I'm after a bit of advice as to why I've just got an electric shock. i
have an old but quality lathe with a seperate switch with on/off
buttons. The switch has a metal case. The live wire from the plug had
chafed and come into contact with the box and when I went to switch it
on I got a shock.

The bit I don't understand is why nothing tripped. The live and neutral
wires are both wired into the contactor and the earth from the lathe and
from the feed from the plug both connect to an earth terminal on the
switch casing and were done up tight. The socket in the garage is fed
from a dedicated 16 amp breaker in a modern MK consumer unit with an
RCD. Should that not have protected me?

I don't understand electricity as well as I should and would be grateful
for advice!

Peter.
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,766
Default Electric shock - why?

PJK wrote on 24/06/2018 :
The bit I don't understand is why nothing tripped. The live and neutral
wires are both wired into the contactor and the earth from the lathe and from
the feed from the plug both connect to an earth terminal on the switch casing
and were done up tight. The socket in the garage is fed from a dedicated 16
amp breaker in a modern MK consumer unit with an RCD. Should that not have
protected me?


The RCD will only trip, if sufficient current passes through you, to
earth. Possibly there was not a sufficiently low resistance path
through you to ground to trip it. Another possibility is that the RCD
is faulty or seized up. All are fitted with a test button, does it trip
if that button is pressed?
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,829
Default Electric shock - why?

Harry Bloomfield wrote:

The RCD will only trip, if sufficient current passes through you, to
earth.


From the description, I assumed the chafed live was touching the
earthed case, so shouldn't be waiting for anyone to touch anything
before a trip...

Maybe the earth in the garage (exported from the house?) is faulty.

  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,157
Default Electric shock - why?

On 24/06/2018 11:31, PJK wrote:
I'm after a bit of advice as to why I've just got an electric shock.Â* i
have an old but quality lathe with a seperate switch with on/off
buttons.Â* The switch has a metal case.Â* The live wire from the plug had
chafed and come into contact with the box and when I went to switch it
on I got a shock.

The bit I don't understand is why nothing tripped.Â* The live and neutral
wires are both wired into the contactor and the earth from the lathe and
from the feed from the plug both connect to an earth terminal on the
switch casing and were done up tight.Â* The socket in the garage is fed
from a dedicated 16 amp breaker in a modern MK consumer unit with an
RCD.Â* Should that not have protected me?

I don't understand electricity as well as I should and would be grateful
for advice!


30mA is a modest current for you to feel. I suspect the current you felt
was less than this. It shouldn't trip at a current less than 15mA.

It sounds like your lathe has a faulty earth connection. As soon as the
live had made contact with the 'box', which I assume is metal and should
be earthed, the RCD should ha tripped.

As another poster has suggested, it might be a good opportunity to test
your RCD.
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Electric shock - why?

On 24/06/2018 11:31, PJK wrote:
I'm after a bit of advice as to why I've just got an electric shock.Â* i
have an old but quality lathe with a seperate switch with on/off
buttons.Â* The switch has a metal case.Â* The live wire from the plug had
chafed and come into contact with the box and when I went to switch it
on I got a shock.

The bit I don't understand is why nothing tripped.Â* The live and neutral
wires are both wired into the contactor and the earth from the lathe and
from the feed from the plug both connect to an earth terminal on the
switch casing and were done up tight.Â* The socket in the garage is fed
from a dedicated 16 amp breaker in a modern MK consumer unit with an
RCD.Â* Should that not have protected me?


Yes it should. So it suggests you have one or more faults somewhere.

I don't understand electricity as well as I should and would be grateful
for advice!


Generally the way earthing works is to force the supply to disconnect by
operating a circuit protective device - typically a fuse, or circuit
breaker or RCD. The objective being to limit the duration of any shock
you can receive so that its is not long enough cause serious injury.

You also have an additional protection from the RCD. That looks at the
current flowing in both live and neutral at the same time, and trips
when it sees anything more than a tiny mismatch in those currents (the
theory being that if some current is flowing to earth somewhere in the
circuit (say from a live switch casing, though you to earth), then it
will see and imbalance and trip.

So lets look at the earthing first:

So with your lathe, the metalwork of the whole machine and its switch
box should be well connected to earth. When that live wire made contact
to the metalwork, you should have had a very large current (often called
a "Fault current") flow between live and earth, and that should have
tripped an upstream protective device.

So assuming the lathe actually works, it seems likely that you have a
good connection on both live and neutral. So the most likely problem is
that your earth connection is either broken completely, or is has a high
electrical resistance for whatever reason. Its important you find where
the fault is, since it is safety critical.

