I intend to replace my existing 8.5kW shower for a 9.5kW one. The
present one is wired in 6mm through a 40A mcb in the CU with a run of about 7 metres with a double-pole isolator in the airing cupboard. My intention is to replace the cable with 10mm through a 50A mcb, and to replace the isolator with a separate shower CU (of this type, Wylex NH204/63), again with a 50A mcb. Any thoughts/recommendations? |
#2
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
Joe Bloggs presented the following explanation :
I intend to replace my existing 8.5kW shower for a 9.5kW one. The present one is wired in 6mm through a 40A mcb in the CU with a run of about 7 metres with a double-pole isolator in the airing cupboard. Assuming 240v - Your 40a and 6mm is just on the borderline for 9.5kW, ignoring any volts drop. Our 9.5Kw was originally an 8Kw shower wired in 6mm on a 40a MCB. It has been fine for the past 10 years. Modern showers can modulate their current needs as well as their flow. |
#3
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
Modern showers can modulate their
current needs as well as their flow. But I bet most users need them on full all the time. |
#4
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22-Jan-17 10:29 AM, Harry Bloomfield wrote:
Joe Bloggs presented the following explanation : I intend to replace my existing 8.5kW shower for a 9.5kW one. The present one is wired in 6mm through a 40A mcb in the CU with a run of about 7 metres with a double-pole isolator in the airing cupboard. Assuming 240v - Your 40a and 6mm is just on the borderline for 9.5kW, ignoring any volts drop. That's why I'm upgrading the supply cable and mcb. Our 9.5Kw was originally an 8Kw shower wired in 6mm on a 40a MCB. It has been fine for the past 10 years. Modern showers can modulate their current needs as well as their flow. What I was really unsure about was the necessity of the separate shower CU. I intend to fit one, even though the shower would be fed from the main CU which is RCD protected. But am I correct in thinking that the shower needs a separate RCD? |
#5
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22/01/2017 11:24, Joe Bloggs wrote:
On 22-Jan-17 10:29 AM, Harry Bloomfield wrote: Joe Bloggs presented the following explanation : I intend to replace my existing 8.5kW shower for a 9.5kW one. The present one is wired in 6mm through a 40A mcb in the CU with a run of about 7 metres with a double-pole isolator in the airing cupboard. Assuming 240v - Your 40a and 6mm is just on the borderline for 9.5kW, ignoring any volts drop. That's why I'm upgrading the supply cable and mcb. Our 9.5Kw was originally an 8Kw shower wired in 6mm on a 40a MCB. It has been fine for the past 10 years. Modern showers can modulate their current needs as well as their flow. What I was really unsure about was the necessity of the separate shower CU. I intend to fit one, even though the shower would be fed from the main CU which is RCD protected. But am I correct in thinking that the shower needs a separate RCD? The shower does not need two lots of RCD protection. -- Adam |
#6
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22/01/2017 10:29, Harry Bloomfield wrote:
Joe Bloggs presented the following explanation : I intend to replace my existing 8.5kW shower for a 9.5kW one. The present one is wired in 6mm through a 40A mcb in the CU with a run of about 7 metres with a double-pole isolator in the airing cupboard. Assuming 240v - Your 40a and 6mm is just on the borderline for 9.5kW, ignoring any volts drop. I would not call it borderline. -- Adam |
#7
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
Joe Bloggs formulated the question :
On 22-Jan-17 10:29 AM, Harry Bloomfield wrote: Joe Bloggs presented the following explanation : I intend to replace my existing 8.5kW shower for a 9.5kW one. The present one is wired in 6mm through a 40A mcb in the CU with a run of about 7 metres with a double-pole isolator in the airing cupboard. Assuming 240v - Your 40a and 6mm is just on the borderline for 9.5kW, ignoring any volts drop. That's why I'm upgrading the supply cable and mcb. Borderline, as in just adequate. Were it already installed I would leave it as is, but would increase the capacity for a new install. Our 9.5Kw was originally an 8Kw shower wired in 6mm on a 40a MCB. It has been fine for the past 10 years. Modern showers can modulate their current needs as well as their flow. What I was really unsure about was the necessity of the separate shower CU. I intend to fit one, even though the shower would be fed from the main CU which is RCD protected. But am I correct in thinking that the shower needs a separate RCD? No point in adding a second RCD of the same trip rating, there would be no discrimination - so either or both could trip. They don't need a separate CU, just a local means of isolation. Either a pull switch or an isolator outside the door, with an indicator. |
#8
