Default Confirm switch wiring, please

Light switch 2 gang both are 2-way.
The stair switch works ok at the top of stairs, at bottom stairs it only
works dependent on the position of the upstair switch.
I opened up and there appears to be a loose wire, can someone please
confirm that the yellow wire is needing reconnected as per image.

https://imgur.com/a/pnUTTWQ
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,110
Default Confirm switch wiring, please

On Sun, 27 Jan 2019 10:36:11 +0000, ss wrote:

Light switch 2 gang both are 2-way.
The stair switch works ok at the top of stairs, at bottom stairs it only
works dependent on the position of the upstair switch.
I opened up and there appears to be a loose wire, can someone please
confirm that the yellow wire is needing reconnected as per image.

https://imgur.com/a/pnUTTWQ


No I cannot anyway! Try prayer, or an oija board.

https://circuitdigest.com/sites/defa...ire-method.png

AB



  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Confirm switch wiring, please

On 27/01/2019 10:46, Archibald Tarquin Blenkinsopp wrote:
On Sun, 27 Jan 2019 10:36:11 +0000, ss wrote:

Light switch 2 gang both are 2-way.
The stair switch works ok at the top of stairs, at bottom stairs it only
works dependent on the position of the upstair switch.
I opened up and there appears to be a loose wire, can someone please
confirm that the yellow wire is needing reconnected as per image.

https://imgur.com/a/pnUTTWQ


No I cannot anyway! Try prayer, or an oija board.

https://circuitdigest.com/sites/defa...ire-method.png


That is a deprecated way of wiring a two way switched system, and also
as evidenced from the use of 3&E in the OPs photo, not what is being
used here.

The more appropriate diagram would be the second one in this section:

http://wiki.diyfaq.org.uk/index.php/...tching_circuit




--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,110
Default Confirm switch wiring, please

On Sun, 27 Jan 2019 14:15:40 +0000, John Rumm
wrote:

On 27/01/2019 10:46, Archibald Tarquin Blenkinsopp wrote:
On Sun, 27 Jan 2019 10:36:11 +0000, ss wrote:

Light switch 2 gang both are 2-way.
The stair switch works ok at the top of stairs, at bottom stairs it only
works dependent on the position of the upstair switch.
I opened up and there appears to be a loose wire, can someone please
confirm that the yellow wire is needing reconnected as per image.

https://imgur.com/a/pnUTTWQ


No I cannot anyway! Try prayer, or an oija board.

https://circuitdigest.com/sites/defa...ire-method.png


That is a deprecated way of wiring a two way switched system, and also
as evidenced from the use of 3&E in the OPs photo, not what is being
used here.

The more appropriate diagram would be the second one in this section:

http://wiki.diyfaq.org.uk/index.php/...tching_circuit


Hard to say how it is wired, I have never seen yellow used in a
lighting circuit, I can only assume the cable was left over after some
ancient three phase control project.

The piccy strongly suggests further investigation is needed, not just
stick the wire in what looks like an appropriate hole and screw it up.

DIY or professional, there should be no uncertainties with electrical
power.

AB

  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 5,061
Default Confirm switch wiring, please

In article ,
Archibald Tarquin Blenkinsopp wrote:
On Sun, 27 Jan 2019 14:15:40 +0000, John Rumm
wrote:


On 27/01/2019 10:46, Archibald Tarquin Blenkinsopp wrote:
On Sun, 27 Jan 2019 10:36:11 +0000, ss wrote:

Light switch 2 gang both are 2-way.
The stair switch works ok at the top of stairs, at bottom stairs it only
works dependent on the position of the upstair switch.
I opened up and there appears to be a loose wire, can someone please
confirm that the yellow wire is needing reconnected as per image.

https://imgur.com/a/pnUTTWQ

No I cannot anyway! Try prayer, or an oija board.

https://circuitdigest.com/sites/defa...ire-method.png


That is a deprecated way of wiring a two way switched system, and also
as evidenced from the use of 3&E in the OPs photo, not what is being
used here.

The more appropriate diagram would be the second one in this section:

http://wiki.diyfaq.org.uk/index.php/...tching_circuit


Hard to say how it is wired, I have never seen yellow used in a
lighting circuit, I can only assume the cable was left over after some
ancient three phase control project.


the three core (+ECC) cable I bought in about 1980 (for 2way switching of
lights) certainly had yellow as one of its cores. Blue & white for the
other two.

