Default 220 V wiring question

I recently inherited my dad's Delta/Rockwell Unisaw with a 220V
motor. The saw is a dream to use compared to my old Craftsman.

Luckily my shop is wired for 220 but I have a wiring question...

The wall plug is a 4 blade and the saw has a 3 blade plug so I need a
new plug for the saw. I was going to just buy a new 4 blade male plug
and replace the existing 3 blade on the saw.

So do I wire the ground/common from the saw to the ground or to the
common on the plug? I can't seem to figure out which is appropriate.

Or should I just buy a length of 12/3 and use all 4 lugs? Does it
matter? I assume if I did that all I would need to do is screw the
ground to the saw frame somewhere... right?

  #2   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 10,043
Default 220 V wiring question


"LA" wrote in message

I recently inherited my dad's Delta/Rockwell Unisaw with a 220V
motor. The saw is a dream to use compared to my old Craftsman.

Luckily my shop is wired for 220 but I have a wiring question...

The wall plug is a 4 blade and the saw has a 3 blade plug so I need a
new plug for the saw. I was going to just buy a new 4 blade male plug
and replace the existing 3 blade on the saw.

So do I wire the ground/common from the saw to the ground or to the
common on the plug? I can't seem to figure out which is appropriate.

Or should I just buy a length of 12/3 and use all 4 lugs? Does it
matter? I assume if I did that all I would need to do is screw the
ground to the saw frame somewhere... right?


If it's wired correctly, in your four plug wall receptacle there should be
two hot leads, a ground, and a common (white) for a total of four. The
latter (white) is used with one of the hot leads to supply 120v to appliance
lights, timers, etc.

All you need to wire the saw correctly is the two hot leads and a ground.

If it were mine, I would change the wall plug to an appropriate female
receptacle, wired as last above, for your saw's male plug, and cap off the
common (white) with a wire nut and some electrician's tape, just in case
you/next owner ever wants to plug a dryer/appliance back in.

--
www.e-woodshop.net
Last update: 6/21/06


  #3   Report Post  
Posted to rec.woodworking
LA LA is offline
external usenet poster
 
Posts: 7
Default 220 V wiring question


Thanks Swingman!

  #4   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 59
Default 220 V wiring question

The wall plug is a 4 blade and the saw has a 3 blade plug so I need a
new plug for the saw. I was going to just buy a new 4 blade male plug
and replace the existing 3 blade on the saw.

So do I wire the ground/common from the saw to the ground or to the
common on the plug? I can't seem to figure out which is appropriate.

Or should I just buy a length of 12/3 and use all 4 lugs? Does it
matter? I assume if I did that all I would need to do is screw the
ground to the saw frame somewhere... right?


No.

The saw needs two hots (of opposite phase) and a ground to function. It does
not want or need neutral. The 4-prong plug will work fine. From the saw,
connect hot, hot and ground to the appropriate prongs. Do not connect
anything to the neutral prong. Its that simple.

Regards,

Steve


  #5   Report Post  
Posted to rec.woodworking
LA LA is offline
external usenet poster
 
Posts: 7
Default 220 V wiring question


Thanks Steve. That IS simple!



  #6   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 2,377
Default 220 V wiring question

"LA" writes:
I recently inherited my dad's Delta/Rockwell Unisaw with a 220V
motor. The saw is a dream to use compared to my old Craftsman.

Luckily my shop is wired for 220 but I have a wiring question...

The wall plug is a 4 blade and the saw has a 3 blade plug so I need a
new plug for the saw. I was going to just buy a new 4 blade male plug
and replace the existing 3 blade on the saw.

So do I wire the ground/common from the saw to the ground or to the
common on the plug? I can't seem to figure out which is appropriate.

Or should I just buy a length of 12/3 and use all 4 lugs? Does it
matter? I assume if I did that all I would need to do is screw the
ground to the saw frame somewhere... right?


First, before you make any changes, check the rating of the wiring
to your 240V receptacle and check the rating of the fuse or circuit
breaker protecting the wiring. The rating of the circuit breaker
and wiring determines the receptacle used. If the circuit is not
rated for 20 Amperes or is rated for more than 20 Amperes, then
you'll be best served by having an electrician do what is necessary
to get you a 240V 20A circuit.

Note that running your saw on a 50A dryer or range circuit is
very dangerous, as the saw internal wiring, cord wiring and motor
are not able to handle the large overcurrents that the 50A
circuit is capable of providing.

