My 10-year old boiler (conventional, open flue) has started smelling
of gas when it fires up (and recently set my CO detector off). The
flue and ventillation are all fine. I've checked the input and burner
pressures and gas rate - all spot on.

The flames don't look too good - very yellow and look too big. All the
burners etc. have been properly serviced recently and this hasn't
fixed the problem.

regards,
Alan
  #2   Report Post  
John
 
Posts: n/a
Default


"Alan" wrote in message
m...
My 10-year old boiler (conventional, open flue) has started smelling
of gas when it fires up (and recently set my CO detector off).


Make and model please?

The flue and ventillation are all fine. I've checked the input and burner
pressures and gas rate - all spot on.


On what basis do you state that the flue and the ventilation are all fine?


The flames don't look too good - very yellow and look too big. All the
burners etc. have been properly serviced recently and this hasn't
fixed the problem.


who carried out the service and what did it cover?



regards,
Alan



  #3   Report Post  
Bob Minchin
 
Posts: n/a
Default


Alan wrote in message ...
My 10-year old boiler (conventional, open flue) has started smelling
of gas when it fires up (and recently set my CO detector off). The
flue and ventillation are all fine. I've checked the input and burner
pressures and gas rate - all spot on.

The flames don't look too good - very yellow and look too big. All the
burners etc. have been properly serviced recently and this hasn't
fixed the problem.

regards,
Alan


Yellow flames indicate insufficient air flow either because the air inlet to
the burner is restricted in some way or the flue is not allowing all the
combustion gasses out. As your CO detector is triggering I would suspect the
latter.
Yellow flames means soot which could well helpblock the flue even more. Do
get this checked out before there are serious consequences.
In the short term you couldback off the gas flow until the flames turn blue
again. You will get less heat output but at least it should be safe.

Whoever checked the boiler over did not do a good job. Either get him back
or use another reputable one to inspect and report the first one to CORGI


  #4   Report Post  
raden
 
Posts: n/a
Default

In message , Alan
writes
My 10-year old boiler (conventional, open flue) has started smelling
of gas when it fires up (and recently set my CO detector off). The
flue and ventillation are all fine. I've checked the input and burner
pressures and gas rate - all spot on.

The flames don't look too good - very yellow


= incomplete combustion = Carbon monoxide



and look too big. All the
burners etc. have been properly serviced recently and this hasn't
fixed the problem.

Poor air supply? Blocked flue ? crud on the burners?

get it serviced properly

--
geoff
  #5   Report Post  
Alan
 
Posts: n/a
Default

"Alan" wrote in message
om...
My 10-year old boiler (conventional, open flue) has started smelling
of gas when it fires up (and recently set my CO detector off).


Make and model please?


Potterton Kingfisher MkII

The flue and ventillation are all fine. I've checked the input and burner
pressures and gas rate - all spot on.


On what basis do you state that the flue and the ventilation are all fine?


The flue has been smoke tested and draws well without leakage. Looking up
the flue, there are no blockages - you can clearly see the inside of the
terminal. The fins of the heat exchanger have been thoroughly cleaned and
again you can see clear through it.

The boiler is in a utility room on the ground floor with a suitable vent.
However, opening doors, windows etc. in the room or elsewhere in the house
has no effect. The vents on the boiler are clear and all the spacing
around the boiler is well in excess of the manufacturers specification.

The flames don't look too good - very yellow and look too big. All the
burners etc. have been properly serviced recently and this hasn't
fixed the problem.


who carried out the service and what did it cover?


A Corgi registered firm. Supposedly a full service. There are no deposits
on the burners. They also claim to have cleaned the insides of the burners
in accordance with the makers instructions. I've no reason to disbelieve
them.

I have no intention of tackling any of this work myself. What I want to avoid
is:

- paying another technician to do a full service, only for him to be "surprised"
when the problem still isn't cured.
- paying somebody to install a new air brick, then installing a new flue, only
for him to be "surprised" when the problem isn't cured.
- installing a new boiler simply because the problem can't be correctly
diagnosed.

