UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,093
Default No earth in lighting circuit?

No 1 daughter has bought a fancy metal chandelier for the dining room
and asked me to fit it.

Upon unscrewing the ceiling rose, there is no earth. Isn't one in the
switch either, so I'm guessing the wiring dates from when lighting
circuits weren't earthed?

I've told her it can't be fitted. No 1 daughter, like most females, is
not easily dissuaded once she has made her mind up...

What are the dangers of a class 1 lighting fitment not being earthed, so
I can reinforce my argument?



--
Dave - The Medway Handyman www.medwayhandyman.co.uk
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default No earth in lighting circuit?

On 12/12/2014 09:09, The Medway Handyman wrote:
No 1 daughter has bought a fancy metal chandelier for the dining room
and asked me to fit it.

Upon unscrewing the ceiling rose, there is no earth. Isn't one in the
switch either, so I'm guessing the wiring dates from when lighting
circuits weren't earthed?

I've told her it can't be fitted.


Well there is a way... but she may not like it!

No 1 daughter, like most females, is
not easily dissuaded once she has made her mind up...


The "proper" solution is to rewire the circuit completely.

The next best is to:

1) fit a RCBO for the lighting circuit in question (and any other
similar ones)
2) Fix a sticker on the CU highlighting the circuits without earths and
pointing out that all accessories must be Class II

The cheating alternative, if she really *must* have the fitting is:

1) Disconnect the existing line in and out cables from the rose, and
join them in a wago box or similar, and poke em back into the ceiling.
2) Find a nearby socket circuit, fit a FCU with 3A fuse, and take a feed
from it to the light. Power the lamp from that. If not also replacing
the switch drop wire then make sure she does not want a class I fancy
metal switch.

What are the dangers of a class 1 lighting fitment not being earthed, so
I can reinforce my argument?


Electrocution mainly...

More background he

http://wiki.diyfaq.org.uk/index.php?...thout_an_Earth


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,560
Default No earth in lighting circuit?

On Friday, December 12, 2014 9:50:35 AM UTC, John Rumm wrote:
On 12/12/2014 09:09, The Medway Handyman wrote:
No 1 daughter has bought a fancy metal chandelier for the dining room
and asked me to fit it.

Upon unscrewing the ceiling rose, there is no earth. Isn't one in the
switch either, so I'm guessing the wiring dates from when lighting
circuits weren't earthed?

I've told her it can't be fitted.


snip

One other option sometimes is to bring the fitting upto Class 2 standard.


NT
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,339
Default No earth in lighting circuit?


"The Medway Handyman" wrote in message
...
No 1 daughter has bought a fancy metal chandelier for the dining room and
asked me to fit it.

Upon unscrewing the ceiling rose, there is no earth. Isn't one in the
switch either, so I'm guessing the wiring dates from when lighting
circuits weren't earthed?

I've told her it can't be fitted. No 1 daughter, like most females, is
not easily dissuaded once she has made her mind up...

What are the dangers of a class 1 lighting fitment not being earthed, so I
can reinforce my argument?


Just run a separate earth wire. Ideally go round the other light positions
too.
It should go back to the consumer unit, not to the nearest socket.


  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,564
Default No earth in lighting circuit?

On Friday, December 12, 2014 9:08:59 AM UTC, The Medway Handyman wrote:
What are the dangers of a class 1 lighting fitment not being earthed, so
I can reinforce my argument?


Death, mostly.

Is No. 1 daughter the paramedic?

Another option not so far mentioned is to supply via an isolating transformer i.e. extra low voltage, and use 12 volt lamps or leds. 12 volt SBC and SES lamps are fairly readily available - try cpc.

Owain




  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 277
Default No earth in lighting circuit?

On Friday, 12 December 2014 09:08:59 UTC, The Medway Handyman wrote:
No 1 daughter has bought a fancy metal chandelier for the dining room
and asked me to fit it.

Upon unscrewing the ceiling rose, there is no earth. Isn't one in the
switch either, so I'm guessing the wiring dates from when lighting
circuits weren't earthed?

I've told her it can't be fitted. No 1 daughter, like most females, is
not easily dissuaded once she has made her mind up...

What are the dangers of a class 1 lighting fitment not being earthed, so
I can reinforce my argument?



--
Dave - The Medway Handyman www.medwayhandyman.co.uk


There are currently a lot of metal (usually chrome plated) floor and desk lamps in all the stores which lack any earth connection. Are these compliant with any regs?
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,254
Default No earth in lighting circuit?

therustyone wrote:

There are currently a lot of metal (usually chrome plated) floor and
desk lamps in all the stores which lack any earth connection. Are
these compliant with any regs?