--
from KT24 in Surrey, England
"I'd rather die of exhaustion than die of boredom" Thomas Carlyle


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Confirm switch wiring, please

In article ,
charles wrote:
the three core (+ECC) cable I bought in about 1980 (for 2way switching of
lights) certainly had yellow as one of its cores. Blue & white for the
other two.


Older cable was usually red blue yellow. The old three phase colours.

--
*Half the people in the world are below average.

Dave Plowman London SW
To e-mail, change noise into sound.
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 49
Default Confirm switch wiring, please



"Archibald Tarquin Blenkinsopp" wrote in
message ...
On Sun, 27 Jan 2019 14:15:40 +0000, John Rumm
wrote:

On 27/01/2019 10:46, Archibald Tarquin Blenkinsopp wrote:
On Sun, 27 Jan 2019 10:36:11 +0000, ss wrote:

Light switch 2 gang both are 2-way.
The stair switch works ok at the top of stairs, at bottom stairs it
only
works dependent on the position of the upstair switch.
I opened up and there appears to be a loose wire, can someone please
confirm that the yellow wire is needing reconnected as per image.

https://imgur.com/a/pnUTTWQ

No I cannot anyway! Try prayer, or an oija board.

https://circuitdigest.com/sites/defa...ire-method.png


That is a deprecated way of wiring a two way switched system, and also
as evidenced from the use of 3&E in the OPs photo, not what is being
used here.

The more appropriate diagram would be the second one in this section:

http://wiki.diyfaq.org.uk/index.php/...tching_circuit


Hard to say how it is wired,


But it is clear that 6 wires are involved, so it can't be your config.

I have never seen yellow used in a
lighting circuit, I can only assume the cable was left over after some
ancient three phase control project.

The piccy strongly suggests further investigation is needed, not just
stick the wire in what looks like an appropriate hole and screw it up.


Not when there are 6 wires involved, a common config used in that situation.

DIY or professional, there should be no uncertainties with electrical
power.


There isnt when there are clearly 6 wires involved and one of them
has clearly come adrift from where it would be in a 6 wire config.

  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,110
Default Confirm switch wiring, please

On Mon, 28 Jan 2019 06:07:06 +1100, "Steven" wrote:



"Archibald Tarquin Blenkinsopp" wrote in
message ...
On Sun, 27 Jan 2019 14:15:40 +0000, John Rumm
wrote:

On 27/01/2019 10:46, Archibald Tarquin Blenkinsopp wrote:
On Sun, 27 Jan 2019 10:36:11 +0000, ss wrote:

Light switch 2 gang both are 2-way.
The stair switch works ok at the top of stairs, at bottom stairs it
only
works dependent on the position of the upstair switch.
I opened up and there appears to be a loose wire, can someone please
confirm that the yellow wire is needing reconnected as per image.

https://imgur.com/a/pnUTTWQ

No I cannot anyway! Try prayer, or an oija board.

https://circuitdigest.com/sites/defa...ire-method.png

That is a deprecated way of wiring a two way switched system, and also
as evidenced from the use of 3&E in the OPs photo, not what is being
used here.

The more appropriate diagram would be the second one in this section:

http://wiki.diyfaq.org.uk/index.php/...tching_circuit


Hard to say how it is wired,


But it is clear that 6 wires are involved, so it can't be your config.

I have never seen yellow used in a
lighting circuit, I can only assume the cable was left over after some
ancient three phase control project.

The piccy strongly suggests further investigation is needed, not just
stick the wire in what looks like an appropriate hole and screw it up.


Not when there are 6 wires involved, a common config used in that situation.

DIY or professional, there should be no uncertainties with electrical
power.


There isnt when there are clearly 6 wires involved and one of them
has clearly come adrift from where it would be in a 6 wire config.


Er, sorry I didn't think it necessary to explain. One two way switch
= 3 wires Two two way switches = six wires, or maybe five and a link.

Anyway if I'm forgiven for my overestimation of your abilities perhaps
you would care to use this.

http://www.math.com/students/calcula...urce/basic.htm

AB
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,153
Default More Heavy Trolling by Senile Nym-Shifting Rot Speed!

On Mon, 28 Jan 2019 06:07:06 +1100, Steven, better known as cantankerous
trolling senile geezer Rot Speed, wrote:

Not when there are 6 wires involved, a common config used in that situation.