If the circuit is a 20A 240V circuit and the wiring is
at least 12AWG, replace the wall receptacle with
the correct NEMA fitting to match the plug on the saw.

What you have on the saw is either a NEMA 6-15P or 6-20P. What
you have on the wall is probably a NEMA 14-30R (or 14-50R).

Replace the NEMA 14-[53]0R on the wall with a NEMA 6-20R (which
will accomodate either a NEMA 6-15P or 6-20P plug). When you
replace the receptacle, clip the stripped end of the grounded
(neutral/white) conductor, tape it off and stuff it back in the
box; the NEMA 6-20R receptacle needs only the two current
carrying conductors(typ. black & red) and the grounding
(bare/green) conductor.

There is no point in running the grounded (aka neutral) conductor
from the receptacle to the saw.

For NEMA patterns: http://www.leviton.com/sections/techsupp/nema.htm

scott
  #7   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 38
Default 220 V wiring question

"Scott Lurndal" wrote in message
. ..
"LA" writes:
snip


Note that running your saw on a 50A dryer or range circuit is
very dangerous, as the saw internal wiring, cord wiring and motor
are not able to handle the large overcurrents that the 50A
circuit is capable of providing.



This statement makes no sense to me. I can run my 3.5A drill just fine on a
15A 120V circuit. I can run a 100W light (0.8A?) just fine on the same 120V
circuit. Heck, I can run a 6W (0.05A) light off a 120V 20A circuit, if I
like. None of these are considered dangerous.

I'm not an electrician and I don't play one on TV, but my understanding is
that the circuit breakers are designed to protect the circuit and plug, not
the devices plugged into them. The motors typically have a thermal overload
protector that switches them off if they over-heat or draw too much power.
If the manufacturer is really concerned about that, they can provide a fuse
on the device to protect it.

Clint


  #8   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 2,377
Default 220 V wiring question

"Clint" writes:
"Scott Lurndal" wrote in message
...
"LA" writes:
snip


Note that running your saw on a 50A dryer or range circuit is
very dangerous, as the saw internal wiring, cord wiring and motor
are not able to handle the large overcurrents that the 50A
circuit is capable of providing.



This statement makes no sense to me. I can run my 3.5A drill just fine on a
15A 120V circuit. I can run a 100W light (0.8A?) just fine on the same 120V
circuit. Heck, I can run a 6W (0.05A) light off a 120V 20A circuit, if I
like. None of these are considered dangerous.

I'm not an electrician and I don't play one on TV, but my understanding is
that the circuit breakers are designed to protect the circuit and plug, not


Circuit breakers are designed to protect, first and foremost, the wiring
from the circuit breaker to the protected device. The code makes exceptions
for 20A circuits, as UL-listed small-appliance wiring is rated sufficiently
to handle the transient overcurrent conditions on 20A circuits.

However, once the circuit breaker is rated higher than 20A, the code requires
that everything downstream of the breaker (wiring, switches and motors) to be
rated for minimum current matching the breaker.

Feeding 50A through #12AWG wiring is a recipe for disaster. Just because your
saw doesn't pull 50A normally, doesn't mean that it won't pull that during
a blade stall, for example. Melted wiring smells bad and causes other
inconvenient events, like fires.

the devices plugged into them. The motors typically have a thermal overload
protector that switches them off if they over-heat or draw too much power.


While the motor _may_ have thermal overload protection, and if you have an
industrial motor controller, it also has thermal protection, the O.P. was
planning on plugging his saw into the recept. That means #12 awg in the
path between the overcurrent protection device (the circuit breaker) and the
motor/motor-controller. That's your weak spot, and one of the areas
the code is intending to protect.

If the manufacturer is really concerned about that, they can provide a fuse
on the device to protect it.


Please read and understand the code. The manufacturer has no control over
the wiring between the circuit breaker and his device.

scott
  #9   Report Post  
Posted to rec.woodworking
 
Posts: n/a
Default 220 V wiring question

NEC stops at the socket for devices that plug in. Put a plug to match
the exisiting socket on your saw and you'll be fine.
--

Larry Wasserman Baltimore, Maryland


  #10   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 172
Default 220 V wiring question

Scott Lurndal wrote:

"Clint" writes:
"Scott Lurndal" wrote in message
t...
"LA" writes:
snip


Note that running your saw on a 50A dryer or range circuit is
very dangerous, as the saw internal wiring, cord wiring and motor
are not able to handle the large overcurrents that the 50A
circuit is capable of providing.



