yet another subpanel question
Greetings All!
I am in the process of wiring up a shed in the backyard for use as a workshop. I have a new SquareD load center panel (QO8-16L100S) that I want to use but need some clarification. 1. This particular panel only has one grounding/neutral bar, but I was under the impression the ground and neutral must be separated in a subpanel installed in a stand alone structure. Should I just buy a ground bar and install it in the panel and connect it to a new grounding rod? 2. The panel is rated for 100A, but I was hoping to use a 60A-75A breaker in the main box to feed this subpanel. Is this a problem? The subpanel does not have a main breaker in it. 3. The run from the main panel to the sub will only be about 15 ft. total. What size wire do you suggest I run? Thanks, Robb |
#2
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
Check here for guidance on the grounding:
http://www.ecmweb.com/mag/electric_g...g_5/index.html I recently called my local building inspector and found him to be very helpful and forthcoming without ever asking for my address. |
#3
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
1. This particular panel only has one grounding/neutral bar, but I was
under the impression the ground and neutral must be separated in a subpanel installed in a stand alone structure. Should I just buy a ground bar and install it in the panel and connect it to a new grounding rod? I'll defer to others on this one. The conduit should serve as a ground, but some placed might require a separate ground wire. 2. The panel is rated for 100A, but I was hoping to use a 60A-75A breaker in the main box to feed this subpanel. Is this a problem? The subpanel does not have a main breaker in it. I did exactly this. It's not a problem since the breaker protects the wire. 3. The run from the main panel to the sub will only be about 15 ft. total. What size wire do you suggest I run? Size it to match the breaker you put in the main panel. You'll need something like #8 or #6 for 60 amps. I can't remember what I used. It will be disasterous if you size it too small. brian |
#4
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
That is OK if you have less than 6 breakers in the sub.
Should have said 6 or less How does the number of breakers in the subpanel matter? brian |
#7
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
On 19 Apr 2006 09:38:44 -0700, brianlanning wrote:
That is OK if you have less than 6 breakers in the sub. Should have said 6 or less How does the number of breakers in the subpanel matter? NEC requires a main for more than 6 breakers. -- Art |
#8
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
brianlanning, or somebody so disguised, wrote the following at or about
4/19/2006 11:38 AM: That is OK if you have less than 6 breakers in the sub. Should have said 6 or less How does the number of breakers in the subpanel matter? Probably just to give you a margin of "safety" so you're not continually popping the main breaker. 60 Main and 6 or less 15a breakers. How likely is it that you'll have a 10a+ load on six of them at the same time? Low, I'd say. 60A Main and, say, 12 breakers (mixed bag of 15A and 20A) much more likely to pop the main. Not a safety issue, per se, more like a "this standard is engineered for the dumbest person." Think "I still have breakers and open outlets. How can I possibly overload this panel?" The financial corollary would be, "I can't be overdrawn! I still have checks in my checkbook!"g |
#9
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
Thank you for the detailed reply, Scott.
Scott Lurndal wrote: writes: Greetings All! I am in the process of wiring up a shed in the backyard for use as a workshop. I have a new SquareD load center panel (QO8-16L100S) that I want to use but need some clarification. 1. This particular panel only has one grounding/neutral bar, but I was under the impression the ground and neutral must be separated in a subpanel installed in a stand alone structure. Should I just buy a ground bar and install it in the panel and connect it to a new grounding rod? First, remove the bonding screw that bonds the grounded (neutral) busbar to the enclosure. Second, purchase an accessory busbar and fasten it to the enclosure as the grounding busbar. Third, bond the grounding busbar in the subpanel to the grounding busbar in the service entrance with the appropriate gauge green/bare conductor. You'll also want to bond the grounded busbar in the subpanel to the grounded busbar in the service entrance panel with suitably sized white conductor. I should also use the bonding screw for the grounding busbar, right? snip 3. The run from the main panel to the sub will only be about 15 ft. total. What size wire do you suggest I run? If you use a 60A breaker, #6 should be sufficient at that length. Check the NEC tables for definitive value based upon your conductor temperature rating. Are you using conduit and a thermoplastic insulated 90 degree-rated conductor such as THHN or #6/3 w/g jacketed (which IIRC are 60 degree-rated conductors)? I was planning on burying with PVC type conduit and running #6/3 w/g...assuming I can find that wire. Sounds good? Robb |
#11
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
No - you should run 4 - two hots, a neutral and a ground.