On a related note, how should I expect a competent technician to set about
diagnosing this problem?

thank you for your responses,
Alan


  #6   Report Post  
Andy Hall
 
Posts: n/a
Default

On 12 Sep 2004 03:31:18 -0700, (Alan) wrote:



A Corgi registered firm. Supposedly a full service. There are no deposits
on the burners. They also claim to have cleaned the insides of the burners
in accordance with the makers instructions. I've no reason to disbelieve
them.

I have no intention of tackling any of this work myself. What I want to avoid
is:

- paying another technician to do a full service, only for him to be "surprised"
when the problem still isn't cured.
- paying somebody to install a new air brick, then installing a new flue, only
for him to be "surprised" when the problem isn't cured.
- installing a new boiler simply because the problem can't be correctly
diagnosed.

On a related note, how should I expect a competent technician to set about
diagnosing this problem?

thank you for your responses,
Alan


One obvious test would have been for the firm servicing the boiler to
have used a flue gas analyser to measure the CO , CO/CO2, and O2
levels.

This kind of analyser has a probe which goes into a special port in
the combustion chamber on some boilers or into the flue.
It would confirm the situation and give figures as to how bad it is.

Yellow flames are still a strong indicator that all is not well.

I don't believe that it is a mandatory requirement for a CORGI
engineer to have one of these, but considering that they start at
about £200, there is no reason that somebody servicing boilers should
not have one.

I would call back the firm that serviced the boiler, ask them to do
these measurements and provide the figures. Then contact the
manufacturer and ask them whether the results are satisfactory.

If they don't agree to this, then report them to CORGI and ask the
manufacturer for the name of an authorised engineer of theirs.





..andy

To email, substitute .nospam with .gl
  #7   Report Post  
Andy Wade
 
Posts: n/a
Default

raden wrote:

Poor air supply? Blocked flue ? crud on the burners?


Blocked lint arrester? (Should have been cleaned as part of the service
of course.)

--
Andy
  #8   Report Post  
Andrew Gabriel
 
Posts: n/a
Default

In article ,
Andy Hall writes:

I don't believe that it is a mandatory requirement for a CORGI
engineer to have one of these, but considering that they start at
about £200, there is no reason that somebody servicing boilers should
not have one.


It can't be mandatory -- I couldn't find a CORGI gas fitter who had one
when running through them in the Yellow Pages. I mentioned this to
Keston (having just fitted my Keston at the time), and the chap I was
speaking to agreed that they mostly didn't.

--
Andrew Gabriel
  #10   Report Post  
John
 
Posts: n/a
Default


"John" wrote in message
...

"Alan" wrote in message
m...
My 10-year old boiler (conventional, open flue) has started smelling
of gas when it fires up (and recently set my CO detector off).


Make and model please?

The flue and ventillation are all fine. I've checked the input and burner
pressures and gas rate - all spot on.


On what basis do you state that the flue and the ventilation are all fine?


The flames don't look too good - very yellow and look too big. All the
burners etc. have been properly serviced recently and this hasn't
fixed the problem.


who carried out the service and what did it cover?



regards,
Alan




Oh and do not use it until this problem has been addressed




  #11   Report Post  
John
 
Posts: n/a
Default


"Andy Hall" wrote in message
...
On 12 Sep 2004 17:10:46 GMT, (Andrew
Gabriel) wrote:

In article ,
Andy Hall writes:

I don't believe that it is a mandatory requirement for a CORGI
engineer to have one of these, but considering that they start at
about £200, there is no reason that somebody servicing boilers should
not have one.


It can't be mandatory -- I couldn't find a CORGI gas fitter who had one
when running through them in the Yellow Pages. I mentioned this to
Keston (having just fitted my Keston at the time), and the chap I was
speaking to agreed that they mostly didn't.


Somewhat concerning in a way.


I would agree with you but with reservations. There was very little point in
owning an analyser for the majority of domestic boiler work. The situation
is changing now since premix and modulating burners are becoming common.
The emphasis previously has been to ensure that any products of combustion
were correctly evacuated with no spillage or leakage from flue into room
space, and that combustion was basically correct as viewed by flame picture
and gas rate relying on the manufacturer making appliances to an agreed
standard in the\first place.
For commercial appliance service the situation is somewhat different and
personally I'd never go near a blown gas burner without a full spec analyser
its not possible to be certain that one of these is burning correctly any
other way - too little air = CO due to incomplete combustion, too much air
=CO due to flame chilling

Quite a lot of the boilers coming onto the market, especially those
with premix burners, seem to have use of a combustion analyser in the
setup procedure - typically that the emission composition should be
checked at low and high end and the gas rate adjusted to match the air
supply from the fan at the given burn rate.

