Default Is it OK to borrow an earth?

My 89 y/o mother can no longer reach the switch above the mirror and I
want to change it for a LED pullcord light.

The old light was installed by a bathroom fitter and was not earthed.

This light requires an earth connection but further investigation has
revealed that her upstairs lighting circuit has no earth.

Can I borrow an earth from an accessible ring-circuit in these
circumstances?
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 10,998
Default Is it OK to borrow an earth?

And you need an earth because?
If its a pull cord the likelihood of earth being useful considering most of
the lighting has none seems debatable.
Brian

--
----- -
This newsgroup posting comes to you directly from...
The Sofa of Brian Gaff...

Blind user, so no pictures please!
"SteveE" wrote in message
...
My 89 y/o mother can no longer reach the switch above the mirror and I
want to change it for a LED pullcord light.

The old light was installed by a bathroom fitter and was not earthed.

This light requires an earth connection but further investigation has
revealed that her upstairs lighting circuit has no earth.

Can I borrow an earth from an accessible ring-circuit in these
circumstances?



  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,523
Default Is it OK to borrow an earth?

On 08/03/2018 16:44, SteveE wrote:
My 89 y/o mother can no longer reach the switch above the mirror and I
want to change it for a LED pullcord light.

The old light was installed by a bathroom fitter and was not earthed.

This light requires an earth connection but further investigation has
revealed that her upstairs lighting circuit has no earth.

Can I borrow an earth from an accessible ring-circuit in these
circumstances?

If it's a pullcord don't bother with the earth. Put a label on the
switch: No earth.

Bill
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 101
Default Is it OK to borrow an earth?

On Thu, 08 Mar 2018 16:44:54 +0000, SteveE wrote:


This light requires an earth connection but further investigation has
revealed that her upstairs lighting circuit has no earth.

Can I borrow an earth from an accessible ring-circuit in these
circumstances?


Yes.
But label it appropriately.
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Is it OK to borrow an earth?

On 08/03/2018 16:44, SteveE wrote:
My 89 y/o mother can no longer reach the switch above the mirror and I
want to change it for a LED pullcord light.

The old light was installed by a bathroom fitter and was not earthed.

This light requires an earth connection but further investigation has
revealed that her upstairs lighting circuit has no earth.

Can I borrow an earth from an accessible ring-circuit in these
circumstances?


Its not a good idea to borrow conductors from other circuits.

If you must* take a feed from another circuit, then take the Line and
Neutral from there as well (via a FCU). Remember to include the earth
for the new circuit into the bathroom's equipotential bonding.

* One could argue that for a pull cord switch, where any metallic part
of the switch is out of reach, one could omit the earthing without too
much risk. Better choose a lamp fitting that is double insulated and
does not require an earth.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,157
Default Is it OK to borrow an earth?

On 08/03/2018 22:17, pamela wrote:
On 16:44 8 Mar 2018, SteveE wrote:

My 89 y/o mother can no longer reach the switch above the mirror
and I want to change it for a LED pullcord light.

The old light was installed by a bathroom fitter and was not
earthed.

This light requires an earth connection but further investigation
has revealed that her upstairs lighting circuit has no earth.

Can I borrow an earth from an accessible ring-circuit in these
circumstances?


Depending on your situation, I wonder if it may be easier for your
mum to have a motion sensor switch. It could be a replacement for
the existing switch or some bathroom light fittings come with one
built in.


I think the issue is the light doesn't have an earth connection.

A pull cord switch doesn't need an earth.

I have often thought passive IR motion sensors are not used often
enough, but if still in a bath, such a switch is of little use, and a
pain if you actually want darkness.

  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default Is it OK to borrow an earth?

On Thursday, 8 March 2018 16:45:03 UTC, SteveE wrote:

My 89 y/o mother can no longer reach the switch above the mirror and I
want to change it for a LED pullcord light.

The old light was installed by a bathroom fitter and was not earthed.

This light requires an earth connection but further investigation has
revealed that her upstairs lighting circuit has no earth.

Can I borrow an earth from an accessible ring-circuit in these
circumstances?


Better to take all 3 conductors from where you plan to take the earth.
Borrowing of earths does work, it's not regs compliant of course, and perhaps someone one day will disable part of the wiring system leaving the light unintentionally unearthed. By then it should be all RCDed anyway, but who knows. So don't do it.


NT
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Is it OK to borrow an earth?

In article ,
SteveE wrote:
My 89 y/o mother can no longer reach the switch above the mirror and I
want to change it for a LED pullcord light.


