Unisaw Switch Issue
Our delema: Changed a 3 phase motor to a 4 hp single phase. Bought a
standard Unisaw switch for single phase, 220 volts. We either have something wired wrong or the 4 hp motor requires a different switch. Too late to call out an electrician for help. Do 4 hp motors require a different switch? And/or does a 4 hp motor require a different breaker. We have a 20 amp breaker. Otherwise, I think we wired the switch wrong. There is no LVC box on this saw. The wiring from breaker to socket seems to be ok. When we plug the saw into the socket, the breaker trips. The motor came wired, but not to the switch, since there was no switch. Any comments are welcome. Sonny |
#2
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
On 5/18/2012 5:09 PM, Sonny wrote:
Our delema: Changed a 3 phase motor to a 4 hp single phase. Bought a standard Unisaw switch for single phase, 220 volts. We either have something wired wrong or the 4 hp motor requires a different switch. Too late to call out an electrician for help. Do 4 hp motors require a different switch? And/or does a 4 hp motor require a different breaker. We have a 20 amp breaker. Otherwise, I think we wired the switch wrong. There is no LVC box on this saw. The wiring from breaker to socket seems to be ok. When we plug the saw into the socket, the breaker trips. The motor came wired, but not to the switch, since there was no switch. Any comments are welcome. Sonny I think you will need a starter for a 4 HP motor. Perhaps an electrician will help out on this. If I recall, anything bigger than 1 /12- 2 HP needs a magnetic starter. Here is some information: http://www.emsco.net/faq.htm http://www.southlandelectric.com/mot...hart_for_s.htm -- ___________________________________ Keep the whole world singing . . . Dan G remove the seven |
#3
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
On 5/18/2012 5:09 PM, Sonny wrote:
Our delema: Changed a 3 phase motor to a 4 hp single phase. Bought a standard Unisaw switch for single phase, 220 volts. We either have something wired wrong or the 4 hp motor requires a different switch. Too late to call out an electrician for help. Do 4 hp motors require a different switch? And/or does a 4 hp motor require a different breaker. We have a 20 amp breaker. Otherwise, I think we wired the switch wrong. There is no LVC box on this saw. The wiring from breaker to socket seems to be ok. When we plug the saw into the socket, the breaker trips. The motor came wired, but not to the switch, since there was no switch. Any comments are welcome. See if this helps: http://media.ptg-online.com/media/dm...2-04-01-04.pdf -- www.eWoodShop.com Last update: 4/15/2010 KarlCaillouet@ (the obvious) http://gplus.to/eWoodShop |
#4
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
In article ,
Sonny wrote: Our delema: Changed a 3 phase motor to a 4 hp single phase. Bought a standard Unisaw switch for single phase, 220 volts. We either have something wired wrong or the 4 hp motor requires a different switch. Too late to call out an electrician for help. Do 4 hp motors require a different switch? And/or does a 4 hp motor require a different breaker. We have a 20 amp breaker. Otherwise, I think we wired the switch wrong. There is no LVC box on this saw. The wiring from breaker to socket seems to be ok. When we plug the saw into the socket, the breaker trips. The motor came wired, but not to the switch, since there was no switch. Any comments are welcome. If the breaker trips *immediately* when you plug the saw in, with the saw switched _off_, you obviously have something wired VERY WRONG. A 4hp single-phase motor on a 20A 220v circuit is 'iffy', at best. The running power consumption is within the limits for a 'plug in' device on a 20A circuit, but 'start-up' power draw is -much- higher. A 30 A circuit, with 10 ga (minimum!!) wiring is recommended. FURTHER, check the power rating _on_the_switch_. It should state the maximum number of amps, _and_ the max. horsepower rating of a motor, that it can be used to control. DO NOT EXCEED those ratings -- if you do, the device may NOT TURN OFF when you turn the switch 'off'. |
#5
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
Thanks Dan. We probably should put a LVC on it, to be safe. I had