DIY or professional, there should be no uncertainties with electrical
power.


There isnt when there are clearly 6 wires involved and one of them
has clearly come adrift from where it would be in a 6 wire config.


In auto-contradicting mode again, senile Ozzietard? LOL
--
Kerr-Mudd,John addressing senile Rot:
"Auto-contradictor Rod is back! (in the KF)"
MID:
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default Confirm switch wiring, please

On Sunday, 27 January 2019 19:07:18 UTC, Steven wrote:
"Archibald Tarquin Blenkinsopp" wrote in
message ...


DIY or professional, there should be no uncertainties with electrical
power.


There are. Welcome to the real world.


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Confirm switch wiring, please

In article ,
Archibald Tarquin Blenkinsopp wrote:
Hard to say how it is wired, I have never seen yellow used in a
lighting circuit, I can only assume the cable was left over after some
ancient three phase control project.


Triple and earth is often used domestically. Two way lighting circuits and
thermostats. Two lighting circuits on the same switch to the same room,
and so on. Anywhere where it is more economical.

--
*Never underestimate the power of stupid people in large groups

Dave Plowman London SW
To e-mail, change noise into sound.
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,110
Default Confirm switch wiring, please

On Sun, 27 Jan 2019 15:21:22 +0000 (GMT), "Dave Plowman (News)"
wrote:

In article ,
Archibald Tarquin Blenkinsopp wrote:
Hard to say how it is wired, I have never seen yellow used in a
lighting circuit, I can only assume the cable was left over after some
ancient three phase control project.


Triple and earth is often used domestically. Two way lighting circuits and
thermostats. Two lighting circuits on the same switch to the same room,
and so on. Anywhere where it is more economical.


Thank you, I have not come across this. All the switch wiring I have
dealt with was using red and black or the new stuff.

I did ensure the circuits were wired correctly regardless of
colour.:-)


AB




  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Confirm switch wiring, please

On 27/01/2019 10:46, Archibald Tarquin Blenkinsopp wrote:
On Sun, 27 Jan 2019 10:36:11 +0000, ss wrote:

Light switch 2 gang both are 2-way.
The stair switch works ok at the top of stairs, at bottom stairs it only
works dependent on the position of the upstair switch.
I opened up and there appears to be a loose wire, can someone please
confirm that the yellow wire is needing reconnected as per image.

https://imgur.com/a/pnUTTWQ


No I cannot anyway! Try prayer, or an oija board.

https://circuitdigest.com/sites/defa...ire-method.png


That is a deprecated way of wiring a two way switched system, and also
as evidenced from the use of 3&E in the OPs photo, not what is being
used here.

The more appropriate diagram would be the second one in this section:

http://wiki.diyfaq.org.uk/index.php/...tching_circuit




--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,640
Default Confirm switch wiring, please

On 27/01/2019 10:36, ss wrote:
Light switch 2 gang both are 2-way.
The stair switch works ok at the top of stairs, at bottom stairs it only
works dependent on the position of the upstair switch.
I opened up and there appears to be a loose wire, can someone please
confirm that the yellow wire is needing reconnected as per image.

https://imgur.com/a/pnUTTWQ

Highly likely especially if there is the end of the broken wire in the
terminal.
  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 10,998
Default Confirm switch wiring, please

Also of course if you get it wrong the cb will ping and there are not that
many choices to try. I know it sounds daft but one has to have fun and you
have also proved the cb works as well!

Brian

--
----- --
This newsgroup posting comes to you directly from...
The Sofa of Brian Gaff...

Blind user, so no pictures please
Note this Signature is meaningless.!
"Bob Minchin" wrote in message
...
On 27/01/2019 10:36, ss wrote:
Light switch 2 gang both are 2-way.
The stair switch works ok at the top of stairs, at bottom stairs it only
works dependent on the position of the upstair switch.
I opened up and there appears to be a loose wire, can someone please
confirm that the yellow wire is needing reconnected as per image.

https://imgur.com/a/pnUTTWQ
Highly likely especially if there is the end of the broken wire in the
terminal.





  #16   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,110
Default Confirm switch wiring, please

On Sun, 27 Jan 2019 10:55:03 -0000, "Brian Gaff"
wrote:

Also of course if you get it wrong the cb will ping and there are not that
many choices to try. I know it sounds daft but one has to have fun and you
have also proved the cb works as well!

