Has anyone experience of gluing 20mm air gap glazing into crittal
steel frames?

They would end up flush with the outer edge and I suppose some
allowance must be made for drainage or breathing to prevent premature
"blown" panels.

Reason being pvc frames would be out of keeping and aluminium not much
better and too expensive.

I would consider gluing some insulation strips to the steel inside to
make a thermal break.

AJH
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 245
Default retro fitting double glazing

On Wed, 11 Oct 2017 12:53:16 +0100 (GMT+01:00), jim k wrote:

Wrote in message:
Has anyone experience of gluing 20mm air gap glazing into crittal
steel frames?

They would end up flush with the outer edge and I suppose some
allowance must be made for drainage or breathing to prevent premature
"blown" panels.

Reason being pvc frames would be out of keeping and aluminium not much
better and too expensive.

I would consider gluing some insulation strips to the steel inside to
make a thermal break.

AJH


Would the critall frames offer any protection to the dg unit's
perimeter seal?

Uv exposure (at least) degrades the seal leading to premature failure.


Does the seal come over the outer pane of glass as this is the only
bit that would be slightly proud I think?

AJH
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default retro fitting double glazing

On Wednesday, 11 October 2017 12:17:31 UTC+1, wrote:
Has anyone experience of gluing 20mm air gap glazing into crittal
steel frames?

They would end up flush with the outer edge and I suppose some
allowance must be made for drainage or breathing to prevent premature
"blown" panels.

Reason being pvc frames would be out of keeping and aluminium not much
better and too expensive.

I would consider gluing some insulation strips to the steel inside to
make a thermal break.

AJH


Frame conduction is the major problem with Crittalls. I would have thought you'd be better off with secondary dg.


NT
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,066
Default retro fitting double glazing

On Wednesday, 11 October 2017 12:17:31 UTC+1, wrote:
Has anyone experience of gluing 20mm air gap glazing into crittal
steel frames?

They would end up flush with the outer edge and I suppose some
allowance must be made for drainage or breathing to prevent premature
"blown" panels.

Reason being pvc frames would be out of keeping and aluminium not much
better and too expensive.

I would consider gluing some insulation strips to the steel inside to
make a thermal break.

AJH


Steel frames are bad news.
Get rid of them.

  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,024
Default retro fitting double glazing

On Wed, 11 Oct 2017 12:17:27 +0100, wrote:

Has anyone experience of gluing 20mm air gap glazing into crittal
steel frames?


No, but I have lived with these dreadful windows on a number of
houses. For evolutionary biologists they are wonderful, over a winter
the condensation on them supports vast colonies of fungi which alter
colour from virulent purple through snot green to bright yellow.
Attacked with bleach the hardiest survivors start growing the second
you turn your back.

As replacing the windows wasn't an option most occupants resorted to
retrofitting closed cell foam draught proofing around the window/frame
and fitting secondary glazing which was removed in summer. This kept
the fungal growth to a minimum and stopped the draughts which are
Crittal's trademark attribute.

They would end up flush with the outer edge and I suppose some
allowance must be made for drainage or breathing to prevent premature
"blown" panels.


Reason being pvc frames would be out of keeping and aluminium not much
better and too expensive.

I would consider gluing some insulation strips to the steel inside to
make a thermal break.


I can't see adding a thermal break inside achieving much, it would
leave a cold strip which would still attract condensation. Looking
around the web using secondary glazing appears to be the method of
choice for dealing with the things.



  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default retro fitting double glazing

In article ,
Peter Parry wrote:
Has anyone experience of gluing 20mm air gap glazing into crittal
steel frames?


No, but I have lived with these dreadful windows on a number of
houses. For evolutionary biologists they are wonderful, over a winter
the condensation on them supports vast colonies of fungi which alter
colour from virulent purple through snot green to bright yellow.
Attacked with bleach the hardiest survivors start growing the second
you turn your back.


Had them in my parent's house. Other trick was rust and or expansion etc
broke glass regularly. Which lead me to believe it was normal to have to
replace several panes of glass every year.

--
*Ah, I see the f**k-up fairy has visited us again

Dave Plowman London SW
To e-mail, change noise into sound.
  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 245
Default retro fitting double glazing

On Wed, 11 Oct 2017 18:37:23 +0100, "Dave Plowman (News)"
wrote:

In article ,
Peter Parry wrote:
Has anyone experience of gluing 20mm air gap glazing into crittal
steel frames?


No, but I have lived with these dreadful windows on a number of
houses. For evolutionary biologists they are wonderful, over a winter
the condensation on them supports vast colonies of fungi which alter
colour from virulent purple through snot green to bright yellow.
Attacked with bleach the hardiest survivors start growing the second
you turn your back.


Not in my experience of these in the last 35 years Peter, perhaps you
should visit and see?