always understood an LVC was required for commercial use, but a private saw didn't have to have one. I really don't know, though. I've never had this problem. I suspect this 4 ph mptor needs a larger breaker, like 40 amps. Leeson motor, Cat# 120998.00, model - C145K34FB16D. This model motor may be discontinued, as it is not listed on the Leeson website. There is a model C145K34FB16E, though (same Cat#)..... only difference is the last letter - D & E. We were hoping to get this thing fixed and running today/this weekend. We may have to wait until Monday, when electricians are available, for help. *Oh, no matter if the saw switch is turned on or off, with the saw plugged into the socket and then the breaker is turned on, it trips. Sonny |
#6
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
On May 18, 6:08*pm, (Robert Bonomi) wrote:
In article , Sonny wrote: Our delema: *Changed a 3 phase motor to a 4 hp single phase. *Bought a standard Unisaw switch for single phase, 220 volts. *We either have something wired wrong or the 4 hp motor requires a different switch. Too late to call out an electrician for help. Do 4 hp motors require a different switch? * And/or does a 4 hp motor require a different breaker. *We have a 20 amp breaker. Otherwise, I think we wired the switch wrong. There is no LVC box on this saw. *The wiring from breaker to socket seems to be ok. *When we plug the saw into the socket, the breaker trips. *The motor came wired, but not to the switch, since there was no switch. Any comments are welcome. If the breaker trips *immediately* when you plug the saw in, with the saw switched _off_, you obviously have something wired VERY WRONG. A 4hp single-phase motor on a 20A 220v circuit is 'iffy', at best. The running power consumption is within the limits for a 'plug in' device on a 20A circuit, but 'start-up' power draw is -much- higher. A 30 A circuit, with 10 ga (minimum!!) wiring is recommended. FURTHER, check the power rating _on_the_switch_. *It should state the maximum number of amps, _and_ the max. horsepower rating of a motor, that it can be used to control. *DO NOT EXCEED those ratings -- if you do, the device may NOT TURN OFF when you turn the switch 'off'.- Hide quoted text - - Show quoted text - Okay, our problem may, in part, be some of these issues. We did read the switch load and compare it to the motor. It does appear the switch may be too weak. I'll double check that tomorrow. We did wire it with 12-2 wire, not 10 guage wire. We probably wired it incorrectly, anyway. I think we need to call in an expert. This is definitely not my or my friend's field. |
#7
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
On May 18, 6:07*pm, Swingman wrote:
On 5/18/2012 5:09 PM, Sonny wrote: Our delema: *Changed a 3 phase motor to a 4 hp single phase. *Bought a standard Unisaw switch for single phase, 220 volts. *We either have something wired wrong or the 4 hp motor requires a different switch. Too late to call out an electrician for help. Do 4 hp motors require a different switch? * And/or does a 4 hp motor require a different breaker. *We have a 20 amp breaker. Otherwise, I think we wired the switch wrong. There is no LVC box on this saw. *The wiring from breaker to socket seems to be ok. *When we plug the saw into the socket, the breaker trips. *The motor came wired, but not to the switch, since there was no switch. Any comments are welcome. See if this helps: http://media.ptg-online.com/media/dm...0331153155_En4... --www.eWoodShop.com Last update: 4/15/2010 KarlCaillouet@ (the obvious)http://gplus.to/eWoodShop- Hide quoted text - - Show quoted text - Thanks Karl. I glanced at that earlier. today. Those wiring diagrams were Greek to me. Too late, now, to mess with that, anyway. I've been invited to go eat and watch the baseball game. Sonny |
#8
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
Sonny wrote:
Thanks Dan. We probably should put a LVC on it, to be safe. I had always understood an LVC was required for commercial use, but a private saw didn't have to have one. I really don't know, though. I've never had this problem. What is this LVC you speak of? I suspect this 4 ph mptor needs a larger breaker, like 40 amps. No way. I have not done the math, but at first blush - 20A might be just fine. Certainly NOT 40A. Leeson motor, Cat# 120998.00, model - C145K34FB16D. This model motor may be discontinued, as it is not listed on the Leeson website. There is a model C145K34FB16E, though (same Cat#)..... only difference is the last letter - D & E. We were hoping to get this thing fixed and running today/this weekend. We may have to wait until Monday, when electricians are available, for help. *Oh, no matter if the saw switch is turned on or off, with the saw plugged into the socket and then the breaker is turned on, it trips. You have wired your switch/motor wrong. You should have two hots (black and red or black and white) and a ground going to the outlet. Look at the wiring diagram in the motor to see which terminals to hook to coming out of your switch. Your plug/wire should go to the switch, and both legs should hit the switch. Then, from the switch, on to the appropriate spades on the motor. If you are tripping the breaker as soon as you plug it in, your wiring to the switch is hosed. -- -Mike- |
