UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 249
Default Lights and sockets onto one radial

Lights and sockets are usually on different circuits but must they be?

Can I have a 35ish meter 2.5mm radial from 16mm RCD running a few sockets and lights in what was once Ladies and Gents toilets, sockets to be used for occasional garden extension leads and a 480 watt frost heater?

If so must the wires from the switches to the lights be in 2.5mm too?
Or could i use 1mm wire from switch to lights as it would only run one bulb?


George
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,396
Default Lights and sockets onto one radial

George Miles wrote in
:

Lights and sockets are usually on different circuits but must they be?

Can I have a 35ish meter 2.5mm radial from 16mm RCD running a few
sockets and lights in what was once Ladies and Gents toilets, sockets
to be used for occasional garden extension leads and a 480 watt frost
heater?

If so must the wires from the switches to the lights be in 2.5mm too?
Or could i use 1mm wire from switch to lights as it would only run one
bulb?


George


Use a 5amp fused spur box to create a lighting circuit then you can use
1mm.
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,766
Default Lights and sockets onto one radial

DerbyBorn formulated on Sunday :
Use a 5amp fused spur box to create a lighting circuit then you can use
1mm.


The garden extension needs to be protected by an RCD.
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 249
Default Lights and sockets onto one radial

But the whole circuit will be on a 30ma RCD at the consumer unit.

Does it need another one at the garden socket?

In my experience both would probably trip together if they have the same characteristics

[g]

On Sunday, November 18, 2018 at 12:15:51 PM UTC, Harry Bloomfield wrote:
DerbyBorn formulated on Sunday :
Use a 5amp fused spur box to create a lighting circuit then you can use
1mm.


The garden extension needs to be protected by an RCD.


  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 355
Default Lights and sockets onto one radial

On 18/11/18 12:54, George Miles wrote:
But the whole circuit will be on a 30ma RCD at the consumer unit.

Does it need another one at the garden socket?



No.



In my experience both would probably trip together if they have the same characteristics


Likely, yes.

[g]

On Sunday, November 18, 2018 at 12:15:51 PM UTC, Harry Bloomfield wrote:
DerbyBorn formulated on Sunday :
Use a 5amp fused spur box to create a lighting circuit then you can use
1mm.


The garden extension needs to be protected by an RCD.




--
Email does not work


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,624
Default Lights and sockets onto one radial

Our conservatory lights are run off the ring main through a 5A fused FSU. Should imagine you could do the same off a radial circuit depending on wire cross-section and the number of sockets already on that radial.

Richard

  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Lights and sockets onto one radial

On 18/11/2018 11:34, George Miles wrote:

Lights and sockets are usually on different circuits but must they
be?


No, they don't have to be. It would be up to the installer to decide how
acceptable that would be, and what (if any) mitigation would be required
in the circumstances.

Can I have a 35ish meter 2.5mm radial from 16mm RCD running a few
sockets and lights in what was once Ladies and Gents toilets, sockets
to be used for occasional garden extension leads and a 480 watt frost
heater?


Yes

Probably prudent to check the voltage drop though since we are deviating
from one of the tabulated circuits:

If we assume 35m of 2.5mm^2 and say 4m of 1.0mm^2. If we put 2A of load
on the end of the thinner cable, and 14A of load on the thicker one
(over and above the 2A - making 16A total load), we get a voltage drop
on the sockets of:

25 x 14 x 0.018 = 6.3V on the sockets, which is acceptable.

For the lighting circuit bit we get an additional 4 x 2 x 0.044 = 0.35V
giving a total of 6.65V of drop. That's just inside the 6.9V allowed
(i.e. = 3% drop)

So nothing much to worry about there.

If so must the wires from the switches to the lights be in 2.5mm
too? Or could i use 1mm wire from switch to lights as it would only
run one bulb?


The elegant and sensible solution would be to take a 5A fused spur and
feed the lights from that. Possibly also include at least one non
maintained emergency light if loss of lighting would be a safety issue.

However, as an academic exercise, we can probably demonstrate that the
fuse could safely be omitted.

Depending on the installation method the 1.0 mm^2 T&E can have a
capacity of as much as 16A (method C), the lighting load will be
substantially less than that in all likelihood, and the possibility for
the user to create an overload by changing lamps etc seems very slim. So
overload protection for the 1.00 mm^2 cable does not need to be provided
by the MCB at the origin of the circuit. It only needs to provide fault
protection.

So we can do an adiabatic calculation check on the cable to ensure it
could withstand a fault at the far end.

So if we say 35m of 2.5mm^2, and lets allow 4m of 1mm^2, that gives a
loop impedance contribution from the cable of:

35 x 17.78 + 4 x 43.4 = 796 mOhms.

