  #1   Report Post  
Nate
 
Posts: n/a
Default Heating my hot water--four options

Hi-
We just moved into our new 1940 era house. There is inadequate hot
water for our needs. We live in the northeast and have an oil fired
furnace with a steam heating system, radiators. The furnace is a
Peerless, circa 1977. Running through this boiler is a tankless coil
for 'instant' hot water. Everything works fine except the tankless coil
doesn't produce hot water fast enough to give a bath to my kids.

So here are my options, as I see them. . . I don't mind paying more up
front if it means fuel savings down the road.

1. Irving (my oil supplier) wants to put in a 40 gallon indirect hot
water heater that would essentially be a new zone from my furnace . .
$2000, installed.

2. My local plumber also suggested putting in an indirect heated 40
gallon hot water tank but suggested we use the existing coil running
thorough the boiler to heat the water. ... $1300 installed.

3. My friend, who is a plumber who lives in another state who I saw at
a conference this weekend suggested a sperate oil fired hot water
heater . . cost ????.

4. I was considering putting in a regular gas fired (like from home
depot) hot water heater myself. (we have a city natural gas line). And
I was also considering running the water through the coil in the boiler
to preheat it in the winter when the boiler's running anyway (not sure
if that would save money or not).

Any advice greatly appreciated. Many thanks. -Nate Greene

  #2   Report Post  
John Harlow
 
Posts: n/a
Default

Why does hot water need to be heated?


  #3   Report Post  
 
Posts: n/a
Default

Hi, Nate.

Climate varies greatly across the NE, with varying degree and intensity
of summer. During which you (well, at least I) would not want to be
running a steam-boiler, for a bunch of reasons. That makes the
separate water-heater preferable.

Which one, which fuel, would depend on factors invisible from here. An
oil-burner is going to cost much more than a gas-burner, and require
regular service. Your expertise with water and gas piping are a matter
for you and your building inspector, not to mention SO, and her
valuation of safety/peace-of-mind.

As an aside, it would seem that in winter, with a steam-boiler, an
"economizer" (heat-exchanger in the stack) with a loop to the hw
storage tank & a circ-pump that runs with the oil-burner, would be a
Good Thing.

HTH,
John

  #4   Report Post  
Beachcomber
 
Posts: n/a
Default

On Wed, 6 Apr 2005 10:16:18 -0400, "John Harlow"
wrote:

Why does hot water need to be heated?


Both oil and natural gas prices flucuate these days...

But right now, the price of oil is going to the stratosphere.

I would go with option #4 (separate gas)

Beachcomber


  #5   Report Post  
John_B
 
Posts: n/a
Default

Nate wrote:
Hi-
We just moved into our new 1940 era house. There is inadequate hot
water for our needs. We live in the northeast and have an oil fired
furnace with a steam heating system, radiators. The furnace is a
Peerless, circa 1977. Running through this boiler is a tankless coil
for 'instant' hot water. Everything works fine except the tankless coil
doesn't produce hot water fast enough to give a bath to my kids.

So here are my options, as I see them. . . I don't mind paying more up
front if it means fuel savings down the road.

1. Irving (my oil supplier) wants to put in a 40 gallon indirect hot
water heater that would essentially be a new zone from my furnace . .
$2000, installed.

2. My local plumber also suggested putting in an indirect heated 40
gallon hot water tank but suggested we use the existing coil running
thorough the boiler to heat the water. ... $1300 installed.

3. My friend, who is a plumber who lives in another state who I saw at
a conference this weekend suggested a sperate oil fired hot water
heater . . cost ????.

4. I was considering putting in a regular gas fired (like from home
depot) hot water heater myself. (we have a city natural gas line). And
I was also considering running the water through the coil in the boiler
to preheat it in the winter when the boiler's running anyway (not sure
if that would save money or not).

Any advice greatly appreciated. Many thanks. -Nate Greene


I lived in an 1850s house with an oil fired steam heating system
and a water heating coil in the boiler for seventeen years.
During the heating season the domestic hot water got TOO hot
because it was inside boiling water. During the rest of the year
the aquastat which heated the boiler feed water to heat the
domestic water maintained a sensible temperature.

