I've had to top up my Alpha HE CB33 combi boiler (which is, I think,
about 6-7 years old) every day this week, and prior to turning up the CH
temperature, it was every few days. Obviously this shouldn't be needed.

Today I finally had time in daylight to check the pressure relief exit
(which is in an old coalshed), and sure enough, it's dripping very
slightly when the boiler is running. Each time the boiler has failed to
start I've topped the pressure up to the middle of the green area on the
indicator- about 1 bar. When running, it's hitting around 2.5 bar when
fully hot, which seems a bit high to me, but I have to admit I cannot
remember what is normal, and the manual is no help, apart from stating
that all pipework etc should be able to handle 3.0 bar.

Can anyone suggest if this is normal, or has perhaps the expansion
vessel failed? If it makes any difference, it's a 7-radiator system on
microbore in a 2 storey house.

If that's normal, seemingly the relief valve must be knackered. I'll be
getting my friendly local boiler chap to do it, but it'd be nice to be
able to be clued up beforehand. It's no emergency, as it's working, but
obviously I don't want to introduce too much water, diluting the inhibitor.
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Expansion vessel or relief valve?

On 26/12/2014 15:59, Chris Bartram wrote:
I've had to top up my Alpha HE CB33 combi boiler (which is, I think,
about 6-7 years old) every day this week, and prior to turning up the CH
temperature, it was every few days. Obviously this shouldn't be needed.

Today I finally had time in daylight to check the pressure relief exit
(which is in an old coalshed), and sure enough, it's dripping very
slightly when the boiler is running. Each time the boiler has failed to
start I've topped the pressure up to the middle of the green area on the
indicator- about 1 bar. When running, it's hitting around 2.5 bar when
fully hot, which seems a bit high to me, but I have to admit I cannot
remember what is normal, and the manual is no help, apart from stating
that all pipework etc should be able to handle 3.0 bar.

Can anyone suggest if this is normal, or has perhaps the expansion
vessel failed? If it makes any difference, it's a 7-radiator system on
microbore in a 2 storey house.

If that's normal, seemingly the relief valve must be knackered. I'll be
getting my friendly local boiler chap to do it, but it'd be nice to be
able to be clued up beforehand. It's no emergency, as it's working, but
obviously I don't want to introduce too much water, diluting the inhibitor.


If you need to extra expansion room as a stop gap, bleed some water from
a radiator and leave a pocket of air at the top.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 748
Default Expansion vessel or relief valve?

On 26/12/14 16:24, John Rumm wrote:
On 26/12/2014 15:59, Chris Bartram wrote:
I've had to top up my Alpha HE CB33 combi boiler (which is, I think,
about 6-7 years old) every day this week, and prior to turning up the CH
temperature, it was every few days. Obviously this shouldn't be needed.

Today I finally had time in daylight to check the pressure relief exit
(which is in an old coalshed), and sure enough, it's dripping very
slightly when the boiler is running. Each time the boiler has failed to
start I've topped the pressure up to the middle of the green area on the
indicator- about 1 bar. When running, it's hitting around 2.5 bar when
fully hot, which seems a bit high to me, but I have to admit I cannot
remember what is normal, and the manual is no help, apart from stating
that all pipework etc should be able to handle 3.0 bar.

Can anyone suggest if this is normal, or has perhaps the expansion
vessel failed? If it makes any difference, it's a 7-radiator system on
microbore in a 2 storey house.

If that's normal, seemingly the relief valve must be knackered. I'll be
getting my friendly local boiler chap to do it, but it'd be nice to be
able to be clued up beforehand. It's no emergency, as it's working, but
obviously I don't want to introduce too much water, diluting the
inhibitor.


If you need to extra expansion room as a stop gap, bleed some water from
a radiator and leave a pocket of air at the top.

Cheers, but it seems OK, in that I top it up each morning and it
continues to work until it cools again overnight.
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,339
Default Expansion vessel or relief valve?


"Chris Bartram" wrote in message
...
I've had to top up my Alpha HE CB33 combi boiler (which is, I think, about
6-7 years old) every day this week, and prior to turning up the CH
temperature, it was every few days. Obviously this shouldn't be needed.