The old light was installed by a bathroom fitter and was not earthed.


This light requires an earth connection but further investigation has
revealed that her upstairs lighting circuit has no earth.


Can I borrow an earth from an accessible ring-circuit in these
circumstances?


Not advisable.

Why not find a fitting which doesn't require an earth?

--
*Whatever kind of look you were going for, you missed.

Dave Plowman London SW
To e-mail, change noise into sound.
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 15
Default Is it OK to borrow an earth?

On Thu, 8 Mar 2018 19:48:14 +0000
John Rumm wrote:

On 08/03/2018 16:44, SteveE wrote:
My 89 y/o mother can no longer reach the switch above the mirror
and I want to change it for a LED pullcord light.

The old light was installed by a bathroom fitter and was not
earthed.

This light requires an earth connection but further investigation
has revealed that her upstairs lighting circuit has no earth.

Can I borrow an earth from an accessible ring-circuit in these
circumstances?


Its not a good idea to borrow conductors from other circuits.


Thanks, this is why I was uneasy about doing it.


If you must* take a feed from another circuit, then take the Line and
Neutral from there as well (via a FCU). Remember to include the earth
for the new circuit into the bathroom's equipotential bonding.


I think I'll take this approach as it will be as easy as just taking a
single earth wire down.

* One could argue that for a pull cord switch, where any metallic
part of the switch is out of reach, one could omit the earthing
without too much risk. Better choose a lamp fitting that is double
insulated and does not require an earth.


Yes, the pull cord will provide some isolation and she is under
instruction not to touch the metallic part until it's sorted.

  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,970
Default Is it OK to borrow an earth?

James Wilkinson Sword wrote:

All my lights are motion sensors, I have zero light switches in my house.
Switches are for the last century.


So when you fall asleep watching the TV you wake up in darkness?

OK I suppose but I think I'd find it a bit worrying.

--
Chris Green
·


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,434
Default Is it OK to borrow an earth?

On 09/03/18 05:42, SteveE wrote:

I think I'll take this approach as it will be as easy as just taking a
single earth wire down.



You could legitimately take a single earth to the nearest light on the
same circuit that does have an earth. For this, it would be preferable
to use a single insulated earth wire with green/yellow insulation. Often
called "singles" and available from all good electrical wholesalers
(some like TLC should be able to sell a length rather than a reel).

I don't have the regs to hand so not 100% sure if a CPC (earth) in this
scenario *must* be insulated, but it shows the purpose clearly which is
worthwhile.
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Is it OK to borrow an earth?

In article ,
Tim Watts wrote:
You could legitimately take a single earth to the nearest light on the
same circuit that does have an earth. For this, it would be preferable
to use a single insulated earth wire with green/yellow insulation. Often
called "singles" and available from all good electrical wholesalers
(some like TLC should be able to sell a length rather than a reel).


Chances are since it's old wiring there is no earth to any lighting
circuit.

--
*Very funny Scotty, now beam down my clothes.

Dave Plowman London SW
To e-mail, change noise into sound.
  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Is it OK to borrow an earth?

In article ,
James Wilkinson Sword wrote:
If I fall asleep I want it dark so I can sleep properly. The light
simply comes on as soon as I stand up or wave my hand.


And actually it stays on most of the time due to cats wandering about.


A real energy saver, that.

--
*Real men don't waste their hormones growing hair

Dave Plowman London SW
To e-mail, change noise into sound.
  #14   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Is it OK to borrow an earth?

On 09/03/2018 00:52, James Wilkinson Sword wrote:
On Thu, 08 Mar 2018 16:44:54 -0000, SteveE wrote:

My 89 y/o mother can no longer reach the switch above the mirror and I
want to change it for a LED pullcord light.

The old light was installed by a bathroom fitter and was not earthed.

This light requires an earth connection but further investigation has
revealed that her upstairs lighting circuit has no earth.

Can I borrow an earth from an accessible ring-circuit in these
circumstances?


Of course.* All earths are the same, they're just connected together in
the CU.* They don't go through seperate fuses/breakers/switches or
anything.


I was going to say it was not allowed. And you have just confirmed that.

--
Adam
  #15   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Is it OK to borrow an earth?

On 09/03/2018 11:29, Tim Watts wrote:
On 09/03/18 05:42, SteveE wrote:

I think I'll take this approach as it will be as easy as just taking a
single earth wire down.