Questions: Is the coil clogged? Is there some crud inside the
coil which is reducing the rate of heat transfer so it does not
heat water fast enough? Is the aquastat [which controls the
boiler feed water temperature when the thermostat is not telling
the oil burner to make steam to heat the house] set at the proper
temperature?


  #6   Report Post  
Edwin Pawlowski
 
Posts: n/a
Default


"Nate" wrote in message
Everything works fine except the tankless coil
doesn't produce hot water fast enough to give a bath to my kids.

So here are my options, as I see them. . . I don't mind paying more up
front if it means fuel savings down the road.

1. Irving (my oil supplier) wants to put in a 40 gallon indirect hot
water heater that would essentially be a new zone from my furnace . .
$2000, installed.


Good in the winter, probably not so good in the summer for efficiencly.


2. My local plumber also suggested putting in an indirect heated 40
gallon hot water tank but suggested we use the existing coil running
thorough the boiler to heat the water. ... $1300 installed.


About the same as above.


3. My friend, who is a plumber who lives in another state who I saw at
a conference this weekend suggested a sperate oil fired hot water
heater . . cost ????.


Better option, IMO.


4. I was considering putting in a regular gas fired (like from home
depot) hot water heater myself. (we have a city natural gas line). And
I was also considering running the water through the coil in the boiler
to preheat it in the winter when the boiler's running anyway (not sure
if that would save money or not).


This is probably the best so far. I'm not sre about hte pre-het though. NG
is usually a bit ceaper than oil, much cheaper than electric.


Any advice greatly appreciated. Many thanks. -Nate Greene



How about a point of use heater for the bathroom? It will satisfy the bath
and not detract from existing supplies if the DW is running at the same
time.


  #7   Report Post  
m Ransley
 
Posts: n/a
Default

Your boiler is probably no more than 70% efficient even if it has been
maintained, the hot water loop in winter is therefore 70% and a drag on
the boiler, In summer it is less than 70% because it is a secondary heat
so maybe it is 50% efficient and heating the house a bit. When AC is on.
1300 for a new gas tank? That is high for a regular cheap water heater.
Consider 2 things, block off boiler coil and a Tankless Takagi Flash TH
-1 is the newest Takagi model out with a Ng efficiency of 92%, 95% on
propane, and will meet a 3 shower house needs. You will save on standby
loss 10-20% , and never run out of hot water. I have a Bosch-Takagi
Tankless and wont go back to tank. My summer gas bill is 6-8$ , I took
out an electric tank and electric went down 25-30$. And my unit is only
82% efficient. There are a few gas tankless units out from 82-87%
Rinnai is good also, but 92-95% is the new Takagi TH-1 www.Takagi.com
Takagi makes Bosches large units of 83% efficiency and are sold at HD
and Menards, tankless will save you the most money in utilities.

  #8   Report Post  
 
Posts: n/a
Default

1. Get rid of kids.
2. Insulate hot water lines. You'd be amazed at how much a difference
this can make.
3. Regular gas water heater.

  #9   Report Post  
Joe S
 
Posts: n/a
Default

John Harlow wrote:
Why does hot water need to be heated?



To make it hotter.

Was this a trick question??????



Joe

  #10   Report Post  
Marilyn & Bob
 
Posts: n/a
Default

Strongly recommend the gas water heater supplied by the tankless coil. If
you (or the local codes) decide not to install it yourself, you'll still do
better with a professional install of a gas heater than the other two
solutions. And you save lots but not having to fire up your boiler in the
non-heating season. If you feed the heater from the tankless coil you will
save a lot of gas. Our gas bill tripled during the summer when the boiler
(hot water, not steam) was not running. Also since your boiler is almost 30
years old, you might need/want to replace it in the next decade. When you
do, you could save a lot by getting a new boiler without a tankless coil
(especially if you choose gas heat) and the gas hot water heater would fit
right into that setup.
--
Peace,
BobJ



wrote in message
oups.com...
1. Get rid of kids.
2. Insulate hot water lines. You'd be amazed at how much a difference
this can make.
3. Regular gas water heater.




