Immersion heater: thinking of doing away with it.
I'm thinking of doing away with the immersion heater
in my bathroom, and getting a power-shower in its place. I'll also have to get a small heater for the wash-basin. I'm wondering if the power supply to the immersion heater will be suitable, or if this will have to be replaced? It is on its own circuit-breaker. Any views on the merits of this? The main reason is to give more space, perhaps for a separate shower. -- Timothy Murphy gayleard /at/ eircom.net School of Mathematics, Trinity College, Dublin |
#2
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
It depends on the size of cable, isolators and the circuit breaker. Most immersion circuits I have seen have used 2.5 T&E with 20A switches and 15/16A circuit breakers, as long as your instantaneous heater current draw does not exceed these parameters then I cannot see a problem. In the UK this installation is probably notifiable as the bathroom is considered a special place - do you have Part P in Ireland?
Richard |
#3
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On 24/07/2015 16:49, Tricky Dicky wrote:
It depends on the size of cable, isolators and the circuit breaker. Most immersion circuits I have seen have used 2.5 T&E with 20A switches and 15/16A circuit breakers, as long as your instantaneous heater current draw does not exceed these parameters then I cannot see a problem. In the UK this installation is probably notifiable as the bathroom is considered a special place - do you have Part P in Ireland? Richard 20A is only ~5kW, which isn't nearly enough for a shower. 7kW is about the smallest you can get IIRC, but that's a bit of a dribble. A 10kW (40A) shower is more reasonable. Cheers -- Syd |
#4
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
Timothy Murphy wrote:
I'm thinking of doing away with the immersion heater in my bathroom, and getting a power-shower in its place. I'll also have to get a small heater for the wash-basin. I'm wondering if the power supply to the immersion heater will be suitable, or if this will have to be replaced? It is on its own circuit-breaker. Unless you want to wash under one of those tiny heaters that dribbles warm water over your hands, you present wiring will be completely inadequate. Existing immersion is probably around 3KW. For an instantaneous heater, 7KW will sort of work in summer but be miserable in winter. Any views on the merits of this? If an immersion heater is your only source of hot water, it's going to be expensive to upgrade. Lots of new wiring needed. The main reason is to give more space, perhaps for a separate shower. if you have gas, a combi boiler would probably be a better bet for you. Tim |
#5
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
Syd the OP is talking about running an instant heater for a wash basin not a shower. Mind you the current draw could be similar to an electric shower hence the comment about current draw and cable sizes etc.
Richard |
#6
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On 24/07/2015 17:13, Tricky Dicky wrote:
Syd the OP is talking about running an instant heater for a wash basin not a shower. Mind you the current draw could be similar to an electric shower hence the comment about current draw and cable sizes etc. Richard OP I'm thinking of doing away with the immersion heater in my bathroom, and getting a power-shower in its place. I'll also have to get a small heater for the wash-basin. /OP I think you misread it and by 'power-shower' I think the OP meant instant heat electric shower. But you may be right. Cheers -- Syd |
#7
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On 24/07/2015 16:33, Timothy Murphy wrote:
I'm thinking of doing away with the immersion heater in my bathroom, and getting a power-shower in its place. I'll also have to get a small heater for the wash-basin. I'm wondering if the power supply to the immersion heater will be suitable, or if this will have to be replaced? It is on its own circuit-breaker. Any views on the merits of this? The main reason is to give more space, perhaps for a separate shower. Judging by the answers received so far, I think we're all a bit confused by the terminology you have used - and are unclear as to what you *actually* want to do. I'm not sure whether by "immersion heater" you mean that literally, or the hot tank which it heats. Similarly, I'm not sure whether by "power shower" you mean a shower booster pump for stored hot water, or something which heats the water as it passes through. The questions below should help to clarify the situation. Do you: a) want to get rid of your hot cylinder - heated by an immersion heater - and install an electric shower which takes mains cold water and heats it in "real time", or b) want to retain your hot cylinder - heated by some other means (gas?) - and simply use the existing immersion heater wiring to power a booster pump to give you more flow to the shower? If the answer is (b), there shouldn't be a problem. However, if the answer is (a), it's extremely unlikely that a circuit designed for a (3kW?) immersion heater will be adequate for a (10kW?) electric shower. If your motivation is to create extra space, I rather suspect that the answer is (a)! -- Cheers, Roger ____________ Please reply to Newsgroup. Whilst email address is valid, it is seldom checked. |
