UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8,019
Default Megger "funny"

Got a heating element in a wallpaper stripper which is blowing 30mA RCD.

Testing live to earth on an old (but "electronic" rather than wind-up)
Megger (which seems to provide 320 volts DC) gives ~ 5 MegOhm.

Testing on a DVM gives ~ 200 kOhm, corresponding to a little over 1 mA
leakage current on mains.

So why the trip, especially given the Megger reading? Or is the megger
f**ed?

Whatever, I guess I need a new megger, any views on the £30 Chinese
models from eBay, or should I be looking at a second hand Avo / Robin /
Fluke etc? This is not for "professional" use, it probably only comes
out a couple of times a year.
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default Megger "funny"

On Thursday, 4 January 2018 21:01:21 UTC, newshound wrote:
Got a heating element in a wallpaper stripper which is blowing 30mA RCD.

Testing live to earth on an old (but "electronic" rather than wind-up)
Megger (which seems to provide 320 volts DC) gives ~ 5 MegOhm.

Testing on a DVM gives ~ 200 kOhm, corresponding to a little over 1 mA
leakage current on mains.

So why the trip, especially given the Megger reading? Or is the megger
f**ed?

Whatever, I guess I need a new megger, any views on the £30 Chinese
models from eBay, or should I be looking at a second hand Avo / Robin /
Fluke etc? This is not for "professional" use, it probably only comes
out a couple of times a year.


A microwave turntable motor can do that. Crank it at suitable speed to put out upto 1kV, use 2 meters to measure V & i. The downside is output voltage is unsteady, affecting accuracy.


NT
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,066
Default Megger "funny"

On Thursday, 4 January 2018 21:01:21 UTC, newshound wrote:
Got a heating element in a wallpaper stripper which is blowing 30mA RCD.

Testing live to earth on an old (but "electronic" rather than wind-up)
Megger (which seems to provide 320 volts DC) gives ~ 5 MegOhm.

Testing on a DVM gives ~ 200 kOhm, corresponding to a little over 1 mA
leakage current on mains.

So why the trip, especially given the Megger reading? Or is the megger
f**ed?

Whatever, I guess I need a new megger, any views on the £30 Chinese
models from eBay, or should I be looking at a second hand Avo / Robin /
Fluke etc? This is not for "professional" use, it probably only comes
out a couple of times a year.


The steam may be getting in somewhere and effecting things.
When it drys out,it may give good reading.
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,766
Default Megger "funny"

newshound explained :
Whatever, I guess I need a new megger, any views on the £30 Chinese models
from eBay, or should I be looking at a second hand Avo / Robin / Fluke etc?
This is not for "professional" use, it probably only comes out a couple of
times a year.


I bought one years ago, unlikely the same model, but it did 1,000, 500
and 250v, with a low voltage resistance test, plus LCD display. I
checked the voltage droop under load and I must say it proved to be
quite well speced for holding up its voltage and accurately calibrated.
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,237
Default Megger "funny"

newshound wrote:

Got a heating element in a wallpaper stripper which is blowing 30mA RCD.

Testing live to earth on an old (but "electronic" rather than wind-up)
Megger (which seems to provide 320 volts DC) gives ~ 5 MegOhm.

Testing on a DVM gives ~ 200 kOhm, corresponding to a little over 1 mA
leakage current on mains.

So why the trip, especially given the Megger reading? Or is the megger
f**ed?

Whatever, I guess I need a new megger, any views on the £30 Chinese
models from eBay, or should I be looking at a second hand Avo / Robin /
Fluke etc? This is not for "professional" use, it probably only comes
out a couple of times a year.


Can you test the leakage to the casing of the element on its own removed
from the stripper? If it is still 5 megohms then it is defective. The
discrepancy in the readings is surprising but the cause is uncertain.
Can you test both instruments on a one megohm high voltage resistor?



--

Roger Hayter


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8,019
Default Megger "funny"

On 05/01/2018 08:52, Roger Hayter wrote:
newshound wrote:

Got a heating element in a wallpaper stripper which is blowing 30mA RCD.

Testing live to earth on an old (but "electronic" rather than wind-up)
Megger (which seems to provide 320 volts DC) gives ~ 5 MegOhm.

Testing on a DVM gives ~ 200 kOhm, corresponding to a little over 1 mA
leakage current on mains.

So why the trip, especially given the Megger reading? Or is the megger
f**ed?