#9
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
Robert Bonomi wrote:
A 4hp single-phase motor on a 20A 220v circuit is 'iffy', at best. I don't think so. It actually should be plenty of protection for a 4hp motor. The running power consumption is within the limits for a 'plug in' device on a 20A circuit, but 'start-up' power draw is -much- higher. Not as much higher as people think. Unloaders greatly reduce the startup power requirements. A 30 A circuit, with 10 ga (minimum!!) wiring is recommended. I believe that is overkill for a 4hp compressor. -- -Mike- |
#10
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
Sonny wrote:
Okay, our problem may, in part, be some of these issues. We did read the switch load and compare it to the motor. It does appear the switch may be too weak. I'll double check that tomorrow. We did wire it with 12-2 wire, not 10 guage wire. That may not be a problem for you Sonny. Again - I have not verified this, but I believe you are well within the capabilities of 12ga/20A. We probably wired it incorrectly, anyway. The fact that you trip the breaker immediately upon plugging it in, regardless of the switch position is an absolute assurance that you wired it wrong. That's where you have to focus. I think we need to call in an expert. This is definitely not my or my friend's field. It's really not rocket science, but if it doesn't make sense to you, then you're best to let someone else do the hook up for you. That way you simply get to enjoy the tool. -- -Mike- |
#11
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
On 5/18/2012 6:02 PM, Mike Marlow wrote:
Robert Bonomi wrote: A 4hp single-phase motor on a 20A 220v circuit is 'iffy', at best. I don't think so. It actually should be plenty of protection for a 4hp motor. The running power consumption is within the limits for a 'plug in' device on a 20A circuit, but 'start-up' power draw is -much- higher. Not as much higher as people think. Unloaders greatly reduce the startup power requirements. A 30 A circuit, with 10 ga (minimum!!) wiring is recommended. I believe that is overkill for a 4hp compressor. It depends on the supply and the run. If the supply to the breaker is "iffy" (too long and of inadequate size) and the distance from the saw to the receptacle is "long", even #10 ain't gonna solve the problem. (You probably know that but I thought I would make that clarification) ;-) Max |
#12
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
On 5/18/2012 6:25 PM, Sonny wrote:
On May 18, 6:07 pm, wrote: On 5/18/2012 5:09 PM, Sonny wrote: Our delema: Changed a 3 phase motor to a 4 hp single phase. Bought a standard Unisaw switch for single phase, 220 volts. We either have something wired wrong or the 4 hp motor requires a different switch. Too late to call out an electrician for help. Do 4 hp motors require a different switch? And/or does a 4 hp motor require a different breaker. We have a 20 amp breaker. Otherwise, I think we wired the switch wrong. There is no LVC box on this saw. The wiring from breaker to socket seems to be ok. When we plug the saw into the socket, the breaker trips. The motor came wired, but not to the switch, since there was no switch. Any comments are welcome. See if this helps: http://media.ptg-online.com/media/dm...0331153155_En4... --www.eWoodShop.com Last update: 4/15/2010 KarlCaillouet@ (the obvious)http://gplus.to/eWoodShop- Hide quoted text - - Show quoted text - Thanks Karl. I glanced at that earlier. today. Those wiring diagrams were Greek to me. Too late, now, to mess with that, anyway. I've been invited to go eat and watch the baseball game. LOL ... therein lies your problem. IME, magnetic switches require a good deal of head scratching understanding to install properly, and you normally must match the motor size to the switch. First check out that the switch indeed corresponds to motor size/horsepower ... Delta sells both a 3 HP and 6 HP Unisaw and, while I'd bet those switches are NOT interchangeable, you might want to DAGS that. I agree, as Robert has indicated, that you would do well to consider a 40A circuit/#10 wire for this motor, as I believe you will find that 20A will be marginal for the task, if not totally underpeckered. I do know that, without doubt, a 220v/40A circuit is a requirement for all 5 HP saws I've dealt with, and your close to that spec ... besides, it won't hurt to run your 4hp motor on that higher amperage circuit in any event. -- www.eWoodShop.com Last update: 4/15/2010 KarlCaillouet@ (the obvious) http://gplus.to/eWoodShop |