#8
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On Friday, 24 July 2015 16:33:05 UTC+1, Timothy Murphy wrote:
I'm thinking of doing away with the immersion heater in my bathroom, and getting a power-shower in its place. I'll also have to get a small heater for the wash-basin. I'm wondering if the power supply to the immersion heater will be suitable, or if this will have to be replaced? It is on its own circuit-breaker. for a hot tap water heater, yes. to power an electric shower, debateable but probably no. Any views on the merits of this? The main reason is to give more space, perhaps for a separate shower. NT |
#10
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On 7/24/2015 4:33 PM, Timothy Murphy wrote:
I'm thinking of doing away with the immersion heater in my bathroom, and getting a power-shower in its place. I take it you mean an electric shower rather than a power shower (the latter does not heat the water, just pumps it for greater pressure / flow rate)? I'll also have to get a small heater for the wash-basin. You could use the immersion heater feed for that. I'm wondering if the power supply to the immersion heater will be suitable, Nope, not a chance. or if this will have to be replaced? It is on its own circuit-breaker. Added to, you will need the exiting feed for your inline basin heater... Any views on the merits of this? The main reason is to give more space, perhaps for a separate shower. Could you cite the cylinder somewhere else? (loft even) Could you use a combination boiler? -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#11
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On 24/07/2015 19:22, DerbyBorn wrote:
wrote in news:b709006c-2a46-442d-83dc- : On Friday, 24 July 2015 16:33:05 UTC+1, Timothy Murphy wrote: I'm thinking of doing away with the immersion heater in my bathroom, and getting a power-shower in its place. I'll also have to get a small heater for the wash-basin. I'm wondering if the power supply to the immersion heater will be suitable, or if this will have to be replaced? It is on its own circuit-breaker. for a hot tap water heater, yes. to power an electric shower, debateable but probably no. Any views on the merits of this? The main reason is to give more space, perhaps for a separate shower. NT Power Shower is the accepted term for a pump to give additional flow to an existing hot mixed with cold water supply. Indeed. And Immersion Heater is the accepted term for the electrical element which fits inside a hot water cylinder to heat the water. But I suspect that the OP is talking about an electrically heated shower and a hot water cylinder. [See my earlier post seeking clarification]. -- Cheers, Roger ____________ Please reply to Newsgroup. Whilst email address is valid, it is seldom checked. |
#12
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On Fri, 24 Jul 2015 17:22:48 +0100, Syd Rumpo
wrote: On 24/07/2015 17:13, Tricky Dicky wrote: Syd the OP is talking about running an instant heater for a wash basin not a shower. Mind you the current draw could be similar to an electric shower hence the comment about current draw and cable sizes etc. Richard OP I'm thinking of doing away with the immersion heater in my bathroom, and getting a power-shower in its place. I'll also have to get a small heater for the wash-basin. /OP I think you misread it and by 'power-shower' I think the OP meant instant heat electric shower. But you may be right. Cheers If he has hot water storage for the pumped shower why can't he use the same source (un-pumped) for the basin hot tap? Unless he *does* mean an electric shower after all, in which case he will need a new cable to the CU. Over to you OP. -- Graham. %Profound_observation% |
#13
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On Friday, 24 July 2015 16:33:05 UTC+1, Timothy Murphy wrote:
I'm thinking of doing away with the immersion heater in my bathroom, and getting a power-shower in its place. I'll also have to get a small heater for the wash-basin. You could use something like this which will do a shower and a basin: http://www.fastlec.co.uk/redring-pow...eater-45793201 Not 'warrantied' for baths or 'large kitchen sinks'. Owain |
#14
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
Tricky Dicky wrote:
do you have Part P in Ireland? It's not called Part P but I think it is more or less equivalent: "It is illegal for anyone other than a Registered Electrical Contractor (REC) to carry out electrical work in your home. Minor electrical works such as changing switches, sockets or light fittings are not covered by this legislation." -- Timothy Murphy gayleard /at/ eircom.net School of Mathematics, Trinity College, Dublin |