Brian


Er! The cables look like nothing I have seen in a 2 Way switch
arrangement. The fact that one has come adrift means that the whole
caboodle is suspect.

A positive ID for each switch cable wouldn't take long and like PPE
MCB's should be a last resort as regards safety.

If an RCD or Breaker needs testing, keep it at that. Dont test one
unknown against another.

A pretty poor job would be to test the breaker first, then rely on it
for protection. Even worse is combining the two.


No short cuts I'm afraid. Get the meter out and check every terminal
in the process.

AB




  #18   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,110
Default Confirm switch wiring, please

On Sun, 27 Jan 2019 11:17:45 -0000, "Brian Gaff"
wrote:

If it was working the chances are that it was OK just strange wire or
whatever. Why look for trouble above that which presents itself.
Brian


In my early days I ran an MOD NAMAS accredited calibration department.
I used to do audits on the work and being as "hands on" as the rest of
the staff, it was more than just a paperwork excercise.

"insignificant problems" like a screw missing or dessicant that was
past it's best were not in themselves problems. The case would be
secure, the odd bit of damp would have no effect in a lot of the gear.

Those little problems were often very good indicators of something
more serious because the shortcuts would appear in the critical areas
also.

The solution, rejection and a full recal.

A philosophy that has served me very well over the years and prevented
many serious failiures in my other jobs.

I have yet to see anything wrong with my approach. Some work is shoddy
and potentially hazardous because of the location of the wiring I
recently found a lghting cable twisted together and insulated with
Silicone rubber. There were other problems with the same system so it
wasn't too much of a surprise. Removing the plasterboard ceiling to
find it wasn't with the intention of investigating the cable though,
it was for a totally different reason. My risk assessment of the
system did not conclude that removing a ceiling under a flat roof was
going to be worthwhile.

The risks were low, but who's to know what load of flammables might
have been left in the recess.

AB

  #19   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Confirm switch wiring, please

On 27/01/2019 11:13, Archibald Tarquin Blenkinsopp wrote:
On Sun, 27 Jan 2019 10:55:03 -0000, "Brian Gaff"
wrote:

Also of course if you get it wrong the cb will ping and there are not that
many choices to try. I know it sounds daft but one has to have fun and you
have also proved the cb works as well!

Brian


Er! The cables look like nothing I have seen in a 2 Way switch
arrangement.


But they look like 50% of the thousands of two way switches I have seen.




--
Adam
  #20   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,110
Default Confirm switch wiring, please

On Sun, 27 Jan 2019 19:09:45 +0000, ARW
wrote:

On 27/01/2019 11:13, Archibald Tarquin Blenkinsopp wrote:
On Sun, 27 Jan 2019 10:55:03 -0000, "Brian Gaff"
wrote:

Also of course if you get it wrong the cb will ping and there are not that
many choices to try. I know it sounds daft but one has to have fun and you
have also proved the cb works as well!

Brian


Er! The cables look like nothing I have seen in a 2 Way switch
arrangement.


But they look like 50% of the thousands of two way switches I have seen.


RGB?


Ones exposure to domestic wiring is a trifle limited, but I have not
come across those colours in a home before.

Whatever the colour, cables do not just "drop out".

AB



  #21   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,213
Default Confirm switch wiring, please

On 27/01/2019 19:09, ARW wrote:
On 27/01/2019 11:13, Archibald Tarquin Blenkinsopp wrote:
On Sun, 27 Jan 2019 10:55:03 -0000, "Brian Gaff"
wrote:

Also of course if you get it wrong the cb will ping and there are not
that
many choices to try. I know it sounds daft but one has to have fun
and you
have also proved the cb works as well!

Brian


Er! The cables look like nothing I have seen in a 2 Way switch
arrangement.


But they look like 50% of the thousands of two way switches I have seen.





My 1976-built house has Red+Yellow+Blue 3+E wiring for the
2-way switching and the (now disconnected) Wired thermostat too.

It did however have a borrowed neutral which I have fixed.


  #22   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,237
Default Confirm switch wiring, please

ss wrote:

Light switch 2 gang both are 2-way.
The stair switch works ok at the top of stairs, at bottom stairs it only
works dependent on the position of the upstair switch.
I opened up and there appears to be a loose wire, can someone please
confirm that the yellow wire is needing reconnected as per image.

https://imgur.com/a/pnUTTWQ


Yes. (With a very high degree of probability, and little chance of
harm.)