If they have the "two squares" double insulated symbol, they ought to be ...


  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 11,175
Default No earth in lighting circuit?

In article ,
writes:
On Friday, December 12, 2014 9:08:59 AM UTC, The Medway Handyman wrote:
What are the dangers of a class 1 lighting fitment not being earthed, so
I can reinforce my argument?


Death, mostly.

Is No. 1 daughter the paramedic?

Another option not so far mentioned is to supply via an isolating transformer i.e. extra low voltage, and use 12 volt lamps or leds. 12 volt SBC and SES lamps are fairly readily available - try cpc.


I converted some living room lighting (3-lamp pendant and 2 wall lamps) to
use 12V capsule lamps. Main reason was they were on a rather expensive X10
dimmer which I wanted to retain, whilst not wanting to run mains filament
lamps anymore. A secondary effect was that halving the power of the lamps
when moving to 12V still resulted in lots more light in the room, because
the 12V filament are very much more efficient than the mains filament lamps.
(This was before LED retrofits were around, but there aren't yet any
suitable for these anyway.)

I had to rewire the 3-lamp fitting to handle the much higher current, and
I had to use 4mm² T&E to connect it to the 12V transformer so as not to
lose too much voltage in the cable. I stuck with T&E so it can be converted
back to mains if required anytime in the future without rewiring the fixed
wiring inside the ceiling.

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]
  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,564
Default No earth in lighting circuit?

On Friday, December 12, 2014 5:50:10 PM UTC, The Medway Handyman wrote:
Her argument is that it would only ever be touched when changing a bulb
and she could turn to power off when she did it.



Protection by placing out of reach is not acceptable in a domestic environment.

Supposing there's a small child in the room waving a conductive light-sabre or similar about?

Owain

  #18   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,703
Default No earth in lighting circuit?

In article , The Medway Handyman
writes
No 1 daughter has bought a fancy metal chandelier for the dining room
and asked me to fit it.

Upon unscrewing the ceiling rose, there is no earth. Isn't one in the
switch either, so I'm guessing the wiring dates from when lighting
circuits weren't earthed?

I've told her it can't be fitted. No 1 daughter, like most females, is
not easily dissuaded once she has made her mind up...

What are the dangers of a class 1 lighting fitment not being earthed, so
I can reinforce my argument?

The short answer is that Class 1 equipment _must_ be earthed, it will
say so in the instructions. Otherwise there is a risk to the user of
electrocution if there a fault.

The long answer is that the designer made reliance on an earth
connection to guarantee its safe operation. It is likely that a single
fault within the appliance (eg. chafing of a single layer of insulation)
could result in the metalwork becoming live and so to cover that failure
mode it is earthed to protect the user. Without the earth, in those
circumstances, the user could receive a fatal electric shock.

You can get metal cased class 2 lamps/products too but they have been
designed in such a way that a single fault will not expose the user to a
risk of shock. They are designed such that it would take 2 distinct and
separate failures[1] to put the user at risk. As a result they are much
safer and so can be used without an earth. This is represented in the
class 2 'double insulated' square within a square symbol.

Having heard you mention your daughter's background here before I was
surprised that she would be so carefree about a safety related issue.
Rules and procedures, sod it, just slap the defib on and set to max,
CLEAR, nah, that's for wooses . . . .

[1] technically it is possible to use 'reinforced' insulation where it
is not practical to use 2 separate ones.
--
fred
it's a ba-na-na . . . .
  #21   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,560
Default No earth in lighting circuit?

On Saturday, December 13, 2014 5:06:57 PM UTC, fred wrote:
In article , The Medway Handyman
writes
No 1 daughter has bought a fancy metal chandelier for the dining room
and asked me to fit it.

Upon unscrewing the ceiling rose, there is no earth. Isn't one in the
switch either, so I'm guessing the wiring dates from when lighting
circuits weren't earthed?

I've told her it can't be fitted. No 1 daughter, like most females, is
not easily dissuaded once she has made her mind up...

What are the dangers of a class 1 lighting fitment not being earthed, so
I can reinforce my argument?

The short answer is that Class 1 equipment _must_ be earthed, it will
say so in the instructions. Otherwise there is a risk to the user of
electrocution if there a fault.

The long answer is that the designer made reliance on an earth
connection to guarantee its safe operation. It is likely that a single
fault within the appliance (eg. chafing of a single layer of insulation)
could result in the metalwork becoming live and so to cover that failure
mode it is earthed to protect the user. Without the earth, in those
circumstances, the user could receive a fatal electric shock.

