everyone,

Have a problem of my A/C not cooling
my home down sufficiently:


Quote:
I would consider 30F condenser dT to be the upper limit on older low
SEER units, beyond which there is an airflow problem. On the newer
high SEER units, I would draw the line at 25F dT.


The lower limit would depend primarily upon load. I would think it
should be about 15F dT or above.


Here is the list of temps I use for online trouble shooting.


Low side:


Evap air in temp = 66°F
Evap air out temp = 48°F
SST (saturated suction temp) - Where is this measured and how?
Suction line temp near compressor = 35°F


High side: (I'll get these soon)


Cond air in temp -
Cond air out temp
SCT (saturated condensing temp)
Liquid line temp near condenser


------------------------------------------------------


description of my system:


2 Ton Copeland Hermetic Recipricating compressor (inside a 1987 seer 8
condenser)
1980 Tappan furnace
1953 brick ranch style house, with insulated attic and insulated
basement, about 1100 sq ft


Performed a test yesterday with monitoring temperatures becuase it was
very calm and stable outdoor air temps today


Outdoor air temp was 81 from 1pm to 5pm
Inside air temp started at 76.8°F @1pm
inside air temp ended at 75.2°F @5pm
ATTIC AIR TEMP was over 103°F during all the hours
Every half hour the main floor temp only dropped about .18°F during
these hours.
Humidity on main floor was 42% at 1pm, and dropped to 38% by 5pm


What would you guys call a low seer unit?


couple more things: the temps that are listed in the quoted text are
from my current setup, I just inserted them thats all. I replaced the
furnace blower motor. The compressor is new (few days)
Basement temp is very close to main floor temp (couple degrees
difference(which I think rules out any bad ducting leaks))
AND when the return air is 72°F, the output air from any room vent is
57°F


Are these okay temps? I want my house temps to fall at little higher
rate when the system runs. Like for example, it never shut off in those

5 hours as my target temp was 72°F !!!


~Will

  #2   Report Post  
Posted to alt.home.repair
dpb
 
Posts: n/a
Default Weak Central Air problem


Lin0 wrote:
everyone,

Have a problem of my A/C not cooling
my home down sufficiently:

....
Outdoor air temp was 81 from 1pm to 5pm
Inside air temp started at 76.8°F @1pm
inside air temp ended at 75.2°F @5pm
ATTIC AIR TEMP was over 103°F during all the hours
Every half hour the main floor temp only dropped about .18°F during
these hours.
Humidity on main floor was 42% at 1pm, and dropped to 38% by 5pm
...AND when the return air is 72°F, the output air from any room vent is
57°F


.... I want my house temps to fall at little higher
rate when the system runs. Like for example, it never shut off in those
5 hours as my target temp was 72°F !!!


Basically, what this tells me is that your heat load is too great for
the capacity of the unit. More attic insulation might help some plus
adding some (more) ventilation or even a power exhaust.

Is the basement finished living space and is it ducted or is it just a
basement?

You don't mention how many windows/doors, etc., nor condition of them
nor presence/absence of thermopane and/or storm windows. Such losses
as that would be another place to consider.

Also, is this an ongoing existing condition or has something changed?
W/ the new compressor, I'm guessing the old unit died and was repaired?
Probably a better choice would have been a new system although unless
the house were brought closer to current-day standards of insulation
and leakage control (or has been _recently_), a 50s vintage house will
probably be very "lossy"...

  #3   Report Post  
Posted to alt.home.repair
Arclight
 
Posts: n/a
Default Weak Central Air problem

http://forum.doityourself.com/forumdisplay.php?f=126



"Lin0" wrote in message
ups.com...
everyone,

Have a problem of my A/C not cooling
my home down sufficiently:


Quote:
I would consider 30F condenser dT to be the upper limit on older low
SEER units, beyond which there is an airflow problem. On the newer
high SEER units, I would draw the line at 25F dT.


The lower limit would depend primarily upon load. I would think it
should be about 15F dT or above.