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
ARW expressed precisely :
I would not call it borderline. Just comfortably adequate then? |
#9
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
After serious thinking Harry Bloomfield wrote :
ARW expressed precisely : I would not call it borderline. Just comfortably adequate then? The OP seems to have his mind set on replacing it with a higher rated cable. |
#10
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On Sunday, 22 January 2017 14:27:43 UTC, Harry Bloomfield wrote:
After serious thinking Harry Bloomfield wrote : ARW expressed precisely : I would not call it borderline. Just comfortably adequate then? The OP seems to have his mind set on replacing it with a higher rated cable. How many sq mm do you get in a pair of 22mm water pipes? NT |
#11
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On Sunday, 22 January 2017 09:55:59 UTC, Joe Bloggs wrote:
I intend to replace my existing 8.5kW shower for a 9.5kW one. Any thoughts/recommendations? Go for a 10.5 kW one. It's the difference between an 11% and a 23% better shower. You're upgrading the cable etc anyway. Owain |
#12
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
Harry Bloomfield explained on 22/01/2017 :
ARW expressed precisely : I would not call it borderline. Just comfortably adequate then? 47amps if installed clipped direct to a wall, or embedded in none insulating materials. 34amps if installed in insulation materials. Likely the OP had in mind some installation method in between? 240v 9.5Kw = 39.58 amps. |
#13
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22/01/2017 09:55, Joe Bloggs wrote:
I intend to replace my existing 8.5kW shower for a 9.5kW one. The present one is wired in 6mm through a 40A mcb in the CU with a run of about 7 metres with a double-pole isolator in the airing cupboard. ok You have not mentioned a RCD... is there one on the current circuit? (if just changing the shower and leaving the rest alone, and the existing installation is meets the required disconnect times - then you could argue there is no requirement to do a full 17th edition style upgrade) My intention is to replace the cable with 10mm through a 50A mcb, and to The "clipped direct" installed capacity of 6mm^2 is 47A. Your load of 9k5W will probably be specified at 240V, so you nominal current will be 39A. So in loading terms you would be fine and nothing is going to overheat etc. Voltage drop is fine at under 2V Chances are the loop impedance that that length is in spec (even with the new 17th edition amendment 3 reductions is max Zs) The adiabatic check suggests a minimum protective conductor size on 40A MCB of s = sqrt( 400^2 x 0.1 ) / 115 = ~1 mm^2 which is also fine. replace the isolator with a separate shower CU (of this type, Wylex NH204/63), again with a 50A mcb. Any thoughts/recommendations? If you don't already have a RCD on the shower, then you could use an enclosure like that to add one. However you may just be able to use B40 RCBO in the current CU (and keep the existing isolator). -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#14
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22/01/2017 11:24, Joe Bloggs wrote:
On 22-Jan-17 10:29 AM, Harry Bloomfield wrote: Joe Bloggs presented the following explanation : I intend to replace my existing 8.5kW shower for a 9.5kW one. The present one is wired in 6mm through a 40A mcb in the CU with a run of about 7 metres with a double-pole isolator in the airing cupboard. Assuming 240v - Your 40a and 6mm is just on the borderline for 9.5kW, ignoring any volts drop. That's why I'm upgrading the supply cable and mcb. Our 9.5Kw was originally an 8Kw shower wired in 6mm on a 40a MCB. It has been fine for the past 10 years. Modern showers can modulate their current needs as well as their flow. What I was really unsure about was the necessity of the separate shower CU. I intend to fit one, even though the shower would be fed from the main CU which is RCD protected. But am I correct in thinking that the shower needs a separate RCD? No. New 17th edition installs would need RCD protection at a maximum trip threshold of 30mA. There is no requirement for that to be an additional or dedicated RCD. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#15
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22/01/2017 14:25, Harry Bloomfield wrote:
Joe Bloggs formulated the question : On 22-Jan-17 10:29 AM, Harry Bloomfield wrote: Joe Bloggs presented the following explanation : I intend to replace my existing 8.5kW shower for a 9.5kW one. The present one is wired in 6mm through a 40A mcb in the CU with a run of about 7 metres with a double-pole isolator in the airing cupboard. Assuming 240v - Your 40a and 6mm is just on the borderline for 9.5kW, ignoring any volts drop. That's why I'm upgrading the supply cable and mcb. Borderline, as in just adequate. If the install is as the OP describes, then its adequate - and that is all that counts really - since it will not exceed any technical parameter. Were it already installed I would leave it as is, but would increase the capacity for a new install. With that I would concur... No point going to all that hassle and fitting a 9.5kW shower. If doing a new install it would obviously be worth going for a higher spec to allow for a more powerful shower. If the OP is set on cable upgrades etc, then he may as well go for a better shower as well. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#16
