I bought an old farmhouse last year and I'm finally getting around to
fixing up some of the out buildings. The two that I'm working on now
each have power that comes from the main breaker panel in the house.
Each building has it's own fuse box with wiring extending from that.
Now on to the problem.

In the main breaker panel there are two seperate 30 Amp breakers that
each have a very large wire coming out of them. They aren't connected
like a double pole and aren't next to each other like a double pole
breaker. The two wires run into a single cable along with another
large wire wired to the neutral bus. The label on the cable is
"E32071 (UL) 3 CDRS AWG 6 TYPE SE CABLE STYLE U TYPE XHHW CDRS 600V".
Now, the cable goes out of the house and through the air to the first
building (Building A). Outside Building A there are severla wired
wired and taped together. One of the hot wires runs into bulding A
and the other wire splits into building A and also heads off to the
other building (Building B). Inside building A there is a fuse box
and the hot and neutral wires run to the normal connections. The
other hot wire and the split from the netural run through the air to
building B where the neutral and other hot wire run into a fuse box
and throughout the building.

Now for the question. I would like to replace the wires in the air
from A to B and replace the fuse boxes with a circuit panel. What I'm
considering is running both hots and the neutral into a 6 circuit
panel inside Building A and then running 1 circuit in A and 3 circuits
over to B through some underground conduit. The other issue that I
see is that currently at the splice outside building A the heavy wire
is spliced to some smaller old wire, it looks like around 10 gauge,
that runs from the outside into the building. I'm guessing that if I
splice the heavy wire coming from the house to a line into Building A
I need to keep it the same guage, right?

Sorry for the long explanation, but I wanted to try and explain the
situation better. If a picture would help, I can sketch one quick and
post it to my website. Any thoughts that you have would be great.

Thanks,
Nate Baxley
  #2   Report Post  
HorneTD
 
Posts: n/a
Default Old electrical wiring to outbuildings

Replies are in line.

Nate Baxley wrote:
I bought an old farmhouse last year and I'm finally getting around to
fixing up some of the out buildings. The two that I'm working on now
each have power that comes from the main breaker panel in the house.
Each building has it's own fuse box with wiring extending from that.
Now on to the problem.

In the main breaker panel there are two seperate 30 Amp breakers that
each have a very large wire coming out of them. They aren't connected
like a double pole and aren't next to each other like a double pole
breaker. The two wires run into a single cable along with another
large wire wired to the neutral bus. The label on the cable is
"E32071 (UL) 3 CDRS AWG 6 TYPE SE CABLE STYLE U TYPE XHHW CDRS 600V".
Now, the cable goes out of the house and through the air to the first
building (Building A). Outside Building A there are severla wired
wired and taped together. One of the hot wires runs into bulding A
and the other wire splits into building A and also heads off to the
other building (Building B). Inside building A there is a fuse box
and the hot and neutral wires run to the normal connections. The
other hot wire and the split from the netural run through the air to
building B where the neutral and other hot wire run into a fuse box
and throughout the building.


Step one is to normalize the arrangement of the supply. Best practice
would be for the two thirty ampere breakers to be replaced with a double
pole breaker. In some panels the two breakers could be a double unit
and yet appear to be separate. Rearranging breakers in a panel must be
carefully done in order to avoid causing problems elsewhere while trying
to solve the problem on which you are focused.

Now for the question. I would like to replace the wires in the air
from A to B and replace the fuse boxes with a circuit panel. What I'm
considering is running both hots and the neutral into a 6 circuit
panel inside Building A and then running 1 circuit in A and 3 circuits
over to B through some underground conduit. The other issue that I
see is that currently at the splice outside building A the heavy wire
is spliced to some smaller old wire, it looks like around 10 gauge,
that runs from the outside into the building. I'm guessing that if I
splice the heavy wire coming from the house to a line into Building A
I need to keep it the same guage, right?


I'm going to guess that the installation will be done in an area were
the US National Electric Code is the standard for installations. You
cannot run multiple branch circuits from one building to another. Each
building must be supplied by a single branch circuit or feeder unless
the second circuit has totally different voltage characteristics or it
is an emergency circuit etc.

I'm guessing that you plan to run the new circuit underground. One way
to do this would be to place a splice box at the end of the first
underground raceway. You then run the feeder inside to the building
disconnecting means from the splices. The other leg of the feeder would
be run to the next building's disconnecting means and it would supply a
second feeder supplied breaker panel.

The other possibility would be to route the feeder to the building that
needs the three circuits. You could then run the single circuit to the
other building.
--
Tom H

Sorry for the long explanation, but I wanted to try and explain the
situation better. If a picture would help, I can sketch one quick and
post it to my website. Any thoughts that you have would be great.

