In a house I moved into recently there is an old 3 wayWylex Consumer unit,
wired fuse holders, 30A ring main, 5A lights, & 15A oven.
At some point a separate hob has been wired in using a secondary 30A
switched single way fuse box fed from the incoming tails in the Wylex CU, in
addition another switched 30A single way fuse box has been wired in from the
meter, this supplied an electrical shower unit in the bathroom via what I
think is 7/.036 or 7/.044 twin & earth.(will check when I can borrow a
micrometer)
Since the shower was redundant I've used this cable to supply a secondary 4
way consumer unit (located outside the bathroom) to provide a separate
supply to the bathroom, it includes earth leakage protection main switch,
and 3 Mcbs,
6A-- lights& fan, shaver socket and mirror demist heater (100W).
15A-- Immersion htr.
15A--Fused switched spur to wall mounted Hair dryer.

My question is, How should the secondary CU be labelled and should the hair
dryer Immersion htr etc have labelling referring to the secondary CU.What do
regs say regarding labelling.
I will in time have the main incoming Wylex replaced by a modern Consumer
unit but it will still feed the secondary CU via the old cable.
Hope that's clear, it seems a bit garbled on rereading it.
Thanks
Tom


  #2   Report Post  
Christian McArdle
 
Posts: n/a
Default

My question is, How should the secondary CU be labelled and should the
hair
dryer Immersion htr etc have labelling referring to the secondary CU.


I'd write on the secondary consumer unit

"Hairdryer"
"Immersion" (or "Water Heater")
and
"Lights"

At the supply end fuse box, I'd write "Bathroom".

Christian.


  #3   Report Post  
Tom
 
Posts: n/a
Default


"Christian McArdle" wrote in message
. net...
My question is, How should the secondary CU be labelled and should the

hair
dryer Immersion htr etc have labelling referring to the secondary CU.


I'd write on the secondary consumer unit

"Hairdryer"
"Immersion" (or "Water Heater")
and
"Lights"

At the supply end fuse box, I'd write "Bathroom".

Christian.

Thanks for that, but is there a standard method of labelling laid down in
IEE regs for multi distribution points or does that only apply in
commercial/industrial buildings where more than one phase is used to balance
the load on a 3Ph incoming supply.
Tom


  #4   Report Post  
Andy Wade
 
Posts: n/a
Default

Tom wrote:

Thanks for that, but is there a standard method of labelling laid down in
IEE regs for multi distribution points or does that only apply in
commercial/industrial buildings where more than one phase is used to balance
the load on a 3Ph incoming supply.


There's no prescribed scheme for circuit numbering, if that's what you
mean. The relevant requirements for identification a

Reg. 514-01-01 requires that the purpose of each item of switchgear and
controlgear is indicated, unless it's obvious.

514-01-02 requires wiring to be arranged so that it can be identified
for inspection, testing, repair or alteration, "as far as is reasonably
practicable."

514-03-xx to 514-07-xx are concerned with identification of conductors
by means of the usual (old or new) colours.

514-08-01 requires each protective device (fuse, MCB or RCD) to be
identified so that the circuit(s) protected "may be easily recognised."

514-09-01 requires documentation to be provided in the form of "a
legible diagram, chart or table" (or equivalent) listing or detailing
the following:
- type of each circuit, (locations of) points served, cable size & type,
- how indirect contact protection is provided (i.e. EEBADS),
- information necessary to identify each device for protection,
isolation and switching,
- details of any items vulnerable to normal testing.
For a domestic installation this information is usually given in the
electrical installation certificate.

HTH
--
Andy
  #5   Report Post  
Tom
 
Posts: n/a
Default


"Andy Wade" wrote in message
...

There's no prescribed scheme for circuit numbering, if that's what you
mean. The relevant requirements for identification a

Reg. 514-01-01 requires that the purpose of each item of switchgear and
controlgear is indicated, unless it's obvious.

514-01-02 requires wiring to be arranged so that it can be identified
for inspection, testing, repair or alteration, "as far as is reasonably
practicable."

514-03-xx to 514-07-xx are concerned with identification of conductors
by means of the usual (old or new) colours.

514-08-01 requires each protective device (fuse, MCB or RCD) to be
identified so that the circuit(s) protected "may be easily recognised."

514-09-01 requires documentation to be provided in the form of "a
legible diagram, chart or table" (or equivalent) listing or detailing
the following:
- type of each circuit, (locations of) points served, cable size & type,
- how indirect contact protection is provided (i.e. EEBADS),
- information necessary to identify each device for protection,
isolation and switching,
- details of any items vulnerable to normal testing.
For a domestic installation this information is usually given in the
electrical installation certificate.


Much obliged Andy for your comprehensive reply, it's exactly the information
I wanted. Since I'm retired I don't have access to IEE regs any more.
Best regards
Tom




Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Petrol in Diesel Engine MartinC UK diy 120 September 5th 05 10:41 PM
Replacing Consumer Units Martin Bosticky UK diy 3 January 28th 04 09:00 PM
Longish query - circuit breakers in consumer units David W.E. Roberts UK diy 9 November 9th 03 12:33 PM


All times are GMT +1. The time now is 12:57 AM.

Powered by vBulletin® Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Copyright ©2004-2025 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"