Web searches have led me nowhere, and a Man hates to ASK for
"directions" But,
I need accurate information for overload heater values,

using a 3 ph. Size 1 magnetic motor starter, to run a 1 phase 220v. 5
hp motor rated at 25 Full Load Amps, using 2 heaters instead of three.
( Q. is each heater the 25 FLA value?? or only half that value?? )
I have Square D and GE starters available.
THANKS for your expert input!

  #2   Report Post  
Posted to rec.woodworking
ATP*
 
Posts: n/a
Default 3ph Motor Starters for 1ph motors


"zzarus" wrote in message
oups.com...
Web searches have led me nowhere, and a Man hates to ASK for
"directions" But,
I need accurate information for overload heater values,

using a 3 ph. Size 1 magnetic motor starter, to run a 1 phase 220v. 5
hp motor rated at 25 Full Load Amps, using 2 heaters instead of three.
( Q. is each heater the 25 FLA value?? or only half that value?? )
I have Square D and GE starters available.
THANKS for your expert input!


The 25 FLA value.


  #3   Report Post  
Posted to rec.woodworking
Wood Butcher
 
Posts: n/a
Default 3ph Motor Starters for 1ph motors

It would be better if you used all 3 heaters. Use any 1 heater
on one leg and the remaining 2 heaters in series on the other
leg.

Art

"zzarus" wrote in message
oups.com...
Web searches have led me nowhere, and a Man hates to ASK for
"directions" But,
I need accurate information for overload heater values,

using a 3 ph. Size 1 magnetic motor starter, to run a 1 phase 220v. 5
hp motor rated at 25 Full Load Amps, using 2 heaters instead of three.
( Q. is each heater the 25 FLA value?? or only half that value?? )
I have Square D and GE starters available.
THANKS for your expert input!



  #4   Report Post  
Posted to rec.woodworking
Bugs
 
Posts: n/a
Default 3ph Motor Starters for 1ph motors

The rule is "one heater for each current leg". You're right in that
score. Pick a heater value the next size larger than your full load
rating for starters "no pun intended". The ambient temperature of the
controller housing can affect the trip point on overload switches, so
there is room for adjustment if you have problems with tripping. There
is nothing wrong with using a 3ph starter for single phase. Gives you a
spare contact for running auxiliary equipment, like a dust collector or
coolant pump.
Good luck,
Bugs

  #5   Report Post  
Posted to rec.woodworking
John Sellers
 
Posts: n/a
Default 3ph Motor Starters for 1ph motors


"zzarus" wrote in message
oups.com...
Web searches have led me nowhere, and a Man hates to ASK for
"directions" But,
I need accurate information for overload heater values,

using a 3 ph. Size 1 magnetic motor starter, to run a 1 phase 220v.

5
hp motor rated at 25 Full Load Amps, using 2 heaters instead of

three.
( Q. is each heater the 25 FLA value?? or only half that value?? )
I have Square D and GE starters available.
THANKS for your expert input!


Yes, use the 25A current value to size your overload heaters. The FLA
values for any motor type indicate the current which flows in each
phase. I.E. - You would still use 25A to size heaters if the motor
was 3-phase.

That being said, the actual heaters you need may not be labeled with
"25A" - the current they're labeled with should be slightly greater
than the full load current of the motor to which they're applied.
Most heaters are manufactured for a 'range' of FLA motor currents.

You'll also need to consider which starter you're using (more
precisely, which overload relay is used in the starter), as each
manufacturer makes heaters for use with their specific equipment.
Look up the manufacturer on the web, you can usually find heater table
references. You need to use heaters specific to the actual overload
relay model in your starter. You can also find overload heater tables
referenced by equipment distributors, such as Graybar and Grainger.

If you really get detailed about this (some might say this is a bit AR
for non-industrial applications), you can size heaters for a
difference in ambient temperature between the motor and the starter
locations. But, that's usually not significant unless it's a large
differential.

For a single-phase motor, you can use just two heaters, and two poles
of a three-phase starter/contactor. A more protective setup would use
all three phases of the starter - just run one leg of the motor
circuit through two poles (in series connection) of the contactor and
overload relay.

Hope this helps,
John Sellers

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Which Book on the selection of electric motors??? [email protected] Electronics Repair 6 October 27th 05 05:34 PM
Coill winding / AC motor construction - book recommendation ? N Cook Electronics Repair 5 February 22nd 05 06:27 PM
Repair data base NSM Electronics Repair 2 February 19th 05 09:27 PM
FS: DC Motors, Stepping Motors Surplus and Salvage therepairman Electronics Repair 0 December 12th 04 05:05 PM
Testing 3 phase motors Pal Metalworking 1 July 11th 04 11:50 PM


All times are GMT +1. The time now is 02:16 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"