Had them in my parent's house. Other trick was rust and or expansion etc
broke glass regularly. Which lead me to believe it was normal to have to
replace several panes of glass every year.


These are galvanised so have not spalled and broken the glass, in fact
the only pane I have replaced was one I broke with a football.

They are set in a 9" solid brick wall so the next thing on my list to
cut thermal losses.

AJH
  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default retro fitting double glazing

In article ,
wrote:
Had them in my parent's house. Other trick was rust and or expansion etc
broke glass regularly. Which lead me to believe it was normal to have to
replace several panes of glass every year.


These are galvanised so have not spalled and broken the glass, in fact
the only pane I have replaced was one I broke with a football.


I've a feeling a modern putty that flexed would have helped - I'm talking
about a long time ago.

--
*Filthy stinking rich -- well, two out of three ain't bad

Dave Plowman London SW
To e-mail, change noise into sound.
  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,300
Default retro fitting double glazing


"Dave Plowman (News)" wrote in message
...
In article ,
wrote:
Had them in my parent's house. Other trick was rust and or expansion etc
broke glass regularly. Which lead me to believe it was normal to have to
replace several panes of glass every year.


These are galvanised so have not spalled and broken the glass, in fact
the only pane I have replaced was one I broke with a football.


I've a feeling a modern putty that flexed would have helped - I'm talking
about a long time ago.


As you always are, Dave.
It's now 2017.
Keep up.
Article 50 has been triggered.
Tough ****.




  #18   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default retro fitting double glazing

On Friday, 13 October 2017 12:31:00 UTC+1, wrote:
On Wed, 11 Oct 2017 14:13:00 +0100, The Natural Philosopher
wrote:
On 11/10/17 13:22, tabbypurr wrote:


Frame conduction is the major problem with Crittalls. I would have thought you'd be better off with secondary dg.


Possibly but I'll pursue this route for a bit: As the galvanised
steel is angle iron and the glass, and its seal, will occupy the
rebate how should I deal with this thermal element.

It is probably worth doing a calculation on the loss through the DG
units versus heatloss throughh the frame

Worse case is that the steel is 3mm thick with a 25mm rebate and 60mm
is exposed on the inside. So on my largest window I have a structural
opening of1550mm wide 1300 with a softwood frame exposed to 30mm and
60mm deep,

Wood surface area 0.1284m2 what's a U value for 60mm softwood?
0.3W/m2 degC

Steel surface area 0.467m2 but what U value as the path is largely a
3mm cross section, possibly 20W/m2 deg C

glass surface area 1.4196 U value 5.6W/m2 degC double glazed might
halve it??

So currently, if the above assumptions are near, I seem to lose about
250W if I heat to 20C and it's OC outside and potentially fitting dg
panes might reduce this by a third. Which may be a saving of 600W
throughout the house.


I do know that they are *******s for frame condensation.


It has never been a problem here.


AJH


If you want to be a lot clearer maybe we can get somewhere.


NT
  #19   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 245
Default retro fitting double glazing

On Sat, 14 Oct 2017 03:51:15 -0700 (PDT), wrote:

On Friday, 13 October 2017 12:31:00 UTC+1, wrote:
On Wed, 11 Oct 2017 14:13:00 +0100, The Natural Philosopher
wrote:
On 11/10/17 13:22, tabbypurr wrote:


Frame conduction is the major problem with Crittalls. I would have thought you'd be better off with secondary dg.


Possibly but I'll pursue this route for a bit: As the galvanised
steel is angle iron and the glass, and its seal, will occupy the
rebate how should I deal with this thermal element.

It is probably worth doing a calculation on the loss through the DG
units versus heatloss throughh the frame

Worse case is that the steel is 3mm thick with a 25mm rebate and 60mm
is exposed on the inside. So on my largest window I have a structural
opening of1550mm wide 1300 with a softwood frame exposed to 30mm and
60mm deep,

Wood surface area 0.1284m2 what's a U value for 60mm softwood?
0.3W/m2 degC

Steel surface area 0.467m2 but what U value as the path is largely a
3mm cross section, possibly 20W/m2 deg C

glass surface area 1.4196 U value 5.6W/m2 degC double glazed might
halve it??

So currently, if the above assumptions are near, I seem to lose about
250W if I heat to 20C and it's OC outside and potentially fitting dg
panes might reduce this by a third. Which may be a saving of 600W
throughout the house.


I do know that they are *******s for frame condensation.


It has never been a problem here.


AJH


If you want to be a lot clearer maybe we can get somewhere.


Okay put more simply: the structural opening is 1550mm wide 1300 high
and has an area of 2.015m2

The timber surround has 30mm exposed and is 60mm deep and thus has an
area of 0.128m2

The steel area viewed from the inside is 0.47m2

The glass area is 1.42

I think I can only reduce loses by 30% with double glazing would
secondary glazing do better?

