We've been having trouble with pumping over. On investigation the
overflow only goes about a foot above water level at its highest, so it
wouldn't take much to make water come out of it.

But what is the overflow for?

Is it just for filling the system?

What would happen if I blocked it?

Andy
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 11,175
Default Header tanks, overflows, and open hot water systems.

In article ,
Vir Campestris writes:
We've been having trouble with pumping over. On investigation the
overflow only goes about a foot above water level at its highest, so it
wouldn't take much to make water come out of it.


This depends on the positioning of the feed and expansion pipe
connections to the system, relative to the pump position and
other flow restrictions.

It can happen if a system is retrofitted with TRV's, increasing
the pressure difference when valves shut off, if the system
wasn't designed for that originally.

Having the feed and expansion pipes connected nearby to each
other avoids this. They can be one common pipe, but it has to
be a thicker pipe, and it can make filling and bleeding the
system more difficult.

But what is the overflow for?


It's not an overflow, it's to allow air to escape, and if a boiler
stat fails on, it allows steam to escape.

Is it just for filling the system?


Not at all.

What would happen if I blocked it?


You might end up with air trapped in parts of the system, and if
the boiler went wrong, you might end up with an explosion of steam
and super-heated water from somewhere, as the fill pipe is usally
thinner and more difficult to eject the water from.

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,066
Default Header tanks, overflows, and open hot water systems.

On Sunday, 22 January 2017 23:59:14 UTC, Andrew Gabriel wrote:
In article ,
Vir Campestris writes:
We've been having trouble with pumping over. On investigation the
overflow only goes about a foot above water level at its highest, so it
wouldn't take much to make water come out of it.


This depends on the positioning of the feed and expansion pipe
connections to the system, relative to the pump position and
other flow restrictions.

It can happen if a system is retrofitted with TRV's, increasing
the pressure difference when valves shut off, if the system
wasn't designed for that originally.

Having the feed and expansion pipes connected nearby to each
other avoids this. They can be one common pipe, but it has to
be a thicker pipe, and it can make filling and bleeding the
system more difficult.

But what is the overflow for?


It's not an overflow, it's to allow air to escape, and if a boiler
stat fails on, it allows steam to escape.

Is it just for filling the system?


Not at all.

What would happen if I blocked it?


You might end up with air trapped in parts of the system, and if
the boiler went wrong, you might end up with an explosion of steam
and super-heated water from somewhere, as the fill pipe is usally
thinner and more difficult to eject the water from.

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]


Another thing that causes pumping over is if a new boiler is fitted.
The waterways are smaller and longer so creating a large pressure difference.
You can especially get a problem if the new boiler has the circulating pump is inside the boiler cabinet.
New heating systems are piped up differently to what they used to be.

When a new boiler is fitted the original pipework often needs to be altered.

This needs fixing toot sweet.
You lose a lot of heat when it's pumping over plus all the water vapour in the roof space can cause condensation and rot. The water gets oxygenated leading to corrosion in your heating system.

Sometimes they get round it by converting the system to a pressurised one. Avoid this if you can, there is a lot more stuff in a pressurised system that can go wrong.
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,564
Default Header tanks, overflows, and open hot water systems.

On Monday, 23 January 2017 08:01:18 UTC, harry wrote:
Sometimes they get round it by converting the system to a pressurised one.
Avoid this if you can, there is a lot more stuff in a pressurised
system that can go wrong.


On the other hand, there's only a finite quantity of water to escape when it does go wrong.

Owain



  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 10,998
Default Header tanks, overflows, and open hot water systems.

Yes if you want to see what happens if it overheats, there were some
admittedly over the top demos on Myth Busters, in one case it went through a
ceiling and roof. Not a good thing.
Brian

--
----- -
This newsgroup posting comes to you directly from...
The Sofa of Brian Gaff...

Blind user, so no pictures please!
"Andrew Gabriel" wrote in message
news
In article ,
Vir Campestris writes:
We've been having trouble with pumping over. On investigation the
overflow only goes about a foot above water level at its highest, so it
wouldn't take much to make water come out of it.


This depends on the positioning of the feed and expansion pipe
connections to the system, relative to the pump position and
other flow restrictions.

It can happen if a system is retrofitted with TRV's, increasing
the pressure difference when valves shut off, if the system
wasn't designed for that originally.

Having the feed and expansion pipes connected nearby to each
other avoids this. They can be one common pipe, but it has to
be a thicker pipe, and it can make filling and bleeding the
system more difficult.

But what is the overflow for?


It's not an overflow, it's to allow air to escape, and if a boiler
stat fails on, it allows steam to escape.

Is it just for filling the system?


Not at all.

What would happen if I blocked it?


You might end up with air trapped in parts of the system, and if
the boiler went wrong, you might end up with an explosion of steam
and super-heated water from somewhere, as the fill pipe is usally
thinner and more difficult to eject the water from.

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]





  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,115
Default Header tanks, overflows, and open hot water systems.

On Sun, 22 Jan 2017 23:05:20 +0000, Vir Campestris wrote:

We've been having trouble with pumping over. On investigation the
overflow only goes about a foot above water level at its highest, so it
wouldn't take much to make water come out of it.

But what is the overflow for?

Is it just for filling the system?

What would happen if I blocked it?

Andy


Blocking it is not a good idea. Things are usually there for a reason.

Two simple solutions:

(1) Turn down the pump

(2) Graft in a small length of pipe to take the pipe higher.

As far as I know the overflow is there to allow for the difference between
the volume of water when hot and cold. As the water heats up it should
move up the pipe, and as it cools it should move down. If the system is
properly set up the water should never come out, but the pipe is also a
safety measure should anything more serious cause the system to build up
pressure. It also copes with the difference in pressure when the pump is
running.