This statement makes no sense to me. I can run my 3.5A drill just fine on
a
15A 120V circuit. I can run a 100W light (0.8A?) just fine on the same
120V
circuit. Heck, I can run a 6W (0.05A) light off a 120V 20A circuit, if I
like. None of these are considered dangerous.

I'm not an electrician and I don't play one on TV, but my understanding is
that the circuit breakers are designed to protect the circuit and plug,
not


Circuit breakers are designed to protect, first and foremost, the wiring
from the circuit breaker to the protected device. The code makes
exceptions for 20A circuits, as UL-listed small-appliance wiring is rated
sufficiently to handle the transient overcurrent conditions on 20A
circuits.

However, once the circuit breaker is rated higher than 20A, the code
requires that everything downstream of the breaker (wiring, switches and
motors) to be rated for minimum current matching the breaker.


The code does not address anything that happens from the plug plugged into
the outlet on out. You're confusing requirements for permanently installed
equipment with requirements for stuff that is plugged into the wall.

Feeding 50A through #12AWG wiring is a recipe for disaster. Just because
your saw doesn't pull 50A normally, doesn't mean that it won't pull that
during
a blade stall, for example. Melted wiring smells bad and causes other
inconvenient events, like fires.


If your saw doesn't have overcurrent protection then your saw is a piece of
****.

the devices plugged into them. The motors typically have a thermal
overload protector that switches them off if they over-heat or draw too
much power.


While the motor _may_ have thermal overload protection, and if you have an
industrial motor controller, it also has thermal protection, the O.P. was
planning on plugging his saw into the recept.


Please identify a UL listed saw that does not.

That means #12 awg in the
path between the overcurrent protection device (the circuit breaker) and
the
motor/motor-controller. That's your weak spot, and one of the areas
the code is intending to protect.


The code doesn't protect anything with a plug on it.

If the manufacturer is really concerned about that, they can provide a
fuse on the device to protect it.


Please read and understand the code. The manufacturer has no control over
the wiring between the circuit breaker and his device.


And the electrician has no control over what gets plugged into the wall.


--
--John
to email, dial "usenet" and validate
(was jclarke at eye bee em dot net)


  #11   Report Post  
Posted to rec.woodworking
zap zap is offline
external usenet poster
 
Posts: 28
Default 220 V wiring question

Oh My My, I hear some truth here, and I hear some weird ideas here.

I am not an expert by any means, but having worked with electrical power
and electrical circuits all my life, Up through 00000 gage wiring and
copper bus bars, 100,000 amp motor generators, and 10,000 amp switches,
and having rewound some motors, and rewiring several houses, I think
that with close to 70 years of experience, that I am entitled to voice
what I know to be true.

1. You will NOT melt the insulation from off of the wires by drawing
more current through a wire than it can handle if it is fused (read that
circuit breaker) correctly, for the fuse will open the circuit before
any damage is done. The wire will not even heat up. And that is what the
standards are for.

2. If a motor locks up for any reason, it will draw full current through
it, even more current than when it starts, thus burning up the windings
in seconds if the fuse does not open right away, or your thermal switch
on the motor does not open. the reason - - When you first turn on the
switch to the motor (the equipment type does not matter)there is applied
across the windings the full electrical voltage and the resulting draw
of current.(virtually a short circuit) But on this application, the
motor starts to turn, and this results in a back voltage (reverse
voltage) being created by the windings and turning armature, which then
limits and reduces the apparent voltage across the windings to only one
to two volts, which is what limits the current through the motor. This
is what the windings of every motor is designed for. Under normal use,
the actual voltage across the windings will remain in that one to two
volt range throughout its normal usage, with its resulting current draw.
It does not matter that you have 120 V. coming from the wall socket. (or
220, or 440 if designed for it)

3. It does not matter how much current or wattage a circuit is capable
of providing, You will draw from that circuit only what the unit you are
operating is designed to use, It is like you holding a water glass under
the surface of a lake, it does not matter how much water the lake is
capable of providing, you still will only get one glass full. . You
cannot hurt it by running off of a Dryer, or electric range line
assuming you are needing 220 volts.


Zap



J. Clarke wrote:
Scott Lurndal wrote:


"Clint" writes:

"Scott Lurndal" wrote in message
et...

"LA" writes:

snip

Note that running your saw on a 50A dryer or range circuit is
very dangerous, as the saw internal wiring, cord wiring and motor
are not able to handle the large overcurrents that the 50A
circuit is capable of providing.



