I've now got my Greenstar HE28 System boiler installed (thanks John!).
Unfortunately, as it is connected to a heat bank, I need the flow temperature to exceed the normal 75C limit. According to the installation/commissioning manual, this is done by removing the yellow end cap from the temperature selection knob and reinserting it 180 degrees to the original. Unfortunately, it doesn't seem to want to budge and I don't want to apply more force than I am, as it might snap the PCB/knob. Has anyone ever been successful in this task? Any ideas? Christian. |
#2
|
|||
|
|||
Bosch-Worcester Greenstar issue
Christian McArdle wrote:
I've now got my Greenstar HE28 System boiler installed (thanks John!). Unfortunately, as it is connected to a heat bank, I need the flow temperature to exceed the normal 75C limit. According to the installation/commissioning manual, this is done by removing the yellow end cap from the temperature selection knob and reinserting it 180 degrees to the original. Unfortunately, it doesn't seem to want to budge and I don't want to apply more force than I am, as it might snap the PCB/knob. Has anyone ever been successful in this task? Any ideas? Yes, use more force.... Seriously, I have a 29HE and it took a lot of force to shift the little B*&&%r. Christian. AndyP -- We were always told that a million monkeys typing for a million years would eventually produce the works of Shakespeare. Now, thanks to the Internet, we know this is not true. |
#3
|
|||
|
|||
Bosch-Worcester Greenstar issue
Yes, use more force.... Seriously, I have a 29HE and it took a lot of
force to shift the little B*&&%r. How do you stop the PCB and knob disintegrating? The front panel is already bulging alarmingly as I try to prise it off. Christian. |
#4
|
|||
|
|||
Bosch-Worcester Greenstar issue
Christian McArdle wrote:
Yes, use more force.... Seriously, I have a 29HE and it took a lot of force to shift the little B*&&%r. How do you stop the PCB and knob disintegrating? The front panel is already bulging alarmingly as I try to prise it off. Christian. I will have a look tonight as to how it comes off, I think it was just very tight and a little screwdriver under the edge did the trick. AP -- We were always told that a million monkeys typing for a million years would eventually produce the works of Shakespeare. Now, thanks to the Internet, we know this is not true. |
#5
|
|||
|
|||
Bosch-Worcester Greenstar issue
I will have a look tonight as to how it comes off, I think it was
just very tight and a little screwdriver under the edge did the trick. Mine has an obvious screwdriver slot. I assume this is what you mean by "edge"? Christian. |
#6
|
|||
|
|||
Bosch-Worcester Greenstar issue
I do not have one.
Are you sure it is not just a rotary control, i.e. to the electrnics world a potentiometer. Has it a screwdriver slot in the top? If so small screwdriver and gently turn. On Tue, 13 Jan 2004 11:52:22 -0000, "Christian McArdle" wrote: I will have a look tonight as to how it comes off, I think it was just very tight and a little screwdriver under the edge did the trick. Mine has an obvious screwdriver slot. I assume this is what you mean by "edge"? Christian. Lawrence usenet at lklyne dt co dt uk |
#7
|
|||
|
|||
Bosch-Worcester Greenstar issue
Are you sure it is not just a rotary control, i.e. to the electrnics
world a potentiometer. Has it a screwdriver slot in the top? If so small screwdriver and gently turn. No. It is a little yellow dot that doubles as the pointer for the temperature control. I suspect is has a protruding lug that prevents the pointer being turned past 75C. By reversing the dot, I suspect the alleged lug will no longer prevent the pointer being turned. The slot is in the edge of the insert supposedly to give something for your screwdriver to grip on when prising it out. It's a weird concept anyway, especially as there is a software setting to limit the temperature as well. Both have to be set to get 75C water. Christian. |
#8
|
|||
|
|||
Bosch-Worcester Greenstar issue
Oh thanks for the delights of oil boilers where. I have no PCB in
sight just a handfull of interwired thermostats and switches. I lie probably, there is a high voltage source in the burner itself and some sequencing logic. I like the KISS principle. Good luck. On Tue, 13 Jan 2004 13:21:51 -0000, "Christian McArdle" wrote: Are you sure it is not just a rotary control, i.e. to the electrnics world a potentiometer. Has it a screwdriver slot in the top? If so small screwdriver and gently turn. No. It is a little yellow dot that doubles as the pointer for the temperature control. I suspect is has a protruding lug that prevents the pointer being turned past 75C. By reversing the dot, I suspect the alleged lug will no longer prevent the pointer being turned. The slot is in the edge of the insert supposedly to give something for your screwdriver to grip on when prising it out. It's a weird concept anyway, especially as there is a software setting to limit the temperature as well. Both have to be set to get 75C water. Christian. Lawrence usenet at lklyne dt co dt uk |
#9
|
|||
|
|||
Bosch-Worcester Greenstar issue
"Lawrence" wrote in message
... Oh thanks for the delights of oil boilers where. I have no PCB in sight just a handfull of interwired thermostats and switches. I lie probably, there is a high voltage source in the burner itself and some sequencing logic. I like the KISS principle. Yes, but what are you using to send that message? ;-) -- John Stumbles -+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-|-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+ -+ Copyright (c) Sirius Cybernetics Corporation (formerly Microsoft) |
#10
|
|||
|
|||
Bosch-Worcester Greenstar issue
"Christian McArdle" wrote in message . net...