If you keep pumping over there will be a constant flow of aerated water
into your system; as the water heats up it spills hot water over into the
header tank and as it cools down this extra water is drawn back into the
system from the header tank. This can lead to corrosion in the system.

So no, please do not block it. Like screwing down a safety valve because
it keeps letting dangerous pressure out. Addressing the symptom not the
cause.

Cheers


Dave R

--
AMD FX-6300 in GA-990X-Gaming SLI-CF running Windows 7 Pro x64

---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 14,085
Default Header tanks, overflows, and open hot water systems.

On Sun, 22 Jan 2017 23:05:20 +0000, Vir Campestris wrote:

We've been having trouble with pumping over. On investigation the
overflow only goes about a foot above water level at its highest, so it
wouldn't take much to make water come out of it.


Do you mean really mean overflow or the vent pipe coming from the
systems primary?

An overflow should always be above the water line other wise will run
down it and out of the warning pipe outside. Normally caused by the
ball valve jamming open but badly setup expansion tanks can also do
it when the primary water expands on heating and raises the level in
the expansion tank.

An expansion pipe is there to vent the primary circuit or the
domestic ho****er (the primary over the expansion tank, the DHW over
the cold water storage tank). Niether should be blocked. Doing so
runs the risk of an explosion should the boiler fail into "on" mode.

Assuming your "overflow" is really the primary's expansion pipe then
the bend being only a foot above the water level is decidedly low.

Is the pump over a constant drip/trickle when the system is running
or only a little spurt when the pump starts and/or stops?

Has the system ever been balanced?

If TRV's are fitted is there a suitable (possibly automatic) bypass?

--
Cheers
Dave.



  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default Header tanks, overflows, and open hot water systems.

On Tuesday, 24 January 2017 11:26:02 UTC, Dave Liquorice wrote:
On Sun, 22 Jan 2017 23:05:20 +0000, Vir Campestris wrote:

We've been having trouble with pumping over. On investigation the
overflow only goes about a foot above water level at its highest, so it
wouldn't take much to make water come out of it.


Do you mean really mean overflow or the vent pipe coming from the
systems primary?

An overflow should always be above the water line other wise will run
down it and out of the warning pipe outside. Normally caused by the
ball valve jamming open but badly setup expansion tanks can also do
it when the primary water expands on heating and raises the level in
the expansion tank.

An expansion pipe is there to vent the primary circuit or the
domestic ho****er (the primary over the expansion tank, the DHW over
the cold water storage tank). Niether should be blocked. Doing so
runs the risk of an explosion should the boiler fail into "on" mode.


not at all, and a single header tank pipe is allowed. Hazard only occurs if both pipes are blocked AND both boiler stats AND HW/CH stats all fail.

Assuming your "overflow" is really the primary's expansion pipe then
the bend being only a foot above the water level is decidedly low.

Is the pump over a constant drip/trickle when the system is running
or only a little spurt when the pump starts and/or stops?

Has the system ever been balanced?

If TRV's are fitted is there a suitable (possibly automatic) bypass?


Low head is fine is the 2 pipes connect close together on the primary circuit. OTOH if they're on oposite sides of the boiler you'd need more than a foot of head.


NT
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,853
Default Header tanks, overflows, and open hot water systems.

On 24/01/2017 12:13, wrote:
On Tuesday, 24 January 2017 11:26:02 UTC, Dave Liquorice wrote:
On Sun, 22 Jan 2017 23:05:20 +0000, Vir Campestris wrote:

We've been having trouble with pumping over. On investigation the
overflow only goes about a foot above water level at its highest, so it
wouldn't take much to make water come out of it.


Do you mean really mean overflow or the vent pipe coming from the
systems primary?

An overflow should always be above the water line other wise will run
down it and out of the warning pipe outside. Normally caused by the
ball valve jamming open but badly setup expansion tanks can also do
it when the primary water expands on heating and raises the level in
the expansion tank.

An expansion pipe is there to vent the primary circuit or the
domestic ho****er (the primary over the expansion tank, the DHW over
the cold water storage tank). Niether should be blocked. Doing so
runs the risk of an explosion should the boiler fail into "on" mode.


not at all, and a single header tank pipe is allowed. Hazard only occurs if both pipes are blocked AND both boiler stats AND HW/CH stats all fail.

Assuming your "overflow" is really the primary's expansion pipe then
the bend being only a foot above the water level is decidedly low.

Is the pump over a constant drip/trickle when the system is running
or only a little spurt when the pump starts and/or stops?

Has the system ever been balanced?

If TRV's are fitted is there a suitable (possibly automatic) bypass?


Low head is fine is the 2 pipes connect close together on the primary circuit. OTOH if they're on oposite sides of the boiler you'd need more than a foot of head.

Since this post is last -

I stand corrected. The vent pipe.

There are two pipes into the loft - one from the bottom of the header
tank, and one into the air above water level.

Expansion should occur up the other pipe if I block off the one in the air.

One of the rads has both the lockshield and TRV set wide open.

I'll look into tracing where they go. This may be difficult - the boiler
is in a cupboard in the ground floor bathroom, and about 10 pipes go
upwards from there. Failing that, splicing in a higher loop should do.

Thanks
Andy

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Precision Exhaust Header Modeling Systems jon_banquer[_2_] Metalworking 0 October 17th 14 05:44 PM
Flushing rads + heating systems - valves on header tank? David Robinson UK diy 8 November 6th 10 09:49 AM
Why do I have two header tanks? [email protected] UK diy 21 October 21st 07 10:47 AM
Inglis Washer Water Doesn't Stop Filling and Overflows [email protected] Home Repair 2 March 22nd 06 12:17 AM
Too many header tanks? MikeR UK diy 2 March 6th 06 11:29 PM


All times are GMT +1. The time now is 07:17 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"