Disconnect the lath from the mains at the plug

You need a basic multimeter to carry out some tests. With the multimeter
set to measure resistance, connect one lead to the earth pin (the top
one) on the plug, and touch the other to the metal case of the lathe.
You should see a nice low resistance - under 1 ohm typically. Check you
still keep the good connection when the flex is flexed a bit (its not
uncommon for wires to break in the flex where they get lots of movement).

If the flex and plug look good, then it may be the socket or its supply
circuit which is faulty.

First a visual check. Turn off the circuit at the CU. Unscrew the socket
faceplate and have a peek behind - check the earth connections look
good. Give a tug on the wires, and make sure they do not pull out of the
terminals. If that looks ok, replace the socket and we need to move on
to some electrical tests.

With the mains on, and your multimeter set to measure AC volts (on a
range were the maximum voltage is more than 240V), you should be be able
to measure 240V (ish) volts between the Live (right hand pin on the
socket) and the earth. You will need to use the probe in the earth pin
to force open the shutters on the live pins. If you can't, then that
suggests that the earth is broken somewhere between the socket and the
CU. (and if the socket is part of a ring circuit, then its broken
twice!) - if this seems to be the case, post back for detailed advice on
finding that.


The RCD

The other question is why did that not trip. There are two likely
possibilities: either it is not working correctly, or the shock you
received did not actually pass enough current to reach its trip
threshold. (its even possible the device installed has too high a trip
threshold).

So first step, check the writing on the front of the RCD and make sure
it has a 30mA (or 0.03A) trip threshold.

Now verify it really is protecting the circuit the lathe is on by
turning it off and machine sure something plugged into the lathe's
socket will not work.

Now try the test button - it should trip the RCD immediately. If it does
not, it needs replacing.

If all those pass, then its likely the shock current was too small to
cause a trip. There are more detailed tests that you can do, but again
post back for more if required.




--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,236
Default Electric shock - why?

On Sun, 24 Jun 2018 11:55:50 +0100, Fredxx wrote:

On 24/06/2018 11:31, PJK wrote:
I'm after a bit of advice as to why I've just got an electric shock.Â* i
have an old but quality lathe with a seperate switch with on/off
buttons.Â* The switch has a metal case.Â* The live wire from the plug had
chafed and come into contact with the box and when I went to switch it
on I got a shock.

The bit I don't understand is why nothing tripped.Â* The live and neutral
wires are both wired into the contactor and the earth from the lathe and
from the feed from the plug both connect to an earth terminal on the
switch casing and were done up tight.Â* The socket in the garage is fed
from a dedicated 16 amp breaker in a modern MK consumer unit with an
RCD.Â* Should that not have protected me?

I don't understand electricity as well as I should and would be grateful
for advice!


30mA is a modest current for you to feel. I suspect the current you felt
was less than this. It shouldn't trip at a current less than 15mA.

It sounds like your lathe has a faulty earth connection. As soon as the
live had made contact with the 'box', which I assume is metal and should
be earthed, the RCD should ha tripped.

As another poster has suggested, it might be a good opportunity to test
your RCD.


and check the earths. Whoever did the extension to our house didn't
connect the earth at the junction box - and the main electrical device
in the extension is a washing machine.

--
AnthonyL
  #7   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Electric shock - why?

On 24/06/2018 11:55, Fredxx wrote:
On 24/06/2018 11:31, PJK wrote:
I'm after a bit of advice as to why I've just got an electric shock.
i have an old but quality lathe with a seperate switch with on/off
buttons.Â* The switch has a metal case.Â* The live wire from the plug
had chafed and come into contact with the box and when I went to
switch it on I got a shock.

The bit I don't understand is why nothing tripped.Â* The live and
neutral wires are both wired into the contactor and the earth from the
lathe and from the feed from the plug both connect to an earth
terminal on the switch casing and were done up tight.Â* The socket in
the garage is fed from a dedicated 16 amp breaker in a modern MK
consumer unit with an RCD.Â* Should that not have protected me?

I don't understand electricity as well as I should and would be
grateful for advice!


30mA is a modest current for you to feel. I suspect the current you felt
was less than this. It shouldn't trip at a current less than 15mA.

It sounds like your lathe has a faulty earth connection. As soon as the
live had made contact with the 'box', which I assume is metal and should
be earthed, the RCD should ha tripped.

As another poster has suggested, it might be a good opportunity to test
your RCD.



A live touching a metal case should also trip a MCB as well as a RCD.

As you said poor earth.



--
Adam
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 10
Default Electric shock - why?

On 24/06/2018 12:22, John Rumm wrote:
On 24/06/2018 11:31, PJK wrote:
I'm after a bit of advice as to why I've just got an electric shock.