You can get metal cased class 2 lamps/products too but they have been
designed in such a way that a single fault will not expose the user to a
risk of shock. They are designed such that it would take 2 distinct and
separate failures[1] to put the user at risk. As a result they are much
safer and so can be used without an earth. This is represented in the
class 2 'double insulated' square within a square symbol.

Having heard you mention your daughter's background here before I was
surprised that she would be so carefree about a safety related issue.
Rules and procedures, sod it, just slap the defib on and set to max,
CLEAR, nah, that's for wooses . . . .

[1] technically it is possible to use 'reinforced' insulation where it
is not practical to use 2 separate ones.


The differences between a modern class 1 & Class 2 product are fairly minor, and its often very easy to turn 1 into 2, hence my suggestion. In a lot of cases it requires nothing more than a cable tie.

Main requirements for class 2:
1. 2 layers of insulation (or occasionally reinforced insulation) between live & case
2. Means of preventing a single broken wire end from touching the case. A cable tie attaching L to N, thus preventing one from touching case if it comes adrift is often enough.

And fwiw the risk in using an unearthed _modern_ metal chandelier is actually very small. We take far bigger risks daily without batting an eyelid.


NT
  #25   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,093
Default No earth in lighting circuit?

On 13/12/2014 19:15, wrote:
On Saturday, December 13, 2014 5:06:57 PM UTC, fred wrote:
In article , The Medway Handyman
writes
No 1 daughter has bought a fancy metal chandelier for the dining room
and asked me to fit it.

Upon unscrewing the ceiling rose, there is no earth. Isn't one in the
switch either, so I'm guessing the wiring dates from when lighting
circuits weren't earthed?

I've told her it can't be fitted. No 1 daughter, like most females, is
not easily dissuaded once she has made her mind up...

What are the dangers of a class 1 lighting fitment not being earthed, so
I can reinforce my argument?

The short answer is that Class 1 equipment _must_ be earthed, it will
say so in the instructions. Otherwise there is a risk to the user of
electrocution if there a fault.

The long answer is that the designer made reliance on an earth
connection to guarantee its safe operation. It is likely that a single
fault within the appliance (eg. chafing of a single layer of insulation)
could result in the metalwork becoming live and so to cover that failure
mode it is earthed to protect the user. Without the earth, in those
circumstances, the user could receive a fatal electric shock.

You can get metal cased class 2 lamps/products too but they have been
designed in such a way that a single fault will not expose the user to a
risk of shock. They are designed such that it would take 2 distinct and
separate failures[1] to put the user at risk. As a result they are much
safer and so can be used without an earth. This is represented in the
class 2 'double insulated' square within a square symbol.

Having heard you mention your daughter's background here before I was
surprised that she would be so carefree about a safety related issue.
Rules and procedures, sod it, just slap the defib on and set to max,
CLEAR, nah, that's for wooses . . . .

[1] technically it is possible to use 'reinforced' insulation where it
is not practical to use 2 separate ones.


The differences between a modern class 1 & Class 2 product are fairly minor, and its often very easy to turn 1 into 2, hence my suggestion. In a lot of cases it requires nothing more than a cable tie.

Main requirements for class 2:
1. 2 layers of insulation (or occasionally reinforced insulation) between live & case
2. Means of preventing a single broken wire end from touching the case. A cable tie attaching L to N, thus preventing one from touching case if it comes adrift is often enough.

And fwiw the risk in using an unearthed _modern_ metal chandelier is actually very small. We take far bigger risks daily without batting an eyelid.


NT

So, if I were to sleeve the live with some shrink wrap & tie the L & N
together, would that be safe?


--
Dave - The Medway Handyman
www.medwayhandyman.co.uk


  #26   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,703
Default No earth in lighting circuit?

In article , The Medway Handyman
writes

So, if I were to sleeve the live with some shrink wrap & tie the L & N
together, would that be safe?

Nope because with the best will in the world you are (respectfully) not
competent to assess and re-design electrical equipment to make a safe
conversion from class 1 to class 2.

You do not know what other works may be required on it to make a safe
conversion and I don't think a series of what-ifs here will change that.


--
fred
it's a ba-na-na . . . .
  #27   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,560
Default No earth in lighting circuit?