AJH
  #20   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default retro fitting double glazing

On Saturday, 14 October 2017 19:54:35 UTC+1, wrote:
On Sat, 14 Oct 2017 03:51:15 -0700 (PDT), tabbypurr wrote:
On Friday, 13 October 2017 12:31:00 UTC+1, wrote:
On Wed, 11 Oct 2017 14:13:00 +0100, The Natural Philosopher
wrote:
On 11/10/17 13:22, tabbypurr wrote:


Frame conduction is the major problem with Crittalls. I would have thought you'd be better off with secondary dg.

Possibly but I'll pursue this route for a bit: As the galvanised
steel is angle iron and the glass, and its seal, will occupy the
rebate how should I deal with this thermal element.

It is probably worth doing a calculation on the loss through the DG
units versus heatloss throughh the frame

Worse case is that the steel is 3mm thick with a 25mm rebate and 60mm
is exposed on the inside. So on my largest window I have a structural
opening of1550mm wide 1300 with a softwood frame exposed to 30mm and
60mm deep,

Wood surface area 0.1284m2 what's a U value for 60mm softwood?
0.3W/m2 degC

Steel surface area 0.467m2 but what U value as the path is largely a
3mm cross section, possibly 20W/m2 deg C

glass surface area 1.4196 U value 5.6W/m2 degC double glazed might
halve it??

So currently, if the above assumptions are near, I seem to lose about
250W if I heat to 20C and it's OC outside and potentially fitting dg
panes might reduce this by a third. Which may be a saving of 600W
throughout the house.


I do know that they are *******s for frame condensation.

It has never been a problem here.


AJH


If you want to be a lot clearer maybe we can get somewhere.


Okay put more simply: the structural opening is 1550mm wide 1300 high
and has an area of 2.015m2

The timber surround has 30mm exposed and is 60mm deep and thus has an
area of 0.128m2

The steel area viewed from the inside is 0.47m2

The glass area is 1.42

I think I can only reduce loses by 30% with double glazing would
secondary glazing do better?

AJH


DG only reduces heat flow through the glass, secondary glazing tackles frame loss too, which is major with Crittalls. Double secondary glazing would of course be better, since Crittalls are so grim thermally.

Crittalls aren't normally fitted into timber frames if that's what you mean.


NT


  #25   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default retro fitting double glazing

In article ,
wrote:
In the 50's and 60's Crittall windows were always fitted directly to
the brick opening, so your experience is indeed limited.

Not always true in the 20s and 30s


I've never seen a new build (in the 20s&30s) with Crittall where wood was
involved. Any examples?

--
*Dancing is a perpendicular expression of a horizontal desire *

Dave Plowman London SW
To e-mail, change noise into sound.


  #26   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 68
Default retro fitting double glazing

On 16/10/2017 14:40, Dave Plowman (News) wrote:
In article ,
wrote:
In the 50's and 60's Crittall windows were always fitted directly to
the brick opening, so your experience is indeed limited.

Not always true in the 20s and 30s


I've never seen a new build (in the 20s&30s) with Crittall where wood was
involved. Any examples?

errr, my house (Arts and Crafts style, built 1930s) for one, but there
is no shortage of examples around and about (and on the web). My frames
are hardwood with quite decorative internal mouldings and the Crittall
casements set into rebates - most will need rather a lot of TLC next year.
  #28   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default retro fitting double glazing

In article ,
wrote:
On 16/10/2017 14:40, Dave Plowman (News) wrote:
In article ,
wrote:
In the 50's and 60's Crittall windows were always fitted directly to
the brick opening, so your experience is indeed limited.

Not always true in the 20s and 30s


I've never seen a new build (in the 20s&30s) with Crittall where wood was
involved. Any examples?

errr, my house (Arts and Crafts style, built 1930s) for one, but there
is no shortage of examples around and about (and on the web). My frames
are hardwood with quite decorative internal mouldings and the Crittall
casements set into rebates - most will need rather a lot of TLC next year.


Ah - right. A fairy uncommon design? I was more thinking of Art Deco -
concrete everywhere.

--
*Arkansas State Motto: Don't Ask, Don't Tell, Don't Laugh.

Dave Plowman London SW
To e-mail, change noise into sound.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Retro fitting gas burners in coal power plants. Tim Lamb[_2_] UK diy 26 January 28th 16 10:28 PM
Double glazing fitting. FENSA needed? MarkG[_2_] UK diy 7 May 31st 11 10:47 PM
Double glazing fitting questions David WE Roberts[_2_] UK diy 2 June 15th 10 03:12 PM
Retro fitting TRV's - new valve fitting type Tony Collins UK diy 5 November 27th 04 01:12 PM
Cracked outer double glazing pane - UK diy 6 July 9th 03 06:36 PM


All times are GMT +1. The time now is 09:10 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"