#13
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
On 5/18/2012 8:54 PM, Swingman wrote:
On 5/18/2012 6:25 PM, Sonny wrote: On May 18, 6:07 pm, wrote: On 5/18/2012 5:09 PM, Sonny wrote: Our delema: Changed a 3 phase motor to a 4 hp single phase. Bought a standard Unisaw switch for single phase, 220 volts. We either have something wired wrong or the 4 hp motor requires a different switch. Too late to call out an electrician for help. Do 4 hp motors require a different switch? And/or does a 4 hp motor require a different breaker. We have a 20 amp breaker. Otherwise, I think we wired the switch wrong. There is no LVC box on this saw. The wiring from breaker to socket seems to be ok. When we plug the saw into the socket, the breaker trips. The motor came wired, but not to the switch, since there was no switch. Any comments are welcome. See if this helps: http://media.ptg-online.com/media/dm...0331153155_En4... --www.eWoodShop.com Last update: 4/15/2010 KarlCaillouet@ (the obvious)http://gplus.to/eWoodShop- Hide quoted text - - Show quoted text - Thanks Karl. I glanced at that earlier. today. Those wiring diagrams were Greek to me. Too late, now, to mess with that, anyway. I've been invited to go eat and watch the baseball game. LOL ... therein lies your problem. IME, magnetic switches require a good deal of head scratching understanding to install properly, and you normally must match the motor size to the switch. First check out that the switch indeed corresponds to motor size/horsepower ... Delta sells both a 3 HP and 6 HP Unisaw Typo ... "5" HP, NOT 6. -- www.eWoodShop.com Last update: 4/15/2010 KarlCaillouet@ (the obvious) http://gplus.to/eWoodShop |
#14
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
Max wrote:
It depends on the supply and the run. If the supply to the breaker is "iffy" (too long and of inadequate size) and the distance from the saw to the receptacle is "long", even #10 ain't gonna solve the problem. (You probably know that but I thought I would make that clarification) ;-) Yeahbut - one can go to any length with the Iffy stuff. If the power company, if the, if the, if the. If the supply to the breaker is inadequate, then the wire run to the device is not an issue. As far as the run goes - you have to go a very long way to worry about that run. Granted - it is a consideration at some point, but that is brought up here way more than it really is a factor. -- -Mike- |
#15
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
Swingman wrote:
I agree, as Robert has indicated, that you would do well to consider a 40A circuit/#10 wire for this motor, as I believe you will find that 20A will be marginal for the task, if not totally underpeckered. #10 would be underpeckered for a 40A circuit as well. I do know that, without doubt, a 220v/40A circuit is a requirement for all 5 HP saws I've dealt with, and your close to that spec ... besides, it won't hurt to run your 4hp motor on that higher amperage circuit in any event. That would be a couple of times the current draw of that motor. Who spec'd that? 5HP doesn't come close to drawing 40A. -- -Mike- |
#16
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
This saw, recently purchased used, is in my friends shop. The
subpanel to the shop is fed by a 60 amp breaker from his house panel, 75' away. The run from the saw to the subpanel is 30', at most, and the saw's power cord is maybe 10' long. He impressed to me he knew some wiring and we both thought we could manage this switch wiring, but apparently not. I had guessed, as to what size breaker was needed for a 4 hp motor, interpolating from this link's chart, which doesn't have a breaker size listed for a 4 hp motor. http://www.groverelectric.com/howto/...c%20Motors.pdf This chart's figures may be a generalization and, apparently (?), an actual breaker size needed may be dependent on a variety of one's individual circumstances, also. I had tried Googling for help before asking here. At least we can speak to the electrician with a bit more knowledge, now, than before, too. I'll give an update when it's all figured out. Sonny |
