On 03/10/2019 13:51, John Rumm wrote:
On 03/10/2019 11:53, Chris B wrote:
I have had 3 extra lights and a fan added to a single lighting circuit.

The base circuit was installed completely new less than two years ago
as part of a CU change and came with anĀ* Electrical Installation
Certificate.

The minor works certificate shows that the extra lights and fan have
had the following effect on the particular circuit characteristics

Circuit Impedance R1+R2 reduced to 0.77 Ohms from 1.31
Earth Fault Loop Impedance reduced to 0.98 from 1.62
RCD Operation Time measured at 24 ms (was 33 ms @I and 16ms @5I)


I would not worry about the RCD time since its a pass in either case.

These changes look quite significant to me but I would like expert
opinion are they

1) Typical for what might be expected following this sort of a mod.


If measuring like for like, then no.

2) Typical variation between test meters as two different electricians
were involved.


Possibly.

3) Some combination of 1&2


4) A fault in the installation which requires further investigation


Unlikely IMHO

5) Some other issue.


Its possible that the original measurements were made at the furthest
lighting point on the circuit, while the new ones were made either at
the newly installed positions, or at a different "furthest" point on the
circuit[1]. If the new readings were made closer to the CU, then that
might account for the difference.

It could also be the original readings were artificially high for some
reason, e.g. test lead resistance not accounted for, or meter
calibration difference.

Less likely, but possible, if could also be there was a lose connection
that was corrected during the new installation work.


As its over two months since the work was done and I have only just
managed to extract the certificate I was wondering if it is possible
that testing was never carried out and they might just be random numbers
that happen to be compliant?




[1] Remember that lighting circuits are typically radials, and might
have any number of branches rather than being one sequential run of
cable from each light to the next. So you would need a table of the
R1+R2 or ELI at all the lighting positions to get the full picture.





--
Chris B (News)
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Changes to electric circuit characteristics

On 03/10/2019 15:09, Chris B wrote:
On 03/10/2019 13:51, John Rumm wrote:
On 03/10/2019 11:53, Chris B wrote:
I have had 3 extra lights and a fan added to a single lighting circuit.

The base circuit was installed completely new less than two years ago
as part of a CU change and came with anĀ* Electrical Installation
Certificate.

The minor works certificate shows that the extra lights and fan have
had the following effect on the particular circuit characteristics

Circuit Impedance R1+R2 reduced to 0.77 Ohms from 1.31
Earth Fault Loop Impedance reduced to 0.98 from 1.62
RCD Operation Time measured at 24 ms (was 33 ms @I and 16ms @5I)


I would not worry about the RCD time since its a pass in either case.

These changes look quite significant to me but I would like expert
opinion are they

1) Typical for what might be expected following this sort of a mod.


If measuring like for like, then no.

2) Typical variation between test meters as two different
electricians were involved.


Possibly.

3) Some combination of 1&2


4) A fault in the installation which requires further investigation


Unlikely IMHO

5) Some other issue.


Its possible that the original measurements were made at the furthest
lighting point on the circuit, while the new ones were made either at
the newly installed positions, or at a different "furthest" point on
the circuit[1]. If the new readings were made closer to the CU, then
that might account for the difference.

It could also be the original readings were artificially high for some
reason, e.g. test lead resistance not accounted for, or meter
calibration difference.

Less likely, but possible, if could also be there was a lose
connection that was corrected during the new installation work.


As its over two months since the work was done and I have only just
managed to extract the certificate I was wondering if it is possible
that testing was never carried out and they might just be random numbers
that happen to be compliant?


Could be - Why not measure them yourself and find out?


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Machining characteristics of plastic pipe Stealth Pilot Metalworking 2 June 9th 09 03:40 PM
Machining characteristics of plastic pipe Stealth Pilot Metalworking 0 June 9th 09 11:20 AM
Machining characteristics of plastic pipe Karl Townsend Metalworking 1 June 9th 09 08:14 AM
Strange motor characteristics in new Ryobi electric brushcutter [email protected] UK diy 4 July 1st 08 06:56 PM
Gradually, the changes in uniform needed to closely match with theform and function of the doctor. This drove significant changes to the nursinguniforms in the way of functionality or practicality. Additional colors wereintroduced to allow for more c [email protected] Home Repair 0 April 23rd 08 07:09 AM


All times are GMT +1. The time now is 12:49 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"