Whatever, I guess I need a new megger, any views on the £30 Chinese
models from eBay, or should I be looking at a second hand Avo / Robin /
Fluke etc? This is not for "professional" use, it probably only comes
out a couple of times a year.


Can you test the leakage to the casing of the element on its own removed
from the stripper? If it is still 5 megohms then it is defective. The
discrepancy in the readings is surprising but the cause is uncertain.
Can you test both instruments on a one megohm high voltage resistor?



That test was with the element removed. I agree that 5 meg is defective,
but wouldn't necessarily trip an RCD. Didn't have any suitable resistors
to hand when checking, will have to drag out a deeply buried box of
"bits too useful to throw away".

Real purpose of post was to get views on cheap Chinese instruments.
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8,019
Default Megger "funny"

On 05/01/2018 08:50, Harry Bloomfield wrote:
newshound explained :
Whatever, I guess I need a new megger, any views on the £30 Chinese
models from eBay, or should I be looking at a second hand Avo / Robin
/ Fluke etc? This is not for "professional" use, it probably only
comes out a couple of times a year.


I bought one years ago, unlikely the same model, but it did 1,000, 500
and 250v, with a low voltage resistance test, plus LCD display. I
checked the voltage droop under load and I must say it proved to be
quite well speced for holding up its voltage and accurately calibrated.


Thanks, that is encouraging.
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,783
Default Megger "funny"

On Thu, 04 Jan 2018 21:01:19 +0000, newshound wrote:

Whatever, I guess I need a new megger, any views on the £30 Chinese
models from eBay, or should I be looking at a second hand Avo / Robin /
Fluke etc? This is not for "professional" use, it probably only comes
out a couple of times a year.



I bought a brand new Megger multimeter last year and it really wasn't
expensive; came in at well under 100 quid.


--
This message may be freely reproduced without limit or charge only via
the Usenet protocol. Reproduction in whole or part through other
protocols, whether for profit or not, is conditional upon a charge of
GBP10.00 per reproduction. Publication in this manner via non-Usenet
protocols constitutes acceptance of this condition.
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,783
Default Megger "funny"

On Fri, 05 Jan 2018 15:43:19 +0000, newshound wrote:

Real purpose of post was to get views on cheap Chinese instruments.


Well, they're a *hell* of a lot better than they used to be. They're even
making some respectable oscilloscopes suitable for pro use, too.



--
This message may be freely reproduced without limit or charge only via
the Usenet protocol. Reproduction in whole or part through other
protocols, whether for profit or not, is conditional upon a charge of
GBP10.00 per reproduction. Publication in this manner via non-Usenet
protocols constitutes acceptance of this condition.
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 40,893
Default Megger "funny"

Cursitor Doom wrote
newshound wrote


Whatever, I guess I need a new megger, any views on the £30
Chinese models from eBay, or should I be looking at a second
hand Avo / Robin / Fluke etc? This is not for "professional" use,
it probably only comes out a couple of times a year.


I bought a brand new Megger multimeter last year and
it really wasn't expensive; came in at well under 100 quid.


Thats stupidly expensive IMO.

I've got a Fluke 19 that didnt cost anything like that.



  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 5,774
Default Megger "funny"

On 04/01/2018 21:01, newshound wrote:


So why the trip, especially given the Megger reading? Or is the megger
f**ed?


Did you test it full of boiling hot water - or when drained?


--
mailto : news {at} admac {dot} myzen {dot} co {dot} uk
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,237
Default Megger "funny"

newshound wrote:

On 05/01/2018 08:52, Roger Hayter wrote:
newshound wrote:

Got a heating element in a wallpaper stripper which is blowing 30mA RCD.

Testing live to earth on an old (but "electronic" rather than wind-up)
Megger (which seems to provide 320 volts DC) gives ~ 5 MegOhm.

Testing on a DVM gives ~ 200 kOhm, corresponding to a little over 1 mA
leakage current on mains.

So why the trip, especially given the Megger reading? Or is the megger
f**ed?

Whatever, I guess I need a new megger, any views on the £30 Chinese
models from eBay, or should I be looking at a second hand Avo / Robin /
Fluke etc? This is not for "professional" use, it probably only comes
out a couple of times a year.


Can you test the leakage to the casing of the element on its own removed
from the stripper? If it is still 5 megohms then it is defective. The
discrepancy in the readings is surprising but the cause is uncertain.
Can you test both instruments on a one megohm high voltage resistor?