Thanks,
Nate Baxley

  #3   Report Post  
HorneTD
 
Posts: n/a
Default Old electrical wiring to outbuildings

Nate Baxley wrote:

I bought an old farmhouse last year and I'm finally getting around to
fixing up some of the out buildings. The two that I'm working on now
each have power that comes from the main breaker panel in the house.
Each building has it's own fuse box with wiring extending from that.
Now on to the problem.

In the main breaker panel there are two seperate 30 Amp breakers that
each have a very large wire coming out of them. They aren't connected
like a double pole and aren't next to each other like a double pole
breaker. The two wires run into a single cable along with another
large wire wired to the neutral bus. The label on the cable is
"E32071 (UL) 3 CDRS AWG 6 TYPE SE CABLE STYLE U TYPE XHHW CDRS 600V".
Now, the cable goes out of the house and through the air to the first
building (Building A). Outside Building A there are severla wired
wired and taped together. One of the hot wires runs into bulding A
and the other wire splits into building A and also heads off to the
other building (Building B). Inside building A there is a fuse box
and the hot and neutral wires run to the normal connections. The
other hot wire and the split from the netural run through the air to
building B where the neutral and other hot wire run into a fuse box
and throughout the building.

Now for the question. I would like to replace the wires in the air
from A to B and replace the fuse boxes with a circuit panel. What I'm
considering is running both hots and the neutral into a 6 circuit
panel inside Building A and then running 1 circuit in A and 3 circuits
over to B through some underground conduit. The other issue that I
see is that currently at the splice outside building A the heavy wire
is spliced to some smaller old wire, it looks like around 10 gauge,
that runs from the outside into the building. I'm guessing that if I
splice the heavy wire coming from the house to a line into Building A
I need to keep it the same guage, right?

Sorry for the long explanation, but I wanted to try and explain the
situation better. If a picture would help, I can sketch one quick and
post it to my website. Any thoughts that you have would be great.

Thanks,
Nate Baxley


If the US NEC applies you will need to install a grounding electrode
system at each building. Best practice would be to use four wire
feeders with separate Equipment Grounding (bonding) Conductors and
Grounded Current Carrying Conductor (neutral). By doing so you will
avoid the very real possibility that there will be stray currents
running around the property. Such currents can cause discomfort and ill
health in live stock and the risk of electric shock to both animals and
humans.
--
Tom H
  #4   Report Post  
... ...
 
Posts: n/a
Default Old electrical wiring to outbuildings HEY TOM ?


Tom you mentioned grounding electrode system and a 4 wire feed. Could
you clearify that a bit?
Did you mean that you should bring the ground with the feeders to each
building ?
When you said grounding electrode I hope you didn't mean ground rods
for each building ? There should only be a grouding electrode at the
main panel then a 4 wire feed to the sub panel with the ground and
neutral terminating on thier own busses (neutral bus being isolated from
ground)
Do you agree or amI missing something?
Bill

  #5   Report Post  
HorneTD
 
Posts: n/a
Default Old electrical wiring to outbuildings HEY TOM ?

.... ... wrote:

Tom you mentioned grounding electrode system and a 4 wire feed. Could
you clearify that a bit?
Did you mean that you should bring the ground with the feeders to each
building ?
When you said grounding electrode I hope you didn't mean ground rods
for each building ? There should only be a grouding electrode at the
main panel then a 4 wire feed to the sub panel with the ground and
neutral terminating on thier own busses (neutral bus being isolated from
ground)
Do you agree or amI missing something?
Bill

I'm afraid your missing something.

I'm not suggesting that he should use a grounding electrode system as a
substitute for an Equipment Grounding Conductor. I'm not even
suggesting a three wire feeder with the neutral bonded to ground at each
building disconnecting means, though in the absence of other metallic
pathways between the buildings that is a permissible practice. What I
am suggesting is the use of a four wire feeder that includes an
Equipment Grounding (bonding) Conductor (EGC) with that EGC bonded to a
Grounding Electrode System at each building disconnecting means. You
are correct in pointing out that the best practice is to maintain the
Grounded Current Carrying Conductor aloof from Ground at any place other
than the service disconnecting means. Be aware, however that the US NEC
specifically permits you to wire each separate building as if it were a
separate service providing there are no other metallic pathways between
the buildings.