--

Roger Hayter
  #23   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,237
Default Confirm switch wiring, please

Roger Hayter wrote:

ss wrote:

Light switch 2 gang both are 2-way.
The stair switch works ok at the top of stairs, at bottom stairs it only
works dependent on the position of the upstair switch.
I opened up and there appears to be a loose wire, can someone please
confirm that the yellow wire is needing reconnected as per image.

https://imgur.com/a/pnUTTWQ


Yes. (With a very high degree of probability, and little chance of
harm.)


PS And tighten the other five terminal screws while you are there.

--

Roger Hayter
  #24   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default Confirm switch wiring, please

On Sunday, 27 January 2019 10:36:14 UTC, ss wrote:
Light switch 2 gang both are 2-way.
The stair switch works ok at the top of stairs, at bottom stairs it only
works dependent on the position of the upstair switch.
I opened up and there appears to be a loose wire, can someone please
confirm that the yellow wire is needing reconnected as per image.

https://imgur.com/a/pnUTTWQ


2 way 2 gang switch requires 6 connections, the yellow coming off is certainly the most likely explanation.


NT
  #25   Report Post  
Posted to uk.d-i-y
ss ss is offline
external usenet poster
 
Posts: 899
Default Confirm switch wiring, please

On 27/01/2019 11:29, wrote:
On Sunday, 27 January 2019 10:36:14 UTC, ss wrote:
Light switch 2 gang both are 2-way.
The stair switch works ok at the top of stairs, at bottom stairs it only
works dependent on the position of the upstair switch.
I opened up and there appears to be a loose wire, can someone please
confirm that the yellow wire is needing reconnected as per image.

https://imgur.com/a/pnUTTWQ

2 way 2 gang switch requires 6 connections, the yellow coming off is certainly the most likely explanation.


NT

OK now sorted and switch working ok now, it was the yellow wire come loose.


  #26   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,110
Default Confirm switch wiring, please

On Sun, 27 Jan 2019 11:32:36 +0000, ss wrote:

On 27/01/2019 11:29, wrote:
On Sunday, 27 January 2019 10:36:14 UTC, ss wrote:
Light switch 2 gang both are 2-way.
The stair switch works ok at the top of stairs, at bottom stairs it only
works dependent on the position of the upstair switch.
I opened up and there appears to be a loose wire, can someone please
confirm that the yellow wire is needing reconnected as per image.

https://imgur.com/a/pnUTTWQ

2 way 2 gang switch requires 6 connections, the yellow coming off is certainly the most likely explanation.


NT

OK now sorted and switch working ok now, it was the yellow wire come loose.


You are not concerned as to why? The yellow wire was just sitting in a
light switch back box, perfectly sound doing it's job, then one day it
falls out.

I must have missed the acceptable time period requirements for cable
retention when I did the 17th :-)

AB

  #27   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,237
Default Confirm switch wiring, please

Archibald Tarquin Blenkinsopp wrote:

On Sun, 27 Jan 2019 11:32:36 +0000, ss wrote:

On 27/01/2019 11:29, wrote:
On Sunday, 27 January 2019 10:36:14 UTC, ss wrote:
Light switch 2 gang both are 2-way.
The stair switch works ok at the top of stairs, at bottom stairs it only
works dependent on the position of the upstair switch.
I opened up and there appears to be a loose wire, can someone please
confirm that the yellow wire is needing reconnected as per image.

https://imgur.com/a/pnUTTWQ

2 way 2 gang switch requires 6 connections, the yellow coming off is
certainly the most likely explanation.


NT

OK now sorted and switch working ok now, it was the yellow wire come loose.


You are not concerned as to why? The yellow wire was just sitting in a
light switch back box, perfectly sound doing it's job, then one day it
falls out.

I must have missed the acceptable time period requirements for cable
retention when I did the 17th :-)

AB


The wiring regs certainly envisage screw terminals failing, and don't
seem to mandate cable retention in light switches at all.

The contact failed because either;

- it was never screwed up properly (and this would not stop it working
for an uncertain period);

- vibration from switching caused the screw to unscrew;

- or the copper gradually deformed under pressure;


The wire fell out when the switch was opened for examination.

Nothing out of the ordinary.