Here is the list of temps I use for online trouble shooting.


Low side:


Evap air in temp = 66°F
Evap air out temp = 48°F
SST (saturated suction temp) - Where is this measured and how?
Suction line temp near compressor = 35°F


High side: (I'll get these soon)


Cond air in temp -
Cond air out temp
SCT (saturated condensing temp)
Liquid line temp near condenser


------------------------------------------------------


description of my system:


2 Ton Copeland Hermetic Recipricating compressor (inside a 1987 seer 8
condenser)
1980 Tappan furnace
1953 brick ranch style house, with insulated attic and insulated
basement, about 1100 sq ft


Performed a test yesterday with monitoring temperatures becuase it was
very calm and stable outdoor air temps today


Outdoor air temp was 81 from 1pm to 5pm
Inside air temp started at 76.8°F @1pm
inside air temp ended at 75.2°F @5pm
ATTIC AIR TEMP was over 103°F during all the hours
Every half hour the main floor temp only dropped about .18°F during
these hours.
Humidity on main floor was 42% at 1pm, and dropped to 38% by 5pm


What would you guys call a low seer unit?


couple more things: the temps that are listed in the quoted text are
from my current setup, I just inserted them thats all. I replaced the
furnace blower motor. The compressor is new (few days)
Basement temp is very close to main floor temp (couple degrees
difference(which I think rules out any bad ducting leaks))
AND when the return air is 72°F, the output air from any room vent is
57°F


Are these okay temps? I want my house temps to fall at little higher
rate when the system runs. Like for example, it never shut off in those

5 hours as my target temp was 72°F !!!


~Will


  #4   Report Post  
Posted to alt.home.repair
Lin0
 
Posts: n/a
Default Weak Central Air problem

Heres the info you requested:
14 windows Anderson Thermopane with Storm windows currently installed.
Great condition.

The basement is finished and I added that into the 1100 sq footage, its
got two additional ducts to heat and cool it, both are under 2 feet in
total length and are shut for the summer.

The condition started when we had some brownouts back in 1995 and we're
just now making the repair on the unit to run again. (weak compressor
due to brownout) We've been just using an attic fan in the summer for
the last 10 years.

Attic is insulated R19

Any tips on finding losses? I went and bought a no-contact temp gun
last night.

Thanks so much!
dpb wrote:
Lin0 wrote:
everyone,

Have a problem of my A/C not cooling
my home down sufficiently:

...
Outdoor air temp was 81 from 1pm to 5pm
Inside air temp started at 76.8°F @1pm
inside air temp ended at 75.2°F @5pm
ATTIC AIR TEMP was over 103°F during all the hours
Every half hour the main floor temp only dropped about .18°F during
these hours.
Humidity on main floor was 42% at 1pm, and dropped to 38% by 5pm
...AND when the return air is 72°F, the output air from any room ventis
57°F


.... I want my house temps to fall at little higher
rate when the system runs. Like for example, it never shut off in those
5 hours as my target temp was 72°F !!!


Basically, what this tells me is that your heat load is too great for
the capacity of the unit. More attic insulation might help some plus
adding some (more) ventilation or even a power exhaust.

Is the basement finished living space and is it ducted or is it just a
basement?

You don't mention how many windows/doors, etc., nor condition of them
nor presence/absence of thermopane and/or storm windows. Such losses
as that would be another place to consider.

Also, is this an ongoing existing condition or has something changed?
W/ the new compressor, I'm guessing the old unit died and was repaired?
Probably a better choice would have been a new system although unless
the house were brought closer to current-day standards of insulation
and leakage control (or has been _recently_), a 50s vintage house will
probably be very "lossy"...


  #5   Report Post  
Posted to alt.home.repair
Lin0
 
Posts: n/a
Default Weak Central Air problem

EDIT
My Temps dropped .4°F PER HOUR
sorry bout that
Lin0 wrote:
Heres the info you requested:
14 windows Anderson Thermopane with Storm windows currently installed.
Great condition.