The US NEC requires a Grounding Electrode System at each building unless
that building is served only by a single branch circuit. So in the OPs
case his building A would not need a Grounding Electrode System as he
only needs one branch circuit in there. Trouble is he plans to run the
feeder there first. If he can run the feeder to the building that he is
calling building B then he can run the single branch circuit that he
needs in building A from either the house or building B and he would not
be required to build a grounding electrode system at building A. If he
does run the feeder to building A then he will not need a Grounding
Electrode System there because it will be served only by a single branch
circuit. The applicable section of the US NEC is copied below.

250.32 Two or More Buildings or Structures Supplied from a Common Service.
(A) Grounding Electrode. Where two or more buildings or structures are
supplied from a common ac service by a feeder(s) or branch circuit(s),
the grounding electrode(s) required in Part III of this article at each
building or structure shall be connected in the manner specified in
250.32(B) or (C). Where there are no existing grounding electrodes, the
grounding electrode(s) required in Part III of this article shall be
installed.
Exception: A grounding electrode at separate buildings or structures
shall not be required where only one branch circuit supplies the
building or structure and the branch circuit includes an equipment
grounding conductor for grounding the conductive non–current-carrying
parts of all equipment. (copyright 2002 the National Fire Protection
Association)

It is worth noticing that this section stands alone and is not modified
by other sections. Any building that contains over current protective
devices has to have a grounding electrode system.

I hope that clears up any confusion.
--
Tom H


  #6   Report Post  
Nate Baxley
 
Posts: n/a
Default Old electrical wiring to outbuildings

HorneTD wrote in message ink.net...
Replies are in line.

Nate Baxley wrote:
I bought an old farmhouse last year and I'm finally getting around to
fixing up some of the out buildings. The two that I'm working on now
each have power that comes from the main breaker panel in the house.
Each building has it's own fuse box with wiring extending from that.
Now on to the problem.

In the main breaker panel there are two seperate 30 Amp breakers that
each have a very large wire coming out of them. They aren't connected
like a double pole and aren't next to each other like a double pole
breaker. The two wires run into a single cable along with another
large wire wired to the neutral bus. The label on the cable is
"E32071 (UL) 3 CDRS AWG 6 TYPE SE CABLE STYLE U TYPE XHHW CDRS 600V".
Now, the cable goes out of the house and through the air to the first
building (Building A). Outside Building A there are severla wired
wired and taped together. One of the hot wires runs into bulding A
and the other wire splits into building A and also heads off to the
other building (Building B). Inside building A there is a fuse box
and the hot and neutral wires run to the normal connections. The
other hot wire and the split from the netural run through the air to
building B where the neutral and other hot wire run into a fuse box
and throughout the building.


Step one is to normalize the arrangement of the supply. Best practice
would be for the two thirty ampere breakers to be replaced with a double
pole breaker. In some panels the two breakers could be a double unit
and yet appear to be separate. Rearranging breakers in a panel must be
carefully done in order to avoid causing problems elsewhere while trying
to solve the problem on which you are focused.

Now for the question. I would like to replace the wires in the air
from A to B and replace the fuse boxes with a circuit panel. What I'm
considering is running both hots and the neutral into a 6 circuit
panel inside Building A and then running 1 circuit in A and 3 circuits
over to B through some underground conduit. The other issue that I
see is that currently at the splice outside building A the heavy wire
is spliced to some smaller old wire, it looks like around 10 gauge,
that runs from the outside into the building. I'm guessing that if I
splice the heavy wire coming from the house to a line into Building A
I need to keep it the same guage, right?


I'm going to guess that the installation will be done in an area were
the US National Electric Code is the standard for installations. You
cannot run multiple branch circuits from one building to another. Each
building must be supplied by a single branch circuit or feeder unless
the second circuit has totally different voltage characteristics or it
is an emergency circuit etc.

I'm guessing that you plan to run the new circuit underground. One way
to do this would be to place a splice box at the end of the first
underground raceway. You then run the feeder inside to the building
disconnecting means from the splices. The other leg of the feeder would
be run to the next building's disconnecting means and it would supply a
second feeder supplied breaker panel.

The other possibility would be to route the feeder to the building that
needs the three circuits. You could then run the single circuit to the
other building.
--
Tom H


Thanks Tom,
OK, I want to make sure I understand what you're telling me. My
explanation of running the main feed from the house to Building A
isn't a problem, it's the part about running the 3 circuits from A to
B, right? The problem is that A is physically between the house and
B. So I'd have to run under or through A to a circuit breaker in B
and then run a single circuit back, probably through the same conduit,
to A. Would that work? Does that make sense?


On your other comment about grounding, are you saying that I need to
have a ground wire that runs back to the main circuit breaker in the
house? What about installing a grounding rod a the new circuit
breaker? Would that aleviate the "stray currents" problem?