I've now got my Greenstar HE28 System boiler installed (thanks John!). Unfortunately, as it is connected to a heat bank, I need the flow temperature to exceed the normal 75C limit. According to the installation/commissioning manual, this is done by removing the yellow end cap from the temperature selection knob and reinserting it 180 degrees to the original. Unfortunately, it doesn't seem to want to budge and I don't want to apply more force than I am, as it might snap the PCB/knob. Has anyone ever been successful in this task? Any ideas? Christian. Christian, once you've got this working, would you mind posting a brief report on the recovery aspects of your Pandora heat bank, coupled with your boiler. I'm considering the same model that you have installed and would be interested in some "real-world" data before I commit. Many thanks Neil |
#11
|
|||
|
|||
Bosch-Worcester Greenstar issue
Christian, once you've got this working, would you mind posting a
brief report on the recovery aspects of your Pandora heat bank, coupled with your boiler. Well, it isn't brilliant with the boiler limited to 75C. However, it does actually heat enough to turn off the 75C cylinder stat eventually. I think the electric immersion was heating higher than 75C. When I get the flow temperature above 80C, then I'm sure the boiler heating will do the same. I tried even harder to remove the dot last night. I'm sure I'll damage the boiler if I pull harder. I'm going to phone Worcester... Christian. |
#12
|
|||
|
|||
Bosch-Worcester Greenstar issue
On Wed, 14 Jan 2004 09:51:27 -0000, "Christian McArdle"
wrote: Christian, once you've got this working, would you mind posting a brief report on the recovery aspects of your Pandora heat bank, coupled with your boiler. Well, it isn't brilliant with the boiler limited to 75C. However, it does actually heat enough to turn off the 75C cylinder stat eventually. I think the electric immersion was heating higher than 75C. When I get the flow temperature above 80C, then I'm sure the boiler heating will do the same. I tried even harder to remove the dot last night. I'm sure I'll damage the boiler if I pull harder. I'm going to phone Worcester... Christian. I've just fitted a 35HE and that yellow bit is tight, I ended up ripping it off with a pair of grips. Luckily the knob is fairly sturdy, a good tug was required. It went back in o.k. just got teeth marks on it, can't see til you look closely though! SJW A.C.S. Ltd. |
#13
|
|||
|
|||
Bosch-Worcester Greenstar issue
I've just fitted a 35HE and that yellow bit is tight, I ended up
ripping it off with a pair of grips. I could try mole grips. However, the thing is mostly buried, so I'm not sure what purchase I can get on it. Luckily the knob is fairly sturdy, a good tug was required. Whilst the knob itself looks sturdy, I'm not sure about the control it is attached to. It moves too much for my comfort. Christian. |
#14
|
|||
|
|||
Bosch-Worcester Greenstar issue
On Wed, 14 Jan 2004 11:49:50 -0000, "Christian McArdle"
wrote: I've just fitted a 35HE and that yellow bit is tight, I ended up ripping it off with a pair of grips. I could try mole grips. However, the thing is mostly buried, so I'm not sure what purchase I can get on it. Luckily the knob is fairly sturdy, a good tug was required. Whilst the knob itself looks sturdy, I'm not sure about the control it is attached to. It moves too much for my comfort. Well, I'm just saying I managed it. It is of course entirely up to you as to whether you want to try it or not. SJW A.C.S. Ltd. |
#15
|
|||
|
|||
Bosch-Worcester Greenstar issue