This statement makes no sense to me. I can run my 3.5A drill just fine on
a
15A 120V circuit. I can run a 100W light (0.8A?) just fine on the same
120V
circuit. Heck, I can run a 6W (0.05A) light off a 120V 20A circuit, if I
like. None of these are considered dangerous.

I'm not an electrician and I don't play one on TV, but my understanding is
that the circuit breakers are designed to protect the circuit and plug,
not


Circuit breakers are designed to protect, first and foremost, the wiring
from the circuit breaker to the protected device. The code makes
exceptions for 20A circuits, as UL-listed small-appliance wiring is rated
sufficiently to handle the transient overcurrent conditions on 20A
circuits.

However, once the circuit breaker is rated higher than 20A, the code
requires that everything downstream of the breaker (wiring, switches and
motors) to be rated for minimum current matching the breaker.



The code does not address anything that happens from the plug plugged into
the outlet on out. You're confusing requirements for permanently installed
equipment with requirements for stuff that is plugged into the wall.


Feeding 50A through #12AWG wiring is a recipe for disaster. Just because
your saw doesn't pull 50A normally, doesn't mean that it won't pull that
during
a blade stall, for example. Melted wiring smells bad and causes other
inconvenient events, like fires.



If your saw doesn't have overcurrent protection then your saw is a piece of
****.


the devices plugged into them. The motors typically have a thermal
overload protector that switches them off if they over-heat or draw too
much power.


While the motor _may_ have thermal overload protection, and if you have an
industrial motor controller, it also has thermal protection, the O.P. was
planning on plugging his saw into the recept.



Please identify a UL listed saw that does not.


That means #12 awg in the
path between the overcurrent protection device (the circuit breaker) and
the
motor/motor-controller. That's your weak spot, and one of the areas
the code is intending to protect.



The code doesn't protect anything with a plug on it.


If the manufacturer is really concerned about that, they can provide a
fuse on the device to protect it.


Please read and understand the code. The manufacturer has no control over
the wiring between the circuit breaker and his device.



And the electrician has no control over what gets plugged into the wall.


  #12   Report Post  
Posted to rec.woodworking
 
Posts: n/a
Default 220 V wiring question

In article ,
Scott Lurndal wrote:
"LA" writes:

...snipped...

First, before you make any changes, check the rating of the wiring
to your 240V receptacle and check the rating of the fuse or circuit
breaker protecting the wiring. The rating of the circuit breaker
and wiring determines the receptacle used. If the circuit is not
rated for 20 Amperes or is rated for more than 20 Amperes, then
you'll be best served by having an electrician do what is necessary
to get you a 240V 20A circuit.

Note that running your saw on a 50A dryer or range circuit is
very dangerous, as the saw internal wiring, cord wiring and motor
are not able to handle the large overcurrents that the 50A
circuit is capable of providing.

I'm impressed by the quoting of plug and socket types in your
your post, but the last sentence of the first paragraph, and the
whole second paragraph quoted above are just SO WRONG!


--

Larry Wasserman Baltimore, Maryland


  #13   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 403
Default 220 V wiring question

On 10 Jul 2006 10:56:25 -0700, "LA" wrote:

I recently inherited my dad's Delta/Rockwell Unisaw with a 220V
motor. The saw is a dream to use compared to my old Craftsman.

Luckily my shop is wired for 220 but I have a wiring question...

The wall plug is a 4 blade and the saw has a 3 blade plug so I need a
new plug for the saw. I was going to just buy a new 4 blade male plug
and replace the existing 3 blade on the saw.

So do I wire the ground/common from the saw to the ground or to the
common on the plug? I can't seem to figure out which is appropriate.

Or should I just buy a length of 12/3 and use all 4 lugs? Does it
matter? I assume if I did that all I would need to do is screw the
ground to the saw frame somewhere... right?


Not to put too fine a point on it, but your saw only *needs* the two
hots to run. True, there *ought* to be a ground, too, but that's a
safety issue (and a pretty significant one), not a requirement for the
motor to run.

If it were me, I'd get a length of 12 ga SJ cord (it has black, white,
and green wires--all you need) at the big box and make myself an
extension cord. Get an inline receptacle to match the plug on your saw
and put it on one end of the cord, wired hot-hot-ground, and get an
inline plug to match the receptacle on your wall and wire it
hot-hot-ground. Ignore the neutral connection on the plug.

The nice thing about the SJ is it's usually bright yellow, so as to
not readily disappear when/if underfoot.