Thanks for your very informative post. I look forward to your reply.
Nate

Sorry for the long explanation, but I wanted to try and explain the
situation better. If a picture would help, I can sketch one quick and
post it to my website. Any thoughts that you have would be great.

Thanks,
Nate Baxley

  #7   Report Post  
HorneTD
 
Posts: n/a
Default Old electrical wiring to outbuildings

Nate Baxley wrote:
HorneTD wrote in message ink.net...

Replies are in line.

Nate Baxley wrote:

I bought an old farmhouse last year and I'm finally getting around to
fixing up some of the out buildings. The two that I'm working on now
each have power that comes from the main breaker panel in the house.
Each building has it's own fuse box with wiring extending from that.
Now on to the problem.

In the main breaker panel there are two seperate 30 Amp breakers that
each have a very large wire coming out of them. They aren't connected
like a double pole and aren't next to each other like a double pole
breaker. The two wires run into a single cable along with another
large wire wired to the neutral bus. The label on the cable is
"E32071 (UL) 3 CDRS AWG 6 TYPE SE CABLE STYLE U TYPE XHHW CDRS 600V".
Now, the cable goes out of the house and through the air to the first
building (Building A). Outside Building A there are severla wired
wired and taped together. One of the hot wires runs into bulding A
and the other wire splits into building A and also heads off to the
other building (Building B). Inside building A there is a fuse box
and the hot and neutral wires run to the normal connections. The
other hot wire and the split from the netural run through the air to
building B where the neutral and other hot wire run into a fuse box
and throughout the building.


Step one is to normalize the arrangement of the supply. Best practice
would be for the two thirty ampere breakers to be replaced with a double
pole breaker. In some panels the two breakers could be a double unit
and yet appear to be separate. Rearranging breakers in a panel must be
carefully done in order to avoid causing problems elsewhere while trying
to solve the problem on which you are focused.


Now for the question. I would like to replace the wires in the air
from A to B and replace the fuse boxes with a circuit panel. What I'm
considering is running both hots and the neutral into a 6 circuit
panel inside Building A and then running 1 circuit in A and 3 circuits
over to B through some underground conduit. The other issue that I
see is that currently at the splice outside building A the heavy wire
is spliced to some smaller old wire, it looks like around 10 gauge,
that runs from the outside into the building. I'm guessing that if I
splice the heavy wire coming from the house to a line into Building A
I need to keep it the same guage, right?


I'm going to guess that the installation will be done in an area were
the US National Electric Code is the standard for installations. You
cannot run multiple branch circuits from one building to another. Each
building must be supplied by a single branch circuit or feeder unless
the second circuit has totally different voltage characteristics or it
is an emergency circuit etc.

I'm guessing that you plan to run the new circuit underground. One way
to do this would be to place a splice box at the end of the first
underground raceway. You then run the feeder inside to the building
disconnecting means from the splices. The other leg of the feeder would
be run to the next building's disconnecting means and it would supply a
second feeder supplied breaker panel.

The other possibility would be to route the feeder to the building that
needs the three circuits. You could then run the single circuit to the
other building.
--
Tom H



Thanks Tom,
OK, I want to make sure I understand what you're telling me. My
explanation of running the main feed from the house to Building A
isn't a problem, it's the part about running the 3 circuits from A to
B, right? The problem is that A is physically between the house and
B. So I'd have to run under or through A to a circuit breaker in B
and then run a single circuit back, probably through the same conduit,
to A. Would that work? Does that make sense?


On your other comment about grounding, are you saying that I need to
have a ground wire that runs back to the main circuit breaker in the
house? What about installing a grounding rod a the new circuit
breaker? Would that aleviate the "stray currents" problem?

Thanks for your very informative post. I look forward to your reply.
Nate

Sorry for the long explanation, but I wanted to try and explain the
situation better. If a picture would help, I can sketch one quick and
post it to my website. Any thoughts that you have would be great.

Thanks,
Nate Baxley


You can run under A but not through it. You then run a single branch
circuit to building A. You might want to consider running a separate
branch circuit to building A from the main panel in the house and run
the feeder to building B. You can run those in the same conduit as long
as the feeder conductors do not enter building A. Having both circuits
run through the same pull box on the outside of building A is OK.

Read my reply to someone else on the grounding issue. Grounding will be
required at the building that has a panel in it. You run a four wire
feeder, terminate the neutral to an insulated neutral buss bar in the
panel, terminate the Equipment Grounding (bonding) Conductor (EGC) to
the bonded buss bar in the building B panel, install a grounding
electrode system at building B, connect the Grounding Electrode
Conductor (GEC) to the bonded buss bar in the building B panel.