On Sunday, December 14, 2014 12:26:18 PM UTC, The Medway Handyman wrote:
On 13/12/2014 19:15, wrote:
On Saturday, December 13, 2014 5:06:57 PM UTC, fred wrote:
In article , The Medway Handyman
writes
No 1 daughter has bought a fancy metal chandelier for the dining room
and asked me to fit it.

Upon unscrewing the ceiling rose, there is no earth. Isn't one in the
switch either, so I'm guessing the wiring dates from when lighting
circuits weren't earthed?

I've told her it can't be fitted. No 1 daughter, like most females, is
not easily dissuaded once she has made her mind up...

What are the dangers of a class 1 lighting fitment not being earthed, so
I can reinforce my argument?

The short answer is that Class 1 equipment _must_ be earthed, it will
say so in the instructions. Otherwise there is a risk to the user of
electrocution if there a fault.

The long answer is that the designer made reliance on an earth
connection to guarantee its safe operation. It is likely that a single
fault within the appliance (eg. chafing of a single layer of insulation)
could result in the metalwork becoming live and so to cover that failure
mode it is earthed to protect the user. Without the earth, in those
circumstances, the user could receive a fatal electric shock.

You can get metal cased class 2 lamps/products too but they have been
designed in such a way that a single fault will not expose the user to a
risk of shock. They are designed such that it would take 2 distinct and
separate failures[1] to put the user at risk. As a result they are much
safer and so can be used without an earth. This is represented in the
class 2 'double insulated' square within a square symbol.

Having heard you mention your daughter's background here before I was
surprised that she would be so carefree about a safety related issue.
Rules and procedures, sod it, just slap the defib on and set to max,
CLEAR, nah, that's for wooses . . . .

[1] technically it is possible to use 'reinforced' insulation where it
is not practical to use 2 separate ones.


The differences between a modern class 1 & Class 2 product are fairly minor, and its often very easy to turn 1 into 2, hence my suggestion. In a lot of cases it requires nothing more than a cable tie.

Main requirements for class 2:
1. 2 layers of insulation (or occasionally reinforced insulation) between live & case
2. Means of preventing a single broken wire end from touching the case. A cable tie attaching L to N, thus preventing one from touching case if it comes adrift is often enough.

And fwiw the risk in using an unearthed _modern_ metal chandelier is actually very small. We take far bigger risks daily without batting an eyelid.


NT

So, if I were to sleeve the live with some shrink wrap & tie the L & N
together, would that be safe?


I've not seen the item, so its hard to be definitive. Often yes, but there are a couple of potential areas that might need more work:
Metal lampholders often have nothing but a few mm of air between live terminal screws and case - if this is the case it doesnt meet Class 2 requirements.
L&N should both be double insulated from the case. Modern kit often uses double inuslated flex, but if not it will generally need sleeving or replacing
The point of tying L&N together is to prevent case contact if one breaks away - just check it will do this.
A choc block connector in a metal housing isnt double insulated, so would need sleeving or similar.


NT
  #28   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,560
Default No earth in lighting circuit?

On Sunday, December 14, 2014 4:04:58 PM UTC, fred wrote:
In article , The Medway Handyman
writes


So, if I were to sleeve the live with some shrink wrap & tie the L & N
together, would that be safe?

Nope because with the best will in the world you are (respectfully) not
competent to assess and re-design electrical equipment to make a safe
conversion from class 1 to class 2.

You do not know what other works may be required on it to make a safe
conversion and I don't think a series of what-ifs here will change that.


That's why we ask each other stuff before diying. This case is simple and orders of magnitude lower risk than most diy we do. You can fear up if you want though.


NT
  #29   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,213
Default No earth in lighting circuit?

On 14/12/2014 08:56, ARW wrote:
"PeterC" wrote in message
.. .
On Sat, 13 Dec 2014 03:32:36 +0000, John Rumm wrote:

On 12/12/2014 19:43, wrote:
On Friday, December 12, 2014 5:50:10 PM UTC, The Medway Handyman wrote:
Her argument is that it would only ever be touched when changing a
bulb
and she could turn to power off when she did it.


Protection by placing out of reach is not acceptable in a domestic
environment.

Supposing there's a small child in the room waving a conductive
light-sabre or similar about?

Not to mention the times I have hit my head on peoples light fittings
because they though that at 6'+ they would be safely out of anybodies
way!


My last GF's place has metal fittings and plates and no earth on the
circuits. Two of the 'chandelier'-type are about 6' 2" from the floor
- just
enough to look high but a couple of inches too low.
So far, no shock.



I have seen hundreds of such setups. The risks of a shock do not
dramatically increase just because there is no earth. You need a fault
and no earth to increase the risk of a shock.