Because the cost difference isn't much, I'd recommend you go with #4 in case you ever want to upgrade from the 60A to 100A. Also, be sure to use large enough conduit (probably 2") so that you don't overfill. Lots of other good responses here. Lastly, do talk to your electrical inspector - not only is it the law (almost everywhere) but it means you'll have a safe install and you won't be on the line if your house burns down and it is traced back to your work! Our local inspector is very helpful and is happy to help DIY'ers. |
#12
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
stormy2084 wrote:
No - you should run 4 - two hots, a neutral and a ground. I think there is a choice here. He can run 4 wires as you say, keeping ground and neutral separate in the subpanel, or he can run 3 wires and put a grounding rod in at the outbuilding with a bonded ground bus in the subpanel. I don't remember if there is some minimum distance between buildings for that. As others have suggested, I'd talk to the local inspector to see what he/she expects. My local inspectors are generally very helpful if you talk to them in advance. Bill Ranck Blacksburg, Va. |
#13
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
stormy2084 wrote:
No - you should run 4 - two hots, a neutral and a ground. Because the cost difference isn't much, I'd recommend you go with #4 in case you ever want to upgrade from the 60A to 100A. Also, be sure to use large enough conduit (probably 2") so that you don't overfill. Lots of other good responses here. You're right, I should go with the bigger stuff. Is wire this large available at the "usual" places? Lastly, do talk to your electrical inspector - not only is it the law (almost everywhere) but it means you'll have a safe install and you won't be on the line if your house burns down and it is traced back to your work! Our local inspector is very helpful and is happy to help DIY'ers. How do you normally contact the local inspector? |
#14
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
I bought 01 at Home Depot when replacing my main panel some years ago. I
suspect they have everything in between. wrote in message oups.com... stormy2084 wrote: No - you should run 4 - two hots, a neutral and a ground. Because the cost difference isn't much, I'd recommend you go with #4 in case you ever want to upgrade from the 60A to 100A. Also, be sure to use large enough conduit (probably 2") so that you don't overfill. Lots of other good responses here. You're right, I should go with the bigger stuff. Is wire this large available at the "usual" places? Lastly, do talk to your electrical inspector - not only is it the law (almost everywhere) but it means you'll have a safe install and you won't be on the line if your house burns down and it is traced back to your work! Our local inspector is very helpful and is happy to help DIY'ers. How do you normally contact the local inspector? |
#16
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
|
#17
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
Since my profession is a "catastrophe" insurance adjuster, may I suggest if
you live in an area that doesn't have a-holes for inspectors, get a permit & have it inspected. Should your workshop burn due to an electrical problem some of the insurance companies will try to use "your" contributory negligence to gain a little wiggle room. Also take pictures of your work and do a diagram with materials used. Keep receipts. It's not often, but some adjusters will push on you to accept less in fear that a battle will yield nothing . . . just my two cents . . . Also always keep your agent up to date on any new out buildings and their content in $$$$$. . . . Most home owner policies only give you 10% on all out buildings combined. That's 10% of your total home owners value. $300,00.00 home, you have $30,000.00 coverage on out buildings . . . If your shop is attached to the home, ie . . garage, that does not apply . . . Also, if you sell anything out of your home shop, make sure you incorporate the work "STUDIO" as in art into the business name . . . . Home being used for business purposes nulls your coverage in most cases . . . . "Lew Hodgett" wrote in message . net... wrote: I have a new SquareD load center panel (QO8-16L100S) that I want to use but need some clarification. 1. This particular panel only has one grounding/neutral bar, but I was under the impression the ground and neutral must be separated in a subpanel installed in a stand alone structure. Buy a separate ground bar kit from a SQ D distributor and install it. 2. The panel is rated for 100A, but I was hoping to use a 60A-75A breaker in the main box to feed this subpanel. Is this a problem? No. Just install a 2P-60 as a main C/B the in the sub panel. 3. The run from the main panel to the sub will only be about 15 ft. total. What size wire do you suggest I run? Bigger is better. I'd run #2 but #4 will do the job. Lew |
#18
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
|
#19
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
|
#20
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
On Wed, 19 Apr 2006 21:18:15 GMT, Doug Miller wrote:
NEC requires a main for more than 6 breakers. Cite, please? I thought that was for service entrances, not subpanels. Hmmm. From my copy of the NEC 2002 Handbook: 230.71(A) "The service disconnecting means for each service permitted by 230.2, or for each set of service-entrance conductors permitted by 230.40, Exception Nos. 1, 3, 4, or 5, shall consist of not more than six switches or sets of circuit breakers ... " 408.16(A) "Each lighting and applicance branch-circuit panelboard shall be individually protected on the supply side by not more than two main circuit breakers or two sets of fuses having a combined rating not greater than that of the panelboard." "Exception No. 1: Individual protection for a lighting and appliance panelboard shall not be required if the panelboard feeder has overcurrent protection not greater than the rating of the panelboard." Seems you're correct, Doug. -- Art |
#21
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
writes:
Thank you for the detailed reply, Scott. Scott Lurndal wrote: writes: Greetings All! I am in the process of wiring up a shed in the backyard for use as a workshop. I have a new SquareD load center panel (QO8-16L100S) that I want to use but need some clarification. 1. This particular panel only has one grounding/neutral bar, but I was under the impression the ground and neutral must be separated in a subpanel installed in a stand alone structure. Should I just buy a ground bar and install it in the panel and connect it to a new grounding rod? First, remove the bonding screw that bonds the grounded (neutral) busbar to the enclosure. Second, purchase an accessory busbar and fasten it to the enclosure as the grounding busbar. Third, bond the grounding busbar in the subpanel to the grounding busbar in the service entrance with the appropriate gauge green/bare conductor. You'll also want to bond the grounded busbar in the subpanel to the grounded busbar in the service entrance panel with suitably sized white conductor. I should also use the bonding screw for the grounding busbar, right? The screw that fastens the grounding busbar to the subpanel enclosure serves as a bonding screw. Discard the bonding screw you remove from the grounded busbar in the subpanel. snip 3. The run from the main panel to the sub will only be about 15 ft. total. What size wire do you suggest I run? If you use a 60A breaker, #6 should be sufficient at that length. Check the NEC tables for definitive value based upon your conductor temperature rating. Are you using conduit and a thermoplastic insulated 90 degree-rated conductor such as THHN or #6/3 w/g jacketed (which IIRC are 60 degree-rated conductors)? I was planning on burying with PVC type conduit and running #6/3 w/g...assuming I can find that wire. Sounds good? If you're burying the conduit, there is really no good reason to use jacketed cable rather than individual conductors. Run four THHN or THW conductors: - #6 or #4 BLACK (current carrying conductor #1) - #6 or #4 RED (current carrying conductor #2) - #6 or #4 WHITE (grounded conductor, aka neutral) - #8 or #6 GREEN (grounding conductor) RED and BLACK are simply convention, you can use any color other than white, green or green with yellow stripes for the current carrying conductors. The RED and BLACK conductors must, of course, be connected to different poles in the service entrance via a two-pole breaker. Watch your conduit fill percentage. 2" should be more than sufficient as only two of the four conductors in the conduit carry current. scott |
#22
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
Unquestionably Confused writes:
brianlanning, or somebody so disguised, wrote the following at or about 4/19/2006 11:38 AM: That is OK if you have less than 6 breakers in the sub. Should have said 6 or less How does the number of breakers in the subpanel matter? Probably just to give you a margin of "safety" so you're not continually popping the main breaker. 60 Main and 6 or less 15a breakers. How likely is it that you'll have a 10a+ load on six of them at the same time? Low, I'd say. ...but the 60A feed would be 240V (two legs of 120V), so it has the capacity of handling 120A of 120V IF it is balanced between the two legs.... 60A Main and, say, 12 breakers (mixed bag of 15A and 20A) much more likely to pop the main. ...not if each breaker is running at 10A and they are balanced between the two 120V feeds. Once you get beyond that (up to the 15 or 20A values on the breakers...) it's time to stand back. Not a safety issue, per se, more like a "this standard is engineered for the dumbest person." Think "I still have breakers and open outlets. How can I possibly overload this panel?" Make 'em all 30A breakers 'cause they keep popping the 15A ones, and see if you can get everything running and pop the main breaker before one of the circuits burns down the house. :-) The financial corollary would be, "I can't be overdrawn! I still have checks in my checkbook!"g ...or "what do you mean the check bounced? There was room for all those zeroes on the line for the amount!" |
#23
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
Somebody wrote:
NEC requires a main for more than 6 breakers. TRUE. Known in some circles as the "6 hand" rule. Regardless of whether a panel is a "sub" or a "main", you must be able to disconnect ALL power distributed by that panel in a maximum of 6 motions of the hand. I seen some very clever schemes used by some contractors in an attempt to avoid a main C/B, but most don't get approved. Lew |
#24
Posted to rec.woodworking
|
|||
|
|||
F/S, Gasoline Generator, SoCal Area
Coleman 10HP, Contractor type, 5,000 Watt engine-generator located Long
Beach. 120/240V output Boat yard has power so have no further use for it so it's for sale. Will make a good back up power supply. SoCal area only. If interested, contact off list. Lew |
#25
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
In article ,
Lew Hodgett wrote: Somebody wrote: NEC requires a main for more than 6 breakers. TRUE. FALSE! Known in some circles as the "6 hand" rule. Regardless of whether a panel is a "sub" or a "main", you must be able to disconnect ALL power distributed by that panel in a maximum of 6 motions of the hand. I -wanted- a master-cut-off in the main breaker panel in my condo when I was rebuilding the kitchen, and replacing the breaker panel. (went from 14 to 20 circuits, original panel mfr long out of business, had to enclosure, et al.) City inspector would not allow a 100A breaker at panel feed, because there was 100A breaker (only) panel in utility entry room. I had, per inspector, choice of: 1) run with *no* 'master-cut-off breaker' in unit. 2) try to find something like a 95A breaker to use as the 'main' in unit. 3) replace (obsolete, mfr out-of-business) breaker at utility entry room with something like 110A,, and use 100A in unit. "1" was the only 'financially viable' alternative. |
#26
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
Robert Bonomi wrote:
Lew Hodgett wrote: Somebody wrote: NEC requires a main for more than 6 breakers. TRUE. FALSE! Known in some circles as the "6 hand" rule. Regardless of whether a panel is a "sub" or a "main", you must be able to disconnect ALL power distributed by that panel in a maximum of 6 motions of the hand. I -wanted- a master-cut-off in the main breaker panel in my condo when I was rebuilding the kitchen, and replacing the breaker panel. (went from 14 to 20 circuits, original panel mfr long out of business, had to enclosure, et al.) City inspector would not allow a 100A breaker at panel feed, because there was 100A breaker (only) panel in utility entry room. I had, per inspector, choice of: 1) run with *no* 'master-cut-off breaker' in unit. 2) try to find something like a 95A breaker to use as the 'main' in unit. 3) replace (obsolete, mfr out-of-business) breaker at utility entry room with something like 110A,, and use 100A in unit. "1" was the only 'financially viable' alternative. I'm not sure I understand your explanation; however, the "6 hand rule" applies if you are going to comply with NEC. Got any idea what this "inspector" had for a day job? Lew |
#27
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
In article ,
Lew Hodgett wrote: Robert Bonomi wrote: Lew Hodgett wrote: Somebody wrote: NEC requires a main for more than 6 breakers. TRUE. FALSE! Known in some circles as the "6 hand" rule. Regardless of whether a panel is a "sub" or a "main", you must be able to disconnect ALL power distributed by that panel in a maximum of 6 motions of the hand. I -wanted- a master-cut-off in the main breaker panel in my condo when I was rebuilding the kitchen, and replacing the breaker panel. (went from 14 to 20 circuits, original panel mfr long out of business, had to enclosure, et al.) City inspector would not allow a 100A breaker at panel feed, because there was 100A breaker (only) panel in utility entry room. I had, per inspector, choice of: 1) run with *no* 'master-cut-off breaker' in unit. 2) try to find something like a 95A breaker to use as the 'main' in unit. 3) replace (obsolete, mfr out-of-business) breaker at utility entry room with something like 110A,, and use 100A in unit. "1" was the only 'financially viable' alternative. I'm not sure I understand your explanation; Doing electrical rework, _with_ a city permit, it was specified _by_the_ city_ that I was to use a sub-panel (24 circuit capacity) *WITHOUT* a main breaker in it. Because the main breaker was in the panel in the building utility room. I _wanted_ a master-cut-off in the sub-panel, but there was no =feasible= way to do it *and* be code compliant. Since it was _not_ required by code, I ended up going without it. Note: *NONE* of the 30-plus units in my condo building has a master- cut-off in the 'in unit' sub-panel. All have at least 14 circuits, and it is comparatively 'modern' construction -- circa 35 years old. however, the "6 hand rule" applies if you are going to comply with NEC. "Cite please". It was established in another sub-thread that that 6-breaker max w/o a main cut-off applied to a 'service entrance' panel only. They even quoted the relevant NEC section. Now, the question is, can you back up -your- claim.