https://www.youtube.com/watch?v=VTXnSgpiCSw

A long ramble which basically says there is no point in replacing fuse
wire with a breaker because they shouldn't go that often.

My current view is that the ease of resetting a breaker compared to
****ing about with fuse wire (possibly in the dark) has much to recommend
it.

What does the team think about the video?

Also, is it worthwhile fitting breakers into the fuse board?

Have requested a picture of the set up; too busy to take one when I was up
there.

Cheers


Dave R


--
AMD FX-6300 in GA-990X-Gaming SLI-CF running Windows 7 Pro x64

---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

  #2   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Replacing fuse wire with RCD - youtube video

On 29/08/2018 18:39, David wrote:
https://www.youtube.com/watch?v=VTXnSgpiCSw

A long ramble which basically says there is no point in replacing fuse
wire with a breaker because they shouldn't go that often.

My current view is that the ease of resetting a breaker compared to
****ing about with fuse wire (possibly in the dark) has much to recommend
it.

What does the team think about the video?

Also, is it worthwhile fitting breakers into the fuse board?

Have requested a picture of the set up; too busy to take one when I was up
there.

Cheers



3m20s of the video.


That should say "That is NOT exactly the same as the fuse here."


Do not **** about with MCB replacements unless you have to [1], swap the
fuse box for a RCD protected CU.

[1] I am sure that someone will say that is all that electricians say,
but for the most part this is a DIY group and I have guided people
through fuse box to CU swaps without paying for an electrician.

--
Adam
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,115
Default Replacing fuse wire with RCD - youtube video

On Wed, 29 Aug 2018 19:29:58 +0100, ARW wrote:

On 29/08/2018 18:39, David wrote:
https://www.youtube.com/watch?v=VTXnSgpiCSw

A long ramble which basically says there is no point in replacing fuse
wire with a breaker because they shouldn't go that often.

My current view is that the ease of resetting a breaker compared to
****ing about with fuse wire (possibly in the dark) has much to
recommend it.

What does the team think about the video?

Also, is it worthwhile fitting breakers into the fuse board?

Have requested a picture of the set up; too busy to take one when I was
up there.

Cheers



3m20s of the video.


That should say "That is NOT exactly the same as the fuse here."


Do not **** about with MCB replacements unless you have to [1], swap the
fuse box for a RCD protected CU.

[1] I am sure that someone will say that is all that electricians say,
but for the most part this is a DIY group and I have guided people
through fuse box to CU swaps without paying for an electrician.


Waiting for a picture, but there looks to be a new RCD protecting the old
CU.

I didn't understand what was going on because I didn't have time to trace
everything through, but there is some new stuff and the old CU.

At the moment I am looking at making resetting a blown fuse easier. I
don't have the time to undertake a CU replacement and funding an
electrician to do this is well down the pecking order at the moment.

Just trying to estimate if a stop gap is worth doing.

Thanks



Dave R


--
AMD FX-6300 in GA-990X-Gaming SLI-CF running Windows 7 Pro x64

---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

  #4   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Replacing fuse wire with RCD - youtube video

On 29/08/2018 19:41, David wrote:
On Wed, 29 Aug 2018 19:29:58 +0100, ARW wrote:

On 29/08/2018 18:39, David wrote:
https://www.youtube.com/watch?v=VTXnSgpiCSw

A long ramble which basically says there is no point in replacing fuse
wire with a breaker because they shouldn't go that often.

My current view is that the ease of resetting a breaker compared to
****ing about with fuse wire (possibly in the dark) has much to
recommend it.

What does the team think about the video?

Also, is it worthwhile fitting breakers into the fuse board?

Have requested a picture of the set up; too busy to take one when I was
up there.

Cheers



3m20s of the video.


That should say "That is NOT exactly the same as the fuse here."


Do not **** about with MCB replacements unless you have to [1], swap the
fuse box for a RCD protected CU.