If there are no metallic pathways between the two buildings you are not
required to run an EGC with the feeder. You are required to have a
grounding electrode system at each building that has more than a single
branch circuit run to it.

If you do not run an EGC with the feeder than you must bond the neutral
buss bar to the building B building disconnecting means enclosure, i.e.
to the building B panel cabinet.

The building B panel must be marked as suitable for use as service
equipment. If the building B panel will contain more than six breakers
either now or in the future you must provide a building disconnecting
means in the form of a main breaker or in a disconnect ahead of the
building B panel that is located on or in building B.

The stray current problem is caused by running a three wire feeder
rather than a four wire feeder with a separate EGC. Since you have to
bond the grounded current carrying conductor to ground at each building
if you do not run a separate EGC with the feeder the neutral currents
will be divided between the neutral conductor and the earth. This can
cause a step potential across the surface of the earth between the two
buildings to which some livestock are extremely sensitive.

Once again the best practice is a four wire feeder even though the code
allows a three wire feeder in the absence of other conductive pathways
between the buildings.

No matter which feeder you run you must build a grounding electrode
system at each building that is supplied by more than one branch circuit.
--
Tom H
  #8   Report Post  
zxcvbob
 
Posts: n/a
Default Old electrical wiring to outbuildings

Nate Baxley wrote:

I bought an old farmhouse last year and I'm finally getting around to
fixing up some of the out buildings. The two that I'm working on now
each have power that comes from the main breaker panel in the house.
Each building has it's own fuse box with wiring extending from that.
Now on to the problem.

In the main breaker panel there are two seperate 30 Amp breakers that
each have a very large wire coming out of them. They aren't connected
like a double pole and aren't next to each other like a double pole
breaker. The two wires run into a single cable along with another
large wire wired to the neutral bus. The label on the cable is
"E32071 (UL) 3 CDRS AWG 6 TYPE SE CABLE STYLE U TYPE XHHW CDRS 600V".
Now, the cable goes out of the house and through the air to the first
building (Building A). Outside Building A there are severla wired
wired and taped together. One of the hot wires runs into bulding A
and the other wire splits into building A and also heads off to the
other building (Building B). Inside building A there is a fuse box
and the hot and neutral wires run to the normal connections. The
other hot wire and the split from the netural run through the air to
building B where the neutral and other hot wire run into a fuse box
and throughout the building.

Now for the question. I would like to replace the wires in the air
from A to B and replace the fuse boxes with a circuit panel. What I'm
considering is running both hots and the neutral into a 6 circuit
panel inside Building A and then running 1 circuit in A and 3 circuits
over to B through some underground conduit. The other issue that I
see is that currently at the splice outside building A the heavy wire
is spliced to some smaller old wire, it looks like around 10 gauge,
that runs from the outside into the building. I'm guessing that if I
splice the heavy wire coming from the house to a line into Building A
I need to keep it the same guage, right?

Sorry for the long explanation, but I wanted to try and explain the
situation better. If a picture would help, I can sketch one quick and
post it to my website. Any thoughts that you have would be great.

Thanks,
Nate Baxley



I've been reading all this, and I almost understand it. I would put a
4-space breaker box in "A" and use a 30A 2-pole breaker to supply the
feeder to building B. I would be tempted to reuse one of your fuseboxes
for the service panel in "A" and use two 30A fuses to feed "B". Put a
shiny new 6-space breaker panel in "B" for its 3 circuits and a little
room for expansion. Both "A" and "B" need ground electrodes. Back at
the house, replace the two 30A 1-pole breakers with a 40A or 50A 2-pole
breaker. Be careful when you move breakers around to keep everything on
its original leg or "phase".

I would probably reuse the existing aerial wire from the house to "A",
and bury 4 new wires from "A" to "B". It would be better to run
4-conductor cable from the house to "A", but 3-conductor is allowed and
I'm a cheapskate. (Did I mention I would try to reuse one of the fuse
boxes?)

Have you though about putting a pole at the corner of "A" and using it
as a distribution point to "A" and "B"?

Farm wiring is a lot of fun. Just keep in mind that cattle are *very*
sensitive to voltage gradients and leakage currents. Pay a lot of
attention to grounding.

