists.

These solutions (and solutions for the future) can only be
accomplished using a dedicated ground. A ground that a plumber
will not compromise.

Ground problems created by plastic pipe are not just limited
to the earthing ground. Some jurisdictions now require a 6
AWG safety ground wire connected directly from bathtub to
breaker box IF the bathtub is metallic. Again, a problem
created by plastic pipes and by plumbers who need not know
anything about electricity.

Vic Dura wrote:
On Wed, 25 May 2005 17:49:55 -0400, in alt.home.repair
Grounding w_tom wrote:
As noted previously, earth ground and safety ground are two
different grounds required by the National Electrical Code
(NEC). A connection to water pipe is no longer sufficient to
earth an AC electric system.


Just curious.

It was sufficient for many years. Now it's not sufficient. What
changed? Is the electricity we use different?

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Easiest way to ground a computer? Julie P. Home Repair 66 May 11th 05 06:10 PM
Old electrical wiring to outbuildings Nate Baxley Home Repair 11 July 19th 04 07:53 PM
Another subpanel grounding question Korey Atterberry Home Repair 9 July 7th 04 01:30 PM
Doulble Receptacle Grounding Question/ Switch Grounding Michael Roback Home Repair 1 September 7th 03 07:37 AM
Grounding Rod *and* Rebar for service grounds? Vinnie Murdico Home Repair 3 June 27th 03 04:13 PM


All times are GMT +1. The time now is 05:21 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"