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22/01/2017 14:45, wrote:
On Sunday, 22 January 2017 14:27:43 UTC, Harry Bloomfield wrote: After serious thinking Harry Bloomfield wrote : ARW expressed precisely : I would not call it borderline. Just comfortably adequate then? The OP seems to have his mind set on replacing it with a higher rated cable. How many sq mm do you get in a pair of 22mm water pipes? You mean in terms of CSA of copper? Over 27mm^2 per pipe if my sums are right... (assuming a 0.8mm wall thickness) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#17
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22/01/2017 14:45, wrote:
On Sunday, 22 January 2017 09:55:59 UTC, Joe Bloggs wrote: I intend to replace my existing 8.5kW shower for a 9.5kW one. Any thoughts/recommendations? Go for a 10.5 kW one. It's the difference between an 11% and a 23% better shower. You're upgrading the cable etc anyway. Yup, if going to the hassle of putting in a bigger cable, you may as well get some benefit from it! -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#18
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22-Jan-17 3:11 PM, John Rumm wrote:
On 22/01/2017 09:55, Joe Bloggs wrote: I intend to replace my existing 8.5kW shower for a 9.5kW one. The present one is wired in 6mm through a 40A mcb in the CU with a run of about 7 metres with a double-pole isolator in the airing cupboard. ok You have not mentioned a RCD... is there one on the current circuit? (if just changing the shower and leaving the rest alone, and the existing installation is meets the required disconnect times - then you could argue there is no requirement to do a full 17th edition style upgrade) My intention is to replace the cable with 10mm through a 50A mcb, and to The "clipped direct" installed capacity of 6mm^2 is 47A. Your load of 9k5W will probably be specified at 240V, so you nominal current will be 39A. So in loading terms you would be fine and nothing is going to overheat etc. Voltage drop is fine at under 2V Chances are the loop impedance that that length is in spec (even with the new 17th edition amendment 3 reductions is max Zs) The adiabatic check suggests a minimum protective conductor size on 40A MCB of s = sqrt( 400^2 x 0.1 ) / 115 = ~1 mm^2 which is also fine. replace the isolator with a separate shower CU (of this type, Wylex NH204/63), again with a 50A mcb. Any thoughts/recommendations? If you don't already have a RCD on the shower, then you could use an enclosure like that to add one. However you may just be able to use B40 RCBO in the current CU (and keep the existing isolator). Thanks for all the, very helpful, replies. To clarify things I'll do a block response to some of the queries raised. I have already run a length of 10mm from the CU to the airing cupboard (not yet connected) so there's no question of sticking with the existing cable. There is a 30mA RCD in the existing CU, so it sounds like that's all that's required. As stated, the cable run is about 7 metres and runs from the CU up into the loft (this is a bungalow) and across and down to the airing cupboard. I will run it under the loft insulation (not clipped to anything) - or over it if this is likely to be a problem. I think I'll just upgrade the existing double pole switch in the airing cupboard - the current one doesn't have a neon indicator - and dispense with the idea of a separate shower CU. The existing shower is fed through a 32A mcb, which I will upgrade to 50A. The suggestion of a 10.5kW shower seems a good one, which I will look into - although I was under the impression that this might run close to a requirement for 16mm cable. I should add that the property has TT earthing. Any additional advice/comments would be very welcome. |
#19
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
Joe Bloggs wrote :
I think I'll just upgrade the existing double pole switch in the airing cupboard - the current one doesn't have a neon indicator - and dispense with the idea of a separate shower CU. The existing shower is fed through a 32A mcb, which I will upgrade to 50A. The suggestion of a 10.5kW shower seems a good one, which I will look into - although I was under the impression that this might run close to a requirement for 16mm cable. Dependent upon the installation conditions of your present 6mm T&E, it might be able to support even the 10.5kW shower at 43.75amps full load(10500w/240v = 43.75amps). Your 10mm is definitely more than adequate for the purpose, absolutely no need for 16mm and you might find it a struggle/impossible to get into the terminals. 6mm unless covered by insulation is rated at 47amps. Avoiding running cables under or through insulation is always a good idea, especially those which carry heavier currents. Your 30mA RCD covers what you need, but if it provides cover for ALL of the circuits, you might find it better to replace that with a 100mA and fit a separate 30mA RCDBO for just the shower circuit - it avoids all your circuits tripping out, due to a fault on one circuit. |