` Note: the person posting the NEC section showing 'service entrance' only was someone who had made the same assentation you did, and was admitting he had been wrong. Got any idea what this "inspector" had for a day job? Yeah, he was the CHIEF ELECTRICAL INSPECTOR for the city, and department head. 25+ years on the job. He was a 'good guy' -- out of six 'somewhat unconventional' things I wanted to do, he found code interpretations (and provided 'chapter and verse' just- ifications) that let me DO five of them. (Just one of which saved me the cost of at least 2 electricians for a full day, and, incidentally, around $200 in parts.) It was only the master-cut-off that didn't fly. to be 'code compliant', I could go _without_ a master-cut-off in the sub-panel, or I could use one that had to be _smaller_ than the main breaker downstairs. (this required either a 'nonstandard' capacity breaker upstairs, or replacing the one downstairs with a bigger standard value. Neither of those options was financially viable, albeit for different reasons.) To this day, I don't understand the 'smaller breaker' requirement. If I've got a 100A breaker on each end of a 100+A-capable wire, "at least" one will trip on an overload. There's no safety issue. The inspector agreed with my logic, but said that, nonetheless, the code didn't allow it. So, I went the 'code compliant' -- no main breaker in the sub-panel way. 22 circuits. |
#28
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
Robert Bonomi wrote:
"Cite please". It was established in another sub-thread that that 6-breaker max w/o a main cut-off applied to a 'service entrance' panel only. They even quoted the relevant NEC section. Now, the question is, can you back up -your- claim.` Note: the person posting the NEC section showing 'service entrance' only was someone who had made the same assentation you did, and was admitting he had been wrong. No longer have access to a current code book. My comment was based on being bloodied from having to work with local inspectors and contractors as a distribution equipment supplier for about 15 years. Your description of your experience is certainly strange. Just curious, was the main C/B visible from the distribution pnl in question? Lew |
#29
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
In article t,
Lew Hodgett wrote: Robert Bonomi wrote: "Cite please". It was established in another sub-thread that that 6-breaker max w/o a main cut-off applied to a 'service entrance' panel only. They even quoted the relevant NEC section. Now, the question is, can you back up -your- claim.` Note: the person posting the NEC section showing 'service entrance' only was someone who had made the same assentation you did, and was admitting he had been wrong. No longer have access to a current code book. My comment was based on being bloodied from having to work with local inspectors and contractors as a distribution equipment supplier for about 15 years. Your description of your experience is certainly strange. Just curious, was the main C/B visible from the distribution pnl in question? Well, if you could see out the door or the condo, across the hall, down three flights of stairs, through the laundry room and into the utility room, then yeah, you could claim it was visible. grin Now, I was straight across the hall from the stairwell, the folks at the far end of the floor had a somewhat more obscured line of sight. |
#30
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
In article , Lew Hodgett wrote:
I'm not sure I understand your explanation; however, the "6 hand rule" applies if you are going to comply with NEC. For a service entrance, yes. If you maintain that the rule applies to subpanels as well, please cite the relevant article and section of the Code. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#31
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
In article ,
Mike M wrote: I suspect he is being impacted by local rules. There was hardly anything in the municipal code that modified in any way the National code. There was an addition that _any_ new (addition or replacement) panel had to be inspected by the city, and something else equally earth-shaking. I have used main breaker panels as sub panels when they are located a long ways from the main. I don't usually as cost of a 3 phase 208 volt 200 amp breaker adds quite an expense. Also since we usually have to protect according to available fault current fuses get a lot more practicle. I don't think NEC prohibits it. Feeders have to be protected where they are powered from unless using the tap rules. Yup. And there is apparently a requirement that _if_ there is a breaker at the 'downstream' End of the feeder, it must be smaller than the one at the 'powered from' end. which meant if I wanted to use a 100A 2-pole in the in-unit panel, I had to have 'something bigger' at the feed end. But, the building was built (1960s) using "Federal" breakers/panels, etc. finding 'standard' replacements is an exercise in futility -- let alone trying to find, say, a 125A one. the other option was to put something 'a little smaller' than 100A in the in-unit panel. It's amazing how scarce 'residential style' breakers are with ratings above 60A, and below 100A. and how _expensive_ something like a 95A breaker of that ilk is. |