Bob
  #9   Report Post  
HorneTD
 
Posts: n/a
Default Old electrical wiring to outbuildings

wrote:
On Wed, 14 Jul 2004 18:19:09 GMT, HorneTD
wrote:


The stray current problem is caused by running a three wire feeder
rather than a four wire feeder with a separate EGC. Since you have to
bond the grounded current carrying conductor to ground at each building
if you do not run a separate EGC with the feeder the neutral currents
will be divided between the neutral conductor and the earth. This can
cause a step potential across the surface of the earth between the two
buildings to which some livestock are extremely sensitive.



I have livestock, and never understood this. What do you mean by
"step potential"?

I have a main pull out fuse box on my transformer pole, and from
there, it feeds to each large building, using overhead triplex. Each
of these large buildings has their own breaker box, with their owm
main disconnect. Each has their own grounding system and each has the
bond screw installed. The only buildings that do not have their own
breaker box are small sheds, and those only have a 110 line feed from
the barn, and are just for a few lights. So, I think I am safe.
However, I want to better understand this "step potential".

PS. I learned a nasty lesson the other day. I have electric fences.
I was filling the livestock water tank, and decided to take a drink
from the hose. I put the hose up to my lips, and the water stream
touched the fence. DAMN THAT STUNG !!!!
It's one thing to touch an electric fence, and I do it often, but
getting it in the mouth was nasty. I never thought it would travel
thru water (except salt water). Guess I was wrong.


Step potential is the difference in voltage on the surface of the earth
across the length of the subjects stride or step. In livestock it is
possible to have a stand potential since they have their feet a yard or
more apart when standing. If any of the neutral current flows through
the earth instead of through the neutral of your triplex, and on ground
laden with animal waste it will, there is a voltage drop between the
animals front and back feet that can cause a measurable flow of current
through the animal. Some stock are more sensitive to this than others.
Losses of thirty percent or more of production have been reported in
dairy herds. Any Qualified electrician can check for this by checking
for current flow on each Grounding Electrode Conductor (GEC) and voltage
drop between the various grounding electrode systems. The cure for any
problem on your farm may be as simple as running quadplex from the yard
pole to each building and isolating the neutral in each buildings panel
by removing the bonding screw and installing a separate Equipment
Grounding Conductor (EGC) buss bar in each panels enclosure to terminate
all EGCs and the GEC for that building. By doing that the neutral will
only be bonded to earth ground at the yard pole service equipment. With
the neutral bonded to earth ground only at one point you eliminate any
current flow between the grounding electrodes at each building as long
as there are no ground faults on the farms electrical system. That will
eliminate step potential as long as there is no problem with the power
companies multi grounded neutral (MGN) causing utility neutral current
flow through the farm.
--
Tom H
  #10   Report Post  
Nate Baxley
 
Posts: n/a
Default Old electrical wiring to outbuildings

zxcvbob wrote in message ...
Nate Baxley wrote:

I bought an old farmhouse last year and I'm finally getting around to
fixing up some of the out buildings. The two that I'm working on now
each have power that comes from the main breaker panel in the house.
Each building has it's own fuse box with wiring extending from that.
Now on to the problem.

In the main breaker panel there are two seperate 30 Amp breakers that
each have a very large wire coming out of them. They aren't connected
like a double pole and aren't next to each other like a double pole
breaker. The two wires run into a single cable along with another
large wire wired to the neutral bus. The label on the cable is
"E32071 (UL) 3 CDRS AWG 6 TYPE SE CABLE STYLE U TYPE XHHW CDRS 600V".
Now, the cable goes out of the house and through the air to the first
building (Building A). Outside Building A there are severla wired
wired and taped together. One of the hot wires runs into bulding A
and the other wire splits into building A and also heads off to the
other building (Building B). Inside building A there is a fuse box
and the hot and neutral wires run to the normal connections. The
other hot wire and the split from the netural run through the air to
building B where the neutral and other hot wire run into a fuse box
and throughout the building.

Now for the question. I would like to replace the wires in the air
from A to B and replace the fuse boxes with a circuit panel. What I'm
considering is running both hots and the neutral into a 6 circuit
panel inside Building A and then running 1 circuit in A and 3 circuits
over to B through some underground conduit. The other issue that I
see is that currently at the splice outside building A the heavy wire
is spliced to some smaller old wire, it looks like around 10 gauge,
that runs from the outside into the building. I'm guessing that if I
splice the heavy wire coming from the house to a line into Building A
I need to keep it the same guage, right?

Sorry for the long explanation, but I wanted to try and explain the
situation better. If a picture would help, I can sketch one quick and
post it to my website. Any thoughts that you have would be great.