#17
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
Sonny wrote in
: Okay, our problem may, in part, be some of these issues. We did read the switch load and compare it to the motor. It does appear the switch may be too weak. I'll double check that tomorrow. We did wire it with 12-2 wire, not 10 guage wire. We probably wired it incorrectly, anyway. I think we need to call in an expert. This is definitely not my or my friend's field. A friend of mine referred to calling in the professionals early as "keeping the repair bill small." If you're not sure, call in the expert early so he doesn't have to fix what you screwed up. Puckdropper -- Make it to fit, don't make it fit. |
#18
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
On Fri, 18 May 2012 16:16:47 -0700 (PDT), Sonny
wrote: Thanks Dan. We probably should put a LVC on it, to be safe. I had always understood an LVC was required for commercial use, but a private saw didn't have to have one. I really don't know, though. I've never had this problem. I suspect this 4 ph mptor needs a larger breaker, like 40 amps. Leeson motor, Cat# 120998.00, model - C145K34FB16D. This model motor may be discontinued, as it is not listed on the Leeson website. There is a model C145K34FB16E, though (same Cat#)..... only difference is the last letter - D & E. This particular Leeson is nameplated at 17.6A, but 4hp@230v gives a nominal 12.8A draw. You might need to go to a heavier breaker, but I doubt it. Then again, the engineering toolbox rule of thumb is 7 amps per horse at single-phase 230v. We were hoping to get this thing fixed and running today/this weekend. We may have to wait until Monday, when electricians are available, for help. *Oh, no matter if the saw switch is turned on or off, with the saw plugged into the socket and then the breaker is turned on, it trips. You have -definitely- wired it incorrectly, Sonny. With the switch off, it shouldn't EVER be able to blow the breaker. Did you ground the saw and motor, then wire the two 120v phase leads through the switch so -both- interrupt when it's off? It's a DPST (or DPDT) switch, right? Have you ohmed it out yet? That will show you where your trouble is if you understand a VOM and the circuit. -- The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore, all progress depends on the unreasonable man. -- George Bernard Shaw |
#19
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
You have -definitely- wired it incorrectly, Sonny. *With the switch off, it shouldn't EVER be able to blow the breaker. Yep, I am now sure we wired something wrong. But there may be something else amiss.... Did you ground the saw and motor, then wire the two 120v phase leads through the switch so -both- interrupt when it's off? *It's a DPST (or DPDT) switch, right? I didn't do the actual wiring, but Jonas was sure he had done so correctly. He did comment that the wires may be positioned to make the saw turn backwards, so that would be tested and reversed if need be. Also, he thought maybe he had wired the "on" button as actually "off", and 'off' to 'on', but said this shouldn't have made the breaker trip. Have you ohmed it out yet? *That will show you where your trouble is if you understand a VOM and the circuit. We have an ohm meter. I don't know how to operate an ohm meter, but Jonas seems to know. I don't know what all Jonas may have ohmed or why. I am confident in wiring a 220 outlet, but not a switch, as this. There may (unlikely?) be another reason for our problem. The motor (discontinued model, maybe?) was recently purchased via Amazon, so it is new. It came with a cord already wired into it, whether this cord would go directly to the switch or to an LVC box, first. Since there is no LVC box on the saw, Jonas ran this cord to the switch. If Jonas did wire the switch correctly, then this motor's cord may be (the unlikely aspect?) incorrectly wired inside the motor. He was confident his wiring of the power cord (from the switch to the plug/ outlet) was correct. I don't know if he tested all of this with the ohm meter.... at this stage of our unknowing, I was searching online trying to troubleshoot the issue. We may play with it again today. Yesterday, we spent most of the day working on the whole of the saw, so some fatigue, late in the day, may have played some role in whatever is screwed up. We may be a little more clear-headed today. I vote to have an electrician check it out, though. This has been a good learning experience for me. Sonny |
#20
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