Today I finally had time in daylight to check the pressure relief exit
(which is in an old coalshed), and sure enough, it's dripping very
slightly when the boiler is running. Each time the boiler has failed to
start I've topped the pressure up to the middle of the green area on the
indicator- about 1 bar. When running, it's hitting around 2.5 bar when
fully hot, which seems a bit high to me, but I have to admit I cannot
remember what is normal, and the manual is no help, apart from stating
that all pipework etc should be able to handle 3.0 bar.

Can anyone suggest if this is normal, or has perhaps the expansion vessel
failed? If it makes any difference, it's a 7-radiator system on microbore
in a 2 storey house.

If that's normal, seemingly the relief valve must be knackered. I'll be
getting my friendly local boiler chap to do it, but it'd be nice to be
able to be clued up beforehand. It's no emergency, as it's working, but
obviously I don't want to introduce too much water, diluting the
inhibitor.


The expansion vessel might just need some air.
See if there's a valve on it.
Foot pump does the job.

If it works OK for while & then you have to put more air in, the diaphragm
in the pressure vessel has ruptured & you will need a new pressure vessel.


  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 748
Default Expansion vessel or relief valve?

On 26/12/14 17:09, harryagain wrote:
"Chris Bartram" wrote in message
...
I've had to top up my Alpha HE CB33 combi boiler (which is, I think, about
6-7 years old) every day this week, and prior to turning up the CH
temperature, it was every few days. Obviously this shouldn't be needed.

Today I finally had time in daylight to check the pressure relief exit
(which is in an old coalshed), and sure enough, it's dripping very
slightly when the boiler is running. Each time the boiler has failed to
start I've topped the pressure up to the middle of the green area on the
indicator- about 1 bar. When running, it's hitting around 2.5 bar when
fully hot, which seems a bit high to me, but I have to admit I cannot
remember what is normal, and the manual is no help, apart from stating
that all pipework etc should be able to handle 3.0 bar.

Can anyone suggest if this is normal, or has perhaps the expansion vessel
failed? If it makes any difference, it's a 7-radiator system on microbore
in a 2 storey house.

If that's normal, seemingly the relief valve must be knackered. I'll be
getting my friendly local boiler chap to do it, but it'd be nice to be
able to be clued up beforehand. It's no emergency, as it's working, but
obviously I don't want to introduce too much water, diluting the
inhibitor.


The expansion vessel might just need some air.
See if there's a valve on it.
Foot pump does the job.

If it works OK for while & then you have to put more air in, the diaphragm
in the pressure vessel has ruptured & you will need a new pressure vessel.


I've just looked at the manual again to see if a valve is present, and
it actually does help- I missed this last time:

"If the system pressure exceeds 2.5 bar when operating at maximum
temperature, the heating expansion vessel should be
checked and re-pressurised, if necessary."

It does have a valve, but that suggests that it may be the relief valve,
perhaps, as it's not exceeding 2.5 bar.


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,120
Default Expansion vessel or relief valve?

On 26/12/2014 15:59, Chris Bartram wrote:
I've had to top up my Alpha HE CB33 combi boiler (which is, I think,
about 6-7 years old) every day this week, and prior to turning up the CH
temperature, it was every few days. Obviously this shouldn't be needed.

Today I finally had time in daylight to check the pressure relief exit
(which is in an old coalshed), and sure enough, it's dripping very
slightly when the boiler is running. Each time the boiler has failed to
start I've topped the pressure up to the middle of the green area on the
indicator- about 1 bar. When running, it's hitting around 2.5 bar when
fully hot, which seems a bit high to me, but I have to admit I cannot
remember what is normal, and the manual is no help, apart from stating
that all pipework etc should be able to handle 3.0 bar.

Can anyone suggest if this is normal, or has perhaps the expansion
vessel failed? If it makes any difference, it's a 7-radiator system on
microbore in a 2 storey house.

If that's normal, seemingly the relief valve must be knackered. I'll be
getting my friendly local boiler chap to do it, but it'd be nice to be
able to be clued up beforehand. It's no emergency, as it's working, but
obviously I don't want to introduce too much water, diluting the inhibitor.


AIUI, the relief valve shouldn't open unless the pressure reaches about
3.5 bar - so if it's opening at 2.5, it seems like it's faulty.

However, have you actually watched the system heat up, and monitored the
pressure as it does so? Is it possible that it *does* get to 3.5 and
then falls back to 2.5 when the relief valve has let some water out?

