Having read all that has gone before, there still seem to be some
areas where the interpretation is unclear.

Do pipework bonds have to be both visible and accessible? If
simply accessible, do the same sort of conditions governing the
use of junction boxes apply (e.g. removable floorboards)? What
about under the bath? Is this influenced by whether or not tools
are needed for access, or does that only affect the need for
bonding?

When connecting to the various CPCs, presumably at existing
fittings, or junction boxes (can't quite see 4mm cable being
accommodated in a light fitting) is there a requirement for
identification somehow?

So far as I can see, it is quite OK for the underfloor bonding
and the ceiling bonding to be joined only by a common length of
pipe. Is this right?

Chris
--
Chris J Dixon Nottingham UK


Have dancing shoes, will ceilidh.
  #2   Report Post  
Andy Wade
 
Posts: n/a
Default

Chris J Dixon wrote:

Do pipework bonds have to be both visible


No.

and accessible?


Yes, unless soldered, welded or crimped, etc. Joints relying on screw
terminals should be accessible.

If simply accessible, do the same sort of conditions governing the
use of junction boxes apply (e.g. removable floorboards)? What about
under the bath?


The same rules apply as for live conductors, yes. "Accessible" isn't
defined in BS 7671 and is open to interpretation - anything is
accessible if you demolish enough of the building! Use common sense -
anything requiring destruction or inconvenience out of proportion to the
task of accessing the connection isn't compliant, IMO.

Is this influenced by whether or not tools are needed for access, or
does that only affect the need for bonding?


That surely affects neither.

When connecting to the various CPCs, presumably at existing
fittings, or junction boxes (can't quite see 4mm cable being
accommodated in a light fitting) is there a requirement for
identification somehow?


Identification of the bonding conductor as a protective colour is by
means of the green/yellow colour. The "safety electrical connection -
do not remove" label is only required, in this context, at connections
to extraneous-conductive-parts (i.e. non-electrical stuff like
pipework); it's not required on bonding connections to
exposed-conductive-parts or CPCs.

The 4mm^2 size is only needed if there's no mechanical protection. An
enclosed bonding conductor on to the CPC of a normal lighting or shaver
point circuit can be 1mm^2 (for circuit cables up to 1.5mm^2) - and of
course you are allowed to use the CPCs as the bonding, provided that
they remain "in close proximity to the [bathroom] location". So on the
lighting circuit it's often more practical to bond to the earth
terminal in the switch enclosure than in a luminaire.

So far as I can see, it is quite OK for the underfloor bonding
and the ceiling bonding to be joined only by a common length of
pipe. Is this right?


Debatable. Reg 547-03-04 allows conductive parts "of a permanent and
reliable nature" to be used as part of the bonding. If you think a
plumber could come along and replace the pipework in question with
plastic and not realise that any bonding would need to be patched then,
IMO, that regulation couldn't be applied. (IOW, if in doubt, bond
separately.)

HTH
--
Andy
  #3   Report Post  
 
Posts: n/a
Default


Andy Wade wrote:
Chris J Dixon wrote:

Do pipework bonds have to be both visible


No.

and accessible?


Yes, unless soldered, welded or crimped, etc. Joints relying on

screw
terminals should be accessible.

If simply accessible, do the same sort of conditions governing the
use of junction boxes apply (e.g. removable floorboards)? What

about
under the bath?


The same rules apply as for live conductors, yes. "Accessible" isn't


defined in BS 7671 and is open to interpretation - anything is
accessible if you demolish enough of the building! Use common sense

-
anything requiring destruction or inconvenience out of proportion to

the
task of accessing the connection isn't compliant, IMO.

Is this influenced by whether or not tools are needed for access,

or
does that only affect the need for bonding?


That surely affects neither.

When connecting to the various CPCs, presumably at existing
fittings, or junction boxes (can't quite see 4mm cable being
accommodated in a light fitting) is there a requirement for
identification somehow?


Identification of the bonding conductor as a protective colour is by
means of the green/yellow colour. The "safety electrical connection

-
do not remove" label is only required, in this context, at

connections
to extraneous-conductive-parts (i.e. non-electrical stuff like
pipework); it's not required on bonding connections to
exposed-conductive-parts or CPCs.

The 4mm^2 size is only needed if there's no mechanical protection.

An
enclosed bonding conductor on to the CPC of a normal lighting or

shaver
point circuit can be 1mm^2 (for circuit cables up to 1.5mm^2) - and

of
course you are allowed to use the CPCs as the bonding, provided that
they remain "in close proximity to the [bathroom] location". So on

the
lighting circuit it's often more practical to bond to the earth
terminal in the switch enclosure than in a luminaire.

So far as I can see, it is quite OK for the underfloor bonding
and the ceiling bonding to be joined only by a common length of
pipe. Is this right?


Debatable. Reg 547-03-04 allows conductive parts "of a permanent and


reliable nature" to be used as part of the bonding. If you think a
plumber could come along and replace the pipework in question with
plastic and not realise that any bonding would need to be patched

then,
IMO, that regulation couldn't be applied. (IOW, if in doubt, bond
separately.)

HTH
--
Andy


I am a bit sceptical about this accessibility issue. How many people
have mains and lighting connectors under their floorboards, I suspect
many of us, and how many have carpets, flooring etc. on top.
, so not really accessible. I have heard the arguments about copper
creep etc. but over the last 15 years of owning a house I havce never
had to rip anything up to find a fault with ring main/lighting circuit.
Am I just lucky?

  #4   Report Post  
Steven Briggs
 
Posts: n/a
Default

In message , Andy Wade
writes
Chris J Dixon wrote:
So far as I can see, it is quite OK for the underfloor bonding
and the ceiling bonding to be joined only by a common length of
pipe. Is this right?


Debatable. Reg 547-03-04 allows conductive parts "of a permanent and
reliable nature" to be used as part of the bonding. If you think a
plumber could come along and replace the pipework in question with
plastic and not realise that any bonding would need to be patched then,
IMO, that regulation couldn't be applied. (IOW, if in doubt, bond
separately.)

HTH


In a sense this is a slight extension of Fig 4d in the OSG - several
separate supplementary bonds taken back to the plumbing - which ties
everything together. So say your cold riser from underfloor up into the
loft _could_ be used as the path to link lighting circuit bonding to the
rest, subject to the proviso as above that its unlikely to be replaced
without Joe Plumber getting sufficient clue that the bonding was at both
ends of it. So if the earth clamps are well away from the vertical run,
then not a good idea, but if the clamps are say just above the ceiling
at the top, and at say floor level in the airing cupboard, then I
wouldn't see a problem.



--
Steve

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Earth bonding at Consumer Unit. chris French UK diy 20 September 23rd 04 02:56 PM
Further Earth Bonding questions [email protected] UK diy 34 September 15th 04 08:49 AM
Earth bonding in a bathroom EricP UK diy 4 September 13th 04 11:37 PM
Earth bonding cable? Jeff UK diy 7 February 7th 04 07:34 AM
Earth bonding queries Lobster UK diy 20 January 31st 04 08:54 AM


All times are GMT +1. The time now is 10:26 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"