[1] I am sure that someone will say that is all that electricians say,
but for the most part this is a DIY group and I have guided people
through fuse box to CU swaps without paying for an electrician.


Waiting for a picture, but there looks to be a new RCD protecting the old
CU.

I didn't understand what was going on because I didn't have time to trace
everything through, but there is some new stuff and the old CU.

At the moment I am looking at making resetting a blown fuse easier. I
don't have the time to undertake a CU replacement and funding an
electrician to do this is well down the pecking order at the moment.

Just trying to estimate if a stop gap is worth doing.


For a one off on one circuit go for it.



--
Adam
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default Replacing fuse wire with RCD - youtube video

On Wednesday, 29 August 2018 19:41:38 UTC+1, David WE Roberts (Google) wrote:
On Wed, 29 Aug 2018 19:29:58 +0100, ARW wrote:
On 29/08/2018 18:39, David wrote:


https://www.youtube.com/watch?v=VTXnSgpiCSw

A long ramble which basically says there is no point in replacing fuse
wire with a breaker because they shouldn't go that often.

My current view is that the ease of resetting a breaker compared to
****ing about with fuse wire (possibly in the dark) has much to
recommend it.

What does the team think about the video?

Also, is it worthwhile fitting breakers into the fuse board?

Have requested a picture of the set up; too busy to take one when I was
up there.

Cheers



3m20s of the video.


That should say "That is NOT exactly the same as the fuse here."


Do not **** about with MCB replacements unless you have to [1], swap the
fuse box for a RCD protected CU.

[1] I am sure that someone will say that is all that electricians say,
but for the most part this is a DIY group and I have guided people
through fuse box to CU swaps without paying for an electrician.


Waiting for a picture, but there looks to be a new RCD protecting the old
CU.

I didn't understand what was going on because I didn't have time to trace
everything through, but there is some new stuff and the old CU.

At the moment I am looking at making resetting a blown fuse easier. I
don't have the time to undertake a CU replacement and funding an
electrician to do this is well down the pecking order at the moment.

Just trying to estimate if a stop gap is worth doing.

Thanks



Dave R


You've not shown us the current fusebox, nor the RCD/ELCB/whatever providing some unknown level of shock protection. So nothing conclusive can be offered really.

MCB vs fusewi MCBs are easy to reset, more prone to false trips. Fusewire can be abused. MCBs are the choice for rented properties - no call outs, no dangerous miswiring by some drunk, no risk of handling live bits.

RCBOs can't be retrofitted to most rewirable fuse boxes.

MCBs are a couple of quid on ebay, so not much to lose.


NT


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,904
Default Replacing fuse wire with RCD - youtube video

On Wed, 29 Aug 2018 19:29:58 +0100, ARW
wrote:

On 29/08/2018 18:39, David wrote:
https://www.youtube.com/watch?v=VTXnSgpiCSw

A long ramble which basically says there is no point in replacing fuse
wire with a breaker because they shouldn't go that often.

My current view is that the ease of resetting a breaker compared to
****ing about with fuse wire (possibly in the dark) has much to recommend
it.

What does the team think about the video?

Also, is it worthwhile fitting breakers into the fuse board?

Have requested a picture of the set up; too busy to take one when I was up
there.

Cheers



3m20s of the video.


That should say "That is NOT exactly the same as the fuse here."


Do not **** about with MCB replacements unless you have to [1], swap the
fuse box for a RCD protected CU.


RCBOs Shirley? You don't want the entire supply brought down because
of a fault on one circuit.

[1] I am sure that someone will say that is all that electricians say,
but for the most part this is a DIY group and I have guided people
through fuse box to CU swaps without paying for an electrician.

  #7   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Replacing fuse wire with RCD - youtube video

On 29/08/2018 19:44, Scott wrote:
On Wed, 29 Aug 2018 19:29:58 +0100, ARW
wrote:

On 29/08/2018 18:39, David wrote:
https://www.youtube.com/watch?v=VTXnSgpiCSw

A long ramble which basically says there is no point in replacing fuse
wire with a breaker because they shouldn't go that often.