Finally, what kind of plug is on the saw? If it's a molded (to the
cord) plug, with a (--.--) configuration (which is a 240V 15 A Nema
style), I'd leave it on. I consider the molded 240V cordsets to be
like gold, but that's only in terms of trying to replace one.

Lots of people like the twist locks (I have one on my feed from the
ceiling, but it's the first one I've had in 30 years), but they are
bulkier and more expensive than the equivalent to your plug.

If there's a different plug on the cord, either put whatever you want
on it or just select a matching receptacle when making up the
extension cord.

--
LRod

Master Woodbutcher and seasoned termite

Shamelessly whoring my website since 1999

http://www.woodbutcher.net

Proud participant of rec.woodworking since February, 1997

email addy de-spam-ified due to 1,000 spams per month.
If you can't figure out how to use it, I probably wouldn't
care to correspond with you anyway.
  #14   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 47
Default 220 V wiring question

LRod duckecho@gmail-dot-com wrote:
If it were me, I'd get a length of 12 ga SJ cord (it has black, white,
and green wires--all you need) at the big box and make myself an
extension cord. Get an inline receptacle to match the plug on your saw
and put it on one end of the cord, wired hot-hot-ground, and get an
inline plug to match the receptacle on your wall and wire it
hot-hot-ground. Ignore the neutral connection on the plug.


I've found it's usually cheaper (and easier) to just get an extension
cord with the right ends to match one side, and cut off the other end.
That leaves just one plug end to buy and wire up. Less work and less
money than building your own from scratch.
  #15   Report Post  
Posted to rec.woodworking
LA LA is offline
external usenet poster
 
Posts: 7
Default 220 V wiring question


Thanks all... I think you straightened me out and I know what to do
next.

I appreciate the help!



  #18   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 2,047
Default 220 V wiring question

LRod wrote:

Great idea for 120V. Where do you find 240V extension cords?


You don't care, all you want is the wire.

Buy the lowest cost, #10, 2Wire with ground, molded cord set you can find.

Whack of the female and wire that end to the saw.

If the male plug is not what you want, whack it off and wire the
correct one on to that end.

For a table saw, I like a 30A, locking plug, but that is my preference.

Problem solved, you'll be money ahead.

Lew
  #20   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 172
Default 220 V wiring question

Roy Smith wrote:

In article ,
LRod wrote:

On Mon, 10 Jul 2006 21:39:06 +0000 (UTC), (Roy Smith)
wrote:

LRod duckecho@gmail-dot-com wrote:
If it were me, I'd get a length of 12 ga SJ cord (it has black, white,
and green wires--all you need) at the big box and make myself an
extension cord. Get an inline receptacle to match the plug on your saw
and put it on one end of the cord, wired hot-hot-ground, and get an
inline plug to match the receptacle on your wall and wire it
hot-hot-ground. Ignore the neutral connection on the plug.

I've found it's usually cheaper (and easier) to just get an extension
cord with the right ends to match one side, and cut off the other end.
That leaves just one plug end to buy and wire up. Less work and less
money than building your own from scratch.


Great idea for 120V. Where do you find 240V extension cords?


Home Depot lists some (in the guise of 6' appliance pigtails) on their web
site. Other than that, I'd try a welding supply place or an appliance
store (especially one that sells lots of big air conditioners).

Google for "extension cord 6-20" and you'll find a few sources. Granted,
they're pretty rare compared to standard 120V cords.


Lowes usually has them in stock for use with generator sets.

--
--John
to email, dial "usenet" and validate
(was jclarke at eye bee em dot net)


  #21   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 311
Default 220 V wiring question


LRod writes:
Great idea for 120V. Where do you find 240V extension cords?


I make mine. It's just a wire with a plug on one end, and a socket on
the other. Any electrical supply house can get you all the parts you
need (all three of them .
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Circuit Breaker Wiring Question ? Robert11 Home Repair 3 August 7th 05 01:11 PM
Cooker element wiring question (and LPG deconversion as well) Diplomat APD5701 Martin P Matthews UK diy 1 August 1st 05 10:00 AM
Programmable Thermostat wiring question -rth7500 [email protected] Home Repair 5 January 2nd 05 08:04 PM
230V 15A wiring question. Dave Hammond Home Ownership 4 November 18th 04 06:44 AM
circuit wiring question twiedeman Home Repair 4 November 17th 03 01:14 PM


All times are GMT +1. The time now is 10:36 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"