--

Roger Hayter
  #28   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 5,061
Default Confirm switch wiring, please

In article ,
Roger Hayter wrote:
Archibald Tarquin Blenkinsopp wrote:


On Sun, 27 Jan 2019 11:32:36 +0000, ss wrote:

On 27/01/2019 11:29, wrote:
On Sunday, 27 January 2019 10:36:14 UTC, ss wrote:
Light switch 2 gang both are 2-way.
The stair switch works ok at the top of stairs, at bottom stairs it only
works dependent on the position of the upstair switch.
I opened up and there appears to be a loose wire, can someone please
confirm that the yellow wire is needing reconnected as per image.

https://imgur.com/a/pnUTTWQ

2 way 2 gang switch requires 6 connections, the yellow coming off is
certainly the most likely explanation.


NT

OK now sorted and switch working ok now, it was the yellow wire come
loose.


You are not concerned as to why? The yellow wire was just sitting in a
light switch back box, perfectly sound doing it's job, then one day it
falls out.

I must have missed the acceptable time period requirements for cable
retention when I did the 17th :-)

AB


The wiring regs certainly envisage screw terminals failing, and don't
seem to mandate cable retention in light switches at all.


The contact failed because either;


- it was never screwed up properly (and this would not stop it working
for an uncertain period);


met this in our village hall - a professional installation

- vibration from switching caused the screw to unscrew;


met this at home

--
from KT24 in Surrey, England
"I'd rather die of exhaustion than die of boredom" Thomas Carlyle
  #29   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,766
Default Confirm switch wiring, please

It happens that Roger Hayter formulated :
The contact failed because either;

- it was never screwed up properly (and this would not stop it working
for an uncertain period);

- vibration from switching caused the screw to unscrew;

- or the copper gradually deformed under pressure;


It looks to me as if the copper core failed and snapped, leaving the
copper part still in the terminal. Possibly the installer nicked the
copper as he stripped the insulation and it subsequently snapped. Poor
or careless technique.
  #30   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,110
Default Confirm switch wiring, please




The wire fell out when the switch was opened for examination.

Nothing out of the ordinary.



Methinks your approach to electrical work is fundamentally flawed if
you consider cables falling out an "ordinary" event.

AB



  #31   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 49
Default Confirm switch wiring, please



"Archibald Tarquin Blenkinsopp" wrote in
message ...
On Sun, 27 Jan 2019 11:32:36 +0000, ss wrote:

On 27/01/2019 11:29, wrote:
On Sunday, 27 January 2019 10:36:14 UTC, ss wrote:
Light switch 2 gang both are 2-way.
The stair switch works ok at the top of stairs, at bottom stairs it
only
works dependent on the position of the upstair switch.
I opened up and there appears to be a loose wire, can someone please
confirm that the yellow wire is needing reconnected as per image.

https://imgur.com/a/pnUTTWQ

2 way 2 gang switch requires 6 connections, the yellow coming off is
certainly the most likely explanation.


NT

OK now sorted and switch working ok now, it was the yellow wire come
loose.


You are not concerned as to why? The yellow wire was just sitting in a
light switch back box, perfectly sound doing it's job, then one day it
falls out.


Because that screw had not been fully tightened initially.

I must have missed the acceptable time period requirements for cable
retention when I did the 17th :-)



  #32   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,153
Default More Heavy Trolling by Senile Nym-Shifting Rot Speed!

On Mon, 28 Jan 2019 05:42:57 +1100, Steven, better known as cantankerous
trolling senile geezer Rot Speed, wrote:



Because that screw had not been fully tightened initially.


NO screw could be as untightened as the one in your senile head, Ozzietard!

--
Norman Wells addressing senile Rot:
"Ah, the voice of scum speaks."
MID:
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Could someone please confirm usage for these LED bulbs ss UK diy 13 August 5th 14 12:09 AM
How to confirm a TV tuner is at fault? alitonto Electronics Repair 16 August 6th 05 05:21 PM
Sony KV-2670 R has problems and is probably dead but please confirm John Stevens Electronics Repair 4 August 2nd 05 01:32 AM
Just to confirm my diagnosis [Ikea uplighter] David W.E. Roberts UK diy 13 March 17th 05 07:57 AM
Confirm a DW621 R for $129 patrick conroy Woodworking 6 October 16th 04 08:08 PM


All times are GMT +1. The time now is 05:01 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"