My current view is that the ease of resetting a breaker compared to
****ing about with fuse wire (possibly in the dark) has much to recommend
it.

What does the team think about the video?

Also, is it worthwhile fitting breakers into the fuse board?

Have requested a picture of the set up; too busy to take one when I was up
there.

Cheers



3m20s of the video.


That should say "That is NOT exactly the same as the fuse here."


Do not **** about with MCB replacements unless you have to [1], swap the
fuse box for a RCD protected CU.


RCBOs Shirley? You don't want the entire supply brought down because
of a fault on one circuit.

[1] I am sure that someone will say that is all that electricians say,
but for the most part this is a DIY group and I have guided people
through fuse box to CU swaps without paying for an electrician.



A split load RCD CU is a minimum. Ta for pointing that error of mine out.

--
Adam
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 307
Default Replacing fuse wire with RCD - youtube video

I'd be a lot happier about offering advice,if I thought you knew the difference between fuses, mcb's rcd's and rcbo's
The opportunities for creating mayhem are wondrous
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,115
Default Replacing fuse wire with RCD - youtube video

On Wed, 29 Aug 2018 11:47:30 -0700, Cynic wrote:

I'd be a lot happier about offering advice,if I thought you knew the
difference between fuses, mcb's rcd's and rcbo's The opportunities for
creating mayhem are wondrous


Perhaps you could provide some clarity?



--
AMD FX-6300 in GA-990X-Gaming SLI-CF running Windows 7 Pro x64

---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,679
Default Replacing fuse wire with RCD - youtube video

David Wrote in message:
On Wed, 29 Aug 2018 11:47:30 -0700, Cynic wrote:

I'd be a lot happier about offering advice,if I thought you knew the
difference between fuses, mcb's rcd's and rcbo's The opportunities for
creating mayhem are wondrous


Perhaps you could provide some clarity?


FFS - "oop north Leeds way" is not a lot of miles from ARWs home
turf .... Ask him if he'll do the whole thing ??
--
--
Jim K


----Android NewsGroup Reader----
http://usenet.sinaapp.com/


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,554
Default Replacing fuse wire with RCD - youtube video

On 29/08/2018 18:39, David wrote:
https://www.youtube.com/watch?v=VTXnSgpiCSw

A long ramble which basically says there is no point in replacing fuse
wire with a breaker because they shouldn't go that often.

My current view is that the ease of resetting a breaker compared to
****ing about with fuse wire (possibly in the dark) has much to recommend
it.

What does the team think about the video?

Also, is it worthwhile fitting breakers into the fuse board?


I'll let you know if a fuse ever blows, its only been 30 years so far.


  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Replacing fuse wire with RCD - youtube video

On 29/08/2018 18:39, David wrote:
https://www.youtube.com/watch?v=VTXnSgpiCSw

A long ramble which basically says there is no point in replacing fuse
wire with a breaker because they shouldn't go that often.


Usually true...

My current view is that the ease of resetting a breaker compared to
****ing about with fuse wire (possibly in the dark) has much to recommend
it.


That's a good argument for modern MCBs - but not retrofitting them to an
old wylex CU.

What does the team think about the video?


Its a fair assessment of the situation IMHO.

Also, is it worthwhile fitting breakers into the fuse board?


Not really - since it does not address most of the shortcomings of those
old style fuse boxes i.e. lack of adequate numbers of circuits for a
modern install, and no way to incorporate RCD protection. You may also
find (depending on the age of the cables) that the BS3036 fuses might
leave some circuits without adequate fault protection (especially spurs
on ring circuits using a 1mm^2 earth or imperial equivalent)

About the only time it might be worth retrofitting would be on a
lighting circuit in a property where there are old or inform users, you
don't want the disruption of a CU replacement and there are still lots
of filament bulbs in use, and so there is some possibility of a nuisance
fuse blow on a lamp failure.