BG seem to have them, although this seems to be mainly so that they
can just check the flue with the probe and pronounce the boiler OK
without taking it apart.


The BG analyser is often only a minimalistic job giving CO/CO2 ratio
readings and while satisfactory is not a full analyser
.
One day's visits and they've paid for the analyser comfortably.


Yup!



  #12   Report Post  
Andy Hall
 
Posts: n/a
Default

On Sun, 12 Sep 2004 19:58:03 +0000 (UTC), "John"
wrote:



I would agree with you but with reservations. There was very little point in
owning an analyser for the majority of domestic boiler work.



Technology was fairly simple and a manometer on the outlet of the gas
valve was good enough - right?



The situation
is changing now since premix and modulating burners are becoming common.
The emphasis previously has been to ensure that any products of combustion
were correctly evacuated with no spillage or leakage from flue into room
space, and that combustion was basically correct as viewed by flame picture
and gas rate relying on the manufacturer making appliances to an agreed
standard in the\first place.


Largely similar to one another, and one could also time the meter,
although I have never seen an installer do that.

For commercial appliance service the situation is somewhat different and
personally I'd never go near a blown gas burner without a full spec analyser
its not possible to be certain that one of these is burning correctly any
other way - too little air = CO due to incomplete combustion, too much air
=CO due to flame chilling


Of the two boilers that I shortlisted, the Keston Celsius could be set
up by checking the gas rate - the gas valve being preset. The
manufacturer does give combustion gas figures for later checks.

On the MAN Micromat, that I eventually installed, an analyser is
required for set up. Gas rate is checked and then top and bottom
combustion gas composition is measured - there being gas valve
adjustments for each. In practice, little change was needed, but at
the extremities of the settings, CO does rise.
There is no question of doing pressure tests at the gas valve. The
nipple is there, but the pressure is negative.




Quite a lot of the boilers coming onto the market, especially those
with premix burners, seem to have use of a combustion analyser in the
setup procedure - typically that the emission composition should be
checked at low and high end and the gas rate adjusted to match the air
supply from the fan at the given burn rate.

BG seem to have them, although this seems to be mainly so that they
can just check the flue with the probe and pronounce the boiler OK
without taking it apart.


The BG analyser is often only a minimalistic job giving CO/CO2 ratio
readings and while satisfactory is not a full analyser


Possibly beyond the comprehension of the average operative. They just
seem to write down the number and that's it.


.
One day's visits and they've paid for the analyser comfortably.


Yup!



..andy

To email, substitute .nospam with .gl
  #13   Report Post  
Ed Sirett
 
Posts: n/a
Default

On Sat, 11 Sep 2004 20:13:46 +0000, Bob Minchin wrote:


Alan wrote in message ...
My 10-year old boiler (conventional, open flue) has started smelling
of gas when it fires up (and recently set my CO detector off). The
flue and ventillation are all fine. I've checked the input and burner
pressures and gas rate - all spot on.

The flames don't look too good - very yellow and look too big. All the
burners etc. have been properly serviced recently and this hasn't
fixed the problem.

regards,
Alan


Yellow flames indicate insufficient air flow either because the air inlet to
the burner is restricted in some way or the flue is not allowing all the
combustion gasses out. As your CO detector is triggering I would suspect the
latter.
Yellow flames means soot which could well helpblock the flue even more. Do
get this checked out before there are serious consequences.
In the short term you could back off the gas flow until the flames turn blue
again. You will get less heat output but at least it should be safe.


Well the the correct approach is that you EITHER fix it properly: (blue
flames [1], gas pressure at correct setting, gas rate 90-105% of nominal,
flue clear and passes a flow test. ) OR you turn it off.


Whoever checked the boiler over did not do a good job. Either get him back
or use another reputable one to inspect and report the first one to

CORGI.