#32
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
In article ,
Mike M wrote: On Sun, 23 Apr 2006 16:19:53 -0000, (Robert Bonomi) wrote: In article , Mike M wrote: I suspect he is being impacted by local rules. There was hardly anything in the municipal code that modified in any way the National code. There was an addition that _any_ new (addition or replacement) panel had to be inspected by the city, and something else equally earth-shaking. I have used main breaker panels as sub panels when they are located a long ways from the main. I don't usually as cost of a 3 phase 208 volt 200 amp breaker adds quite an expense. Also since we usually have to protect according to available fault current fuses get a lot more practicle. I don't think NEC prohibits it. Feeders have to be protected where they are powered from unless using the tap rules. Yup. And there is apparently a requirement that _if_ there is a breaker at the 'downstream' End of the feeder, it must be smaller than the one at the 'powered from' end. which meant if I wanted to use a 100A 2-pole in the in-unit panel, I had to have 'something bigger' at the feed end. But, the building was built (1960s) using "Federal" breakers/panels, etc. finding 'standard' replacements is an exercise in futility -- let alone trying to find, say, a 125A one. the other option was to put something 'a little smaller' than 100A in the in-unit panel. It's amazing how scarce 'residential style' breakers are with ratings above 60A, and below 100A. and how _expensive_ something like a 95A breaker of that ilk is. Where I am we have NEC, state, and then local rules, not to mention sometimes building code or fire marshalls. Arguing with inspectors is a little like wallowing in the mud with pigs. Eventually you figure out they like it. LOL, and usually they can cite the code section. Mike Ah well, I rarely argue with inspectors. Except when they're out-and-out wrong, and I can prove it, that is. At another place, I crossed swords with a City of Chicago electrical inspector -- over the City of Chicago Electrical code. (The Chicago Code is _not_ based on the NEC, in fact it predates it. It is much stricter than the NEC about some things, and more lax about others. It is also written such that it is _very_ difficult to figure out exactly what is, or is -not-, allowed in any given situation. Methinks that this is deliberate, to enhance inspector revenues.) Anyway, this inspector didn't like the way something had been done. And cited the code section that it was in violation of. And I cited the section that said _his_ section "didn't apply" if conditions X, Y and Z were met, and that =this= installation have conditions X, Y, and Z. He countered with a section that said condition Y had this other requirement under "these" circumstances, and that we did fall under that. Whereupon I pointed out that section thus-and-such said his section applied only when condition W existed, which did not exist here. This went on for a while, but eventually he "went away mad" -- *without* writing a violation, *or* getting a bribe. He was _not_ a happy camper. The next week the fire inspectors came calling. *sigh* They were thorough, but didn't find anything that they could write a violation for, either. |
#33
Posted to rec.woodworking
|
|||
|
|||
yet another subpanel question
Mike M wrote:
Where I am we have NEC, state, and then local rules, not to mention sometimes building code or fire marshalls. Arguing with inspectors is a little like wallowing in the mud with pigs. Eventually you figure out they like it. LOL, and usually they can cite the code section. Mike I agree, but the *code* they cite isn't always in the books... In my town the inspector was busting my gonads about building a simple shed, and he was using some interesting *interpretations* of state code. So when I copied the code from the book and then called the state and made a recording of the official telling me the inspector cannot supersede state code on that matter (and played it for him), he relented. But I'm wary of what he will do upon final inspection of the site - these guys tend to have long (and mean) memories. In another town when we had an inspection of the new breaker panel replacement in my mother's house, the town electrical inspector insisted we pay for a plumbing permit and refused to sign off on the electrical inspection. He was looking at a short piece of PVC that was used as a drain from the furnace's humidifier down to the sump (this was on the other side of the basement, no connection to the electrical work). That installation was from more than 20 years ago, and since mom died we couldn't ask her for the copy of the paper work from the contractor for the installation, so the inspector said we could not have a C.O. for the house. These guys are just plain evil. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Dehumidification, fan speed, and backfeed question | Home Repair | |||
Another subpanel grounding question | Home Repair | |||
Simple question regarding Ceiling tiles and sound? | UK diy | |||
Simple question regarding Ceiling tiles and sound? | Home Repair |