Default MCB discrimination and size?

I've just run 6mm SWA from the consumer unit in the house to a
workshop some 25m away. The workshop has 4 circuits - 2 lighting and 2
smallish ringmains, run in 2.5mm. The SWA from the house will feed a 4
way CU in the workshop via a separate RCD - my questions a

1. What size MCB needs to be fitted to the 6mm SWA in the house CU -
32a or 40a?
2. What size MCB needs to be fitted in the workshop's CU - 32a for the
ring and 6a for the lights?
3. How do I avoid the lack of discrimination caused by running 2 MCB's
in line - ideas include i, using type C's in the workshop or ii,
discrimination will be provided by having 40a MCB in the house and 32a
in the workshop or iii fitting traditional fuses in the workshop,
rather than MCB's

Am I on the right wavelength? Any guidance/advice/tips or suggestions
wll be lapped up... thanks everyone for a great NG
cheers, Patrick
  #2   Report Post  
BigWallop
 
Posts: n/a
Default MCB discrimination and size?


"Patrick Olner" wrote in message
om...
I've just run 6mm SWA from the consumer unit in the house to a
workshop some 25m away. The workshop has 4 circuits - 2 lighting and 2
smallish ringmains, run in 2.5mm. The SWA from the house will feed a 4
way CU in the workshop via a separate RCD - my questions a


What size is the armoured cable ? An RCD only gives protection if an earth
fault occurs, so make sure you have a good earth point at the workshop and
don't rely on the armoured cable taking the whole brunt. The MCB you use in
the house is to protect the supply cable to the workshop from melting and
not just to give you enough load for the workshop.


1. What size MCB needs to be fitted to the 6mm SWA in the house CU -
32a or 40a?


Depends on what you intend to use in the workshop.

2. What size MCB needs to be fitted in the workshop's CU - 32a for the
ring and 6a for the lights?


This would be the norm' for a standard installation, but it depends on what
your supply cable can handle in terms of maximum load at that length.

3. How do I avoid the lack of discrimination caused by running 2 MCB's
in line - ideas include i, using type C's in the workshop or ii,
discrimination will be provided by having 40a MCB in the house and 32a
in the workshop or iii fitting traditional fuses in the workshop,
rather than MCB's

Am I on the right wavelength? Any guidance/advice/tips or suggestions
wll be lapped up... thanks everyone for a great NG
cheers, Patrick


If you can, try taking the workshop supply from a separate single way metal
clad consumer unit in the house. This doesn't have to have any RCD if you
have one installed in the workshop with a good earthing point and can be
used with a hard wired fuse to reduce any erroneous tripping. It gives more
protection from faults in the workshop back to the house.

Get some 16 mm Double Insulted Cable and Two Terminal Blocks from your
wholesaler. Take the fuse out from the mains supply unit (the bit before
the meter) and then disconnect the supply cables from the meter at the mains
switch of the existing consumer unit and put them in the big terminal
blocks. Cut the double insulated to the lengths you need to go to both the
existing fuse box and your new single way unit. Connect them all up to the
terminal blocks and you then have two separate supplies, one for the house
and one for the workshop, but all running through the same meter. Believe
me, it stops any conflicts.


---
www.basecuritysystems.no-ip.com
Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.504 / Virus Database: 302 - Release Date: 24/07/03


  #3   Report Post  
Dave Liquorice
 
Posts: n/a
Default MCB discrimination and size?

On 27 Jul 2003 12:38:25 -0700, Patrick Olner wrote:

1. What size MCB needs to be fitted to the 6mm SWA in the house CU -
32a or 40a?


You also need and RCD at this point.

2. What size MCB needs to be fitted in the workshop's CU - 32a for
the ring and 6a for the lights?


That is what I would fit.

3. How do I avoid the lack of discrimination caused by running 2
MCB's in line - ideas include i, using type C's in the workshop


Type C are the "slower" ones so that really needs to be at the house
end so the faster type B has a (slim) chance to operate before the
type C.

ii, discrimination will be provided by having 40a MCB in the house
and 32a in the workshop or


TBH there is not that much difference between a 40 and 32A trip.
Remember they are designed to carry that current indefinitely and will
take a significant amount of time to trip at double their rating.

iii fitting traditional fuses in the workshop, rather than MCB's


Fuses are even slower. I was sort of thinking that with an RCD in the
house you don't need overload protection at that point but I guess
that it still is conceivable that a LN fault could occur causing
overload of the SWA. So fuse it at the house end and have MCBs in the
workshop CU. It may even be useful to fit another RCD in the workshop
CU feeding the rings. Indeed any socket that may have an appliance
plugged in that is used outside must have RCD protection. Be aware of
the problems of cascading RCDs...