Have requested a picture of the set up; too busy to take one when I was up
there.

Cheers


Dave R




--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 10,998
Default Replacing fuse wire with RCD - youtube video

Of course its easier and if there is a fault you can have a days work for
you to find it if it blows the fuse every time. I never understood why old
fuses did not use a cartridge like plugs and appliances did, Seems strangely
retro even all those years ago and hands up those who have used strands from
stranded wire and a bit of guess to mend them when you misplace the roll of
fuse wire.
Brian

--
----- --
This newsgroup posting comes to you directly from...
The Sofa of Brian Gaff...

Blind user, so no pictures please
Note this Signature is meaningless.!
"David" wrote in message
...
https://www.youtube.com/watch?v=VTXnSgpiCSw

A long ramble which basically says there is no point in replacing fuse
wire with a breaker because they shouldn't go that often.

My current view is that the ease of resetting a breaker compared to
****ing about with fuse wire (possibly in the dark) has much to recommend
it.

What does the team think about the video?

Also, is it worthwhile fitting breakers into the fuse board?

Have requested a picture of the set up; too busy to take one when I was up
there.

Cheers


Dave R


--
AMD FX-6300 in GA-990X-Gaming SLI-CF running Windows 7 Pro x64

---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus



  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 5,061
Default Replacing fuse wire with RCD - youtube video

In article , Brian Gaff
wrote:
Of course its easier and if there is a fault you can have a days work
for you to find it if it blows the fuse every time. I never understood
why old fuses did not use a cartridge like plugs and appliances did,
Seems strangely retro even all those years ago and hands up those who
have used strands from stranded wire and a bit of guess to mend them when
you misplace the roll of fuse wire. Brian


1. You could get cartridge fuses to fit some CUs

2. I suspect that when wire fuses were first brought in, cartridge fuses
hadn't been invented

--
from KT24 in Surrey, England
"I'd rather die of exhaustion than die of boredom" Thomas Carlyle
  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,554
Default Replacing fuse wire with RCD - youtube video

On 30/08/2018 08:52, charles wrote:
In article , Brian Gaff
wrote:
Of course its easier and if there is a fault you can have a days work
for you to find it if it blows the fuse every time. I never understood
why old fuses did not use a cartridge like plugs and appliances did,
Seems strangely retro even all those years ago and hands up those who
have used strands from stranded wire and a bit of guess to mend them when
you misplace the roll of fuse wire. Brian


1. You could get cartridge fuses to fit some CUs

2. I suspect that when wire fuses were first brought in, cartridge fuses
hadn't been invented


My parent's, house built in the 50's had cartridge fuses.

It was all metal cases too.



  #16   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,853
Default Replacing fuse wire with RCD - youtube video

On 30/08/2018 08:52, charles wrote:
In article , Brian Gaff
wrote:
Of course its easier and if there is a fault you can have a days work
for you to find it if it blows the fuse every time. I never understood
why old fuses did not use a cartridge like plugs and appliances did,
Seems strangely retro even all those years ago and hands up those who
have used strands from stranded wire and a bit of guess to mend them when
you misplace the roll of fuse wire. Brian


1. You could get cartridge fuses to fit some CUs

2. I suspect that when wire fuses were first brought in, cartridge fuses
hadn't been invented

I had cartridge fuses in my old house.

And a right PITA they were.

Instead of that roll of different fuse wires I inherited from my
granddad, and hadn't used up, I had to go out and buy one whenever a
light bulb popped the fuse.

Hard to find, and stupid prices in the shops too.

Andy
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Comsumer unit RCD trips on non-RCD protected circuit activity ian UK diy 4 April 25th 06 08:59 PM
Immersion - RCD or non-RCD? Goonerak UK diy 14 September 25th 05 08:46 PM
RCD - all MCBs off (no L) + no N-output from RCD connected (no N) = still trips instantly dorothy UK diy 11 November 3rd 04 11:15 PM