#21
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
It happens that ARW formulated :
Just run the 6mm t&E next to the showers water pipe for extra performance. Or use oxygen free copper pipe Þ |
#22
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22/01/2017 14:51, Harry Bloomfield wrote:
Harry Bloomfield explained on 22/01/2017 : ARW expressed precisely : I would not call it borderline. Just comfortably adequate then? 47amps if installed clipped direct to a wall, or embedded in none insulating materials. 34amps if installed in insulation materials. Likely the OP had in mind some installation method in between? 240v 9.5Kw = 39.58 amps. ****ing hell. Is this the Spanish inquisition? -- Adam |
#23
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22-Jan-17 6:13 PM, Harry Bloomfield wrote:
Joe Bloggs wrote : I think I'll just upgrade the existing double pole switch in the airing cupboard - the current one doesn't have a neon indicator - and dispense with the idea of a separate shower CU. The existing shower is fed through a 32A mcb, which I will upgrade to 50A. The suggestion of a 10.5kW shower seems a good one, which I will look into - although I was under the impression that this might run close to a requirement for 16mm cable. Dependent upon the installation conditions of your present 6mm T&E, it might be able to support even the 10.5kW shower at 43.75amps full load(10500w/240v = 43.75amps). Your 10mm is definitely more than adequate for the purpose, absolutely no need for 16mm and you might find it a struggle/impossible to get into the terminals. 6mm unless covered by insulation is rated at 47amps. Avoiding running cables under or through insulation is always a good idea, especially those which carry heavier currents. Your 30mA RCD covers what you need, but if it provides cover for ALL of the circuits, you might find it better to replace that with a 100mA and fit a separate 30mA RCDBO for just the shower circuit - it avoids all your circuits tripping out, due to a fault on one circuit. Thanks again for that. What about running the shower through a 50A 30mA RCBO fitted on the non-RCD side of my CU? |
#24
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22/01/2017 18:13, Harry Bloomfield wrote:
Joe Bloggs wrote : I think I'll just upgrade the existing double pole switch in the airing cupboard - the current one doesn't have a neon indicator - and dispense with the idea of a separate shower CU. The existing shower is fed through a 32A mcb, which I will upgrade to 50A. The suggestion of a 10.5kW shower seems a good one, which I will look into - although I was under the impression that this might run close to a requirement for 16mm cable. Dependent upon the installation conditions of your present 6mm T&E, it might be able to support even the 10.5kW shower at 43.75amps full load(10500w/240v = 43.75amps). Your 10mm is definitely more than adequate for the purpose, absolutely no need for 16mm and you might find it a struggle/impossible to get into the terminals. 6mm unless covered by insulation is rated at 47amps. Avoiding running cables under or through insulation is always a good idea, especially those which carry heavier currents. I agree. -- Adam |
#25
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22/01/2017 19:21, Joe Bloggs wrote:
Thanks again for that. What about running the shower through a 50A 30mA RCBO fitted on the non-RCD side of my CU? Then get a pro in. A TT supply should not have a non RCD side. -- Adam |
#26
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22/01/2017 16:24, Joe Bloggs wrote:
Thanks for all the, very helpful, replies. To clarify things I'll do a block response to some of the queries raised. I have already run a length of 10mm from the CU to the airing cupboard (not yet connected) so there's no question of sticking with the existing cable. There is a 30mA RCD in the existing CU, so it sounds like that's all that's required. As stated, the cable run is about 7 metres and runs from the CU up into the loft (this is a bungalow) and across and down to the airing cupboard. I will run it under the loft insulation (not clipped to anything) - or over it if this is likely to be a problem. Under the insulation you *must not* do in this circumstance - even with 10mm^2 cable. Assuming you have 100mm or more of insulation that would mean you are using installation