--
Cheers
Dave. pam is missing e-mail



  #4   Report Post  
Toby
 
Posts: n/a
Default MCB discrimination and size?

BigWallop wrote:
Get some 16 mm Double Insulted Cable ...

You're fat and you've gone grey.
I'll lend you my insulting tape if you like.

Toby.



  #5   Report Post  
Andrew Gabriel
 
Posts: n/a
Default MCB discrimination and size?

In article ,
(Patrick Olner) writes:
I've just run 6mm SWA from the consumer unit in the house to a
workshop some 25m away. The workshop has 4 circuits - 2 lighting and 2
smallish ringmains, run in 2.5mm. The SWA from the house will feed a 4
way CU in the workshop via a separate RCD - my questions a

1. What size MCB needs to be fitted to the 6mm SWA in the house CU -
32a or 40a?


You can use 40A with 6mm cable. As you also have an RCD at
the house end, you can ignore earth fault loop impedance.
At 40A design load, your 25m of 6mm cable has used up 80%
of the permitted voltage drop -- this probably doesn't
matter as the length of circuits in the workshop won't be
large, and your design load probably isn't really anywhere
near 40A (nearly 10kW).

2. What size MCB needs to be fitted in the workshop's CU - 32a for the
ring and 6a for the lights?


Yes.

3. How do I avoid the lack of discrimination caused by running 2 MCB's
in line - ideas include i, using type C's in the workshop or ii,
discrimination will be provided by having 40a MCB in the house and 32a
in the workshop or iii fitting traditional fuses in the workshop,
rather than MCB's


You can't avoid the lack of discrimination caused by running 2 MCB's
in line, except by not doing so. You could use a 40A BS1361 cartridge
fuse at the house end, or you could ignore the problem -- how often
have you had a ring circuit short out live to neutral (which is what
will cause this problem) verses having an earth fault in an appliance
(which will have much the same effect, tripping the RCD in the house)?
I would suggest to you that the RCD represents a much more likely
reason for losing all the power to the workshop than a live-neutral
short circuit on a ring circuit, so I wouldn't worry about lack of
discrimination.

I would ask if you really need two ring circuits -- that's more than
7kW load, and a damn hot workshop;-) I would have thought one would do
or if you want more than one circuit, what about two 20A radial ones?
Still won't help discrimination issue much though.

You might also want to make the workshop a TT system with its own
earth rod, rather than exporting the house earth. If you do this,
you still earth the SWA armour at the house end, but you make sure
it isn't connected to anything at the workshop end, indeed make sure
it's insulated and not exposed. You have to have an RCD if you do
this.

If the workshop contains machinary which might cause a danger if all
the power is suddenly cut and you lost lighting whilst machinary is
still in motion under its momentum, I would look at schemes which
didn't compromise the lighting in the event of an earth fault. Please
say if this is the case, and I (or someone else) will suggest some
suitable alternative schemes.

--
Andrew Gabriel


  #6   Report Post  
Patrick Olner
 
Posts: n/a
Default MCB discrimination and size?

- thanks very much to one and all - yet again this fantastic resource
and the absolute stars within it have saved the day!

- Andrew, no problem with machines and lighting etc - the workshop
will be half darkroom and half craft area, so it does need to supply
some pretty hefty items - print processor, water heater, etc, as well
as the more usual run o'the mill stuff.

With regard to workshop having it's own earth rod - is this strongly
advised? I also should have mentioned that that the fuse supplying the
workshop is on the RCD side of a split way consumer unit ... so do I
really need RCD protection with the workshop too? Should I decide to
do so .. would the 40a cartridge fuse in the house consumer unit be OK
being fitted on the RCD side of the house CU?

cheers
patrick
  #7   Report Post  
Andrew Gabriel
 
Posts: n/a
Default MCB discrimination and size?

In article ,
(Patrick Olner) writes:
- thanks very much to one and all - yet again this fantastic resource
and the absolute stars within it have saved the day!

- Andrew, no problem with machines and lighting etc - the workshop
will be half darkroom and half craft area, so it does need to supply
some pretty hefty items - print processor, water heater, etc, as well
as the more usual run o'the mill stuff.


