I came home after 3 weeks holiday to find no electricity. I have a
split load consumer unit. The unprotected circuits were ok until I
switched on one of the lights and a bulb blew and tripped that MCB.
I switched on the protected circuits expecting the RCCD to trip out
again but it has been ok. I guess that the power was off for about 2
weeks judging by the contents of a freezer in the garage.
Is it normal for an RCCD to trip without a definite faulty device. What
was likely to have tripped it out?

Kevin

  #3   Report Post  
Christian McArdle
 
Posts: n/a
Default

Is it normal for an RCCD to trip without a definite faulty device. What
was likely to have tripped it out?


Could be absolutely anything, particularly if you have the RCD protecting a
garage, where wires might get damp. It is the reason that it is advisable to
(a) split into several different RCDs or RCBOs and (b) put fridges and
freezers on independent circuits with as little RCD protection as is allowed
by the regs for the earthing system in use.

I wouldn't be concerned by a single unexplained trip. If they start getting
more frequent, then you may have a faulty appliance or wiring.

Christian.


  #4   Report Post  
Ric
 
Posts: n/a
Default

wrote in message
oups.com...
I came home after 3 weeks holiday to find no electricity. I have a
split load consumer unit. The unprotected circuits were ok until I
switched on one of the lights and a bulb blew and tripped that MCB.
I switched on the protected circuits expecting the RCCD to trip out
again but it has been ok. I guess that the power was off for about 2
weeks judging by the contents of a freezer in the garage.
Is it normal for an RCCD to trip without a definite faulty device. What
was likely to have tripped it out?


It is not uncommon for RCDs to trip during a power cut - it is possible I
suppose that there was a temporary loss of power while you were away.


  #5   Report Post  
Fred
 
Posts: n/a
Default


wrote in message
oups.com...
I came home after 3 weeks holiday to find no electricity. I have a
split load consumer unit. The unprotected circuits were ok until I
switched on one of the lights and a bulb blew and tripped that MCB.
I switched on the protected circuits expecting the RCCD to trip out
again but it has been ok. I guess that the power was off for about 2
weeks judging by the contents of a freezer in the garage.
Is it normal for an RCCD to trip without a definite faulty device. What
was likely to have tripped it out?

Kevin


My main bug bear with RCDs is regarding suppression. Most machinery such as
washing machines usually have suppressors (capacitors) between power and
earth. A result is that earth currents flow causing an imbalance between
live and neutral. Some years ago I had to remove a suppressor from a
dishwasher to stop the RCD from tripping.

If such suppression is fitted the RCD becomes very sensitive to mains spikes
which I experienced recently due to a deteriorating sub-station. Other
houses around here don't have RCDs and hence weren't affected.

I'm not sure if the regs allow connecting things like freezers to the mains
without RCDs in the same way lighting circuits need not have an RCD. My
understanding is that new wiring, PME excepting, all outlets should have an
RCD.




  #6   Report Post  
Christian McArdle
 
Posts: n/a
Default

My understanding is that new wiring, PME excepting, all outlets
should have an RCD.


Absolutely not. There is no requirement for socket outlets to have RCDs
unless they are likely to supply outdoor equipment. A single socket clearly
intended for the purpose of a fridge freezer will not fall under that
category. Indeed, if you have a dedicated IP rated outside socket, or no
garden at all, then it would be easy to claim that all sockets indoors are
exempt from the requirement to have an RCD.

However, it is good practice to RCD protect all sockets that aren't intended
for the sole use of fixed appliances such as refrigeration and laundry for
secondary protection against direct and indirect contact.

Christian.


  #7   Report Post  
Stefek Zaba
 
Posts: n/a
Default

Fred wrote:

I'm not sure if the regs allow connecting things like freezers to the mains
without RCDs in the same way lighting circuits need not have an RCD. My
understanding is that new wiring, PME excepting, all outlets should have an
RCD.

Not quite sure if that claim is worthy of the term "understanding", I'm
afraid.

There's no requirement *at all* for supplies to normal appliances inside
the house to have RCD protection. RCD protection is required for sockets
where it's "reasonably foreseeable" that outdoor portable appliances
will be connected: and the normal interpretation is that ground-floor
rings therefore should be on an RCD - though if you make other,
convenience arrangements for outside power - e.g. 13A or other external
sockets at several points - you can argue away from RCDs on the internal
-only ring(s). The Regs also require RCDing sockets in bedrooms with
shower cubicles (i.e. a room which isn't a bathroom as such, so can have
socketses, but does have a shower cubie in the corner and socketses in
the same room but Far Away), and in a few other Special Situations.

With a TT supply (*not* PME, or the other common
supplier-provides-an-earth arrangement) a 100mA RCD is
required/recommended, as the local earth spike can't be relied upon to
produce a low enough resistance to get enough current to flow to
reliably trip MCBs/blow fuses in the event of a phase-to-earth fault.
But the 100mA rating is too high to do anything much for personal safety
protection...

Stefek
  #8   Report Post  
Dorothy Bradbury
 
Posts: n/a
Default

Check outside lighting if you have them & on the RCD:
o Very common for light fittings to get wet this time of year
o Does not take much to trip an RCD

Quite a few Merlin Gerin bulk-pack RCBOs on Ebay right now,
not mine & no connection with me - but 4-5 for about £55. That
is the same price as one single Merlin Gerin RCBO.
--
Dorothy Bradbury


  #9   Report Post  
Peter Scott
 
Posts: n/a
Default

Another possible cause is computers. Do you have more than one? One office I
worked in had constant problems with tripping (electrical variety) until the
trip was changed to 100mA. It only started when computers were used on that
circuit for the first time. I have a problem at home that seems to be linked
with PCs. Surprisingly it happens when a UPS box is switched on. I'm
changing the consumer unit to have parts of the system non-protected.