The basement is finished and I added that into the 1100 sq footage, its
got two additional ducts to heat and cool it, both are under 2 feet in
total length and are shut for the summer.

The condition started when we had some brownouts back in 1995 and we're
just now making the repair on the unit to run again. (weak compressor
due to brownout) We've been just using an attic fan in the summer for
the last 10 years.

Attic is insulated R19

Any tips on finding losses? I went and bought a no-contact temp gun
last night.

Thanks so much!
dpb wrote:
Lin0 wrote:
everyone,

Have a problem of my A/C not cooling
my home down sufficiently:

...
Outdoor air temp was 81 from 1pm to 5pm
Inside air temp started at 76.8°F @1pm
inside air temp ended at 75.2°F @5pm
ATTIC AIR TEMP was over 103°F during all the hours
Every half hour the main floor temp only dropped about .4°F during
these hours.
Humidity on main floor was 42% at 1pm, and dropped to 38% by 5pm
...AND when the return air is 72°F, the output air from any room vent is
57°F


.... I want my house temps to fall at little higher
rate when the system runs. Like for example, it never shut off in those
5 hours as my target temp was 72°F !!!


Basically, what this tells me is that your heat load is too great for
the capacity of the unit. More attic insulation might help some plus
adding some (more) ventilation or even a power exhaust.

Is the basement finished living space and is it ducted or is it just a
basement?

You don't mention how many windows/doors, etc., nor condition of them
nor presence/absence of thermopane and/or storm windows. Such losses
as that would be another place to consider.

Also, is this an ongoing existing condition or has something changed?
W/ the new compressor, I'm guessing the old unit died and was repaired?
Probably a better choice would have been a new system although unless
the house were brought closer to current-day standards of insulation
and leakage control (or has been _recently_), a 50s vintage house will
probably be very "lossy"...




  #6   Report Post  
Posted to alt.home.repair
dpb
 
Posts: n/a
Default Weak Central Air problem


Lin0 wrote:
EDIT
My Temps dropped .4°F PER HOUR
sorry bout that

,,,

Actually, I overlooked that -- that's really not too bad.

As noted, w/ the air temperature at the duct outlets you have plenty
cool enough air so either you have to move more air or reduce the heat
load.

The thing I forgot to look for specifically and when I did look in your
description is the house construction. My guess is right-BRICK. Brick
houses are terribly difficult to cool once they're hot owing to the
high heat capacity of the brick--it just keeps on radiating into the
living space even after out of the direct sun. In that age of house
the amount of wall insulation is minimal at best and possibly might not
have been if it was a tract house. There's where I'd start looking and
of course, only a few air gaps can make a big difference. Plus, shade
to minimize the solar heating of the roof and brick veneer can make a
significant difference.

The other thing that can make a big difference in overall comfort is to
leave the fan on and use ceiling fans to keep some air movement.

  #7   Report Post  
Posted to alt.home.repair
Lin0
 
Posts: n/a
Default Weak Central Air problem

Cool take a look at these temps and see if the current insulation is
doing its job

Right now 1:31pm Flat Rock michigan = 84°F
My A/C is not on, and there are no fans bringing in outside air
79°F on main floor
104°F in attic
All outside walls ranging between 76° and 81°F
100% sunny and 1/4 of roof is in tree shade

I'll reply back sunday night as I am leaving to Lansing. Be back, and
thanks for everything! =)


dpb wrote:
Lin0 wrote:
EDIT
My Temps dropped .4°F PER HOUR
sorry bout that

,,,

Actually, I overlooked that -- that's really not too bad.

As noted, w/ the air temperature at the duct outlets you have plenty
cool enough air so either you have to move more air or reduce the heat
load.