#15
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
Syd Rumpo wrote:
I think you misread it and by 'power-shower' I think the OP meant instant heat electric shower. That is what I meant. I guess that would mean a new wire back to the CU, which would be rather expensive in my case. -- Timothy Murphy gayleard /at/ eircom.net School of Mathematics, Trinity College, Dublin |
#16
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On Friday, 24 July 2015 23:50:53 UTC+1, Timothy Murphy wrote:
Syd Rumpo wrote: I think you misread it and by 'power-shower' I think the OP meant instant heat electric shower. That is what I meant. I guess that would mean a new wire back to the CU, which would be rather expensive in my case. Yes, unless you can use a low power unit. Last shower I measured was using 3kW in summer, 4kW in winter, and that should be no problem on an immersion feed. I don't know if you'd need to look at non-shower heaters for that. NT |
#17
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On Friday, 24 July 2015 19:22:05 UTC+1, DerbyBorn wrote:
nt wrote in news:b709006c-2a46-442d-83dc- : On Friday, 24 July 2015 16:33:05 UTC+1, Timothy Murphy wrote: I'm thinking of doing away with the immersion heater in my bathroom, and getting a power-shower in its place. I'll also have to get a small heater for the wash-basin. I'm wondering if the power supply to the immersion heater will be suitable, or if this will have to be replaced? It is on its own circuit-breaker. for a hot tap water heater, yes. to power an electric shower, debateable but probably no. Any views on the merits of this? The main reason is to give more space, perhaps for a separate shower. Power Shower is the accepted term for a pump to give additional flow to an existing hot mixed with cold water supply. it is, but that doesn't make sense here NT |
#18
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
wrote:
On Friday, 24 July 2015 23:50:53 UTC+1, Timothy Murphy wrote: Syd Rumpo wrote: I think you misread it and by 'power-shower' I think the OP meant instant heat electric shower. That is what I meant. I guess that would mean a new wire back to the CU, which would be rather expensive in my case. Yes, unless you can use a low power unit. Last shower I measured was using 3kW in summer, 4kW in winter, and that should be no problem on an immersion feed. I don't know if you'd need to look at non-shower heaters for that. NT Apart from hand washing units, where can you get such a low powered shower? My experience of one rated at 7KW was that it could only be described as "barely adequate". Tim |
#19
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On 24/07/2015 23:50, Timothy Murphy wrote:
Syd Rumpo wrote: I think you misread it and by 'power-shower' I think the OP meant instant heat electric shower. That is what I meant. I guess that would mean a new wire back to the CU, which would be rather expensive in my case. Not only that, but it would also need a hefty breaker in the CU - and some CUs only have one suitable slot for that, so all of the other wiring could need re-arranging. -- Cheers, Roger ____________ Please reply to Newsgroup. Whilst email address is valid, it is seldom checked. |
#20
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On Saturday, 25 July 2015 14:17:30 UTC+1, Tim+ wrote:
Apart from hand washing units, where can you get such a low powered shower? Caravan suppliers possibly, intended for use on a 13A / 16A supply. http://www.ebay.co.uk/itm/Mini-Porta...-/251593017367 Come complete with chinese lettering and australian plug :-) Owain |
#21
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
|
#22
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
wrote in message
... On Friday, 24 July 2015 23:50:53 UTC+1, Timothy Murphy wrote: Syd Rumpo wrote: I think you misread it and by 'power-shower' I think the OP meant instant heat electric shower. That is what I meant. I guess that would mean a new wire back to the CU, which would be rather expensive in my case. Yes, unless you can use a low power unit. Last shower I measured was using 3kW in summer, 4kW in winter, and that should be no problem on an immersion feed. I don't know if you'd need to look at non-shower heaters for that. What the **** are you talking about? -- Adam |
#23
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On 7/25/2015 2:39 PM, Roger Mills wrote:
On 24/07/2015 23:50, Timothy Murphy wrote: Syd Rumpo wrote: I think you misread it and by 'power-shower' I think the OP meant instant heat electric shower. That is what I meant. I guess that would mean a new wire back to the CU, which would be rather expensive in my case. Not only that, but it would also need a hefty breaker in the CU - and some CUs only have one suitable slot for that, so all of the other wiring could need re-arranging. In which case just add a secondary CU for the shower. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#24