As others have said, it would be worth checking the charge in the
expansion vessel. With the system cold and the wet side depressurised,
the air pressure should be around 0.7 to 0.8 bar. You can check it with
a car tyre pressure gauge, and top it up with a car tyre pump if necessary.

That may be all that's needed. However, if water comes out of the air
valve, the vessel is shot!
--
Cheers,
Roger
____________
Please reply to Newsgroup. Whilst email address is valid, it is seldom
checked.
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Expansion vessel or relief valve?

On 26/12/2014 16:38, Chris Bartram wrote:
On 26/12/14 16:24, John Rumm wrote:
On 26/12/2014 15:59, Chris Bartram wrote:
I've had to top up my Alpha HE CB33 combi boiler (which is, I think,
about 6-7 years old) every day this week, and prior to turning up the CH
temperature, it was every few days. Obviously this shouldn't be needed.

Today I finally had time in daylight to check the pressure relief exit
(which is in an old coalshed), and sure enough, it's dripping very
slightly when the boiler is running. Each time the boiler has failed to
start I've topped the pressure up to the middle of the green area on the
indicator- about 1 bar. When running, it's hitting around 2.5 bar when
fully hot, which seems a bit high to me, but I have to admit I cannot
remember what is normal, and the manual is no help, apart from stating
that all pipework etc should be able to handle 3.0 bar.

Can anyone suggest if this is normal, or has perhaps the expansion
vessel failed? If it makes any difference, it's a 7-radiator system on
microbore in a 2 storey house.

If that's normal, seemingly the relief valve must be knackered. I'll be
getting my friendly local boiler chap to do it, but it'd be nice to be
able to be clued up beforehand. It's no emergency, as it's working, but
obviously I don't want to introduce too much water, diluting the
inhibitor.


If you need to extra expansion room as a stop gap, bleed some water from
a radiator and leave a pocket of air at the top.

Cheers, but it seems OK, in that I top it up each morning and it
continues to work until it cools again overnight.


The more times you let the blow off valve operate though, the more
chance you get of it getting some crud in it and then refusing to seal
again in future.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,339
Default Expansion vessel or relief valve?


"Roger Mills" wrote in message
...
On 26/12/2014 15:59, Chris Bartram wrote:
I've had to top up my Alpha HE CB33 combi boiler (which is, I think,
about 6-7 years old) every day this week, and prior to turning up the CH
temperature, it was every few days. Obviously this shouldn't be needed.

Today I finally had time in daylight to check the pressure relief exit
(which is in an old coalshed), and sure enough, it's dripping very
slightly when the boiler is running. Each time the boiler has failed to
start I've topped the pressure up to the middle of the green area on the
indicator- about 1 bar. When running, it's hitting around 2.5 bar when
fully hot, which seems a bit high to me, but I have to admit I cannot
remember what is normal, and the manual is no help, apart from stating
that all pipework etc should be able to handle 3.0 bar.

Can anyone suggest if this is normal, or has perhaps the expansion
vessel failed? If it makes any difference, it's a 7-radiator system on
microbore in a 2 storey house.

If that's normal, seemingly the relief valve must be knackered. I'll be
getting my friendly local boiler chap to do it, but it'd be nice to be
able to be clued up beforehand. It's no emergency, as it's working, but
obviously I don't want to introduce too much water, diluting the
inhibitor.


AIUI, the relief valve shouldn't open unless the pressure reaches about
3.5 bar - so if it's opening at 2.5, it seems like it's faulty.

However, have you actually watched the system heat up, and monitored the
pressure as it does so? Is it possible that it *does* get to 3.5 and then
falls back to 2.5 when the relief valve has let some water out?

As others have said, it would be worth checking the charge in the
expansion vessel. With the system cold and the wet side depressurised, the
air pressure should be around 0.7 to 0.8 bar. You can check it with a car
tyre pressure gauge, and top it up with a car tyre pump if necessary.

That may be all that's needed. However, if water comes out of the air
valve, the vessel is shot!


You might also find the "tyre valve" itself is leaking air. (Quite unusual
though) Check in the usual way with a bit of spit.
(Always check the easy stuff first!)


  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 748
Default Expansion vessel or relief valve?

On 26/12/14 23:23, John Rumm wrote:


The more times you let the blow off valve operate though, the more
chance you get of it getting some crud in it and then refusing to seal
again in future.