You could legitimately take a single earth to the nearest light on the
same circuit that does have an earth. For this, it would be preferable
to use a single insulated earth wire with green/yellow insulation. Often
called "singles" and available from all good electrical wholesalers
(some like TLC should be able to sell a length rather than a reel).

I don't have the regs to hand so not 100% sure if a CPC (earth) in this
scenario *must* be insulated, but it shows the purpose clearly which is
worthwhile.



It's worse than that. It would have to be 4mm green/yellow and follow
the route/cable run of the live conductor unless that circuit is RCD
protected.

It's a while since this one came up at work but I am sure that was the
outcome.

--
Adam


  #16   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,434
Default Is it OK to borrow an earth?

On 09/03/18 19:24, ARW wrote:
On 09/03/2018 11:29, Tim Watts wrote:
On 09/03/18 05:42, SteveE wrote:

I think I'll take this approach as it will be as easy as just taking a
single earth wire down.



You could legitimately take a single earth to the nearest light on the
same circuit that does have an earth. For this, it would be preferable
to use a single insulated earth wire with green/yellow insulation.
Often called "singles" and available from all good electrical
wholesalers (some like TLC should be able to sell a length rather than
a reel).

I don't have the regs to hand so not 100% sure if a CPC (earth) in
this scenario *must* be insulated, but it shows the purpose clearly
which is worthwhile.



It's worse than that. It would have to be 4mm green/yellow


Is that coming from the same rules that govern the size of a lone earth
rod conductor (mechanical strength)?

and follow
the route/cable run of the live conductor unless that circuit is RCD
protected.


I wouldn't even know where to start looking that one up!


It's a while since this one came up at work but I am sure that was the
outcome.


  #17   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Is it OK to borrow an earth?

In article ,
James Wilkinson Sword wrote:
I don't have auto-lights to save energy, I have them to save the bother
of trying to turn on a switch when my hands are full.


Thought at your age it would be better to wank in the dark? Saves scaring
the pets too.

--
*A day without sunshine is like... night.*

Dave Plowman London SW
To e-mail, change noise into sound.
  #18   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Is it OK to borrow an earth?

On 09/03/2018 20:33, Tim Watts wrote:
On 09/03/18 19:24, ARW wrote:
On 09/03/2018 11:29, Tim Watts wrote:
On 09/03/18 05:42, SteveE wrote:

I think I'll take this approach as it will be as easy as just taking a
single earth wire down.


You could legitimately take a single earth to the nearest light on
the same circuit that does have an earth. For this, it would be
preferable to use a single insulated earth wire with green/yellow
insulation. Often called "singles" and available from all good
electrical wholesalers (some like TLC should be able to sell a length
rather than a reel).

I don't have the regs to hand so not 100% sure if a CPC (earth) in
this scenario *must* be insulated, but it shows the purpose clearly
which is worthwhile.



It's worse than that. It would have to be 4mm green/yellow


Is that coming from the same rules that govern the size of a lone earth
rod conductor (mechanical strength)?


And supplementary bonding

and follow the route/cable run of the live conductor unless that
circuit is RCD protected.


I wouldn't even know where to start looking that one up!


I am pretty sure that it is in one of my NICEIC snags and solutions
books. I'll take them to work today as I really will be doing nothing at
all when I get there apart from getting paid.


--
Adam
  #19   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Is it OK to borrow an earth?

On 09/03/2018 18:53, Dave Plowman (News) wrote:
In article ,
James Wilkinson Sword wrote:
If I fall asleep I want it dark so I can sleep properly. The light
simply comes on as soon as I stand up or wave my hand.


And actually it stays on most of the time due to cats wandering about.


A real energy saver, that.

:-)

--
Adam
  #20   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,523
Default Is it OK to borrow an earth?

On 10/03/2018 00:48, James Wilkinson Sword wrote:
On Sat, 10 Mar 2018 00:28:31 -0000, Dave Plowman (News)
wrote:

In article ,
** James Wilkinson Sword wrote:
I don't have auto-lights to save energy, I have them to save the bother
of trying to turn on a switch when my hands are full.


Thought at your age it would be better to wank in the dark? Saves scaring
the pets too.


I like the way you assume I use two hands to wank.* Are you dreaming of
my huge cock?


Gentlemen! Please!

Bill


  #21   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 10,487
Default Is it OK to borrow an earth?

On Sat, 10 Mar 2018 09:16:01 +0000, Bill Wright wrote:


Gentlemen! Please!

Bill


"Gentlemen"? What an oaf!
  #22   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Is it OK to borrow an earth?