Very comprehensive advice snipped

If all those pass, then its likely the shock current was too small to
cause a trip. There are more detailed tests that you can do, but again
post back for more if required.





Thanks for the detailed answer, very much appreciated. I'll investigate
and post back asap.

Peter
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Electric shock - why?

In article ,
PJK wrote:
I'm after a bit of advice as to why I've just got an electric shock. i
have an old but quality lathe with a seperate switch with on/off
buttons. The switch has a metal case. The live wire from the plug had
chafed and come into contact with the box and when I went to switch it
on I got a shock.


The bit I don't understand is why nothing tripped. The live and neutral
wires are both wired into the contactor and the earth from the lathe and
from the feed from the plug both connect to an earth terminal on the
switch casing and were done up tight. The socket in the garage is fed
from a dedicated 16 amp breaker in a modern MK consumer unit with an
RCD. Should that not have protected me?


I don't understand electricity as well as I should and would be grateful
for advice!


Have you got a DVM? Try measuring the resistance between the metal part
where you got the short and the earth pin on the plug. Not a definitive
test by any means, but a poor connection between earth lead and the
machine metalwork is pretty likely with age.

--
*There are two kinds of pedestrians... the quick and the dead.

Dave Plowman London SW
To e-mail, change noise into sound.
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 10
Default Electric shock - why?

On 24/06/2018 12:22, John Rumm wrote:
On 24/06/2018 11:31, PJK wrote:
I'm after a bit of advice as to why I've just got an electric shock.


Snip detailed advice


If all those pass, then its likely the shock current was too small to
cause a trip. There are more detailed tests that you can do, but again
post back for more if required.





Thanks for the detailed answer, very much appreciated. I'll investigate
and post back asap.

Peter


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,783
Default Electric shock - why?

On Sun, 24 Jun 2018 11:31:15 +0100, PJK wrote:


I don't understand electricity as well as I should and would be grateful
for advice!


I had exactly the same problem. Driving in a separate earth spike through
the workshop floor next to the lathe sorted the issue.



--
This message may be freely reproduced without limit or charge only via
the Usenet protocol. Reproduction in whole or part through other
protocols, whether for profit or not, is conditional upon a charge of
GBP10.00 per reproduction. Publication in this manner via non-Usenet
protocols constitutes acceptance of this condition.
  #12   Report Post  
Posted to uk.d-i-y
GB GB is offline
external usenet poster
 
Posts: 4,768
Default Electric shock - why?

On 24/06/2018 13:43, ARW wrote:

A live touching a metal case should also trip a MCB as well as a RCD.

As you said poor earth.


A live lead touching an earthed case *ought* to have produced a big bang
and as you say immediately tripped the MCB. The *only* explanation I can
see is that it wasn't earthed properly.






  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 10,998
Default Electric shock - why?

Also of course, are you absolutely sure that the earth itself is real, IE is
the wire at the switch end and the supply end actually connected? You may
laugh, but screws have a habit of working loose and wires bent at right
angles in a short space can also break if quite old. I had an ally one break
to a cooker like this some years ago.
There has to be a reason as otherwise when the live shorted and the earth
on the box formed a circuit some protection somewhere would have tripped.
Brian

--
----- --
This newsgroup posting comes to you directly from...
The Sofa of Brian Gaff...

Blind user, so no pictures please
Note this Signature is meaningless.!
"Harry Bloomfield" wrote in message
news
PJK wrote on 24/06/2018 :
The bit I don't understand is why nothing tripped. The live and neutral
wires are both wired into the contactor and the earth from the lathe and
from the feed from the plug both connect to an earth terminal on the
switch casing and were done up tight. The socket in the garage is fed
from a dedicated 16 amp breaker in a modern MK consumer unit with an RCD.
Should that not have protected me?


The RCD will only trip, if sufficient current passes through you, to
earth. Possibly there was not a sufficiently low resistance path through
you to ground to trip it. Another possibility is that the RCD is faulty or
seized up. All are fitted with a test button, does it trip if that button
is pressed?



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Got electric shock while touching pot rack and electric range at thesame time Jackson Hawk Home Repair 55 January 24th 16 05:59 PM
shock proof and non shock test indicators Cydrome Leader Metalworking 18 February 4th 13 05:41 PM
Why does this shock me? Sunbeam UK diy 18 November 9th 04 11:54 PM
Electric Shock Device Jonathan Britten Electronics 7 September 7th 04 03:03 AM
Electric Shock with RCD Andrew Barnes UK diy 25 October 29th 03 10:22 AM


All times are GMT +1. The time now is 07:07 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"