method 101 which would drop the tabulated current carrying capacity of the cable to 36A (and that is if it remains in contact with the plasterboard below - its even lower if surrounded by insulation). See the table he http://wiki.diyfaq.org.uk/index.php/Cables#Cable_Sizes also look at the insulation methods he http://wiki.diyfaq.org.uk/index.php/...lation_Methods (note there are many more scenarios described in BS7671, but the ones listed there are the most commonly applicable to domestic wiring). So above the insulation is vastly preferable. (and leave a bit of space round it where it goes through the insulation on the way up and down) Note also that if the airing cupboard is normally above 30 degrees, then you may also need to allow for some de-rating due to ambient temperature. See the table 4B1 he http://wiki.diyfaq.org.uk/index.php/...you r_circuit I think I'll just upgrade the existing double pole switch in the airing cupboard - the current one doesn't have a neon indicator - and dispense with the idea of a separate shower CU. The existing shower is fed through a 32A mcb, which I will upgrade to 50A. The suggestion of a 10.5kW shower seems a good one, which I will look into - although I was under the impression that this might run close to a requirement for 16mm cable. So long as you don't complicate it with running cables in insulation then the 10mm^2 cable is good for up to 64A, which will be more than adequate by a long way. (in reality, even the 6mm^2 cable would be ok on a 10.5kW shower) I should add that the property has TT earthing. Not going to make much difference in this particular case... Any additional advice/comments would be very welcome. I take it your incoming main fuse is rated at 60A or better? (otherwise a more powerful shower may push you close to the limit with other household loads). -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#27
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22-Jan-17 7:23 PM, ARW wrote:
On 22/01/2017 19:21, Joe Bloggs wrote: Thanks again for that. What about running the shower through a 50A 30mA RCBO fitted on the non-RCD side of my CU? Then get a pro in. A TT supply should not have a non RCD side. There is nothing connected to the non-RCD side of the CU. But what would be wrong with taking the shower supply from it through a 30mA RCBO? |
#28
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22-Jan-17 7:31 PM, John Rumm wrote:
On 22/01/2017 16:24, Joe Bloggs wrote: Thanks for all the, very helpful, replies. To clarify things I'll do a block response to some of the queries raised. I have already run a length of 10mm from the CU to the airing cupboard (not yet connected) so there's no question of sticking with the existing cable. There is a 30mA RCD in the existing CU, so it sounds like that's all that's required. As stated, the cable run is about 7 metres and runs from the CU up into the loft (this is a bungalow) and across and down to the airing cupboard. I will run it under the loft insulation (not clipped to anything) - or over it if this is likely to be a problem. Under the insulation you *must not* do in this circumstance - even with 10mm^2 cable. Assuming you have 100mm or more of insulation that would mean you are using installation method 101 which would drop the tabulated current carrying capacity of the cable to 36A (and that is if it remains in contact with the plasterboard below - its even lower if surrounded by insulation). See the table he http://wiki.diyfaq.org.uk/index.php/Cables#Cable_Sizes also look at the insulation methods he http://wiki.diyfaq.org.uk/index.php/...lation_Methods (note there are many more scenarios described in BS7671, but the ones listed there are the most commonly applicable to domestic wiring). So above the insulation is vastly preferable. (and leave a bit of space round it where it goes through the insulation on the way up and down) Note also that if the airing cupboard is normally above 30 degrees, then you may also need to allow for some de-rating due to ambient temperature. See the table 4B1 he http://wiki.diyfaq.org.uk/index.php/...you r_circuit I think I'll just upgrade the existing double pole switch in the airing cupboard - the current one doesn't have a neon indicator - and dispense with the idea of a separate shower CU. The existing shower is fed through a 32A mcb, which I will upgrade to 50A. The suggestion of a 10.5kW shower seems a good one, which I will look into - although I was under the impression that this might run close to a requirement for 16mm cable. So long as you don't complicate it with running cables in insulation then the 10mm^2 cable is good for up to 64A, which will be more than adequate by a long way. (in reality, even the 6mm^2 cable would be ok on a 10.5kW shower) Ok, thanks. I certainly won't run it under the insulation then. I should add that the property has TT earthing. Not going to make much difference in this particular case... Any additional advice/comments would be very welcome. I take it your incoming main fuse is rated at 60A or better? (otherwise a more powerful shower may push you close to the limit with other household loads). The incoming fuse is 80A. |