That test was with the element removed. I agree that 5 meg is defective,
but wouldn't necessarily trip an RCD. Didn't have any suitable resistors
to hand when checking, will have to drag out a deeply buried box of
"bits too useful to throw away".

Real purpose of post was to get views on cheap Chinese instruments.


The trouble with cheap Chinese imports is that they may be good,
mediocre or plain fraudulent, and it is hard to tell in advance.

The market for insulation testers is mainly to electricians and I would
suggest buying one from a UK based wholesaler who has to take some
responsibility for what is being sold. e.g.

http://cpc.farnell.com/c/test-equipm...earchlookahead

BTW, your element might leak a lot more when it is hot. I don't know
the full failure mechanism, but they tend to fail abruptly with an arc
to earth internally at some point.



--

Roger Hayter
  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 108
Default Megger "funny"

On 2018-01-05 15:43, newshound wrote:
On 05/01/2018 08:52, Roger Hayter wrote:
newshound wrote:

Got a heating element in a wallpaper stripper which is blowing 30mA RCD.

Testing live to earth on an old (but "electronic" rather than wind-up)
Megger (which seems to provide 320 volts DC) gives ~ 5 MegOhm.

Testing on a DVM gives ~ 200 kOhm, corresponding to a little over 1 mA
leakage current on mains.


Can you test both instruments on a one megohm high voltage resistor?

That test was with the element removed. I agree that 5 meg is defective,
but wouldn't necessarily trip an RCD. Didn't have any suitable resistors
to hand when checking...


You've already told us you've got one. Your DVM should have a constant
input resistance (usually 10 MOhms, but check the manual). So, while
you're reading the 320 V output of the Megger on your DVM also check the
Megger to see what resistance it sees looking in to the DVM.


--
Graham Nye
news(a)thenyes.org.uk
  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8,019
Default Megger "funny"

On 05/01/2018 21:31, Roger Hayter wrote:
newshound wrote:

On 05/01/2018 08:52, Roger Hayter wrote:
newshound wrote:

Got a heating element in a wallpaper stripper which is blowing 30mA RCD.

Testing live to earth on an old (but "electronic" rather than wind-up)
Megger (which seems to provide 320 volts DC) gives ~ 5 MegOhm.

Testing on a DVM gives ~ 200 kOhm, corresponding to a little over 1 mA
leakage current on mains.

So why the trip, especially given the Megger reading? Or is the megger
f**ed?

Whatever, I guess I need a new megger, any views on the £30 Chinese
models from eBay, or should I be looking at a second hand Avo / Robin /
Fluke etc? This is not for "professional" use, it probably only comes
out a couple of times a year.

Can you test the leakage to the casing of the element on its own removed
from the stripper? If it is still 5 megohms then it is defective. The
discrepancy in the readings is surprising but the cause is uncertain.
Can you test both instruments on a one megohm high voltage resistor?



That test was with the element removed. I agree that 5 meg is defective,
but wouldn't necessarily trip an RCD. Didn't have any suitable resistors
to hand when checking, will have to drag out a deeply buried box of
"bits too useful to throw away".

Real purpose of post was to get views on cheap Chinese instruments.


The trouble with cheap Chinese imports is that they may be good,
mediocre or plain fraudulent, and it is hard to tell in advance.

The market for insulation testers is mainly to electricians and I would
suggest buying one from a UK based wholesaler who has to take some
responsibility for what is being sold. e.g.

http://cpc.farnell.com/c/test-equipm...earchlookahead


Good point, I suppose this one

http://cpc.farnell.com/tenma/72-9400...ohm/dp/IN07406

is just about affordable (for my very limited use)


BTW, your element might leak a lot more when it is hot. I don't know
the full failure mechanism, but they tend to fail abruptly with an arc
to earth internally at some point.



Realise that, but all this testing was done "cold". Took the element out
when it failed open circuit, just did the insulation resistance test out
of interest.
  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8,019
Default Megger "funny"

On 05/01/2018 20:49, alan_m wrote:
On 04/01/2018 21:01, newshound wrote:


So why the trip, especially given the Megger reading? Or is the megger
f**ed?


Did you test it full of boiling hot water - or when drained?


This was cold, it went open circuit first (on a supply without RCD),
only discovered the 30 mA trip when I took it home to test.