If the first guy is half decent he will be round pronto 'with tail down'
when you say you have yellow flames from a open flued appliance and the CO
alarm has gone off. There are no more lines of safety left, just
fortuitous ventilation, timing & luck.

TRANSCO will give you an opinion but will (nigh on certain) condemn the
appliance.
HTH

[1] If using a combustion analyser then I'd reckon on CO/CO2 0.003 say.
--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html


  #14   Report Post  
Ed Sirett
 
Posts: n/a
Default

On Sun, 12 Sep 2004 03:31:18 -0700, Alan wrote:

"Alan" wrote in message
. com...
My 10-year old boiler (conventional, open flue) has started smelling
of gas when it fires up (and recently set my CO detector off).


Make and model please?


Potterton Kingfisher MkII

The flue and ventillation are all fine. I've checked the input and burner
pressures and gas rate - all spot on.


On what basis do you state that the flue and the ventilation are all fine?


The flue has been smoke tested and draws well without leakage. Looking up
the flue, there are no blockages - you can clearly see the inside of the
terminal. The fins of the heat exchanger have been thoroughly cleaned and
again you can see clear through it.

The boiler is in a utility room on the ground floor with a suitable vent.
However, opening doors, windows etc. in the room or elsewhere in the house
has no effect. The vents on the boiler are clear and all the spacing
around the boiler is well in excess of the manufacturers specification.

The flames don't look too good - very yellow and look too big. All the
burners etc. have been properly serviced recently and this hasn't
fixed the problem.


who carried out the service and what did it cover?


A Corgi registered firm. Supposedly a full service. There are no deposits
on the burners. They also claim to have cleaned the insides of the burners
in accordance with the makers instructions. I've no reason to disbelieve
them.

I have no intention of tackling any of this work myself. What I want to avoid
is:

- paying another technician to do a full service, only for him to be "surprised"
when the problem still isn't cured.
- paying somebody to install a new air brick, then installing a new flue, only
for him to be "surprised" when the problem isn't cured.
- installing a new boiler simply because the problem can't be correctly
diagnosed.

On a related note, how should I expect a competent technician to set about
diagnosing this problem?

Since the pressure and gas rate are correct, the flue clear and opening a
door make no change the problem MUST lie between the injector(s) and the
burners. There are often gauzes in the mixing tube which can get blocked
with very fine dust.

More surprising is the CO alarm going off this implies the products of
cumbustion are not being correctly drawn into the flue which is odd since
it is apparently clear.

Anyway fixing (or even replacing) the burner should be the first approach
but the alarm makes me think there is another problem to be found.

--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html


  #15   Report Post  
Badger
 
Posts: n/a
Default



Alan wrote:

The flue and ventillation are all fine. I've checked the input and burner
pressures and gas rate - all spot on.



On what basis do you state that the flue and the ventilation are all fine?



The flue has been smoke tested and draws well without leakage. Looking up
the flue, there are no blockages - you can clearly see the inside of the
terminal. The fins of the heat exchanger have been thoroughly cleaned and
again you can see clear through it.

The boiler is in a utility room on the ground floor with a suitable vent.
However, opening doors, windows etc. in the room or elsewhere in the house
has no effect. The vents on the boiler are clear and all the spacing
around the boiler is well in excess of the manufacturers specification.


The flames don't look too good - very yellow and look too big. All the
burners etc. have been properly serviced recently and this hasn't
fixed the problem.



who carried out the service and what did it cover?



A Corgi registered firm. Supposedly a full service. There are no deposits
on the burners. They also claim to have cleaned the insides of the burners
in accordance with the makers instructions. I've no reason to disbelieve
them.

I have no intention of tackling any of this work myself. What I want to avoid
is:

- paying another technician to do a full service, only for him to be "surprised"
when the problem still isn't cured.
- paying somebody to install a new air brick, then installing a new flue, only
for him to be "surprised" when the problem isn't cured.
- installing a new boiler simply because the problem can't be correctly
diagnosed.

