Hi We have oil fired boiler Camray quartet with one pump and two acl
lifestyle 2 port valves, everything has been working fine last few years but
now boiler and pump running constantly even with programmer set to off for
both HW and CH only way I can stop running is to turn of main supply to
system. Any ideas what problem could be.


  #2   Report Post  
Malc
 
Posts: n/a
Default


"Martin Evans" wrote in message
...
Hi We have oil fired boiler Camray quartet with one pump and two acl
lifestyle 2 port valves, everything has been working fine last few years

but
now boiler and pump running constantly even with programmer set to off for
both HW and CH only way I can stop running is to turn of main supply to
system. Any ideas what problem could be.


I think the controller's knackered. Probably the relay/s have welded on. I
suppose it's possible that a tank stat could give the same result but
without checking diagrams I wouldn't know. If you've got a meter can you get
it onto the terminals in the controller with the controller on and see if
the outputs are being switched. which controller is it by the way?

--
Malc


  #3   Report Post  
raden
 
Posts: n/a
Default

In message , Martin Evans
writes
Hi We have oil fired boiler Camray quartet with one pump and two acl
lifestyle 2 port valves, everything has been working fine last few years but
now boiler and pump running constantly even with programmer set to off for
both HW and CH only way I can stop running is to turn of main supply to
system. Any ideas what problem could be.

Have the contacts in the programmer welded themselves together ?

--
geoff
  #4   Report Post  
John
 
Posts: n/a
Default


"raden" wrote in message
...
In message , Martin Evans
writes
Hi We have oil fired boiler Camray quartet with one pump and two acl
lifestyle 2 port valves, everything has been working fine last few years
but
now boiler and pump running constantly even with programmer set to off for
both HW and CH only way I can stop running is to turn of main supply to
system. Any ideas what problem could be.

Have the contacts in the programmer welded themselves together ?



If there are two valves it suggests an S plan system so the current drawn
through the programmer contacts is negligible (valve motor only) I'd suggest
the contacts in one of the motorised valve limit switches might be the
culprit. In each valve cable there will be an orange wire and a grey wire
from the limit switches. These will be connected together in the wiring
centre terminal box (orange to orange and grey to grey) with a live feed to
(usually) the grey wires and a switched supply from the orange wires to the
boiler and the pump. Carefully seperate one grey at a time from the terminal
(isolating while doing this or you will get the little men up your arm) and
try each time to see when the short circuited one is found. You then have a
choice of changing the microswitch which is a buggering about task or
changing the valve head if its of a vintage with a removable head and a five
wire swap, just keep a note of where the old wire colours went before
pulling them apart.


  #5   Report Post  
The Natural Philosopher
 
Posts: n/a
Default

Martin Evans wrote:

Hi We have oil fired boiler Camray quartet with one pump and two acl
lifestyle 2 port valves, everything has been working fine last few years but
now boiler and pump running constantly even with programmer set to off for
both HW and CH only way I can stop running is to turn of main supply to
system. Any ideas what problem could be.


Stuck motorised valve.

Same here. Must replace it.
Simple job.
So far its responded to hammer blows..


  #6   Report Post  
The Natural Philosopher
 
Posts: n/a
Default

John wrote:

"raden" wrote in message
...

In message , Martin Evans
writes

Hi We have oil fired boiler Camray quartet with one pump and two acl
lifestyle 2 port valves, everything has been working fine last few years
but
now boiler and pump running constantly even with programmer set to off for
both HW and CH only way I can stop running is to turn of main supply to
system. Any ideas what problem could be.


Have the contacts in the programmer welded themselves together ?




If there are two valves it suggests an S plan system so the current drawn
through the programmer contacts is negligible (valve motor only) I'd suggest
the contacts in one of the motorised valve limit switches might be the
culprit. In each valve cable there will be an orange wire and a grey wire
from the limit switches. These will be connected together in the wiring
centre terminal box (orange to orange and grey to grey) with a live feed to
(usually) the grey wires and a switched supply from the orange wires to the
boiler and the pump. Carefully seperate one grey at a time from the terminal
(isolating while doing this or you will get the little men up your arm) and
try each time to see when the short circuited one is found. You then have a
choice of changing the microswitch which is a buggering about task or
changing the valve head if its of a vintage with a removable head and a five
wire swap, just keep a note of where the old wire colours went before
pulling them apart.



I my case its teh valve motor nd gear train that is the problem, not the
switch. In order to actually have the rads getting hot, the valve must
be stuck open, not just the switch shorted.

If teh switch shorts but teh valve closes you get pum.boiler running but
short cycling and no hot rads..