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
"Roger Mills" wrote in message
... On 24/07/2015 23:50, Timothy Murphy wrote: Syd Rumpo wrote: I think you misread it and by 'power-shower' I think the OP meant instant heat electric shower. That is what I meant. I guess that would mean a new wire back to the CU, which would be rather expensive in my case. Not only that, but it would also need a hefty breaker in the CU - and some CUs only have one suitable slot for that, so all of the other wiring could need re-arranging. Thats a new one for me. -- Adam |
#25
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On 25/07/2015 17:28, ARW wrote:
"Roger Mills" wrote in message ... Not only that, but it would also need a hefty breaker in the CU - and some CUs only have one suitable slot for that, so all of the other wiring could need re-arranging. Thats a new one for me. Probably before your time! The Wylex 6-way CU which I fitted in the 1980's had a notice saying that all the slots were limited to 30A except for the one nearest the on/off switch - which could take 40+A (I forget the exact rating). I'm still using the CU, but the cartridge fuses have subsequently been replaced with MCBs. -- Cheers, Roger ____________ Please reply to Newsgroup. Whilst email address is valid, it is seldom checked. |
#26
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
"Roger Mills" wrote in message
... On 25/07/2015 17:28, ARW wrote: "Roger Mills" wrote in message ... Not only that, but it would also need a hefty breaker in the CU - and some CUs only have one suitable slot for that, so all of the other wiring could need re-arranging. Thats a new one for me. Probably before your time! The Wylex 6-way CU which I fitted in the 1980's had a notice saying that all the slots were limited to 30A except for the one nearest the on/off switch - which could take 40+A (I forget the exact rating). I'm still using the CU, but the cartridge fuses have subsequently been replaced with MCBs. So a fuse box not a CU? -- Adam |
#27
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On Saturday, 25 July 2015 21:25:14 UTC+1, ARW wrote:
So a fuse box not a CU? No, a consumer unit formerly fitted with fuses. "Consumer Unit (may also be known as a consumer control unit). A particular type of distribution board comprising a type-tested co-ordinated assembly for the control and distribution of electrical energy, principally in domestic premises, incorporating manual means of double-pole isolation on the incoming circuit(s) and an assembly of one or more fuses, circuit breakers, residual current operated devices or signalling and other devices proven during the type-test of the assembly as suitable for use." IEE Wiring Regulations Seventeenth Edition - British Standard BS7671:2008, Part 2 Definitions (cited in wikipedia: consumer unit) A fuse box would be a box with fuses in it, usually not having a switch. Owain |
#28
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
wrote in message
... On Saturday, 25 July 2015 21:25:14 UTC+1, ARW wrote: So a fuse box not a CU? No, a consumer unit formerly fitted with fuses. "Consumer Unit (may also be known as a consumer control unit). A particular type of distribution board comprising a type-tested co-ordinated assembly for the control and distribution of electrical energy, principally in domestic premises, incorporating manual means of double-pole isolation on the incoming circuit(s) and an assembly of one or more fuses, circuit breakers, residual current operated devices or signalling and other devices proven during the type-test of the assembly as suitable for use." IEE Wiring Regulations Seventeenth Edition - British Standard BS7671:2008, Part 2 Definitions (cited in wikipedia: consumer unit) A fuse box would be a box with fuses in it, usually not having a switch. https://en.wikipedia.org/wiki/Consumer_unit That wiki article is a joke. And there is little chance that a Wylex fuse box could be used to power a new shower installation due to the lack of RCD protection, -- Adam |
#29
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On 25/07/2015 21:25, ARW wrote:
"Roger Mills" wrote in message ... On 25/07/2015 17:28, ARW wrote: "Roger Mills" wrote in message ... Not only that, but it would also need a hefty breaker in the CU - and some CUs only have one suitable slot for that, so all of the other wiring could need re-arranging. Thats a new one for me. Probably before your time! The Wylex 6-way CU which I fitted in the 1980's had a notice saying that all the slots were limited to 30A except for the one nearest the on/off switch - which could take 40+A (I forget the exact rating). I'm still using the CU, but the cartridge fuses have subsequently been replaced with MCBs. So a fuse box not a CU? Is there a difference? I thought that "Consumer Unit" was simply a fancy new name for "Fuse Box". I can't remember what it was called when I bought it - I *think* it was described an a CU but I can't swear to it. AIUI, they both take an input from the meter and allow a number of individually protected circuits to be connected - using re-wirable fuses, cartridge fuses, MCBs, RCBOs, whatever. OK, modern ones now have dual RCDs and all sorts of fancy tat - but weren't they called CUs before all of that? -- Cheers, Roger ____________ Please reply to Newsgroup. Whilst email address is valid, it is seldom checked. |