On Sat, 19 May 2012 05:58:13 -0700 (PDT), Sonny
wrote: You have -definitely- wired it incorrectly, Sonny. *With the switch off, it shouldn't EVER be able to blow the breaker. Yep, I am now sure we wired something wrong. But there may be something else amiss.... Did you ground the saw and motor, then wire the two 120v phase leads through the switch so -both- interrupt when it's off? *It's a DPST (or DPDT) switch, right? I didn't do the actual wiring, but Jonas was sure he had done so correctly. He did comment that the wires may be positioned to make the saw turn backwards, so that would be tested and reversed if need be. Also, he thought maybe he had wired the "on" button as actually "off", and 'off' to 'on', but said this shouldn't have made the breaker trip. Are you certain it's a single-phase motor, not 3-phase? Have you ohmed it out yet? *That will show you where your trouble is if you understand a VOM and the circuit. We have an ohm meter. I don't know how to operate an ohm meter, but Jonas seems to know. I don't know what all Jonas may have ohmed or why. I am confident in wiring a 220 outlet, but not a switch, as this. If I didn't know how to use a VOM, I wouldn't feel comfortable wiring anything, be it switch, outlet, or motor. It's a very good time to learn how to read and use one, Sonny. It could save your life. There may (unlikely?) be another reason for our problem. The motor (discontinued model, maybe?) was recently purchased via Amazon, so it is new. It came with a cord already wired into it, whether this cord would go directly to the switch or to an LVC box, first. Since there is no LVC box on the saw, Jonas ran this cord to the switch. If Jonas did wire the switch correctly, then this motor's cord may be (the unlikely aspect?) incorrectly wired inside the motor. He was confident his wiring of the power cord (from the switch to the plug/ outlet) was correct. I don't know if he tested all of this with the ohm meter.... at this stage of our unknowing, I was searching online trying to troubleshoot the issue. He should have opened the little cover to see exactly how the motor was wired. I hope you find an electrician. The stuff you two are toying with can kill ya. We may play with it again today. Yesterday, we spent most of the day working on the whole of the saw, so some fatigue, late in the day, may have played some role in whatever is screwed up. We may be a little more clear-headed today. I vote to have an electrician check it out, though. Excellent idea. Dead shorts which blow 40A of breaker are dangerous. This has been a good learning experience for me. Good. Keep learning and stay very careful, please. -- The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore, all progress depends on the unreasonable man. -- George Bernard Shaw |
#21
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
In article ,
Mike Marlow wrote: Robert Bonomi wrote: A 4hp single-phase motor on a 20A 220v circuit is 'iffy', at best. I don't think so. It actually should be plenty of protection for a 4hp motor. And you don't know the NEC. grin The OP has since posted that the moter is plated at 17.6 A. For 'plug' items, you are limited, by NEC to 80% of the breaker capacity. 80% of 20A is 16A. 17.6 A definitely exceeds the 'legal' limit. The running power consumption is within the limits for a 'plug in' device on a 20A circuit, but 'start-up' power draw is -much- higher. Not as much higher as people think. Unloaders greatly reduce the startup power requirements. An 'unloader' on a _table_saw_?? *snort* I've measured transient start-up current draw of motors, under no load, at well over 2x the rated 'full load" draw. A 30 A circuit, with 10 ga (minimum!!) wiring is recommended. I believe that is overkill for a 4hp compressor. Your 'belief' doesn't change the reality of the situation. First off, we're not dealing with a compressor. Second, you admit you haven't done the math. You should have. Using 'real world' efficiency numbers, not 'theoretical' 100% efficiency conversions. For a 'plug in' device, the 'legal limit' on a 20 A circuit is 3-3.5 HP. Lastly, 12 ga _is_ sufficient for the load, BARELY. Running the saw as a 'plug in' device requires _more_ than a 20 A breaker, however -- because it has a 'plate' draw that is more than the allowable 80% of the breaker rating. The next larger standard breaker is a 30A one. Or you can pay through the nose for a 25 A one. Either way, you have to upgrade to 10 ga wiring though -- because 12 ga, in conduit, is not rated for even 25A. And the wiring must be of a size sufficient for the rated breaker ampacity. Now, if this was a 'permanently wired' device, you'd be 'legal' with 12 ga wiring on a 20 A breaker. BUT, the start-up draw would still be a potential issue. It depends tremendously on the 'small overload' characteristics of the breaker -- how quickly it trips at what level over rated ampacity. |