My fathers house was built in 1956 and had four wall lights in the
living room with nice 'shell' glasses. Step mother decided (that the
house was now hers) and to junk them in favour of some horrendous metal
carriage lights. Sparky obviously said, 'no earth, so I must fit an rcd'
- whole house. As they got older, the only bulbs came from tesco or M&S
where they do all their shopping (convenient parking).

ABout 2 years ago a cheap tesco bulb went pop and plunged whole house
into darkness. Step mother tried to change bulb from a 2-step ladder
using a torch - couldn't manage. Much swearing and arguing, so father
got up (aged 89 and with weak legs). Next thing he was on the floor with
leg bent at an awkward angle. By the time neighbour had been summoned
the damage was done, and he could hardly walk. Eventually doctor agreed
hip replacement was needed, which was done after only a short wait (In
South Wales too), and now he can get about again.

Moral of the tale. Sometimes the risk of electocution is far less than
the certainty of a fall if the house is plunged into darkness. The old
rewirable fuses would not have blown when a cheap bulb went pop. And
£10K was spent on a hip replacement that would never have been needed.

  #30   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 40,893
Default No earth in lighting circuit?



"Andrew" wrote in message
...
On 14/12/2014 08:56, ARW wrote:
"PeterC" wrote in message
.. .
On Sat, 13 Dec 2014 03:32:36 +0000, John Rumm wrote:

On 12/12/2014 19:43, wrote:
On Friday, December 12, 2014 5:50:10 PM UTC, The Medway Handyman
wrote:
Her argument is that it would only ever be touched when changing a
bulb
and she could turn to power off when she did it.


Protection by placing out of reach is not acceptable in a domestic
environment.

Supposing there's a small child in the room waving a conductive
light-sabre or similar about?

Not to mention the times I have hit my head on peoples light fittings
because they though that at 6'+ they would be safely out of anybodies
way!

My last GF's place has metal fittings and plates and no earth on the
circuits. Two of the 'chandelier'-type are about 6' 2" from the floor
- just
enough to look high but a couple of inches too low.
So far, no shock.



I have seen hundreds of such setups. The risks of a shock do not
dramatically increase just because there is no earth. You need a fault
and no earth to increase the risk of a shock.

My fathers house was built in 1956 and had four wall lights in the living
room with nice 'shell' glasses. Step mother decided (that the house was
now hers) and to junk them in favour of some horrendous metal carriage
lights. Sparky obviously said, 'no earth, so I must fit an rcd' - whole
house. As they got older, the only bulbs came from tesco or M&S where they
do all their shopping (convenient parking).

ABout 2 years ago a cheap tesco bulb went pop and plunged whole house into
darkness. Step mother tried to change bulb from a 2-step ladder using a
torch - couldn't manage. Much swearing and arguing, so father got up (aged
89 and with weak legs). Next thing he was on the floor with leg bent at an
awkward angle. By the time neighbour had been summoned the damage was
done, and he could hardly walk. Eventually doctor agreed hip replacement
was needed, which was done after only a short wait (In South Wales too),
and now he can get about again.

Moral of the tale. Sometimes the risk of electocution is far less than the
certainty of a fall if the house is plunged into darkness. The old
rewirable fuses would not have blown when a cheap bulb went pop. And £10K
was spent on a hip replacement that would never have been needed.


There is no risk of electrocution at all if double insulated light fittings
had been used.



  #31   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,896
Default No earth in lighting circuit?

Eventually doctor agreed
hip replacement was needed, which was done after only a short wait (In
South Wales too), and now he can get about again.

Moral of the tale. Sometimes the risk of electocution is far less than
the certainty of a fall if the house is plunged into darkness. The old
rewirable fuses would not have blown when a cheap bulb went pop.



And
£10K was spent on a hip replacement that would never have been needed.


Yes but surely that hip replacement has bettered his mobility if nothing
else?..

A few people I know who have had them done have much better mobility!...
--
Tony Sayer



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Lighting circuit earth at 120V Martin Brook UK diy 26 October 21st 17 12:44 PM
Lighting circuit with no earth wire? The Medway Handyman UK diy 29 July 13th 08 07:35 PM
Wiring - no earth for lighting Perry Gunn UK diy 26 July 15th 05 11:42 AM
Wiring an earth in LV lighting Charlie UK diy 10 January 20th 05 10:10 PM
2 wire circuit - no earth Stephen Fasham UK diy 5 December 13th 04 02:29 PM


All times are GMT +1. The time now is 12:22 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us