"Christian McArdle" wrote in message et... I've now got my Greenstar HE28 System boiler installed (thanks John!). Unfortunately, as it is connected to a heat bank, I need the flow temperature to exceed the normal 75C limit. According to the installation/commissioning manual, this is done by removing the yellow end cap from the temperature selection knob and reinserting it 180 degrees to the original. Unfortunately, it doesn't seem to want to budge and I don't want to apply more force than I am, as it might snap the PCB/knob. Has anyone ever been successful in this task? Any ideas? Do you need to do something softwarewise to get it to stay at 80C? Can you have it at 80C for DHW and modulation on CH? --- -- Checked by AVG anti-virus system (http://www.grisoft.com). Version: 6.0.558 / Virus Database: 350 - Release Date: 02/01/2004 |
#16
|
|||
|
|||
Bosch-Worcester Greenstar issue
Well, I'm just saying I managed it. It is of course entirely up to
you as to whether you want to try it or not. It's nice to know two people have managed it! I think I'll give the grips a try. It's a shame that this problem has blighted an otherwise well designed boiler. Given that there is also a software setting for this, I don't even see why they bothered making it so difficult. Christian. |
#17
|
|||
|
|||
Bosch-Worcester Greenstar issue
Do you need to do something softwarewise to get it to stay at 80C?
No. The software is currently set for a maximum of 88C. Unfortunately, the little peg in the knob physically prevents you turning the thermostat that high. The peg is useless. They would have been better to have just had the default software setting at 75C which would have just ignored any thermostat knob setting above that value. I wonder how many Greenstars there are round the country with chewed up yellow pointer knobs... Can you have it at 80C for DHW and modulation on CH? No. They had an internal diverter valve option with separate temperatures for both sides, but the hot water flow is limited to 75C. Of course, it was only later that it occured to me that I could have run the radiators on the hot water circuit and the cylinder off the radiator circuit to bypass this. OTOH, this may have defeated some internal algorithms. Christian. |
#18
|
|||
|
|||
Bosch-Worcester Greenstar issue
In uk.d-i-y, Christian McArdle wrote:
Do you need to do something softwarewise to get it to stay at 80C? No. The software is currently set for a maximum of 88C. Unfortunately, the little peg in the knob physically prevents you turning the thermostat that high. The peg is useless. Aha! Have we at last found a use for a Dremel for you - to grind the little peg off the knob (giggles)? |
#19
|
|||
|
|||
Bosch-Worcester Greenstar issue
Aha! Have we at last found a use for a Dremel for you - to grind the
little peg off the knob (giggles)? If I could get it out first. The peg is only presumed to stick out of the back as it is the obvious method of accomplishing its task. I haven't seen it yet! Christian. |
#20
|
|||
|
|||
Bosch-Worcester Greenstar issue
"Christian McArdle" wrote in message et... Do you need to do something softwarewise to get it to stay at 80C? No. The software is currently set for a maximum of 88C. Unfortunately, the little peg in the knob physically prevents you turning the thermostat that high. The peg is useless. They would have been better to have just had the default software setting at 75C which would have just ignored any thermostat knob setting above that value. I wonder how many Greenstars there are round the country with chewed up yellow pointer knobs... Can you have it at 80C for DHW and modulation on CH? No. They had an internal diverter valve option with separate temperatures for both sides, but the hot water flow is limited to 75C. Of course, it was only later that it occured to me that I could have run the radiators on the hot water circuit and the cylinder off the radiator circuit to bypass this. OTOH, this may have defeated some internal algorithms. So it will modulate on the load compensation software, either in CHG or DHW mode? --- -- Checked by AVG anti-virus system (http://www.grisoft.com). Version: 6.0.558 / Virus Database: 350 - Release Date: 02/01/2004 |
#21
|
|||
|
|||
Bosch-Worcester Greenstar issue
OTOH, this may have defeated some internal algorithms.