  #16   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8,019
Default Megger "funny"

On 09/01/2018 16:48, Graham Nye wrote:
On 2018-01-05 15:43, newshound wrote:
On 05/01/2018 08:52, Roger Hayter wrote:
newshound wrote:

Got a heating element in a wallpaper stripper which is blowing 30mA RCD.

Testing live to earth on an old (but "electronic" rather than wind-up)
Megger (which seems to provide 320 volts DC) gives ~ 5 MegOhm.

Testing on a DVM gives ~ 200 kOhm, corresponding to a little over 1 mA
leakage current on mains.


Can you test both instruments on a one megohm high voltage resistor?

That test was with the element removed. I agree that 5 meg is defective,
but wouldn't necessarily trip an RCD. Didn't have any suitable resistors
to hand when checking...


You've already told us you've got one. Your DVM should have a constant
input resistance (usually 10 MOhms, but check the manual). So, while
you're reading the 320 V output of the Megger on your DVM also check the
Megger to see what resistance it sees looking in to the DVM.


Didn't think of that! I have a collection of DVMs but I think the
manuals are long gone. Could of course do some cross calibration.
  #17   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 108
Default Megger "funny"

On 2018-01-09 21:45, newshound wrote:
On 09/01/2018 16:48, Graham Nye wrote:
On 2018-01-05 15:43, newshound wrote:
On 05/01/2018 08:52, Roger Hayter wrote:
newshound wrote:


Can you test both instruments on a one megohm high voltage resistor?

That test was with the element removed. I agree that 5 meg is defective,
but wouldn't necessarily trip an RCD. Didn't have any suitable resistors
to hand when checking...


You've already told us you've got one. Your DVM should have a constant
input resistance (usually 10 MOhms, but check the manual). So, while
you're reading the 320 V output of the Megger on your DVM also check the
Megger to see what resistance it sees looking in to the DVM.


Didn't think of that! I have a collection of DVMs but I think the
manuals are long gone. Could of course do some cross calibration.


If you have multiple DMMs you can use one to check the input resistance
of another at the low voltage used by a DMM. You can then use the
checked one with the Megger.



--
Graham Nye
news(a)thenyes.org.uk
  #18   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,237
Default Megger "funny"

newshound wrote:

On 05/01/2018 21:31, Roger Hayter wrote:

snip


BTW, your element might leak a lot more when it is hot. I don't know
the full failure mechanism, but they tend to fail abruptly with an arc
to earth internally at some point.



Realise that, but all this testing was done "cold". Took the element out
when it failed open circuit, just did the insulation resistance test out
of interest.


Did you mention it had gone open circuit? When they do so they often
seem to have a brief arc internally and sputter metal all over the
insulation, which is generally mineral granules. Then the leakage to
earth is anything from like yours to a dead short.

--

Roger Hayter
  #19   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8,019
Default Megger "funny"

On 09/01/2018 23:06, Roger Hayter wrote:
newshound wrote:

On 05/01/2018 21:31, Roger Hayter wrote:

snip


BTW, your element might leak a lot more when it is hot. I don't know
the full failure mechanism, but they tend to fail abruptly with an arc
to earth internally at some point.



Realise that, but all this testing was done "cold". Took the element out
when it failed open circuit, just did the insulation resistance test out
of interest.


Did you mention it had gone open circuit? When they do so they often
seem to have a brief arc internally and sputter metal all over the
insulation, which is generally mineral granules. Then the leakage to
earth is anything from like yours to a dead short.

Yes I thought that might be what had happened. Just interested that a
megger with 320V DC seemed to give about 1 mA while 240V AC gives 30
mA. But I guess the AC was kicking off an arc.
  #20   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 307
Default Megger "funny"

Aren't mergers limited to 1mA to prevent being used to discipline apprentices?
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generic "megger" Peter Andrews UK diy 21 November 19th 09 09:44 AM
AVO MEGGER insulation tester BM400/2 Adri Electronics Repair 0 May 9th 06 11:10 AM
Service Manual/Full Schematic for Biddle BM10 Megger The Boz Electronics Repair 3 December 1st 05 01:11 AM
CNC machine insulation testing with a megger Mike Metalworking 2 January 29th 05 03:28 AM
BIDDLE megger malfunction... Tor Tveitane Electronics Repair 0 March 12th 04 06:15 PM


All times are GMT +1. The time now is 11:27 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"