#22
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
On 5/18/2012 9:56 PM, Sonny wrote:
This saw, recently purchased used, is in my friends shop. The subpanel to the shop is fed by a 60 amp breaker from his house panel, 75' away. The run from the saw to the subpanel is 30', at most, and the saw's power cord is maybe 10' long. He impressed to me he knew some wiring and we both thought we could manage this switch wiring, but apparently not. I had guessed, as to what size breaker was needed for a 4 hp motor, interpolating from this link's chart, which doesn't have a breaker size listed for a 4 hp motor. http://www.groverelectric.com/howto/...c%20Motors.pdf This chart's figures may be a generalization and, apparently (?), an actual breaker size needed may be dependent on a variety of one's individual circumstances, also. I had tried Googling for help before asking here. At least we can speak to the electrician with a bit more knowledge, now, than before, too. I'll give an update when it's all figured out. Be careful because IME you're getting some bad information above on the two components for a motor circuit: the ampacity of the branch circuit, and wire size of that branch circuit. This is not a cut and dried situation when you take into account a motor with a starter and thermal overload protection on a branch circuit that will most likely be classed as "continuous duty" by any inspector that comes along, which an electrician, or anyone else doing the work, is going to have to take into account to size the circuit properly (and in many cases, I wouldn't even bet that a journeyman electrician is going to be up to speed on the many issues and requirements) In short, just be aware that motor calculations are very different than other types of loads ... you can't just look at the Amp on the motor nameplate and look it up in table to determine the correct branch circuit wiring, which is pretty obviously the basis of the advice you've received thus far on the issue. -- www.eWoodShop.com Last update: 4/15/2010 KarlCaillouet@ (the obvious) http://gplus.to/eWoodShop |
#23
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
As long as he has the wiring in the saw and wall to support 40A.
If not 40A won't trip before there is a serious problem. On 5/18/2012 9:54 PM, Swingman wrote: On 5/18/2012 6:25 PM, Sonny wrote: On May 18, 6:07 pm, wrote: On 5/18/2012 5:09 PM, Sonny wrote: Our delema: Changed a 3 phase motor to a 4 hp single phase. Bought a standard Unisaw switch for single phase, 220 volts. We either have something wired wrong or the 4 hp motor requires a different switch. Too late to call out an electrician for help. Do 4 hp motors require a different switch? And/or does a 4 hp motor require a different breaker. We have a 20 amp breaker. Otherwise, I think we wired the switch wrong. There is no LVC box on this saw. The wiring from breaker to socket seems to be ok. When we plug the saw into the socket, the breaker trips. The motor came wired, but not to the switch, since there was no switch. Any comments are welcome. See if this helps: http://media.ptg-online.com/media/dm...0331153155_En4... --www.eWoodShop.com Last update: 4/15/2010 KarlCaillouet@ (the obvious)http://gplus.to/eWoodShop- Hide quoted text - - Show quoted text - Thanks Karl. I glanced at that earlier. today. Those wiring diagrams were Greek to me. Too late, now, to mess with that, anyway. I've been invited to go eat and watch the baseball game. LOL ... therein lies your problem. IME, magnetic switches require a good deal of head scratching understanding to install properly, and you normally must match the motor size to the switch. First check out that the switch indeed corresponds to motor size/horsepower ... Delta sells both a 3 HP and 6 HP Unisaw and, while I'd bet those switches are NOT interchangeable, you might want to DAGS that. I agree, as Robert has indicated, that you would do well to consider a 40A circuit/#10 wire for this motor, as I believe you will find that 20A will be marginal for the task, if not totally underpeckered. I do know that, without doubt, a 220v/40A circuit is a requirement for all 5 HP saws I've dealt with, and your close to that spec ... besides, it won't hurt to run your 4hp motor on that higher amperage circuit in any event. |