Thanks,
Nate Baxley



I've been reading all this, and I almost understand it. I would put a
4-space breaker box in "A" and use a 30A 2-pole breaker to supply the
feeder to building B. I would be tempted to reuse one of your fuseboxes
for the service panel in "A" and use two 30A fuses to feed "B". Put a
shiny new 6-space breaker panel in "B" for its 3 circuits and a little
room for expansion. Both "A" and "B" need ground electrodes. Back at
the house, replace the two 30A 1-pole breakers with a 40A or 50A 2-pole
breaker. Be careful when you move breakers around to keep everything on
its original leg or "phase".

I would probably reuse the existing aerial wire from the house to "A",
and bury 4 new wires from "A" to "B". It would be better to run
4-conductor cable from the house to "A", but 3-conductor is allowed and
I'm a cheapskate. (Did I mention I would try to reuse one of the fuse
boxes?)

Have you though about putting a pole at the corner of "A" and using it
as a distribution point to "A" and "B"?

Farm wiring is a lot of fun. Just keep in mind that cattle are *very*
sensitive to voltage gradients and leakage currents. Pay a lot of
attention to grounding.

Bob


Bob,
Thanks for the reply. So if I hear you correctly, I need to put a
circuit panel in A, and use a double pole breaker there to send
another feeder into another circuit panel in B. I can just use a
grounding wire into the ground for each panel, but I still need to run
a 4 wire feeder cable from A to B. That sound correct? As for moving
the breakers around and upping them to 40 Amps on the main breaker in
the house, is that really neccesary? Not to question, but what makes
it necesary to move them together and up the ampage? The main reason
I ask is that the breaker box is a mess (obviously been added to by
some people in a hurry) and I'm dreading haveing to unplug breakers
and reroute wires around that box. If it's something that needs to be
done, I'll do it but I was just curious as to the reasons.

We currently don't have any cattle, but I'll bone up on my grounding
skills before I get into this too much.

Thanks again,
Nate Baxley


  #11   Report Post  
HA HA Budys Here
 
Posts: n/a
Default Old electrical wiring to outbuildings

From: (Nate Baxley)


zxcvbob wrote in message
...
Nate Baxley wrote:

I bought an old farmhouse last year and I'm finally getting around to
fixing up some of the out buildings. The two that I'm working on now
each have power that comes from the main breaker panel in the house.
Each building has it's own fuse box with wiring extending from that.
Now on to the problem.

In the main breaker panel there are two seperate 30 Amp breakers that
each have a very large wire coming out of them. They aren't connected
like a double pole and aren't next to each other like a double pole
breaker. The two wires run into a single cable along with another
large wire wired to the neutral bus. The label on the cable is
"E32071 (UL) 3 CDRS AWG 6 TYPE SE CABLE STYLE U TYPE XHHW CDRS 600V".
Now, the cable goes out of the house and through the air to the first
building (Building A). Outside Building A there are severla wired
wired and taped together. One of the hot wires runs into bulding A
and the other wire splits into building A and also heads off to the
other building (Building B). Inside building A there is a fuse box
and the hot and neutral wires run to the normal connections. The
other hot wire and the split from the netural run through the air to
building B where the neutral and other hot wire run into a fuse box
and throughout the building.

Now for the question. I would like to replace the wires in the air
from A to B and replace the fuse boxes with a circuit panel. What I'm
considering is running both hots and the neutral into a 6 circuit
panel inside Building A and then running 1 circuit in A and 3 circuits
over to B through some underground conduit. The other issue that I
see is that currently at the splice outside building A the heavy wire
is spliced to some smaller old wire, it looks like around 10 gauge,
that runs from the outside into the building. I'm guessing that if I
splice the heavy wire coming from the house to a line into Building A
I need to keep it the same guage, right?

Sorry for the long explanation, but I wanted to try and explain the
situation better. If a picture would help, I can sketch one quick and
post it to my website. Any thoughts that you have would be great.

Thanks,
Nate Baxley



I've been reading all this, and I almost understand it. I would put a
4-space breaker box in "A" and use a 30A 2-pole breaker to supply the
feeder to building B. I would be tempted to reuse one of your fuseboxes
for the service panel in "A" and use two 30A fuses to feed "B". Put a
shiny new 6-space breaker panel in "B" for its 3 circuits and a little
room for expansion. Both "A" and "B" need ground electrodes. Back at
the house, replace the two 30A 1-pole breakers with a 40A or 50A 2-pole
breaker. Be careful when you move breakers around to keep everything on
its original leg or "phase".

I would probably reuse the existing aerial wire from the house to "A",
and bury 4 new wires from "A" to "B". It would be better to run
4-conductor cable from the house to "A", but 3-conductor is allowed and
I'm a cheapskate. (Did I mention I would try to reuse one of the fuse
boxes?)