#30
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
|
#31
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On 25/07/2015 22:39, ARW wrote:
And there is little chance that a Wylex fuse box could be used to power a new shower installation due to the lack of RCD protection, Not under current regulations, anyway. Interestingly, I had an extension built in 1994 which included an en-suite - and the original intention was to have an electric shower in the en-suite. So I had a circuit installed with 6mm (I think) cable - utilising this first slot in the CU. In the event, I ran a hot feed to the shower from the HW cylinder and only used this circuit for a shower pump - but it would otherwise have powered an electric shower without RCD protection - perfectly legally at that time as far as I am aware. Whether or not I'd still have been here now is another matter! g -- Cheers, Roger ____________ Please reply to Newsgroup. Whilst email address is valid, it is seldom checked. |
#32
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On Saturday, 25 July 2015 14:41:32 UTC+1, Roger Mills wrote:
On 25/07/2015 12:58, nt wrote: On Friday, 24 July 2015 23:50:53 UTC+1, Timothy Murphy wrote: Syd Rumpo wrote: I think you misread it and by 'power-shower' I think the OP meant instant heat electric shower. That is what I meant. I guess that would mean a new wire back to the CU, which would be rather expensive in my case. Yes, unless you can use a low power unit. Last shower I measured was using 3kW in summer, 4kW in winter, and that should be no problem on an immersion feed. I don't know if you'd need to look at non-shower heaters for that. NT You are of course joking! What sort of shower flow rate can you get with 3 or 4 kW? Likely to be not much more than a dribble! No. 2.25 lpm. NT |
#33
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On Saturday, 25 July 2015 14:17:30 UTC+1, Tim+ wrote:
nt wrote: On Friday, 24 July 2015 23:50:53 UTC+1, Timothy Murphy wrote: Syd Rumpo wrote: I think you misread it and by 'power-shower' I think the OP meant instant heat electric shower. That is what I meant. I guess that would mean a new wire back to the CU, which would be rather expensive in my case. Yes, unless you can use a low power unit. Last shower I measured was using 3kW in summer, 4kW in winter, and that should be no problem on an immersion feed. I don't know if you'd need to look at non-shower heaters for that. Apart from hand washing units, where can you get such a low powered shower? My experience of one rated at 7KW was that it could only be described as "barely adequate". then I guess that's not what you want There are a few ways to reduce shower power with it still feeling good: aeration, pressure, drain heat exchanger. NT |
#34
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
|
#35
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
wrote:
On Saturday, 25 July 2015 14:17:30 UTC+1, Tim+ wrote: nt wrote: On Friday, 24 July 2015 23:50:53 UTC+1, Timothy Murphy wrote: Syd Rumpo wrote: I think you misread it and by 'power-shower' I think the OP meant instant heat electric shower. That is what I meant. I guess that would mean a new wire back to the CU, which would be rather expensive in my case. Yes, unless you can use a low power unit. Last shower I measured was using 3kW in summer, 4kW in winter, and that should be no problem on an immersion feed. I don't know if you'd need to look at non-shower heaters for that. Apart from hand washing units, where can you get such a low powered shower? My experience of one rated at 7KW was that it could only be described as "barely adequate". then I guess that's not what you want There are a few ways to reduce shower power with it still feeling good: aeration, pressure, drain heat exchanger. NT Drain heat exchanger?? To recover feck all heat from a 3kw shower? I trust you've costed this out and can point us all to a suitable device that's already available? Tim |
#36
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
wrote in message