So it will modulate on the load compensation software, either in CHG or DHW mode? That I don't know. I suspect it will modulate on any mode. However, it seems to be cycling on a regular basis anyway. Even modulated right down, my average heating requirement is very low. It is an Edwardian terrace. I calculated 8.4kW when it is -3C. At 10C outside, my requirement will be a fraction of this (probably around 3-4kW) which is below the modulating range. It definitely is modulating down, though, as the gas rate at the meter varies. At some point, I might bother to redo the heating circuit with a TMV and pump to make the radiators cooler and reduce the return temp. The pluming I get from it is very slight whatever the return temperature, especially compared with the Icos I had in the last place, which created sufficient fog bank to have saved the Tirpitz. Christian. |
#22
|
|||
|
|||
Bosch-Worcester Greenstar issue
"Christian McArdle" wrote in message . net...
Christian, once you've got this working, would you mind posting a brief report on the recovery aspects of your Pandora heat bank, coupled with your boiler. Well, it isn't brilliant with the boiler limited to 75C. However, it does actually heat enough to turn off the 75C cylinder stat eventually. I think the electric immersion was heating higher than 75C. When I get the flow temperature above 80C, then I'm sure the boiler heating will do the same. I tried even harder to remove the dot last night. I'm sure I'll damage the boiler if I pull harder. I'm going to phone Worcester... Christian. Thanks for this. I'll be interested to hear the outcome when (if) you manage to get the flow temp above your store design temp. Regards Neil |
#23
|
|||
|
|||
Bosch-Worcester Greenstar issue
On Wed, 14 Jan 2004 14:34:28 -0000, "Christian McArdle"
wrote: OTOH, this may have defeated some internal algorithms. So it will modulate on the load compensation software, either in CHG or DHW mode? That I don't know. I suspect it will modulate on any mode. However, it seems to be cycling on a regular basis anyway. Even modulated right down, my average heating requirement is very low. It is an Edwardian terrace. I calculated 8.4kW when it is -3C. At 10C outside, my requirement will be a fraction of this (probably around 3-4kW) which is below the modulating range. It definitely is modulating down, though, as the gas rate at the meter varies. At some point, I might bother to redo the heating circuit with a TMV and pump to make the radiators cooler and reduce the return temp. The pluming I get from it is very slight whatever the return temperature, especially compared with the Icos I had in the last place, which created sufficient fog bank to have saved the Tirpitz. Do you have a feeling as to whether this is because the bottom modulating point is less or because it's condensing more internally and delivering to the condensate drain? Christian. ..andy To email, substitute .nospam with .gl |
#24
|
|||
|
|||
Bosch-Worcester Greenstar issue
On Wed, 14 Jan 2004 13:58:34 -0000, "Christian McArdle"
wrote: Aha! Have we at last found a use for a Dremel for you - to grind the little peg off the knob (giggles)? If I could get it out first. The peg is only presumed to stick out of the back as it is the obvious method of accomplishing its task. I haven't seen it yet! Christian. I'd get the installer back - clearly down to him ;-) ..andy To email, substitute .nospam with .gl |
#25
|
|||
|
|||
Bosch-Worcester Greenstar issue
Do you have a feeling as to whether this is because the bottom
modulating point is less or because it's condensing more internally and delivering to the condensate drain? I'm not quite sure. We were going to pull the condensate drain apart and take a peek, but never got round to it, as I needed the cooker point moved the same day. One major difference is that the flue is much longer. Not very long, mind. However, it does have a couple of bends, an extension piece and a vertical flue terminal. This would give a much greater chance of flue condensing. I still don't know if it isn't pluming because the flue gas is too hot, or too cold for major condensing at the terminal. If anything, there are more wisps at higher return temperatures than lower ones. It seems a shame really, having gone to all the trouble of having the terminal in a place where pluming wouldn't be a problem! (It goes out through the roof). Christian. |
#26
|
|||
|
|||
Bosch-Worcester Greenstar issue
On Wed, 14 Jan 2004 15:51:05 -0000, "Christian McArdle"