Have you though about putting a pole at the corner of "A" and using it
as a distribution point to "A" and "B"?

Farm wiring is a lot of fun. Just keep in mind that cattle are *very*
sensitive to voltage gradients and leakage currents. Pay a lot of
attention to grounding.

Bob


Bob,
Thanks for the reply. So if I hear you correctly, I need to put a
circuit panel in A, and use a double pole breaker there to send
another feeder into another circuit panel in B. I can just use a
grounding wire into the ground for each panel, but I still need to run
a 4 wire feeder cable from A to B. That sound correct? As for moving
the breakers around and upping them to 40 Amps on the main breaker in
the house, is that really neccesary? Not to question, but what makes
it necesary to move them together and up the ampage? The main reason
I ask is that the breaker box is a mess (obviously been added to by
some people in a hurry) and I'm dreading haveing to unplug breakers
and reroute wires around that box. If it's something that needs to be
done, I'll do it but I was just curious as to the reasons.

We currently don't have any cattle, but I'll bone up on my grounding
skills before I get into this too much.

Thanks again,
Nate Baxley



OK Nate - you've got your answers, reasons, reasonings, code quotes, etc. Now
shutup and get off the internet and do the damn work.
  #12   Report Post  
zxcvbob
 
Posts: n/a
Default Old electrical wiring to outbuildings

Nate Baxley wrote:

Bob,
Thanks for the reply. So if I hear you correctly, I need to put a
circuit panel in A, and use a double pole breaker there to send
another feeder into another circuit panel in B. I can just use a
grounding wire into the ground for each panel, but I still need to run
a 4 wire feeder cable from A to B. That sound correct?


There are quite a few correct ways to do it; some better than others.

"A" and "B" should each have only one feeder circuit coming in. It
doesn't matter whether B's panel is fed from A or from the house.
Feeding B off of A's panel sounds simplest to me, although someone else
mentioned a tap in an underground juncion box that sounded
interesting... but I'd hate to have to dig it up again later and try to
find the box if it needed service.

Every building should have a ground.

If you run 4 wires from the house to A, you have to run 4 wires from A
to B. If you run 3 wires from the house to A I think you *could* run
just 3 wires from A to B, but I wouldn't recommend it.


As for moving
the breakers around and upping them to 40 Amps on the main breaker in
the house, is that really neccesary? Not to question, but what makes
it necesary to move them together and up the ampage? The main reason
I ask is that the breaker box is a mess (obviously been added to by
some people in a hurry) and I'm dreading haveing to unplug breakers
and reroute wires around that box. If it's something that needs to be
done, I'll do it but I was just curious as to the reasons.


I depends on how right you want to do it. The mess you have now will
work, but it doesn't provide a common trip (if one side overloads and
trip it opens the other breaker too, and if you manually turn off one
breaker the other is also turned off.) And there's no need to up the
breaker size, but you can if you want -- the existing wires can handle
it. I mentioned a 40A breaker because I thought you would be buying a
new 2-pole breaker anyway to get the feeder circuit into one switch with
a common trip.

If you reuse the existing wires, (overhead wires, right? I don't
remember) you can start at the outbuildings and get them working first.
You can redo the house breaker box later when you get around to it --
which can be postponed indefinitely.

If the breaker box in the house was made by Federal Pacific or Zinsco, I
wouldn't open it up either until I was ready to replace it completely
(which would be pretty high on my todo list)

We currently don't have any cattle, but I'll bone up on my grounding
skills before I get into this too much.

Thanks again,
Nate Baxley



Best regards,
Bob -- not an electrician

P.S. I just had another idea. You can run 3 insulated wires in a metal
conduit from the panel in A to the point where the wires connect from
the house. If you ever decide you want 4 wires from the house instead
of 3, you can replace the old triplex cable with quadraplex; connect the
bare messenger wire to the metal conduit with an appropriate clamp or
grounding bushing, and you won't have to pull another wire into the
panel. (you will have to seperate the ground from the neutral inside
the panel.)
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wiring "new" electrical c barry martin Home Repair 0 December 13th 03 03:32 AM
Overhead electrical service to a storage shed Timothy J. Trace Home Repair 3 December 3rd 03 04:21 AM
Electrical wiring inspector? phil UK diy 14 November 25th 03 12:54 AM
Installing Electrical Outlet In Sink Cabinet Matty Home Repair 0 August 27th 03 03:08 PM
Electrical Wiring Grouping Factors in IEE Regs pickerel UK diy 5 July 14th 03 01:26 AM


All times are GMT +1. The time now is 08:33 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"