The thing I forgot to look for specifically and when I did look in your
description is the house construction. My guess is right-BRICK. Brick
houses are terribly difficult to cool once they're hot owing to the
high heat capacity of the brick--it just keeps on radiating into the
living space even after out of the direct sun. In that age of house
the amount of wall insulation is minimal at best and possibly might not
have been if it was a tract house. There's where I'd start looking and
of course, only a few air gaps can make a big difference. Plus, shade
to minimize the solar heating of the roof and brick veneer can make a
significant difference.

The other thing that can make a big difference in overall comfort is to
leave the fan on and use ceiling fans to keep some air movement.


  #8   Report Post  
Posted to alt.home.repair
Stormin Mormon
 
Posts: n/a
Default Weak Central Air problem

I'd sure like to know the operating pressures. The suction line temp
helps to get the superheat. First two things come to mind, check the
airflow through the evaporator, and clean the condensor.

--

Christopher A. Young
You can't shout down a troll.
You have to starve them.
..

"Lin0" wrote in message
ups.com...
everyone,

Have a problem of my A/C not cooling
my home down sufficiently:


Quote:
I would consider 30F condenser dT to be the upper limit on older low
SEER units, beyond which there is an airflow problem. On the newer
high SEER units, I would draw the line at 25F dT.


The lower limit would depend primarily upon load. I would think it
should be about 15F dT or above.


Here is the list of temps I use for online trouble shooting.


Low side:


Evap air in temp = 66°F
Evap air out temp = 48°F
SST (saturated suction temp) - Where is this measured and how?
Suction line temp near compressor = 35°F


High side: (I'll get these soon)


Cond air in temp -
Cond air out temp
SCT (saturated condensing temp)
Liquid line temp near condenser


------------------------------------------------------


description of my system:


2 Ton Copeland Hermetic Recipricating compressor (inside a 1987 seer 8
condenser)
1980 Tappan furnace
1953 brick ranch style house, with insulated attic and insulated
basement, about 1100 sq ft


Performed a test yesterday with monitoring temperatures becuase it was
very calm and stable outdoor air temps today


Outdoor air temp was 81 from 1pm to 5pm
Inside air temp started at 76.8°F @1pm
inside air temp ended at 75.2°F @5pm
ATTIC AIR TEMP was over 103°F during all the hours
Every half hour the main floor temp only dropped about .18°F during
these hours.
Humidity on main floor was 42% at 1pm, and dropped to 38% by 5pm


What would you guys call a low seer unit?


couple more things: the temps that are listed in the quoted text are
from my current setup, I just inserted them thats all. I replaced the
furnace blower motor. The compressor is new (few days)
Basement temp is very close to main floor temp (couple degrees
difference(which I think rules out any bad ducting leaks))
AND when the return air is 72°F, the output air from any room vent is
57°F


Are these okay temps? I want my house temps to fall at little higher
rate when the system runs. Like for example, it never shut off in
those

5 hours as my target temp was 72°F !!!


~Will


  #9   Report Post  
Posted to alt.home.repair
dpb
 
Posts: n/a
Default Weak Central Air problem


Lin0 wrote:
Cool take a look at these temps and see if the current insulation is
doing its job

Right now 1:31pm Flat Rock michigan = 84°F
My A/C is not on, and there are no fans bringing in outside air
79°F on main floor
104°F in attic


I'll bet you would see a noticeable change if you were to add more
attic ventilation

All outside walls ranging between 76° and 81°F


How did you measure that? Surface temperature measurement is difficult
and not necessarily very accurate owing to whatever the surface
actually is.

But, what's more important is the difference between the inner and
outer temperatures which is nearly nothing at that point in time --
that indicates more likely that it simply hasn't warmed up that much
yet but _could_ also be saying there essentially isn't any thermal
barrier-- impossible to tell the difference from only one data point
even assuming the values are correct.

The only thing that makes think you would likely have at least some is
that you're in a northern cold-weather climate where I would _presume_
they routinely did insulate. But, not knowing anything about the
particular house, that's still simply supposition--a lot of tract
houses were built around that time in a real hurry and energy saving at
the time was _way_ down on the list of priorities.