  #11   Report Post  
Nate
 
Posts: n/a
Default

Thank you everyone so much for the information. Sounds like a seperate
gas heater is the way to go. I'll have a pro do the gas line.

Bob- If I do a preheat through my boiler. would I remove the mixing
valve from the current tankless coil and just do a straight shot
through the tankless coil then into my new hot water heater, or would I
leave the mixing valve for safety.

Also anyone know the pros and cons of tankless versus tank gas hot
water heaters?

Thanks again. I am really grateful for the response. -Nate Greene


Marilyn & Bob wrote:
Strongly recommend the gas water heater supplied by the tankless

coil. If
you (or the local codes) decide not to install it yourself, you'll

still do
better with a professional install of a gas heater than the other two


solutions. And you save lots but not having to fire up your boiler

in the
non-heating season. If you feed the heater from the tankless coil

you will
save a lot of gas. Our gas bill tripled during the summer when the

boiler
(hot water, not steam) was not running. Also since your boiler is

almost 30
years old, you might need/want to replace it in the next decade.

When you
do, you could save a lot by getting a new boiler without a tankless

coil
(especially if you choose gas heat) and the gas hot water heater

would fit
right into that setup.
--
Peace,
BobJ



wrote in message
oups.com...
1. Get rid of kids.
2. Insulate hot water lines. You'd be amazed at how much a

difference
this can make.
3. Regular gas water heater.


  #12   Report Post  
Nate
 
Posts: n/a
Default

About face.

I just called my gas company. Although I have a gas line into my house,
it has been 'retired'. I was assuming it just needed to be turned on,
but I was wrong. They want about $2000 to run a new line into the
house. But if I convert my furnace to natural gas, they'll do it for
free. Any opinions?

  #13   Report Post  
Doug Miller
 
Posts: n/a
Default

In article . com, "Nate" wrote:
About face.

I just called my gas company. Although I have a gas line into my house,
it has been 'retired'. I was assuming it just needed to be turned on,
but I was wrong. They want about $2000 to run a new line into the
house. But if I convert my furnace to natural gas, they'll do it for
free. Any opinions?


Furnace conversion sounds cheaper than a new gas line...

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?
  #14   Report Post  
m Ransley
 
Posts: n/a
Default

You could get a new 83% gas boiler and save over your old unit,and have
cheaper gas to use for cooking and the dryer. Run your numbers before
you say no, I pay apx 1$ a therm Ng and 0.12kwh. electric for me is
several times more than gas or aps 3$ a therm, compared to Ng 1$ a
therm. Is you go all electric for cooking and your dryer and HW, you
will be paying many times more then if you convert. A new gas boiler may
save you 10-20% and yours is not new at all . I would go new boiler,
and tankless Takagi and a free gas line. The Takagi drawback is 2- 3
reduced flow showers at one time I dont find a drawback I like the
savings on my bill.

  #15   Report Post  
Marilyn & Bob
 
Posts: n/a
Default


"Nate" wrote in message
oups.com...
Thank you everyone so much for the information. Sounds like a seperate
gas heater is the way to go. I'll have a pro do the gas line.

Bob- If I do a preheat through my boiler. would I remove the mixing
valve from the current tankless coil and just do a straight shot
through the tankless coil then into my new hot water heater, or would I
leave the mixing valve for safety.


It looks like this question may no longer be relevant if you decide to get a
new gas boiler without a tankless coil. But if you still need an answer,
I'm sure someone else here could supply it. Ours was an oil fired boiler
for a hot water (not steam) heating system, so no mixing valve was necessary
as the water was at an appropriate faucet temperature when it left the coil.
--
Peace,
BobJ


Also anyone know the pros and cons of tankless versus tank gas hot
water heaters?