Peter Scott


  #11   Report Post  
The Natural Philosopher
 
Posts: n/a
Default

Andrew Gabriel wrote:

In article .com,
writes:

I came home after 3 weeks holiday to find no electricity. I have a
split load consumer unit. The unprotected circuits were ok until I
switched on one of the lights and a bulb blew and tripped that MCB.
I switched on the protected circuits expecting the RCCD to trip out
again but it has been ok. I guess that the power was off for about 2
weeks judging by the contents of a freezer in the garage.



You might want to consider making sure certain things are not RCD
protected, such as fridge/freezer, central heating (and any other
frost protection), alarm, pet life support systems (use individual
RCD), etc. Generally, non-portable appliances don't benefit much
from RCD protection. To some extent, this also depends on your
system's supply earthing type.


I am deeply garteful that my washing machine troipped the RCD, because
oitherise the dangerous partial short to earth might habve gine
unnotoced. Of course uts eartherd, ut if one cable can go, so can
another, and loss of earthing does not get detected untl you get a nasty
shock off it.


Is it normal for an RCCD to trip without a definite faulty device.



No.


Yes, definitely. With two computers, two printers a PaABX, a router,
five TV;s and three stereos all on 'standby; or in action, I simply cold
not keep mine from randomly tripping whenever anything was switched on.
Now up to 100mA and its stable.

But even so, there is enough general leakage that a blowing bulb or a
power surge can take it out sometimes.

IOf there is libve to earth capacitance, there is some leakage. RFI
filters have precisely that in them.

Add a voltage spike, and you can get momentary high imbalance.

Pls how much wioring is in teh roof, where mild condesation may alow
leakage? etc etc.

Earth lakage is a fact of life. Someties it all gets too much and the
thing trips.




What was likely to have tripped it out?



Impossible to say. Is there anything which no longers works?

  #12   Report Post  
The Natural Philosopher
 
Posts: n/a
Default

Fred wrote:

wrote in message
oups.com...

I came home after 3 weeks holiday to find no electricity. I have a
split load consumer unit. The unprotected circuits were ok until I
switched on one of the lights and a bulb blew and tripped that MCB.
I switched on the protected circuits expecting the RCCD to trip out
again but it has been ok. I guess that the power was off for about 2
weeks judging by the contents of a freezer in the garage.
Is it normal for an RCCD to trip without a definite faulty device. What
was likely to have tripped it out?

Kevin



My main bug bear with RCDs is regarding suppression. Most machinery such as
washing machines usually have suppressors (capacitors) between power and
earth. A result is that earth currents flow causing an imbalance between
live and neutral. Some years ago I had to remove a suppressor from a
dishwasher to stop the RCD from tripping.

If such suppression is fitted the RCD becomes very sensitive to mains spikes
which I experienced recently due to a deteriorating sub-station. Other
houses around here don't have RCDs and hence weren't affected.

I'm not sure if the regs allow connecting things like freezers to the mains
without RCDs in the same way lighting circuits need not have an RCD. My
understanding is that new wiring, PME excepting, all outlets should have an
RCD.


They do, but I wouldn't frankly.

What I SHOULD have done apart from uprateying teh whle house to 100mA,
is to add RCBO's to the specal circuits - the ones feeding outdoor
stuff. I have, for example, a Klargester fed by an underground cable to
a switch box that is permentrly in the rain...

And three outside waterprof mains sockets.
  #13   Report Post  
The Natural Philosopher
 
Posts: n/a
Default

Stefek Zaba wrote:

Fred wrote:

I'm not sure if the regs allow connecting things like freezers to the
mains
without RCDs in the same way lighting circuits need not have an RCD. My
understanding is that new wiring, PME excepting, all outlets should
have an
RCD.

Not quite sure if that claim is worthy of the term "understanding", I'm
afraid.

There's no requirement *at all* for supplies to normal appliances inside
the house to have RCD protection. RCD protection is required for sockets
where it's "reasonably foreseeable" that outdoor portable appliances
will be connected: and the normal interpretation is that ground-floor
rings therefore should be on an RCD - though if you make other,
convenience arrangements for outside power - e.g. 13A or other external
sockets at several points - you can argue away from RCDs on the internal
-only ring(s). The Regs also require RCDing sockets in bedrooms with
shower cubicles (i.e. a room which isn't a bathroom as such, so can have
socketses, but does have a shower cubie in the corner and socketses in
the same room but Far Away), and in a few other Special Situations.

With a TT supply (*not* PME, or the other common
supplier-provides-an-earth arrangement) a 100mA RCD is
required/recommended, as the local earth spike can't be relied upon to
produce a low enough resistance to get enough current to flow to
reliably trip MCBs/blow fuses in the event of a phase-to-earth fault.
But the 100mA rating is too high to do anything much for personal safety
protection...

Stefek



Mmm. That depends. On how much residual leakage there is anyway.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AC tripped at main breaker.....please advise HvacTech2 Home Repair 14 March 8th 05 01:27 AM
Circuit breaker tripped while on vacation, how to get smell out of refrigerator? Dan K Home Repair 9 December 10th 04 04:30 PM
Should this have tripped the breaker? Ged UK diy 5 February 18th 04 07:52 PM
RCD tripped & will not reset Neil UK diy 4 August 5th 03 01:43 PM
Help -- Power out in one area but circuit breaker not tripped Joseph Meehan Home Repair 0 June 27th 03 02:29 AM


All times are GMT +1. The time now is 10:06 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"