I'm actually thinking that ship has sailed and the valve itself has
failed, as well as /possibly/ the expansion vessel. Back in the
summer/autumn, the filling tap was leaking and overpressurised the
system a couple of times, and I think the valve is now failing to seat.
Certainly it's a steady drip from the valve rather than a surge.

It will have to be an external vessel, unless repressurising it works,
as there's not enough clearance above to get it out.

Following my initial post I found a bit in the manual saying operating
pressure could be up to 2.5 bar when fully hot, and it's running just
past that when the burner runs, so I'll turn down the CH temp control a
bit to try to keep it below that.
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 748
Default Expansion vessel or relief valve?

On 27/12/14 08:25, harryagain wrote:
"Roger Mills" wrote in message

AIUI, the relief valve shouldn't open unless the pressure reaches about
3.5 bar - so if it's opening at 2.5, it seems like it's faulty.

However, have you actually watched the system heat up, and monitored the
pressure as it does so? Is it possible that it *does* get to 3.5 and then
falls back to 2.5 when the relief valve has let some water out?

As others have said, it would be worth checking the charge in the
expansion vessel. With the system cold and the wet side depressurised, the
air pressure should be around 0.7 to 0.8 bar. You can check it with a car
tyre pressure gauge, and top it up with a car tyre pump if necessary.

That may be all that's needed. However, if water comes out of the air
valve, the vessel is shot!


You might also find the "tyre valve" itself is leaking air. (Quite unusual
though) Check in the usual way with a bit of spit.
(Always check the easy stuff first!)


Cheers both. Just cranked the temp up to max and let the boiler run; it
got just past 3 bar before I turned the temp control back down, so
clearly the vessel is not working. The manual states the relief valve
opens at 3 bar. Manual states vessel pressure at 1.0 bar.

Think I might light a fire and let the heating cool down and see if I
can reach the valve (it's accessed from above and the boiler is fairly
close to the ceiling- within spec by 5mm at 240, but the manual states
that if there's less than 450mm and the vessel has failed, you need an
external one). I've got in touch with my friendly neighbourhood boiler chap.



  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 748
Default Expansion vessel or relief valve?

On 27/12/14 12:30, Chris Bartram wrote:
On 27/12/14 08:25, harryagain wrote:
"Roger Mills" wrote in message

AIUI, the relief valve shouldn't open unless the pressure reaches about
3.5 bar - so if it's opening at 2.5, it seems like it's faulty.

However, have you actually watched the system heat up, and monitored the
pressure as it does so? Is it possible that it *does* get to 3.5 and
then
falls back to 2.5 when the relief valve has let some water out?

As others have said, it would be worth checking the charge in the
expansion vessel. With the system cold and the wet side
depressurised, the
air pressure should be around 0.7 to 0.8 bar. You can check it with a
car
tyre pressure gauge, and top it up with a car tyre pump if necessary.

That may be all that's needed. However, if water comes out of the air
valve, the vessel is shot!


You might also find the "tyre valve" itself is leaking air. (Quite
unusual
though) Check in the usual way with a bit of spit.
(Always check the easy stuff first!)


Cheers both. Just cranked the temp up to max and let the boiler run; it
got just past 3 bar before I turned the temp control back down, so
clearly the vessel is not working. The manual states the relief valve
opens at 3 bar. Manual states vessel pressure at 1.0 bar.

Think I might light a fire and let the heating cool down and see if I
can reach the valve (it's accessed from above and the boiler is fairly
close to the ceiling- within spec by 5mm at 240, but the manual states
that if there's less than 450mm and the vessel has failed, you need an
external one). I've got in touch with my friendly neighbourhood boiler
chap.


As an update: the vessel was ****ed. New external vessel fitted, system
now holding pressure and running below 1.5 bar even at full temp. Relief
valve seems to be OK.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Expansion tank vs relief valve BobK207 Home Repair 22 August 17th 16 04:16 AM
Expansion vessel - Schrader valve Richard Russell UK diy 24 November 7th 12 10:38 PM
vaillant turbomax - expansion vessel + valve sm_jamieson UK diy 1 March 11th 11 10:25 PM
ideal response expansion vessel valve Block UK diy 0 December 10th 07 10:40 PM
Faulty relief valve or expansion vessel BigBird UK diy 5 January 25th 05 05:58 PM


All times are GMT +1. The time now is 12:00 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"