On 09/03/2018 20:33, Tim Watts wrote:
On 09/03/18 19:24, ARW wrote:
On 09/03/2018 11:29, Tim Watts wrote:
On 09/03/18 05:42, SteveE wrote:

I think I'll take this approach as it will be as easy as just taking a
single earth wire down.


You could legitimately take a single earth to the nearest light on
the same circuit that does have an earth. For this, it would be
preferable to use a single insulated earth wire with green/yellow
insulation. Often called "singles" and available from all good
electrical wholesalers (some like TLC should be able to sell a length
rather than a reel).

I don't have the regs to hand so not 100% sure if a CPC (earth) in
this scenario *must* be insulated, but it shows the purpose clearly
which is worthwhile.



It's worse than that. It would have to be 4mm green/yellow


Is that coming from the same rules that govern the size of a lone earth
rod conductor (mechanical strength)?




543.1.1 The cross-sectional area of every protective conductor SNIP
If the protective conductor
(iii) is not an integral part of a cable, or
(iv) is not formed by conduit, ducting or trunking, or
(v) is not contained in an enclosure formed by a wiring system.

the cross-sectional area shall not be less than 2.5mm^2 copper
equivalent if protection against mechanical damage is provided, and
4mm^2 copper equivalent if mechanical damage is not provided


and follow the route/cable run of the live conductor unless that
circuit is RCD protected.


I wouldn't even know where to start looking that one up!


543.6.1 Where overcurrent protective devices are used for fault
protection, the protective conductor shall be incorporated in the same
wiring system as the live conductors or in their immediate proximity

I do believe that should answer your questions.

I dunno where the RCD bit came into it.

--
Adam
  #23   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Is it OK to borrow an earth?

In article ,
James Wilkinson Sword wrote:
Thought at your age it would be better to wank in the dark? Saves scaring
the pets too.


I like the way you assume I use two hands to wank. Are you dreaming of my huge cock?


Was assuming you use one hand to hold down your incontinence pants. But
needing the light on does explain things - so you can find it.

--
*Women like silent men; they think they're listening.

Dave Plowman London SW
To e-mail, change noise into sound.
  #24   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 10,487
Default Is it OK to borrow an earth?

On Sat, 10 Mar 2018 11:25:05 +0000 (GMT), Dave Lowman (News) wrote:


I like the way you assume I use two hands to wank. Are you dreaming of my huge cock?


Was assuming you use one hand to hold down your incontinence pants. But
needing the light on does explain things - so you can find it.


Yeah, KEEP feeding the abnormal filthy ******! tsk
  #25   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,434
Default Is it OK to borrow an earth?

On 10/03/18 07:02, ARW wrote:
and follow the route/cable run of the live conductor unless that
circuit is RCD protected.


I wouldn't even know where to start looking that one up!


I am pretty sure that it is in one of my NICEIC snags and solutions
books. I'll take them to work today as I really will be doing nothing at
all when I get there apart from getting paid.



I've got one of those - I'll have a look...


  #26   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,434
Default Is it OK to borrow an earth?

On 10/03/18 10:17, ARW wrote:
On 09/03/2018 20:33, Tim Watts wrote:
On 09/03/18 19:24, ARW wrote:


Is that coming from the same rules that govern the size of a lone
earth rod conductor (mechanical strength)?




543.1.1 The cross-sectional area of every protective conductor SNIP
If the protective conductor
(iii) is not an integral part of a cable, or
(iv) is not formed by conduit, ducting or trunking, or
(v) is not contained in an enclosure formed by a wiring system.

the cross-sectional area shall not be less than 2.5mm^2 copper
equivalent if protection against mechanical damage is provided, and
4mm^2 copper equivalent if mechanical damage is not provided


Ah - thank you

  #27   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,157
Default Is it OK to borrow an earth?

On 10/03/2018 10:17, ARW wrote:
On 09/03/2018 20:33, Tim Watts wrote:
On 09/03/18 19:24, ARW wrote:
On 09/03/2018 11:29, Tim Watts wrote:
On 09/03/18 05:42, SteveE wrote:

I think I'll take this approach as it will be as easy as just taking a
single earth wire down.


You could legitimately take a single earth to the nearest light on
the same circuit that does have an earth. For this, it would be
preferable to use a single insulated earth wire with green/yellow
insulation. Often called "singles" and available from all good
electrical wholesalers (some like TLC should be able to sell a
length rather than a reel).

I don't have the regs to hand so not 100% sure if a CPC (earth) in
this scenario *must* be insulated, but it shows the purpose clearly
which is worthwhile.