OK, this might be more than I imagined. Can you estimate the power
(or better, the VA rating if you know) of all the devices, and
estimate the total maximum you might operate at once. For the
water heater, please state its type, and in the case of a stored
water heater, its water capacity.

With regard to workshop having it's own earth rod - is this strongly
advised?


It's theoretically safer, but I don't know if many professional
electricians would bother. If the workshop building includes metal
structural members which can be touched from outside, I personally
would certainly do this (metal greenhouse is a good example of such).
What type of earthing system is your house supply? (See
http://www.diyfaq.org.uk/electrical.html#system for descriptions.)

I also should have mentioned that that the fuse supplying the
workshop is on the RCD side of a split way consumer unit ... so do I
really need RCD protection with the workshop too?


No.
However, it's not a good idea to share indoor and external circuits
on the same RCD as it's too easy to trip them (mallicious or water
ingress) and lose power in the house. It is however not against the
regs to do this. You should have a double pole isolating switch for
the external circuit -- a dedicated RCD operating on both poles can
double up to perform this function.

Should I decide to
do so .. would the 40a cartridge fuse in the house consumer unit be OK
being fitted on the RCD side of the house CU?


I should also have asked what the value of your main fuse is. If it's
only 60A for example, that's not enough to provide safe discrimination
against a 40A fuse. If it's 100A, then that's OK. Also, you need to
do a load calculation to ensure you aren't going to be overloading
your house supply.

--
Andrew Gabriel
  #8   Report Post  
Patrick Olner
 
Posts: n/a
Default MCB discrimination and size?

(Andrew Gabriel) wrote in message ...
In article ,
(Patrick Olner) writes:
- thanks very much to one and all - yet again this fantastic resource
and the absolute stars within it have saved the day!

- Andrew, no problem with machines and lighting etc - the workshop
will be half darkroom and half craft area, so it does need to supply
some pretty hefty items - print processor, water heater, etc, as well
as the more usual run o'the mill stuff.


OK, this might be more than I imagined. Can you estimate the power
(or better, the VA rating if you know) of all the devices, and
estimate the total maximum you might operate at once. For the
water heater, please state its type, and in the case of a stored
water heater, its water capacity.

With regard to workshop having it's own earth rod - is this strongly
advised?


It's theoretically safer, but I don't know if many professional
electricians would bother. If the workshop building includes metal
structural members which can be touched from outside, I personally
would certainly do this (metal greenhouse is a good example of such).
What type of earthing system is your house supply? (See
http://www.diyfaq.org.uk/electrical.html#system for descriptions.)

I also should have mentioned that that the fuse supplying the
workshop is on the RCD side of a split way consumer unit ... so do I
really need RCD protection with the workshop too?


No.
However, it's not a good idea to share indoor and external circuits
on the same RCD as it's too easy to trip them (mallicious or water
ingress) and lose power in the house. It is however not against the
regs to do this. You should have a double pole isolating switch for
the external circuit -- a dedicated RCD operating on both poles can
double up to perform this function.

Should I decide to
do so .. would the 40a cartridge fuse in the house consumer unit be OK
being fitted on the RCD side of the house CU?


I should also have asked what the value of your main fuse is. If it's
only 60A for example, that's not enough to provide safe discrimination
against a 40A fuse. If it's 100A, then that's OK. Also, you need to
do a load calculation to ensure you aren't going to be overloading
your house supply.


Andrew .. thank you so much for your guidance it truly is invaluable
... - yes we only have 60A main fuse, how much of a problem do you
think this will and how the hell would I go about changing it? - the
main items that will run at once are
1. Water heater, not sure of it's type - a white box about
16"x16"x12", 2kw, it has a 10 written on a small silver label with
it's voltage, wattage, etc which may or may not be 10 litres, sorry to
be so vague;
2. Print processor, 2.7kw;
3. Ventilation, 70W
4. Enlarger, 250w
5. Film dryer, 500w
6. Depending on the South Wales winter - possibly a heater too, 2-3kw
6. Maybe one or two electric tools such as circular saw, sander,
planer etc
7. Outside lighting, 3x150w halogen PIR security lights
oh .. and the obligatory kettle!

Also Andrew, how do I do a load calculation?
You are the almighty and I am truly humbled - best wishes, Patrick
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT +1. The time now is 11:33 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"