#29
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
|
#30
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
rick brought next idea :
Electric Showers taken a big leap in power since I last installed one. Think it was around 6 or 6.5kW They have changed in capability too. The original showers were only really usable in summer and you had to adjust the flow, to set the temperature. Modern ones are usable in winter and the control system is much more clever. On mine you just set the temperature you desire and it modulates the water flow and current to achieve that. |
#31
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On Sunday, 22 January 2017 15:24:25 UTC, John Rumm wrote:
On 22/01/2017 14:45, tabbypurr wrote: On Sunday, 22 January 2017 14:27:43 UTC, Harry Bloomfield wrote: After serious thinking Harry Bloomfield wrote : ARW expressed precisely : The OP seems to have his mind set on replacing it with a higher rated cable. How many sq mm do you get in a pair of 22mm water pipes? You mean in terms of CSA of copper? Over 27mm^2 per pipe if my sums are right... (assuming a 0.8mm wall thickness) should support the full 100A if you run the pipes through the CU 24kW. NT |
#32
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22/01/2017 19:55, Joe Bloggs wrote:
On 22-Jan-17 7:23 PM, ARW wrote: On 22/01/2017 19:21, Joe Bloggs wrote: Thanks again for that. What about running the shower through a 50A 30mA RCBO fitted on the non-RCD side of my CU? Then get a pro in. A TT supply should not have a non RCD side. There is nothing connected to the non-RCD side of the CU. But what would be wrong with taking the shower supply from it through a 30mA RCBO? That's fine... As you are probably aware, all circuits must have RCD protection on a TT install. Typically this was done with a 100mA time delayed RCD on the incoming side of a traditional split load CU to protect "everything", and then other 30mA RCDs would protect circuits where "direct contact" protection (or "basic protection" as its now called) was required. A traditional split load with shared RCDs on one side, and then all RCBOs on the other is also fine for TT. (all RCBOs being the "nicest" option). -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#33
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22-Jan-17 7:23 PM, ARW wrote:
On 22/01/2017 19:21, Joe Bloggs wrote: Thanks again for that. What about running the shower through a 50A 30mA RCBO fitted on the non-RCD side of my CU? Then get a pro in. A TT supply should not have a non RCD side. I am a 'pro', and I was a 'pro' when you were in short trousers, but I am not an electrician. My world was machine control, telecommunications and electronics, and my qualifications in that area of the electrical world are a great deal higher than most electricians. But domestic electrics are not my thing, and therefore I am not completely au fait with all the regulations that apply. That's why I generally seek advice from those that are before I do anything, and I am very grateful to those here who have been generous with their help and advice. Advice which I shall be careful to take heed of. I can assure you, that I am no fool, and if I come over that way it is largely because I don't believe in pretending to know things that I clearly don't. The electrical world is vast, and contains many specialities and disciplines, a world where it is possible to be an expert in some aspects and know very little about others. It is also one, like most others, that the more you know the more you realise how little you know. Clearly you haven't got there yet. |
#34
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
On 22/01/2017 19:55, Joe Bloggs wrote:
On 22-Jan-17 7:23 PM, ARW wrote: On 22/01/2017 19:21, Joe Bloggs wrote: Thanks again for that. What about running the shower through a 50A 30mA RCBO fitted on the non-RCD side of my CU? Then get a pro in. A TT supply should not have a non RCD side. There is nothing connected to the non-RCD side of the CU. But what would be wrong with taking the shower supply from it through a 30mA RCBO? Nothing, I was looking at your 50A MCB post:-( -- Adam |
#35
Posted to uk.d-i-y
|
|||
|
|||
Shower replacement
Harry Bloomfield Wrote in message:
It happens that ARW formulated : Just run the 6mm t&E next to the showers water pipe for extra performance. Or use oxygen free copper pipe Þ Russ Andrews? -- Jim K ----Android NewsGroup Reader---- http://usenet.sinaapp.com/ |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Cost of shower replacement | UK diy | |||
shower sealant replacement | UK diy | |||
Help!! replacement shower panel | UK diy | |||
Shower tray replacement | UK diy | |||
Shower Drain Needs Replacement HELP | Home Ownership |