On a related note, how should I expect a competent technician to set about
diagnosing this problem?

thank you for your responses,
Alan


Check the inlet side of the flue isn't blocked by leaves, birds nests,
vermin etc, anyone can get the burner to burn clean with the cover off,
but put it back on and you rely on the inlet. British gas never checked
mine and it went that way, pulled the flue from the wall and the inlet
was clogged with leaves....


  #16   Report Post  
Andrew Gabriel
 
Posts: n/a
Default

In article ,
Andy Hall writes:

Largely similar to one another, and one could also time the meter,
although I have never seen an installer do that.


Oh really? That's what I ended up doing with my Keston.
It was supposed to be factory set, but it was miles out.
At the top end, it was (IIRC) 10% too low -- they only allow
+-5%. At the bottom end (which the instructions didn't even
suggest checking), it was about 4kW instead of 7.5kW, which
explained why the gas ignition was travelling back up into
the premix area and making a sound like a 32 foot organ pipe.
There is only one mixture adjustment, but fortunately it
seems to have a much more dramatic effect at the bottom end
than the top end, so it was possible to bring them both in
much nearer to the rated values, although the top hit the
correct value whilst the bottom was still a bit under.

Of the two boilers that I shortlisted, the Keston Celsius could be set
up by checking the gas rate - the gas valve being preset. The
manufacturer does give combustion gas figures for later checks.

On the MAN Micromat, that I eventually installed, an analyser is
required for set up. Gas rate is checked and then top and bottom
combustion gas composition is measured - there being gas valve
adjustments for each. In practice, little change was needed, but at
the extremities of the settings, CO does rise.
There is no question of doing pressure tests at the gas valve. The
nipple is there, but the pressure is negative.


That is one of the checks on the Keston. I says something like
it should be at least -1.25" -- it's not at all clear which side
of the -1.25" is the 'OK' side, and it was off (can't recall which
way). Having adjusted the power input via meter timing, fortunately
it ended up being exactly -1.25" so I didn't need to worry which
way was 'OK'.

--
Andrew Gabriel
  #17   Report Post  
Andy Hall
 
Posts: n/a
Default

On 12 Sep 2004 21:52:19 GMT, (Andrew
Gabriel) wrote:

In article ,
Andy Hall writes:

Largely similar to one another, and one could also time the meter,
although I have never seen an installer do that.


Oh really? That's what I ended up doing with my Keston.


That's 'cos you read the instructions.... :-)


It was supposed to be factory set, but it was miles out.
At the top end, it was (IIRC) 10% too low -- they only allow
+-5%. At the bottom end (which the instructions didn't even
suggest checking), it was about 4kW instead of 7.5kW, which
explained why the gas ignition was travelling back up into
the premix area and making a sound like a 32 foot organ pipe.
There is only one mixture adjustment, but fortunately it
seems to have a much more dramatic effect at the bottom end
than the top end, so it was possible to bring them both in
much nearer to the rated values, although the top hit the
correct value whilst the bottom was still a bit under.


That was my experience as well. The bottom end was more critical
than the top and there was a certain amount of iteration.



Of the two boilers that I shortlisted, the Keston Celsius could be set
up by checking the gas rate - the gas valve being preset. The
manufacturer does give combustion gas figures for later checks.

On the MAN Micromat, that I eventually installed, an analyser is
required for set up. Gas rate is checked and then top and bottom
combustion gas composition is measured - there being gas valve
adjustments for each. In practice, little change was needed, but at
the extremities of the settings, CO does rise.
There is no question of doing pressure tests at the gas valve. The
nipple is there, but the pressure is negative.


That is one of the checks on the Keston. I says something like
it should be at least -1.25" -- it's not at all clear which side
of the -1.25" is the 'OK' side, and it was off (can't recall which
way). Having adjusted the power input via meter timing, fortunately
it ended up being exactly -1.25" so I didn't need to worry which
way was 'OK'.



Hmm curious.... Presumably that is at full burn rate?


..andy

To email, substitute .nospam with .gl
  #18   Report Post  
Andrew Gabriel
 
Posts: n/a
Default

That is one of the checks on the Keston. I says something like
it should be at least -1.25" -- it's not at all clear which side
of the -1.25" is the 'OK' side, and it was off (can't recall which
way). Having adjusted the power input via meter timing, fortunately
it ended up being exactly -1.25" so I didn't need to worry which
way was 'OK'.


