Home |
Search |
Today's Posts |
#1
Posted to misc.consumers.house
|
|||
|
|||
weird electrical problem
I just discovered some strange wiring in my house. When we moved in,
the breaker box was only 60 amps, so you can imagine the density of the various electrical loads on each circuit. One 15 amp circuit now serves the laundry room, including a shoplight, and the dishwasher upstairs, plus an upstairs bathroom, and who knows what else. One day I was running the washer, the dryer, and the dishwasher all at the same time, with no ill effects. The hairdryer up in the bathroom blew the circuit, no surprise. The surprise was that even though the breaker was off, the washer and dryer were still running (the dishwasher I'm not sure about, but the light was off, and so was the hairdryer, after the breaker blew). What should I look for to solve this problem? I plan to run a new line just for the laundry room, but I also want to disconnect what's there now so no one uses this old circuit in that room. I don't want to accidentally disconnect the upstairs bathroom. |
#2
Posted to misc.consumers.house
|
|||
|
|||
weird electrical problem
In article ,
KLS wrote: One day I was running the washer, the dryer, and the dishwasher all at the same time, with no ill effects. The hairdryer up in the bathroom blew the circuit, no surprise. The surprise was that even though the breaker was off, the washer and dryer were still running (the dishwasher I'm not sure about, but the light was off, and so was the hairdryer, after the breaker blew). What should I look for to solve this problem? I plan to run a new line just for the laundry room, but I also want to disconnect what's there now so no one uses this old circuit in that room. I don't want to accidentally disconnect the upstairs bathroom. The dryer is a 220V item, to it needs both legs of the 220 circuit. A hair dryer is a 110V item, so it only needs one leg of a 220 circuit. What is probably going on is that you have a 220 circuit that feeds the dryer. The washer (normally a 110V item) is piggybacked on one side of that circuit, and the bathroom is piggybacked on the other side of that circuit. When the hair dryer came on, it blew one side of the 220. That left the other side running, so the washer was OK, and the clothes driver was running on half power. The only way this can happen is if the dryer is wired to 2 independent breakers. Normally, a circuit like this has a pair of breakers that is ganged together, so when one side blows, the other side is tripped off. This is a pretty easy thing to fix, but that is only one of your problems. Your wiring system is a fire waiting to happen, and you need a rewire. If I am wrong, then something even worse is going on, and my statement on being a fire hazzard goes double. -john- -- ================================================== ==================== John A. Weeks III 952-432-2708 Newave Communications http://www.johnweeks.com ================================================== ==================== |
#3
Posted to misc.consumers.house
|
|||
|
|||
weird electrical problem
On Sun, 02 Sep 2007 15:19:33 -0500, "John A. Weeks III"
wrote: In article , KLS wrote: One day I was running the washer, the dryer, and the dishwasher all at the same time, with no ill effects. The hairdryer up in the bathroom blew the circuit, no surprise. The surprise was that even though the breaker was off, the washer and dryer were still running (the dishwasher I'm not sure about, but the light was off, and so was the hairdryer, after the breaker blew). What should I look for to solve this problem? I plan to run a new line just for the laundry room, but I also want to disconnect what's there now so no one uses this old circuit in that room. I don't want to accidentally disconnect the upstairs bathroom. The dryer is a 220V item, to it needs both legs of the 220 circuit. A hair dryer is a 110V item, so it only needs one leg of a 220 circuit. What is probably going on is that you have a 220 circuit that feeds the dryer. The washer (normally a 110V item) is piggybacked on one side of that circuit, and the bathroom is piggybacked on the other side of that circuit. When the hair dryer came on, it blew one side of the 220. That left the other side running, so the washer was OK, and the clothes driver was running on half power. The only way this can happen is if the dryer is wired to 2 independent breakers. Normally, a circuit like this has a pair of breakers that is ganged together, so when one side blows, the other side is tripped off. John, yes, I realize I need a re-wire, and we have been working on this the four years we've lived here. I do very much appreciate your wisdom here and will follow your advice. Thanks very much for posting! I learned a lot. We most definitely will be running a new line for the laundry room now that I know what's going on here, and I'll be disconnecting as much in the basement as I can without disrupting power to the upstairs bathroom. |
#4
Posted to misc.consumers.house
|
|||
|
|||
weird electrical problem
On Sep 2, 6:07 pm, KLS wrote:
On Sun, 02 Sep 2007 15:19:33 -0500, "John A. Weeks III" wrote: In article , KLS wrote: One day I was running the washer, the dryer, and the dishwasher all at the same time, with no ill effects. The hairdryer up in the bathroom blew the circuit, no surprise. The surprise was that even though the breaker was off, the washer and dryer were still running (the dishwasher I'm not sure about, but the light was off, and so was the hairdryer, after the breaker blew). What should I look for to solve this problem? I plan to run a new line just for the laundry room, but I also want to disconnect what's there now so no one uses this old circuit in that room. I don't want to accidentally disconnect the upstairs bathroom. The dryer is a 220V item, to it needs both legs of the 220 circuit. A hair dryer is a 110V item, so it only needs one leg of a 220 circuit. What is probably going on is that you have a 220 circuit that feeds the dryer. The washer (normally a 110V item) is piggybacked on one side of that circuit, and the bathroom is piggybacked on the other side of that circuit. When the hair dryer came on, it blew one side of the 220. That left the other side running, so the washer was OK, and the clothes driver was running on half power. The only way this can happen is if the dryer is wired to 2 independent breakers. Normally, a circuit like this has a pair of breakers that is ganged together, so when one side blows, the other side is tripped off. John, yes, I realize I need a re-wire, and we have been working on this the four years we've lived here. I do very much appreciate your wisdom here and will follow your advice. Thanks very much for posting! I learned a lot. We most definitely will be running a new line for the laundry room now that I know what's going on here, and I'll be disconnecting as much in the basement as I can without disrupting power to the upstairs bathroom. - Hide quoted text - - Show quoted text - It would be well worth the time and money to have a licensed electrician check out your system for flaws (incuding grounds) and to provide you a written proposal with quoted price for work to be done (by room). Your family's safety is involved as well as your investment in the home. DO NOT DELAY. I suspect from what you have written, you will probably also need to increase the service rating between the house wiring (probably even a new breaker box) and power company lines. GOOD LUCK ... AND BE SAFE! |
#5
Posted to misc.consumers.house
|
|||
|
|||
weird electrical problem
In article , "John A. Weeks III" wrote:
In article , KLS wrote: One day I was running the washer, the dryer, and the dishwasher all at the same time, with no ill effects. The hairdryer up in the bathroom blew the circuit, no surprise. The surprise was that even though the breaker was off, the washer and dryer were still running (the dishwasher I'm not sure about, but the light was off, and so was the hairdryer, after the breaker blew). What should I look for to solve this problem? I plan to run a new line just for the laundry room, but I also want to disconnect what's there now so no one uses this old circuit in that room. I don't want to accidentally disconnect the upstairs bathroom. The dryer is a 220V item, to it needs both legs of the 220 circuit. Unsupported assumption. Gas dryers, and some small electric dryers, are only 120V. Given that the OP's service is only 60A, an electric dryer seems rather unlikely. A hair dryer is a 110V item, so it only needs one leg of a 220 circuit. What is probably going on is that you have a 220 circuit that feeds the dryer. The washer (normally a 110V item) is piggybacked on one side of that circuit, and the bathroom is piggybacked on the other side of that circuit. More unsupported assumptions. When the hair dryer came on, it blew one side of the 220. That left the other side running, so the washer was OK, and the clothes driver was running on half power. Alternative explanation: the laundry room light and the laundry room outlet are on two different 120V circuits. The only way this can happen is if the dryer is wired to 2 independent breakers. The existence of any breakers at all is another unsupported assumption. Since the OP's service is only 60A, it's obviously been there a looooong time, and there's a good chance he has fuses instead of breakers. Normally, a circuit like this has a pair of breakers that is ganged together, so when one side blows, the other side is tripped off. If he has fuses, though... This is a pretty easy thing to fix, but that is only one of your problems. Your wiring system is a fire waiting to happen, and you need a rewire. If I am wrong, then something even worse is going on, and my statement on being a fire hazzard goes double. I think you're jumping to conclusions here. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#6
Posted to misc.consumers.house
|
|||
|
|||
weird electrical problem
KLS wrote:
John, yes, I realize I need a re-wire, and we have been working on this the four years we've lived here. Pfft. You are risking a fire inside a wall. That is serious bad news. Don't fiddle until your house burns. Una |
#7
Posted to misc.consumers.house
|
|||
|
|||
weird electrical problem
I would start by upgrading and bringing up to "code" you main service panel.