  #7   Report Post  
John
 
Posts: n/a
Default


"The Natural Philosopher" wrote in message
...
John wrote:

"raden" wrote in message
...

In message , Martin Evans
writes

Hi We have oil fired boiler Camray quartet with one pump and two acl
lifestyle 2 port valves, everything has been working fine last few years
but
now boiler and pump running constantly even with programmer set to off
for
both HW and CH only way I can stop running is to turn of main supply to
system. Any ideas what problem could be.


Have the contacts in the programmer welded themselves together ?




If there are two valves it suggests an S plan system so the current drawn
through the programmer contacts is negligible (valve motor only) I'd
suggest the contacts in one of the motorised valve limit switches might
be the culprit. In each valve cable there will be an orange wire and a
grey wire from the limit switches. These will be connected together in
the wiring centre terminal box (orange to orange and grey to grey) with a
live feed to (usually) the grey wires and a switched supply from the
orange wires to the boiler and the pump. Carefully seperate one grey at a
time from the terminal (isolating while doing this or you will get the
little men up your arm) and try each time to see when the short circuited
one is found. You then have a choice of changing the microswitch which is
a buggering about task or changing the valve head if its of a vintage
with a removable head and a five wire swap, just keep a note of where the
old wire colours went before pulling them apart.


I my case its teh valve motor nd gear train that is the problem, not the
switch. In order to actually have the rads getting hot, the valve must be
stuck open, not just the switch shorted.

If teh switch shorts but teh valve closes you get pum.boiler running but
short cycling and no hot rads..



I read the ops post as the boiler and pump running but nothing about the
rads or hot water being "on"


  #8   Report Post  
Martin Evans
 
Posts: n/a
Default

hot water and radiators are all hot

"John" wrote in message
...

"The Natural Philosopher" wrote in message
...
John wrote:

"raden" wrote in message
...

In message , Martin Evans
writes

Hi We have oil fired boiler Camray quartet with one pump and two acl
lifestyle 2 port valves, everything has been working fine last few
years but
now boiler and pump running constantly even with programmer set to off
for
both HW and CH only way I can stop running is to turn of main supply to
system. Any ideas what problem could be.


Have the contacts in the programmer welded themselves together ?




If there are two valves it suggests an S plan system so the current
drawn through the programmer contacts is negligible (valve motor only)
I'd suggest the contacts in one of the motorised valve limit switches
might be the culprit. In each valve cable there will be an orange wire
and a grey wire from the limit switches. These will be connected
together in the wiring centre terminal box (orange to orange and grey to
grey) with a live feed to (usually) the grey wires and a switched supply
from the orange wires to the boiler and the pump. Carefully seperate one
grey at a time from the terminal (isolating while doing this or you will
get the little men up your arm) and try each time to see when the short
circuited one is found. You then have a choice of changing the
microswitch which is a buggering about task or changing the valve head
if its of a vintage with a removable head and a five wire swap, just
keep a note of where the old wire colours went before pulling them
apart.


I my case its teh valve motor nd gear train that is the problem, not the
switch. In order to actually have the rads getting hot, the valve must be
stuck open, not just the switch shorted.

If teh switch shorts but teh valve closes you get pum.boiler running but
short cycling and no hot rads..



I read the ops post as the boiler and pump running but nothing about the
rads or hot water being "on"




  #9   Report Post  
John
 
Posts: n/a
Default


"Martin Evans" wrote in message
...
hot water and radiators are all hot


So the valves are both open? Have you taken a look into the wiring centre
and tested to see whether the motor "open" signals are present on the wiring
to the valve motors (brown wires in the multicore flexibles)
Just to help a little a standard s-plan valve head uses brown (or in the
case of Danfoss valves brown&white) as the motor supply, blue as motor
neutral, green&yellow as earth, grey and orange are connected to the limit
switch which closes contact when the valve is open. A few such as Honeywell
also have a white wire which is used with an alternative changeover contact
limit switch for use in a c-plan system.
If the brown wires are live then the problem will be outside the valve motor
heads and the programmer needs more investigation always assuming that there
aren't any external influences such as frost stats.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
central heating programmer re-wiring Mark Downey UK diy 1 October 4th 04 05:56 PM
Upgrading the Central Heating System- BOOM! Alan Dempster UK diy 3 July 21st 04 04:55 PM
Central Heating control unit replacement - advice please Damian Home Repair 1 December 29th 03 01:35 AM
Gravity fed Central Heating System Woes Kev Parkin UK diy 4 October 22nd 03 11:23 AM
Oil-fired central heating control? Frances UK diy 1 October 2nd 03 10:57 AM


All times are GMT +1. The time now is 10:40 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"