It's worse than that. It would have to be 4mm green/yellow


Is that coming from the same rules that govern the size of a lone
earth rod conductor (mechanical strength)?




543.1.1 The cross-sectional area of every protective conductor SNIP
If the protective conductor
(iii) is not an integral part of a cable, or
(iv) is not formed by conduit, ducting or trunking, or
(v) is not contained in an enclosure formed by a wiring system.

the cross-sectional area shall not be less than 2.5mm^2 copper
equivalent if protection against mechanical damage is provided, and
4mm^2 copper equivalent if mechanical damage is not provided


So it doesn't specify it has to follow the cable run of the live conductor?

and follow the route/cable run of the live conductor unless that
circuit is RCD protected.


I wouldn't even know where to start looking that one up!


543.6.1 Where overcurrent protective devices are used for fault
protection, the protective conductor shall be incorporated in the same
wiring system as the live conductors or in their immediate proximity


Is a wiring system in this case the 'whole house'?
  #28   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,679
Default Is it OK to borrow an earth?

pamela Wrote in message:
On 23:06 8 Mar 2018, Fredxx wrote:

On 08/03/2018 22:17, pamela wrote:
On 16:44 8 Mar 2018, SteveE wrote:

My 89 y/o mother can no longer reach the switch above the mirror
and I want to change it for a LED pullcord light.

The old light was installed by a bathroom fitter and was not
earthed.

This light requires an earth connection but further
investigation has revealed that her upstairs lighting circuit
has no earth.

Can I borrow an earth from an accessible ring-circuit in these
circumstances?

Depending on your situation, I wonder if it may be easier for
your mum to have a motion sensor switch. It could be a
replacement for the existing switch or some bathroom light
fittings come with one built in.


I think the issue is the light doesn't have an earth connection.

A pull cord switch doesn't need an earth.

I have often thought passive IR motion sensors are not used often
enough, but if still in a bath, such a switch is of little use,
and a pain if you actually want darkness.


I think there are some sensors which use RF and are exceptionally
sensitive compared to infrared. I can see times when an on or off
override would be useful but for most of the time sensor-based light
could be very convenient.

I popped a couple of battery operated PIR lighting strips into the
bathroom (one is stuck under the bathroom cabinet and provides
temporary lighting when you wash your hands). I would like to have
ther main light on a sensor but the extractor fan comes on for 20
minutes when the room light is operated and it can be a bit
annoying.


Switch it off before putting the light on?
--
Jim K


----Android NewsGroup Reader----
http://usenet.sinaapp.com/
  #29   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 58
Default Is it OK to borrow an earth?

On Friday, March 9, 2018 at 7:41:26 PM UTC, James Wilkinson Sword wrote:
On Fri, 09 Mar 2018 18:53:43 -0000, Dave Plowman (News) wrote:

In article ,
James Wilkinson Sword wrote:
If I fall asleep I want it dark so I can sleep properly. The light
simply comes on as soon as I stand up or wave my hand.


And actually it stays on most of the time due to cats wandering about.


A real energy saver, that.


They're LED. And I prefer my pets to be able to see where they're going.

I don't have auto-lights to save energy, I have them to save the bother of trying to turn on a switch when my hands are full.

--
What lives in the sea, and goes dah di dah dit, dah dah dit dah?
A morse cod.



A sea cu - cumber.(dah di dah dit, dah dah dit dah)

R
  #30   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 10,487
Default Troll-feeding Senile Yank Alert!

On Sun, 25 Mar 2018 10:54:54 -0700 (PDT), , yet another
mentally handicapped, troll-feeding, senile Yank, blabbered:


A sea cu - cumber.(dah di dah dit, dah dah dit dah)

R


Yeah, Yankie idiot, make the Scottish idiot happy!
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Anyone Near Myrtle Beach SC - have a shop I can rent/borrow for a few hours? Rob V Woodworking 7 October 3rd 05 04:28 PM
Help: Need Solartron 7061 manual, borrow EROMs Ancient_Hacker Electronics Repair 0 June 7th 05 12:37 PM
I hate to borrow tools twfsa Home Repair 9 February 18th 05 02:54 AM
Wanted to borrow or rent in London - floor roller anthony james UK diy 14 May 4th 04 09:00 PM
Need to borrow/rent moisture meter in OR Kelly E Jones Woodworking 5 September 9th 03 08:31 PM


All times are GMT +1. The time now is 01:17 AM.

Powered by vBulletin® Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Copyright ©2004-2025 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"