I would suggest a 200 amp service and a 40 slot breaker panel. If you go and look at breaker panels at a home improvement store, you will see that there is not much additional cost for a larger breaker panel. I always see people who run out of breaker slots! Never fails. So get plenty of extras. Note that a new properly wired kitchen can have as many as 10 separate circuits! Upgrading your main service panel will also include proper and good grounding. This is very important for a safe electrical system. You can also get a whole house surge suppressor which will help to protect all those electronic gizmos. I would recommend also having surge suppression power strips as well. But note that if you do not have a properly grounded main service, surge suppressor power strips may not work. Anyway once you get the main service upgraded with a new panel, then you can easily add circuits as needed. Also you can easily add "GFI" circuits as required with GFI breakers and "Arc Fault" breakers as required. Note that in old home bathrooms, the wiring can be quite dangerous. I've seen light fixtures in these homes where the heat from the light has caused the insulation on the wiring to disintegrate and there are bare wires back behind the fixture. Some of these fixtures are also part of a metal medicine cabinet which is not grounded. So you are in bare feet touching a metal cabinet which could be a shock hazard. (Then old wiring has no ground, old main panel may not have a ground.) With a new service panel, you have a good ground there, then new wiring to the bathroom light fixture is "high heat rated" wiring insulation, then metal parts properly grounded to prevent shock, then also GFI on outlets which will cut power before you get shocked. So quite a bit of difference in safety from old bathroom wiring to new bathroom wiring! "KLS" wrote in message I just discovered some strange wiring in my house. When we moved in, the breaker box was only 60 amps, so you can imagine the density of the various electrical loads on each circuit. One 15 amp circuit now serves the laundry room, including a shoplight, and the dishwasher upstairs, plus an upstairs bathroom, and who knows what else. One day I was running the washer, the dryer, and the dishwasher all at the same time, with no ill effects. The hairdryer up in the bathroom blew the circuit, no surprise. The surprise was that even though the breaker was off, the washer and dryer were still running (the dishwasher I'm not sure about, but the light was off, and so was the hairdryer, after the breaker blew). What should I look for to solve this problem? I plan to run a new line just for the laundry room, but I also want to disconnect what's there now so no one uses this old circuit in that room. I don't want to accidentally disconnect the upstairs bathroom. |
#8
Posted to misc.consumers.house
|
|||
|
|||
weird electrical problem
"Himpg" wrote in message oups.com... On Sep 2, 6:07 pm, KLS wrote: On Sun, 02 Sep 2007 15:19:33 -0500, "John A. Weeks III" wrote: In article , KLS wrote: One day I was running the washer, the dryer, and the dishwasher all at the same time, with no ill effects. The hairdryer up in the bathroom blew the circuit, no surprise. The surprise was that even though the breaker was off, the washer and dryer were still running (the dishwasher I'm not sure about, but the light was off, and so was the hairdryer, after the breaker blew). What should I look for to solve this problem? I plan to run a new line just for the laundry room, but I also want to disconnect what's there now so no one uses this old circuit in that room. I don't want to accidentally disconnect the upstairs bathroom. The dryer is a 220V item, to it needs both legs of the 220 circuit. A hair dryer is a 110V item, so it only needs one leg of a 220 circuit. What is probably going on is that you have a 220 circuit that feeds the dryer. The washer (normally a 110V item) is piggybacked on one side of that circuit, and the bathroom is piggybacked on the other side of that circuit. When the hair dryer came on, it blew one side of the 220. That left the other side running, so the washer was OK, and the clothes driver was running on half power. The only way this can happen is if the dryer is wired to 2 independent breakers. Normally, a circuit like this has a pair of breakers that is ganged together, so when one side blows, the other side is tripped off. John, yes, I realize I need a re-wire, and we have been working on this the four years we've lived here. I do very much appreciate your wisdom here and will follow your advice. Thanks very much for posting! I learned a lot. We most definitely will be running a new line for the laundry room now that I know what's going on here, and I'll be disconnecting as much in the basement as I can without disrupting power to the upstairs bathroom. - Hide quoted text - - Show quoted text - It would be well worth the time and money to have a licensed electrician check out your system for flaws (incuding grounds) and to provide you a written proposal with quoted price for work to be done (by room). Your family's safety is involved as well as your investment in the home. DO NOT DELAY. I suspect from what you have written, you will probably also need to increase the service rating between the house wiring (probably even a new breaker box) and power company lines. Yeah, based on the details provided, I think I would probably plan on a rip'n'replace rewire, even if I had to finance it. You can always patch up the holes in the wallboard after the fact, if the others who live in the house won't shoot you first. Stuff That Can Kill You is not the place to cut corners. (I don't cheap out on brakes and tires any more, either.) aem sends... |
#11
Posted to misc.consumers.house
|
|||
|
|||
weird electrical problem
On Mon, 3 Sep 2007 09:06:01 -0700, "Bill"