#24
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
On 5/19/2012 9:37 AM, tiredofspam wrote:
As long as he has the wiring in the saw and wall to support 40A. If not 40A won't trip before there is a serious problem. A "serious problem" where"? _If_ pigs had wings - (for a dedicated motor circuit you will find that you can indeed run higher breaker sizes for a specified wire size ... the motor is considered to have its own thermal protection, so the c'bkr will be dealing with a 'short to ground' fault with be a very high current) Remember, the c'brk is there to protect the wiring, not the equipment. And, the motor used in a table saw generally has its own thermal protection, which guarantees any thermal overload protection from a c'bkr to be a moot point. On 5/18/2012 9:54 PM, Swingman wrote: I do know that, without doubt, a 220v/40A circuit is a requirement for all 5 HP saws I've dealt with, and your close to that spec ... besides, it won't hurt to run your 4hp motor on that higher amperage circuit in any event. If this was not what you're talking about, chalk it up to being another problem with top posting ... making it damned difficult to tell what you're taking exception to. -- www.eWoodShop.com Last update: 4/15/2010 KarlCaillouet@ (the obvious) http://gplus.to/eWoodShop |
#25
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
Robert Bonomi wrote:
In article , Mike Marlow wrote: Robert Bonomi wrote: A 4hp single-phase motor on a 20A 220v circuit is 'iffy', at best. I don't think so. It actually should be plenty of protection for a 4hp motor. And you don't know the NEC. grin The OP has since posted that the moter is plated at 17.6 A. For 'plug' items, you are limited, by NEC to 80% of the breaker capacity. 80% of 20A is 16A. 17.6 A definitely exceeds the 'legal' limit. The running power consumption is within the limits for a 'plug in' device on a 20A circuit, but 'start-up' power draw is -much- higher. Not as much higher as people think. Unloaders greatly reduce the startup power requirements. An 'unloader' on a _table_saw_?? *snort* I've measured transient start-up current draw of motors, under no load, at well over 2x the rated 'full load" draw. A 30 A circuit, with 10 ga (minimum!!) wiring is recommended. I believe that is overkill for a 4hp compressor. Your 'belief' doesn't change the reality of the situation. First off, we're not dealing with a compressor. Second, you admit you haven't done the math. You should have. Using 'real world' efficiency numbers, not 'theoretical' 100% efficiency conversions. For a 'plug in' device, the 'legal limit' on a 20 A circuit is 3-3.5 HP. Lastly, 12 ga _is_ sufficient for the load, BARELY. Running the saw as a 'plug in' device requires _more_ than a 20 A breaker, however -- because it has a 'plate' draw that is more than the allowable 80% of the breaker rating. The next larger standard breaker is a 30A one. Or you can pay through the nose for a 25 A one. Either way, you have to upgrade to 10 ga wiring though -- because 12 ga, in conduit, is not rated for even 25A. And the wiring must be of a size sufficient for the rated breaker ampacity. Although there are additional considerations, the above is much more practical advice ... advice that actually reflects many of the realities of the issues involved. -- www.ewoodshop.com |
#26
Posted to rec.woodworking
|
|||
|
|||
Unisaw Switch Issue
Robert Bonomi wrote:
In article , Mike Marlow wrote: Robert Bonomi wrote: A 4hp single-phase motor on a 20A 220v circuit is 'iffy', at best. I don't think so. It actually should be plenty of protection for a 4hp motor. And you don't know the NEC. grin The OP has since posted that the moter is plated at 17.6 A. For 'plug' items, you are limited, by NEC to 80% of the breaker capacity. 80% of 20A is 16A. 17.6 A definitely exceeds the 'legal' limit. Yes it does. I'm glad I did not omit that part that said I had not done the math. Knee jerk on my behalf was that 4hp would be covered by a 20 amp breaker. It's not so far away - though admitedly, it is over the spec for a 20 plug device. At the time I replied, I don't believe that Sonny had posted the plate information. Kind of hard to act on that information if it's not made available. If he had posted it at or before the time I replied - then I missed that. An 'unloader' on a _table_saw_?? *snort* Caught dead to rights. I have no freakin' idea how I got compressors in my mind. I'd blame it on drinking, but I can't... -- -Mike- |