(that's for a L to N short on the thinner cable - we will assume the RCD
will protect for the L to E short, and its slightly higher loop
impedance. We are also using the "hot" resistance values for the
conductors - i.e. assuming they are already running at full load. That's
being very pessimistic for the 1.00mm^2 cable)

You have not said what the supply earthing system is, and we don't have
a measurement of the external earth loop impedance, so lets go with the
nominal TN-C-S and 0.35 Ohms.

That way we get a total loop impedance at the far end of the circuit of
~1.16 Ohms.

So that means the prospective fault current is going to be:

230 / 1.16 = 198A

That is adequate to trip a B16 MCB on the "instant" (i.e. magnetic) trip
mechanism (it takes 5x In or = 80A for that), so we will assume a
disconnect time of 0.1 secs. So an adiabatic check:

s = sqrt( I^2 x t ) / k

PVC cable, so take k as 115

s = sqrt( 198^2 x 0.1 ) / 115 = 0.54mm^2

So there is plenty of spare CSA in 1mm^2 cable to withstand that fault
current.


(note that BS7671 normally requires a protective device to be present at
each reduction in conductor size in a circuit - so we are deviating
from that based on the demonstration that the head end circuit
protection is actually sized to protect the smaller conductor sized
cable anyway)




--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 249
Default Lights and sockets onto one radial

Gosh that's some calculations from John Rumm:
his use of the word 'elegant' reminds me of maths at Uni...
I'm going to keep his calculations to justify using 3 core 1mm for light switches from 1.5mm circuits without additional fuses.

But for this job I'm going to use 2 separate wires,
one for sockets and one for lights,
its far simpler to justify to Building Control when I get to that stage.

I want as few fuses as possible around the house,
(I found it with 3 different locations of fuse boxes);
all circuits to be from RCDs at the consumer units by the back door
will make it easier for whoever has to deal with trips.

And no ring mains will make it easier for testing

Thanks.

George

On Sunday, November 18, 2018 at 11:34:32 AM UTC, George Miles wrote:
Lights and sockets are usually on different circuits but must they be?

Can I have a 35ish meter 2.5mm radial from 16mm RCD running a few sockets and lights in what was once Ladies and Gents toilets, sockets to be used for occasional garden extension leads and a 480 watt frost heater?

If so must the wires from the switches to the lights be in 2.5mm too?
Or could i use 1mm wire from switch to lights as it would only run one bulb?


George


  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Lights and sockets onto one radial

On 19/11/2018 15:06, George Miles wrote:

Gosh that's some calculations from John Rumm:
his use of the word 'elegant' reminds me of maths at Uni...


Well, part of the elegance of the proposed fused solution, was it avoids
any doubt and any need for calculations. Its also what would be
expected, which is usually the best way to go unless there is a
particular reason not to.

I'm going to keep his calculations to justify using 3 core 1mm for light switches from 1.5mm circuits without additional fuses.


Assuming the circuits are protected by a B6 MCB or similar, then they
would be fine wired all in 1.00mm^2 in most cases... (the larger cable
gives you longer maximum cable runs, and a bit more mechanical strength
- you don't typically use it for additional current carrying capacity on
a lighting circuit).

But for this job I'm going to use 2 separate wires,
one for sockets and one for lights,
its far simpler to justify to Building Control when I get to that stage.

I want as few fuses as possible around the house,
(I found it with 3 different locations of fuse boxes);
all circuits to be from RCDs at the consumer units by the back door
will make it easier for whoever has to deal with trips.

And no ring mains will make it easier for testing

Thanks.

George




--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
table lamp with two lights one outside and one inside body ,if one litghts up the other one is dim Renee Adair Home Repair 6 October 14th 17 03:44 PM
Christmas Lights Los Angeles 310-925-1720 christmaslightinginstall.blogs… — Christmas Lights Los Angeles 310-925-1720 We sale christmas lights and install them for you, house lights, holiday lights, trees lights, christmas lights Now You Know Home Repair 0 November 24th 08 07:02 PM
Lights Lights Christmas Lights Installation Los Angeles, BeverlyHills, Santa Monica, Culver City, Marina Del Rey, Calabasas, Agoura HillsThousand Oaks Holiday Lights Installation 1-310-925-1720 Now You Know Home Repair 0 November 15th 08 02:25 AM
flush fitting 13A sockets onto bare brickwork. Mark Gillespie UK diy 24 August 12th 07 10:06 PM
FS: New: 24 Pin Sockets and 40 Pin Sockets Jerry Rakar Electronics 1 February 4th 04 09:38 AM


All times are GMT +1. The time now is 08:53 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"