  #10   Report Post  
Posted to alt.home.repair
Jeff
 
Posts: n/a
Default Weak Central Air problem

For a point of reference. My AC drops the inside air from 80 to 60 (outside
it was 84), there is a steady stream of water coming from the system. My
system works fine. Too high a delta T is inefficient, too low gives poor
dehumidification. Note the incoming Freon line (smaller line) is barely
warm to the touch. If your system is not similar to this something is
amiss. If it is then it may be too small for your home.

"Lin0" wrote in message
ups.com...
everyone,

Have a problem of my A/C not cooling
my home down sufficiently:


Quote:
I would consider 30F condenser dT to be the upper limit on older low
SEER units, beyond which there is an airflow problem. On the newer
high SEER units, I would draw the line at 25F dT.


The lower limit would depend primarily upon load. I would think it
should be about 15F dT or above.


Here is the list of temps I use for online trouble shooting.


Low side:


Evap air in temp = 66°F
Evap air out temp = 48°F
SST (saturated suction temp) - Where is this measured and how?
Suction line temp near compressor = 35°F


High side: (I'll get these soon)


Cond air in temp -
Cond air out temp
SCT (saturated condensing temp)
Liquid line temp near condenser


------------------------------------------------------


description of my system:


2 Ton Copeland Hermetic Recipricating compressor (inside a 1987 seer 8
condenser)
1980 Tappan furnace
1953 brick ranch style house, with insulated attic and insulated
basement, about 1100 sq ft


Performed a test yesterday with monitoring temperatures becuase it was
very calm and stable outdoor air temps today


Outdoor air temp was 81 from 1pm to 5pm
Inside air temp started at 76.8°F @1pm
inside air temp ended at 75.2°F @5pm
ATTIC AIR TEMP was over 103°F during all the hours
Every half hour the main floor temp only dropped about .18°F during
these hours.
Humidity on main floor was 42% at 1pm, and dropped to 38% by 5pm


What would you guys call a low seer unit?


couple more things: the temps that are listed in the quoted text are
from my current setup, I just inserted them thats all. I replaced the
furnace blower motor. The compressor is new (few days)
Basement temp is very close to main floor temp (couple degrees
difference(which I think rules out any bad ducting leaks))
AND when the return air is 72°F, the output air from any room vent is
57°F


Are these okay temps? I want my house temps to fall at little higher
rate when the system runs. Like for example, it never shut off in those

5 hours as my target temp was 72°F !!!


~Will




  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3
Default Weak Central Air problem

Jeff,

My incoming is barely warm to the touch.

And at 40% humidity, my system does not "stream" water out of it, more
like a rapid drip.
thank you very much for the thoughts! =)
Jeff wrote:
For a point of reference. My AC drops the inside air from 80 to 60 (outside
it was 84), there is a steady stream of water coming from the system. My
system works fine. Too high a delta T is inefficient, too low gives poor
dehumidification. Note the incoming Freon line (smaller line) is barely
warm to the touch. If your system is not similar to this something is
amiss. If it is then it may be too small for your home.


  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3
Default Weak Central Air problem

I'll get them readings tommorow, it rained and was cloudy all day here.
Lin0 wrote:
dpb,

I bet I would also BUT I want a floor up there sitting ontop the
rafters. So what I will do is look for a high R value insulation that
is the thickness of the rafters up there. If anyone has any
suggestions, I'td be much appreciated.

I measured all the INSIDE walls on the outside of all the rooms with a
laser temp gun/no contact gun. I also shot the roof and on the
northwest roof it was 85 - 90° and shaded by a tree
on the southeast roof it was 120°F throughout

I'll take some readings of the inner and outer temps tommorow around
1pm, thanks for the great suggestion!