wrote: I would start by upgrading and bringing up to "code" you main service panel. I would suggest a 200 amp service and a 40 slot breaker panel. If you go and look at breaker panels at a home improvement store, you will see that there is not much additional cost for a larger breaker panel. Done, 4 years ago, when we moved in. We have been using and enjoying the additional slots and have plenty left for the kitchen remodel/rewire that's in the works for next year. |
#12
Posted to misc.consumers.house
|
|||
|
|||
weird electrical problem
In article , "John A. Weeks III" wrote:
In article , (Doug Miller) wrote: In article , "John A. Weeks III" wrote: In article , KLS wrote: One day I was running the washer, the dryer, and the dishwasher all at the same time, with no ill effects. The hairdryer up in the bathroom blew the circuit, no surprise. The surprise was that even though the breaker was off, the washer and dryer were still running (the dishwasher I'm not sure about, but the light was off, and so was the hairdryer, after the breaker blew). What should I look for to solve this problem? The existence of any breakers at all is another unsupported assumption. Since the OP's service is only 60A, it's obviously been there a looooong time, and there's a good chance he has fuses instead of breakers. He stated above that he has breakers. True enough -- but many people don't use terminology correctly. Until the OP confirms that he knows the difference between fuses and breakers, and specifies which he has, I'm not ready to assume a breaker. This is a pretty easy thing to fix, but that is only one of your problems. Your wiring system is a fire waiting to happen, and you need a rewire. If I am wrong, then something even worse is going on, and my statement on being a fire hazzard goes double. I think you're jumping to conclusions here. Are you seriously suggesting that his wiring situation is OK and is not a fire waiting to happen? Not without seeing it, no -- but you haven't seen it either. I see no evidence in the OP's post that he has the 240V electric dryer you assume to exist, nor that only one side of a hypothetical 240V circuit has tripped a breaker, or blown a fuse, whichever he has. Granted, I cannot prove that in court since I have never seen it in person, but anyone who is in the business and reads what he has is reasonable in jumping to that exact conclusion. Let me make my own set of unsupported assumptions, diametrically opposed to yours: 1) the dryer is a gas dryer (or a small electric one) on a 120V circuit 2) the laundry outlet is on a *different* 120V circuit from the laundry lights Given this set of assumptions, please explain what, exactly, in the OP's description of popping the overcurrent device by plugging in a hairdryer would cause you, or anyone else, to conclude that the wiring is an imminent hazard. *That* is why I say you're jumping to conclusions. You don't have all the information, any more than I do. If he wants a better opinion, then he should hire someone to come out and look at it rather than posting on the Internet. No argument there at all. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#13
Posted to misc.consumers.house
|
|||
|
|||
weird electrical problem
In article , KLS wrote:
On Mon, 03 Sep 2007 14:48:27 GMT, (Doug Miller) wrote: In article , "John A. Weeks III" wrote: In article , KLS wrote: One day I was running the washer, the dryer, and the dishwasher all at the same time, with no ill effects. The hairdryer up in the bathroom blew the circuit, no surprise. The surprise was that even though the breaker was off, the washer and dryer were still running (the dishwasher I'm not sure about, but the light was off, and so was the hairdryer, after the breaker blew). What should I look for to solve this problem? I plan to run a new line just for the laundry room, but I also want to disconnect what's there now so no one uses this old circuit in that room. I don't want to accidentally disconnect the upstairs bathroom. The dryer is a 220V item, to it needs both legs of the 220 circuit. Unsupported assumption. Gas dryers, and some small electric dryers, are only 120V. Given that the OP's service is only 60A, an electric dryer seems rather unlikely. OP he The service *WAS* 60A when we moved in, and we immediately upgraded to 200A. The dryer is gas, not electric. In that case, you can disregard Mr. Weeks' conclusion immediately below: When the hair dryer came on, it blew one side of the 220. That left the other side running, so the washer was OK, and the clothes driver was running on half power. Alternative explanation: the laundry room light and the laundry room outlet are on two different 120V circuits. This is possible, but from what I can see of the wiring (which is visible as it's attached to the joists in the basement), it LOOKS LIKE they're all on the same circuit. I haven't taken anything apart to actually check yet; I'm waiting for my electrician to get back to me on when he can get over here and check this out since he installed the 200A box, and I'm asking him to double check that there's not a mistake in the wiring somewhere. Thirty-five or forty bucks at Lowe's or HD will buy you a circuit tracer. It has two components: a transmitter that you plug into an outlet, and a receiver that beeps when its sensor wand is held over the breaker that feeds the circuit the outlet is on. (The transmitter injects a radio-frequency signal on the circuit.) You can test lighting outlets with one of those screw-in adapters that converts a light socket into an outlet. A few minutes with one of those should be enough to tell you whether the lights and outlets are on the same circuit or not. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#14
Posted to misc.consumers.house
|
|||
|
|||
weird electrical problem
|
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Weird Electrical Problem | Home Repair | |||
Weird Electrical Problem | Home Repair | |||
Very weird lawn tractor electrical problem | Home Repair | |||
Weird electrical situation in home | Home Repair | |||
Weird electrical problem | Home Repair |