Hmm curious.... Presumably that is at full burn rate?


Yes. As the burn rate reduces, pressure moves towards zero.
The instructions don't give values other than at full burn
rate though. (This is all from memory -- I don't have the
instructions here to check.)

--
Andrew Gabriel
  #19   Report Post  
Ed Sirett
 
Posts: n/a
Default

On Sun, 12 Sep 2004 20:50:39 +0000, Badger wrote:



Alan wrote:

The flue and ventillation are all fine. I've checked the input and burner
pressures and gas rate - all spot on.



On what basis do you state that the flue and the ventilation are all fine?



The flue has been smoke tested and draws well without leakage. Looking up
the flue, there are no blockages - you can clearly see the inside of the
terminal. The fins of the heat exchanger have been thoroughly cleaned and
again you can see clear through it.

The boiler is in a utility room on the ground floor with a suitable vent.
However, opening doors, windows etc. in the room or elsewhere in the house
has no effect. The vents on the boiler are clear and all the spacing
around the boiler is well in excess of the manufacturers specification.


The flames don't look too good - very yellow and look too big. All the
burners etc. have been properly serviced recently and this hasn't
fixed the problem.



who carried out the service and what did it cover?



A Corgi registered firm. Supposedly a full service. There are no deposits
on the burners. They also claim to have cleaned the insides of the burners
in accordance with the makers instructions. I've no reason to disbelieve
them.

I have no intention of tackling any of this work myself. What I want to avoid
is:

- paying another technician to do a full service, only for him to be "surprised"
when the problem still isn't cured.
- paying somebody to install a new air brick, then installing a new flue, only
for him to be "surprised" when the problem isn't cured.
- installing a new boiler simply because the problem can't be correctly
diagnosed.

On a related note, how should I expect a competent technician to set about
diagnosing this problem?

thank you for your responses,
Alan


Check the inlet side of the flue isn't blocked by leaves, birds nests,
vermin etc, anyone can get the burner to burn clean with the cover off,
but put it back on and you rely on the inlet. British gas never checked
mine and it went that way, pulled the flue from the wall and the inlet
was clogged with leaves....


This is a conventional flue not a balanced or fan assisted flue/duct.


--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html


  #20   Report Post  
Alan
 
Posts: n/a
Default

"John" wrote in message ...
"Alan" wrote in message
m...
My 10-year old boiler (conventional, open flue) has started smelling
of gas when it fires up (and recently set my CO detector off).


Make and model please?

The flue and ventillation are all fine. I've checked the input and burner
pressures and gas rate - all spot on.


On what basis do you state that the flue and the ventilation are all fine?


The flames don't look too good - very yellow and look too big. All the
burners etc. have been properly serviced recently and this hasn't
fixed the problem.


who carried out the service and what did it cover?



regards,
Alan


Well, the original technician who serviced the boiler, then condemed it
reckoned it needed a new burner assembly - "but the boiler was obsolete
so probably wasn't worth repairing". I tried to get some other opinions
- one plumber never returned my call, another said he could fit me in
3 days later, but he never turned up...

In the meantime, I found the service manual on-line, made myself a
manometer with a bit of plastic tube, dis-assembled the boiler to
check the lint arrestor and injector (all fine), did some smoke
tests with some smoldering kitchen roll and found the
heat exchanger still quite sooted (I know I said it was clear, but
I am no expert and the bloke who cleaned it a few days before was...)

Spent a while properly cleaning the heat exchanger, then tested for
leaks and inlet & burner pressure with the manometer and rechecked
gas usage - all seemed fine, the yellow flames have gone, the CO
detector stays off and the bad smell gone. So I peeled the
"Immediately Dangerous" sticker of my boiler.

So if you hear of a large explosion in the Manchester area...

regards,
Alan
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Boiler kettling? David Hearn UK diy 5 January 1st 04 07:47 PM
Replacing a boiler David Hearn UK diy 38 November 12th 03 11:10 PM
New Combi boiler GB UK diy 7 September 7th 03 11:34 PM


All times are GMT +1. The time now is 02:24 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"