Thanks again. I am really grateful for the response. -Nate Greene


Marilyn & Bob wrote:




  #16   Report Post  
Nate
 
Posts: n/a
Default

Followup-
Since I found out my gas line is 'retired', I am currenlty looking at
getting an electric hot water heater, preheated by my tankless coil
(useful in winter only (which is long in Maine). In 10 years when my
oil furnace goes, I'll replace all of it with highly efficent gas
everything. I just don't know if I can afford to replace my furnace,
hot water system, and everything right now, even thought that might be
a good option. Thanks again for everyone's help. If anyone has
comment(s) on my plan, I would love to hear them. This forum is
fantastic.

Thanks.
-Nate


Nate wrote:
Hi-
We just moved into our new 1940 era house. There is inadequate hot
water for our needs. We live in the northeast and have an oil fired
furnace with a steam heating system, radiators. The furnace is a
Peerless, circa 1977. Running through this boiler is a tankless coil
for 'instant' hot water. Everything works fine except the tankless

coil
doesn't produce hot water fast enough to give a bath to my kids.

So here are my options, as I see them. . . I don't mind paying more

up
front if it means fuel savings down the road.

1. Irving (my oil supplier) wants to put in a 40 gallon indirect hot
water heater that would essentially be a new zone from my furnace . .
$2000, installed.

2. My local plumber also suggested putting in an indirect heated 40
gallon hot water tank but suggested we use the existing coil running
thorough the boiler to heat the water. ... $1300 installed.

3. My friend, who is a plumber who lives in another state who I saw

at
a conference this weekend suggested a sperate oil fired hot water
heater . . cost ????.

4. I was considering putting in a regular gas fired (like from home
depot) hot water heater myself. (we have a city natural gas line).

And
I was also considering running the water through the coil in the

boiler
to preheat it in the winter when the boiler's running anyway (not

sure
if that would save money or not).

Any advice greatly appreciated. Many thanks. -Nate Greene


  #17   Report Post  
Marilyn & Bob
 
Posts: n/a
Default


"Nate" wrote in message
oups.com...
Followup-
Since I found out my gas line is 'retired', I am currenlty looking at
getting an electric hot water heater, preheated by my tankless coil
(useful in winter only (which is long in Maine). In 10 years when my
oil furnace goes, I'll replace all of it with highly efficent gas
everything. I just don't know if I can afford to replace my furnace,
hot water system, and everything right now, even thought that might be
a good option. Thanks again for everyone's help. If anyone has
comment(s) on my plan, I would love to hear them. This forum is
fantastic.

Thanks.
-Nate



Sounds like a plan. If you do the work yourself, be sure to get that
tempering valve question answered before you begin.
--
Peace,
BobJ

  #18   Report Post  
Nate
 
Posts: n/a
Default

Thanks Bob. Glad to know the plan doesn't sound too off the wall.

  #19   Report Post  
m Ransley
 
Posts: n/a
Default

An electric water will work but possibly triple your water heating bill
and require an electrician to run 220 to an empty circuit, you do have
one right, and a good main size.

A new 83% Ng steam boiler will save you 15% on heating and you can
find one with a internal WH coil.

Will they even offer re-hookup in 10 yrs?

Is Ng cheaper per Btu than oil in your area, It is in mine by 20-25%
Have you considered your boiler repairs and maintenance, If you don`t do
maintenance you loose efficency and forget 70% , you could be at 60% or
less now. You have alot of numbers to run on payback, instal, and costs
of ng, vs oil, vs electric. You may find Ng the best option after all.
most do. Don`t forget that boiler is almost 30

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AquaTherm Furnace - No Hot Water Issue David Home Repair 11 January 25th 18 08:44 PM
Copper pipe sizing. Is bigger better? Paul J Home Repair 19 February 29th 04 07:52 PM
Flushing / Cleaning Hot Water Heater Help Needed Cuse Home Repair 38 December 1st 03 02:01 AM
Pool water in central heating system Andy Hall UK diy 1 September 2nd 03 05:01 PM
Why is this a bad idea? Mike Hibbert UK diy 18 August 28th 03 11:59 PM


All times are GMT +1. The time now is 12:58 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"