wrote: Do you have a feeling as to whether this is because the bottom modulating point is less or because it's condensing more internally and delivering to the condensate drain? I'm not quite sure. We were going to pull the condensate drain apart and take a peek, but never got round to it, as I needed the cooker point moved the same day. I put a tundish under mine to be able to see the flow. One major difference is that the flue is much longer. Not very long, mind. However, it does have a couple of bends, an extension piece and a vertical flue terminal. This would give a much greater chance of flue condensing. Could have an influence, I suppose. I have a flue kit which is a bend and straight out through the wall, with a downward slope back to the boiler. I still don't know if it isn't pluming because the flue gas is too hot, or too cold for major condensing at the terminal. If anything, there are more wisps at higher return temperatures than lower ones. Given the current conditions, it's probably because it is modulated down. Don't forget that the volume of condensate produced depends on the burn rate as well as the low temperature - i.e. less gas, less water. Also, it looks like this boiler modulates by varying fan speed. This influences the velocity of the flue gases, and I would assume that the longer time spent inside, the greater the amount of condensation inside. It seems a shame really, having gone to all the trouble of having the terminal in a place where pluming wouldn't be a problem! (It goes out through the roof). It would appear that different designs have different characteristics. The Greenstar seems to have a minimum power level of 7.5kW vs. the Ideal's 9kW, although that doesn't suggest a huge difference. Perhaps the heat exchanger arrangement - although both seem to be downfiring types, the Greenstar looks like it has a tall heat exchanger at the side, whereas the Ideal has a shallower one at the top. My boiler drops down to about 3kW on CH output, and under those conditions, there is very little visible from the flue and a steady drip of condensate - perhaps 2-3/second. The only time when there is a more substantial plume is when the boiler starts a hot water cycle with a totally cold cylinder. Then it is wound up to about 28kW with full fan speed and a temperature difference across it of 25 degrees plus. Under those circumstances there is a fairly hefty stream of condensate into the drain. That only lasts for a few minutes, though. There is a temperature sensor on the cylinder, and as the water temperature approaches the set point, the boiler modulates down Christian. ..andy To email, substitute .nospam with .gl |
#27
|
|||
|
|||
Bosch-Worcester Greenstar issue
"Andy Hall" wrote in message
... On Wed, 14 Jan 2004 13:58:34 -0000, "Christian McArdle" wrote: Aha! Have we at last found a use for a Dremel for you - to grind the little peg off the knob (giggles)? If I could get it out first. The peg is only presumed to stick out of the back as it is the obvious method of accomplishing its task. I haven't seen it yet! Christian. I'd get the installer back - clearly down to him ;-) [Ducks! :-)] -- John Stumbles -+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-|-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+ -+ The most dangerous component in a car is the nut that holds the steering wheel |
#28
|
|||
|
|||
Bosch-Worcester Greenstar issue
"Andy Hall" wrote in message
... On Wed, 14 Jan 2004 15:51:05 -0000, "Christian McArdle" wrote: Do you have a feeling as to whether this is because the bottom modulating point is less or because it's condensing more internally and delivering to the condensate drain? I'm not quite sure. We were going to pull the condensate drain apart and take a peek, but never got round to it, as I needed the cooker point moved the same day. I put a tundish under mine to be able to see the flow. I had a bucket under the Isar I did a few weeks back, and got a steady dribble of condensate (it was a cold night, in a cold house, and we'd fired up the system for the first time). But we couldn't see the flue. One major difference is that the flue is much longer. Not very long, mind. However, it does have a couple of bends, an extension piece and a vertical flue terminal. This would give a much greater chance of flue condensing. Could have an influence, I suppose. I have a flue kit which is a bend and straight out through the wall, with a downward slope back to the boiler. I still don't know if it isn't pluming because the flue gas is too hot, or too cold for major condensing at the terminal. If anything, there are more wisps at higher return temperatures than lower ones. Given the current conditions, it's probably because it is modulated down. Don't forget that the volume of condensate produced depends on the burn rate as well as the low temperature - i.e. less gas, less water. Also, it looks like this boiler modulates by varying fan speed. This influences the velocity of the flue gases, and I would assume that the longer time spent inside, the greater the amount of condensation inside. It seems a shame really, having gone to all the trouble of having the terminal in a place where pluming wouldn't be a problem! (It goes out through the roof). It would appear that different designs have different characteristics. The Greenstar seems to have a minimum power level of 7.5kW vs. the Ideal's 9kW, although that doesn't suggest a huge difference. Perhaps the heat exchanger arrangement - although both seem to be downfiring types, the Greenstar looks like it has a tall heat exchanger at the side, whereas the Ideal has a shallower one at the top. My boiler drops down to about 3kW on CH output, and under those conditions, there is very little visible from the flue and a steady drip of condensate - perhaps 2-3/second. The only time when there is a more substantial plume is when the boiler starts a hot water cycle with a totally cold cylinder. Then it is wound up to about 28kW with full fan speed and a temperature difference across it of 25 degrees plus. Under those circumstances there is a fairly hefty stream of condensate into the drain. That only lasts for a few minutes, though. There is a temperature sensor on the cylinder, and as the water temperature approaches the set point, the boiler modulates down When I measured the gas rate it was approx .01 m^3 in 15s immediately the boiler fired up (not measured over the usual 2 minutes for a digital meter as the boiler modulates down too soon) indicating a heat input of 25.73kW. After about 30s(?) the boiler modulated down to half that, staying at that sort of rate for several minutes until it turned off. (It was too cold, late and dark to take more gas rate samples, but when Christian gets a webcam set up on the meter and we can OCR the readings I'm sure we'll get some really interesting data :-) -- John Stumbles -+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-|-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+ -+ The astronomer married a star |
#29
|
|||
|
|||
Bosch-Worcester Greenstar issue
On Wed, 14 Jan 2004 22:08:11 -0000, "John Stumbles"
] wrote: When I measured the gas rate it was approx .01 m^3 in 15s immediately the boiler fired up (not measured over the usual 2 minutes for a digital meter as the boiler modulates down too soon) indicating a heat input of 25.73kW. After about 30s(?) the boiler modulated down to half that, staying at that sort of rate for several minutes until it turned off. (It was too cold, late and dark to take more gas rate samples, but when Christian gets a webcam set up on the meter and we can OCR the readings I'm sure we'll get some really interesting data :-) You mean it isn't a meter with an ethernet connection? ;-) ..andy To email, substitute .nospam with .gl |
#30
|
|||
|
|||
Bosch-Worcester Greenstar issue
I'd get the installer back - clearly down to him ;-)
[Ducks! :-)] Well, Worcester-Bosch got back to me. From the horse's mouth: Thank you for your recent enquiry. I have found that by using a small flat blade screwdriver inserted in to the slot on the button, and a plastic rule as a contact point of leverage, I was able to remove the button successfully. However, I do accept your comment that it does seem to be very tight. I tried it (with a chisel instead of a screwdriver and a piece of offcut T&E rather than a plastic rule). It worked easily with hardly any force. I think that the lever idea works not because of the extra force that could have been applied, but because it applies the force at the specific angle if seems to require. It's too early to say what the recovery performance is now. I haven't even had time to ensure that the flow temp gets above 75C, as I only had 2 minutes to spare and it was during a 3 minute anti cycling cut out. Christian. |
#31
|
|||
|
|||
Bosch-Worcester Greenstar issue
Andy Hall wrote in message . ..
On Wed, 14 Jan 2004 22:08:11 -0000, "John Stumbles" You mean it isn't a meter with an ethernet connection? ;-) But the gas regs require a 25mm separation from electrical cables :-) John S |
#32
|
|||
|
|||
Bosch-Worcester Greenstar issue
|
#33
|
|||
|
|||
Bosch-Worcester Greenstar issue
"Andy Hall" wrote
| John Stumbles wrote: | But the gas regs require a 25mm separation from electrical cables :-) | Well I've heard of some excuses..... | Is that power as in mains cables or any cables though (as a matter | of interest)? I must confess I thought the BT man was taking a bit of a short-cut when he cable-tied a neighbour's line down the outside gas pipe. Owain |
#34
|
|||
|
|||
Bosch-Worcester Greenstar issue
On Fri, 16 Jan 2004 20:28:59 +0000, Andy Hall wrote:
On 16 Jan 2004 11:34:25 -0800, (John Stumbles) wrote: Andy Hall wrote in message . .. On Wed, 14 Jan 2004 22:08:11 -0000, "John Stumbles" You mean it isn't a meter with an ethernet connection? ;-) But the gas regs require a 25mm separation from electrical cables :-) John S Well I've heard of some excuses..... Is that power as in mains cables or any cables though (as a matter of interest)? I always thought it was mains cables. Also it is 150mm to meters and consumer units. -- Ed Sirett - Property maintainer and registered gas fitter. The FAQ for uk.diy is at www.diyfaq.org.uk Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Worcester Bosch Greenstar HE timer instructions? | UK diy | |||
Bosch Tumble Dryers - Best Buy? | UK diy | |||
Bosch Pressure washers - opinions please | UK diy | |||
FS: Brand New Worcester Oil Boiler | UK diy |