Lin0 wrote:
Cool take a look at these temps and see if the current insulation is
doing its job

Right now 1:31pm Flat Rock michigan = 84°F
My A/C is not on, and there are no fans bringing in outside air
79°F on main floor
104°F in attic


I'll bet you would see a noticeable change if you were to add more
attic ventilation

All outside walls ranging between 76° and 81°F


How did you measure that? Surface temperature measurement is difficult
and not necessarily very accurate owing to whatever the surface
actually is.

But, what's more important is the difference between the inner and
outer temperatures which is nearly nothing at that point in time --
that indicates more likely that it simply hasn't warmed up that much
yet but _could_ also be saying there essentially isn't any thermal
barrier-- impossible to tell the difference from only one data point
even assuming the values are correct.

The only thing that makes think you would likely have at least some is
that you're in a northern cold-weather climate where I would _presume_
they routinely did insulate. But, not knowing anything about the
particular house, that's still simply supposition--a lot of tract
houses were built around that time in a real hurry and energy saving at
the time was _way_ down on the list of priorities.


  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3
Default Weak Central Air problem

Nevermind about them readings now. I pulled my A-Coil and cleaned it.
The difference?

Before the cleaning, the system dropped the house temp at a maximum
..4°F an hour.
Afterward, it dropped at 1.65°F an hour minimum. In the room that
counts the most (my room) it was able to do 2.1°F an hour!

I used a fine wired brush to get the crap off the bottom of the coil.
I used my air compressor to blow out the fragments. And I finished up
with Frost King Coil Cleaner, from Lowes. So yes, fiberglass filters
friggin suck. I'd rather use a higher Merv filter and save the time
and headache from pulling that A-Coil out and cleaning it every 6
years.
The filter I am switching to is Merv 7, washable filter. That way I'll
just clean it every month, and save the money and waste.

A large thanks to everyone whom made suggestions and took part in my
thread.

Lin0 wrote:
I'll get them readings tommorow, it rained and was cloudy all day here.
Lin0 wrote:
dpb,

I bet I would also BUT I want a floor up there sitting ontop the
rafters. So what I will do is look for a high R value insulation that
is the thickness of the rafters up there. If anyone has any
suggestions, I'td be much appreciated.

I measured all the INSIDE walls on the outside of all the rooms with a
laser temp gun/no contact gun. I also shot the roof and on the
northwest roof it was 85 - 90° and shaded by a tree
on the southeast roof it was 120°F throughout

I'll take some readings of the inner and outer temps tommorow around
1pm, thanks for the great suggestion!


Lin0 wrote:
Cool take a look at these temps and see if the current insulation is
doing its job

Right now 1:31pm Flat Rock michigan = 84°F
My A/C is not on, and there are no fans bringing in outside air
79°F on main floor
104°F in attic

I'll bet you would see a noticeable change if you were to add more
attic ventilation

All outside walls ranging between 76° and 81°F

How did you measure that? Surface temperature measurement is difficult
and not necessarily very accurate owing to whatever the surface
actually is.

But, what's more important is the difference between the inner and
outer temperatures which is nearly nothing at that point in time --
that indicates more likely that it simply hasn't warmed up that much
yet but _could_ also be saying there essentially isn't any thermal
barrier-- impossible to tell the difference from only one data point
even assuming the values are correct.

The only thing that makes think you would likely have at least some is
that you're in a northern cold-weather climate where I would _presume_
they routinely did insulate. But, not knowing anything about the
particular house, that's still simply supposition--a lot of tract
houses were built around that time in a real hurry and energy saving at
the time was _way_ down on the list of priorities.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Central heating problem asante UK diy 2 October 5th 05 11:46 AM
Central Heating Problem AJJ UK diy 6 September 20th 05 05:54 PM
Central A/C Problem : Blower [email protected] Home Repair 11 September 10th 05 03:22 AM
strange central heating problem... (to me anyway) Tony Commander UK diy 10 March 24th 04 12:08 PM
Central Heating - Serious Air Ingress Problem hodihouk UK diy 2 October 10th 03 01:05 PM


All times are GMT +1. The time now is 06:43 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"