... On Saturday, 25 July 2015 14:41:32 UTC+1, Roger Mills wrote: On 25/07/2015 12:58, nt wrote: On Friday, 24 July 2015 23:50:53 UTC+1, Timothy Murphy wrote: Syd Rumpo wrote: I think you misread it and by 'power-shower' I think the OP meant instant heat electric shower. That is what I meant. I guess that would mean a new wire back to the CU, which would be rather expensive in my case. Yes, unless you can use a low power unit. Last shower I measured was using 3kW in summer, 4kW in winter, and that should be no problem on an immersion feed. I don't know if you'd need to look at non-shower heaters for that. NT You are of course joking! What sort of shower flow rate can you get with 3 or 4 kW? Likely to be not much more than a dribble! No. 2.25 lpm. So only slightly more moist than a nun's **** then? -- Adam |
#37
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On 26/07/2015 16:03, Tim+ wrote:
wrote: On Saturday, 25 July 2015 14:17:30 UTC+1, Tim+ wrote: nt wrote: On Friday, 24 July 2015 23:50:53 UTC+1, Timothy Murphy wrote: Syd Rumpo wrote: I think you misread it and by 'power-shower' I think the OP meant instant heat electric shower. That is what I meant. I guess that would mean a new wire back to the CU, which would be rather expensive in my case. Yes, unless you can use a low power unit. Last shower I measured was using 3kW in summer, 4kW in winter, and that should be no problem on an immersion feed. I don't know if you'd need to look at non-shower heaters for that. Apart from hand washing units, where can you get such a low powered shower? My experience of one rated at 7KW was that it could only be described as "barely adequate". then I guess that's not what you want There are a few ways to reduce shower power with it still feeling good: aeration, pressure, drain heat exchanger. NT Drain heat exchanger?? To recover feck all heat from a 3kw shower? I trust you've costed this out and can point us all to a suitable device that's already available? Tim I'm not so sure it's a bad idea. After all, the water is mostly falling on a warm body. Consider the difference between summer and winter in a 7kW shower. You'd need some good active flow control to maintain a constant temperature, and you'd start off with a dribble before the heat exchanger started working. Perhaps also a proportion of the water could be recirculated as long as you don't have the habit of ****ing in the shower. But it's probably not worth it where power and water in shower quantities are cheap. Cheers -- Syd |
#38
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
On Sunday, 26 July 2015 16:10:20 UTC+1, ARW wrote:
So only slightly more moist than a nun's **** then? You speak from experience? Owain |
#39
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
Syd Rumpo wrote:
On 26/07/2015 16:03, Tim+ wrote: wrote: On Saturday, 25 July 2015 14:17:30 UTC+1, Tim+ wrote: nt wrote: On Friday, 24 July 2015 23:50:53 UTC+1, Timothy Murphy wrote: Syd Rumpo wrote: I think you misread it and by 'power-shower' I think the OP meant instant heat electric shower. That is what I meant. I guess that would mean a new wire back to the CU, which would be rather expensive in my case. Yes, unless you can use a low power unit. Last shower I measured was using 3kW in summer, 4kW in winter, and that should be no problem on an immersion feed. I don't know if you'd need to look at non-shower heaters for that. Apart from hand washing units, where can you get such a low powered shower? My experience of one rated at 7KW was that it could only be described as "barely adequate". then I guess that's not what you want There are a few ways to reduce shower power with it still feeling good: aeration, pressure, drain heat exchanger. NT Drain heat exchanger?? To recover feck all heat from a 3kw shower? I trust you've costed this out and can point us all to a suitable device that's already available? Tim I'm not so sure it's a bad idea. After all, the water is mostly falling on a warm body. Consider the difference between summer and winter in a 7kW shower. You'd need some good active flow control to maintain a constant temperature, and you'd start off with a dribble before the heat exchanger started working. Perhaps also a proportion of the water could be recirculated as long as you don't have the habit of ****ing in the shower. But it's probably not worth it where power and water in shower quantities are cheap. Cheers Oh in theory it may not be a bad idea BUT bear in mind the the "hot" water dribbling out of this 3kw shower will have given up most of its heat to the air before it ever hits the drains. If you can actually find a unit on sale in the UK you're a better googler than I. The only ones I could find don't seem to be on sale any more (I wonder why?) and mention a minimum flow of 5L/min. As a way of improving a shower it must surely be *way* down the list of realistic options. One Dr Drivel would be proud of though. Tim |
#40
Posted to uk.d-i-y
|
|||
|
|||
Immersion heater: thinking of doing away with it.
wrote in message
... On Sunday, 26 July 2015 16:10:20 UTC+1, ARW wrote: So only slightly more moist than a nun's **** then? You speak from experience? A 2.25 lpm shower could not give my ******** a good wash. -- Adam |